“30% is not a reasonable floor to stop discharging a Li-Ion battery. All you 
are doing there is limiting your available capacity. The recommended floor to 
stick to is 20%. However, it is perfectly fine to go as low as 10% without any 
appreciable loss of overall capacity. And in an emergency, you can even go to 
5% and still maintain good long term capacity.

This is where Li-Ion outshines LA by a mile.

Limiting your capacity by not discharging to, at least, 20% SoC, is quite 
pointless based on all the information we have so far, because calendar aging 
is still going to get you either way.”

This is… not quite correct.

Age can be mostly mitigated by proper storage – at around 40% SoC for storage 
charge. I routinely pull out 15-20 (and older!) packs that were manufacturer 
properly storage charged and once jumped up a bit return with 80-90% capacity!

But 30% is a reasonable floor for normal usage, going below that IS a stress 
zone for the battery – you sharply reduce the number of possible full cycles if 
you delve into this range regularly.

Obviously, when you actually need to use the battery, use it up entirely, 
that’s what it’s there for. This guideline’s more in general in terms of if you 
can stop at that point, you really, really should do so.

For what it’s worth, I was misremembering the floors slightly. It was 40% and 
20% I remember, where stopping discharge at 40% gave you nearly *double* the 
number of full cycles compared to a 20% discharge. IE say you get 600 if you 
routinely go to 20%, routinely going to 40% could net you 1500 instead.



From: Mark Tinka <[email protected]>
Sent: Thursday, April 10, 2025 1:12 AM
To: Gary Sparkes <[email protected]>; Vasilenko Eduard 
<[email protected]>; North American Network Operators Group 
<[email protected]>
Subject: Re: [NANOG] Re: Small Capacity UPS


On 4/9/25 14:27, Gary Sparkes wrote:


Long term storage, of course, is different, but that's a much easier solved 
problem, and design specs are often in the -30c to 25c range for optimal 
capacity retention over long term storage. But operationally, 25-50c is 
perfectly fine. Past ... above 5c, I think, you're looking at a 10% capacity 
fluctuation in that 5c to 50c range.

Yes, most LFP batteries will work even at 60°C, but that does not mean you 
should do it if you want to get the most out of your investment.

The biggest issue is battery aging, and keeping it within recommended 
temperature values will ensure they last longer than if you don't.






While true, heat is the enemy of lithium batteries of any type, deep 
discharging is the second worst enemy (BMS prevents actual cell damaging deep 
discharge, but you really should never go below 30% of rated capacity if you 
can ever help it - this is the most stressful zone), then charging too rapidly 
- too high rate of charge.

The point of the BMS is to prevent you from operating your battery in dangerous 
territory.



Mark.