Dear Jose and Ray,

thanks for your replies, I've tested another few things:

I deactivated the other two PV-buses, so there is only one reference bus,
many PQ-buses and the problematic PQ/PV-bus.

With the PQ (result is ok):
- Slack inserts: -60 Mvar
- Problematic bus: 0.118 Mvar, V=1.0335 pu

With PV without limits (result is ok)
- Slack inserts: -61 Mvar
- Problematic bus: 0.851 Mvar, V=1.05 pu (as set as Vg)

With PV with limits (not ok):
- Slack inserts: +84 Mvar (145 Mvar difference)
- Problematic bus: 0.7 Mvar, V=0.15 pu (generator has reached its upper
limit, hence it was converted to PQ)

But the result of V of the problematic bus should be somewhere in between
1.0335 and 1.05 p.u.. All other P and Q of the generators and buses remain
constant within all variants. For me it looks like the result is in the
unstable area of the QV-curve.

@ Jose: when setting Vg=1.0335 than the result is ok again. The problem
starts at the point the generator reaches it's Q-Limit and gets converted
to PQ again.

I don't understand why the result is in the unstable area of the QV-curve,
because the reactive power is capacitive and not inductive, hence I
wouldn't expect a stability Problem (I'm increasing the voltage).

Interesting point: with the fast-decoupled solver the power flow with
Q-limit converges to V=1.0465 p.u. (result is ok), with Gauss-Seidel it
doesn't converge. Maybe there is a problem with Newton's method?!

Thanks for your help/explanations, nice regards,
Chris


2016-05-06 7:33 GMT+02:00 Jose Luis Marín <mari...@aia.es>:

>
> Sorry for the confusion, Ray:  where I said, *"...solvable with the bus
> running as PV, but unfeasible when the bus is running as PQ"*, I meant to
> say:
>
>    "*a valid powerflow solution* with the bus running as PV, but an
> *unstable* one when the bus is running as PQ"
>    (it is one of the multiple low-voltage solutions of the full
> mathematical problem--these solutions are unstable form the point of view
> of real operations)
>
> So yes, in that situation the solution obtained with the bus type being PV
> is (of course) still a mathematical solution to the same problem,
> regardless of the bus type being reinterpreted as PQ.  But the point is
> that, only if you look at the problem in this second case (bus type
> switched to PQ) it is then possible to see that the solution is a low
> voltage one, and therefore not valid.  One way to detect this is to look at
> the slope dQ / dV of the Q-V curve, because this situation corresponds to
> being "on the wrong side" of the curve.  It may happen either if the
> setpoint V was too low, or if the P output is too high.
>
> What the Newton method may do in that case is hard to say, since N-R does
> not "see" the kind of instability that we are talking about here.  It may
> converge to this unstable solution, or to the operationally correct one, or
> diverge.  It all depends on the complex landscape of the respective basins
> of attraction for each solution, which as you know is fractal.  But unless
> the case is right at the bifurcation point (here that would be the minimum
> of the Q-V curve), the basin of attraction around this unstable solution
> will be finite, so there's a good chance that if you provide the original
> solution (obtained when the bus was type PV) and use it as the seed to the
> new problem (bus type now switched to PQ), then NR will converge to the
> same solution.  You'd probably need to start from a flat start in order to
> find the high-voltage solution instead.
>
> --
> Jose L. Marin
> Grupo AIA
>
>
> 2016-05-05 22:17 GMT+02:00 Ray Zimmerman <r...@cornell.edu>:
>
>> Thanks Jose. I’ve added that to the manual as you suggested.
>>
>> I also agree with your suggestions for Chris. However, I’m curious about
>> your [*] note. In the situation you describe, it’s just that the Newton
>> method will diverge, correct? The original solution will still be a
>> solution of the power flow equations won’t they?
>>
>>     Ray
>>
>>
>> On Apr 30, 2016, at 2:01 PM, Jose Luis Marin <mari...@gridquant.com>
>> wrote:
>>
>>
>> Interesting, I didn't know that enforcing Q-limits also affects
>> generators when their bus-type is set to PQ.  Ray, I suggest documenting
>> this behavior in the manual, probably at the end of the last paragraph in
>> Section 4.1.  Something to the effect of *"... Note also that this
>> option affects generators even if the bus they are attached to is already
>> of type PQ."*
>>
>> Going back to Chris's problem, I suggest you approach this as consisting
>> of two orthogonal issues:
>>
>>    - Solving with Q-limits enforced vs. solving without
>>    - Solving with a given generator running as PQ-type vs. running as
>>    PV-type (by manually switching it)
>>
>> With regards to the first issue, I suggest to start by analyzing the
>> behavior of your case *without* enforcing Q limits: in particular, pay
>> close attention to the QG injections obtained *in the solution* for those
>> gens operating as PV-type (and also the specified QG for those operating as
>> PQ), and *compare* those to your specified [QMIN, QMAX] values.  If you
>> observe any large violation, then solving this case with Q limits enforced
>> will yield a *very* different solution.
>>
>> Concerning the second issue, the main thing to check when manually
>> switching a given bus from PQ-type to PV-type, is that the gen setpoint VG
>> has to be set to the bus voltage VM obtained in the previous solution,
>> otherwise your next solution could be again very different.  Conversely,
>> when manually switching a bus from PV-type to PQ-type [*], you have to
>> specify a gen injection QG equal to the value obtained in the previous
>> solution.
>>
>> [*] As I mentioned before, the switch in this direction is not always
>> guaranteed to give you the same solution.  If the setpoint VG is decreased
>> too much, or if the real power PG is increased too much, you can end up
>> with a case that is solvable with the bus running as PV, but unfeasible
>> when the bus is running as PQ (under the switching procedure described
>> here).  Technically: this happens when you're running the PV generator at
>> the unstable branch of its Q-V curve.
>>
>> --
>> Jose L. Marin
>> Grupo AIA
>>
>>
>>
>> On Fri, Apr 29, 2016 at 10:12 AM, Chris Prokop <
>> christophprok...@gmail.com> wrote:
>>
>>> Hi,
>>>
>>> oh, I just realized that the Q-limits also hold on PQ-buses, hence the
>>> generators are limited to it - I wouldn't have thought that. So without
>>> Q-limits the results are the same - huch.
>>>
>>> Anyway, when changing the bus to a PV-bus I've got the problem that the
>>> Q of the PV-buses (generators) are calculated way to high. At a first step
>>> runpf makes the bus with highest gap between the Q-limit and the Q-result
>>> to a PQ bus, in my case this is the reference bus -> the problem starts
>>> (even if I increase the ref-Qmax to 1e20, Qmin to -1e20 - then the problem
>>> repeats after converting the other 2 PV buses to PQ).
>>>
>>> (in a few hours I'll be without internet connection for 8 days so I
>>> wanna apologize for not responding during the next days)
>>>
>>> Nice regards,
>>> Chris
>>>
>>> Am 28.04.2016 um 23:48 schrieb Jose Luis Marin:
>>>
>>>
>>> Looking at those records I think I may have misunderstood what you're
>>> doing.  I thought you were converting a given PQ bus (BUS_I=246) into PV,
>>> but the generator record you're showing is attached to BUS_I=1 instead.
>>>
>>> To be precise, I thought you were starting from (numbers made up for
>>> this example):
>>>
>>> bus_i       type    Pd       Qd      Gs    Bs    area    Vm    Va
>>> baseKV   zone    Vmax   Vmin
>>> 246          1      15.37    1.12    0     0     3       1     0
>>> 20       4       2      0.6;
>>>
>>> And, assuming that the solution for that starting case gave for instance
>>> V=1.0375 on BUS_I=246, then making these changes to the case:
>>>
>>> bus_i       type    Pd       Qd      Gs    Bs    area    Vm    Va
>>> baseKV    zone   Vmax   Vmin
>>> 246          1      0.0      0.0     0     0     3       1     0
>>> 20        4      2      0.6;
>>>
>>> plus adding this generator to the bus:
>>> bus        Pg        Qg        Qmax       Qmin       Vg        mBase
>>> status    Pmax   ...
>>> 246        -15.37     0         999.99     -999.99    1.0375    100
>>>     1       1.3        ...
>>>
>>> Then, provided you are not enforcing MVAR limits (which may change a lot
>>> of things), you should obtain the same powerflow solution in this second
>>> case (with Qg near -1.12, in this example),
>>>
>>>
>>> Did I miss something?
>>>
>>>
>>> --
>>> Jose L. Marin
>>> Grupo AIA
>>>
>>>
>>>
>>> On Thu, Apr 28, 2016 at 7:26 PM, Chris Prokop <
>>> christophprok...@gmail.com> wrote:
>>>
>>>> Hi,
>>>>
>>>> @ Jose L. Marin:
>>>> I used a generator in both cases, hence it should be the correct sign
>>>> (should result in the same I guess). Anyway P was very small, around 1e-6
>>>> MW.
>>>>
>>>> I'm not sure if I've modelled something wrong: S_base is 100, my
>>>> generator is at bus 1 (at the end zeros(1,12)):
>>>> bus        Pg        Qg        Qmax        Qmin    Vg        mBase
>>>> status    Pmax   ...
>>>> 1           0.4        0            0.7        -0.45        1.04
>>>> 100        1            1.3        ...
>>>>
>>>> And the PQ-bus:
>>>> bus_i       type    Pd               Qd    Gs    Bs    area    Vm
>>>> Va    baseKV    zone    Vmax    Vmin
>>>> 246          1         2.64e-06    -30    0      0     3          1
>>>>    0     20            4           2           0.6;
>>>>
>>>> I've tried another thing: I changed the PQ-bus from -30 to +30 Mvar
>>>> (e.g. mpc.bus(1, 4) = 0)  and for another time I did the same with the
>>>> generator from +30 to -30 Mvar (e.g. mpc.gen(1, 3)=30), the other part (gen
>>>> vs. load) was always set to 0. The result was not (!) the same... hm? - I
>>>> guess this is the reason for the problem.
>>>> With the bus I get results from -8 Mvar up to 30 Mvar with v=0.635 to
>>>> 1.46 whereas with the generator the voltage varies only within -1 Mvar and
>>>> +1 Mvar (appr. 1.01 pu to appr. 1.04 pu), for other Q-injections the
>>>> voltage doesn't change.
>>>>
>>>> I uploaded the plot under: http://de.tinypic.com/r/350pk02/9
>>>>
>>>> Do you have any idea why?
>>>>
>>>> Thanks for your help, nice regards,
>>>> Chris
>>>>
>>>>
>>>>
>>>>
>>>> Am 28.04.2016 um 17:41 schrieb Jose Luis Marin:
>>>>
>>>>
>>>> Those are certainly some crazy Mvar injections!  Just checking: are you
>>>> sure you reversed the signs of P properly when switching the type of that
>>>> bus from PQ (load) to PV (gen with neg real power), also taking care of
>>>> making the corresponding changes in the bus row and adding a new gen row?
>>>>
>>>> If you could share your case file I could try to give you a quick
>>>> diagnostic.
>>>>
>>>> --
>>>> Jose L. Marin
>>>> Grupo AIA
>>>>
>>>>
>>>>
>>>> On Thu, Apr 28, 2016 at 5:19 PM, Chris Prokop <
>>>> christophprok...@gmail.com> wrote:
>>>>
>>>>> Thanks for your responses.
>>>>>
>>>>> @ Ray Zimmerman:
>>>>> I can't find the problem here. If I set Q=+0.7 Mvar (cap.), the
>>>>> voltage at this bus is about 1.04 p.u., with Q=-0.7 Mvar (ind.) it
>>>>> decreases to 1.02 p.u., the power flow converges as expected (+the result
>>>>> is as expected). Only converting this bus into a PV-bus results in the
>>>>> problem mentioned above (with or without limits). I don't get why the
>>>>> Newton Power Flow returns for example 1e3 Mvar for this bus as a result, 
>>>>> as
>>>>> only <1 Mvar should have been enough reactive power.
>>>>> Before solving the case the reactive power of the generators at the
>>>>> PV-buses are (variable gen in runpf):
>>>>> - Reference bus: 0 Mvar
>>>>> - PV-Bus1: 0 Mvar
>>>>> - PV-Bus2: 64.4 Mvar
>>>>> - PV-Bus3 (the problematic one): 0.1 Mvar
>>>>> after solving it (after pfsoln), the variable gen is filled with:
>>>>> - Reference bus: 1e6 Mvar
>>>>> - PV-Bus1: 2.7e4 Mvar
>>>>> - PV-Bus2: 9.6e3 Mvar
>>>>> - PV-Bus3 (the problematic one): -600 Mvar
>>>>> whereas the next most reactive power intensive gen&bus has less than
>>>>> 5e2 Mvar. I don't understand where the power comes from/goes to...
>>>>>
>>>>> @ Jose Luis Marin:
>>>>> If I use the voltage from the PQ-calculation (e.g. 20.6668/20
>>>>> p.u.) there remains the same problem. Also without Q-limits I get the the
>>>>> problem...
>>>>> Vg=1 p.u. actually works as a PV-bus, Vg=1.01 or Vg=1.02 etc. don't.
>>>>>
>>>>>
>>>>> Nice regards,
>>>>> Chris
>>>>>
>>>>> 2016-04-28 16:04 GMT+02:00 Ray Zimmerman <r...@cornell.edu>:
>>>>>
>>>>>> It sounds like the voltage at that bus may be very sensitive to the
>>>>>> reactive power injection. One thing you might try to get some idea of 
>>>>>> this
>>>>>> is to change that bus back to PQ with the reactive at the lower limit, 
>>>>>> then
>>>>>> try running a few cases with slightly perturbed values of the reactive
>>>>>> power at that generator and see how the voltage at the bus changes.
>>>>>>
>>>>>>    Ray
>>>>>>
>>>>>>
>>>>>> On Apr 28, 2016, at 8:40 AM, Chris Prokop <christophprok...@gmail.com>
>>>>>> wrote:
>>>>>>
>>>>>> Hi,
>>>>>>
>>>>>>
>>>>>> I'm using Matpower (v5.0b1, but the same holds for v5.1) for a 220
>>>>>> kV/110 kV/20 kV-grid quite a while. The grid has 1 reference bus (220 
>>>>>> kV),
>>>>>> 2 PV-buses (220 kV) and >100 PQ-buses (110 kV & 20 kV). So far 
>>>>>> calculating
>>>>>> the grid using runpf with Newton has never been a problem.
>>>>>>
>>>>>> Now I've tried to change a 20 kV PQ-bus to a PV-bus with the Q-limits
>>>>>> +0.7 for Q_max and -0.45 for Q_min (considering mpopt =
>>>>>> mpoption('pf.enforce_q_lims', 1)). If I set Vg of the generator to
>>>>>> 1.05 I get the error:
>>>>>> "All 4 remaining gens exceed their Q limits : INFEASIBLE PROBLEM"
>>>>>> whereas when using 1.00 as Vg there is no problem (then the generator
>>>>>> is at its lower Q-limit, hence converted to PQ). If the problem is
>>>>>> infeasible the result of pfsoln in runpf are Q-values of all 4
>>>>>> PV generators (Slack+3 PV) that are out of their limits. Why is there 
>>>>>> such
>>>>>> a big difference between the case V=1.05 and V=1.00?
>>>>>>
>>>>>> As a info: the Slack has a Q-Limit of +-10000, both of the already
>>>>>> existing PV buses +720/-290, according to case_info the total generation 
>>>>>> is
>>>>>> -300 MW+j10 Mvar, the total load 300 MW-j50 Mvar, but I've tried several
>>>>>> scenarios which are no problem when using the PQ instead of the PV-bus 
>>>>>> (or
>>>>>> the Vg=1).
>>>>>>
>>>>>>
>>>>>> Does anybody experience a similar problem/has an idea how to fix it?
>>>>>>
>>>>>> Nice regards,
>>>>>> Chris
>>>>>>
>>>>>>
>>>>>>
>>>>>
>>>>
>>>>
>>>
>>>
>>
>>
>