> The less you give the battery a full charge (so keeping it below 100%),
the longer it will last. The less you discharge a battery, the longer it
will last.

This is why lifepo4 is a perfect swap in for old UPS devices like im doing.
usually full charge is 14.6v is what the chargers my talentcell and solar
charge controller cut off at, the batteries rest at about 13.5 full charge.

Currently one of my UPS is floating at 13.7 each battery, another older UPS
at 13.8.

I've easily gotten more runtime out of these than what I have experienced
with SLA or AGM batteries.
my use case (home & home-office), keeping access points (4) internet,
router, switches etc, even home theater (with the exception of the sub
amps) up and running gives me like 2+ hours. Plenty of time to get the
generator up and running. Last time we had an outage for an hour plus I
wasn't even home. Didn't even notice it.

- J


On Fri, Apr 11, 2025 at 12:40 AM Mark Tinka via NANOG <[email protected]>
wrote:

>
>
> On 4/10/25 22:44, Gary Sparkes wrote:
>
> >
> > This is… not quite correct.
> >
> > Age can be mostly mitigated by proper storage – at around 40% SoC for
> > storage charge. I routinely pull out 15-20 (and older!) packs that
> > were manufacturer properly storage charged and once jumped up a bit
> > return with 80-90% capacity!
> >
>
> I'm not talking about batteries that are in storage. Batteries in
> storage are not providing value to anyone :-).
>
> Yes, it is true that Li-Ion batteries store better than LA, because
> Li-Ion self-discharge can be 1.5% - 2% per month. LA batteries
> self-discharge at a rate of 4% - 6% per month. But that is not what we
> are talking about here.
>
>
> > But 30% is a reasonable floor for normal usage, going below that IS a
> > stress zone for the battery – you sharply reduce the number of
> > possible full cycles if you delve into this range regularly.
> >
>
> No, not true at all. While you do reduce SoH when you discharge below
> 20% or if you hold SoC above 80% for too long, how far you go in either
> direction and for what period does matter. The lower you discharge below
> 20%, the more internal resistance you introduce into the battery. The
> higher you charge above 80%, the faster you cause capacity fade due to a
> high battery voltage.
>
> Battery manufacturers all generally use a DoD (Depth of Discharge) of
> 80% to rate a battery, i.e., discharging from 100% down to 20%.
>
> EV's typically charge to 80% and discharged to 30% to increase mileage.
> But as the battery ages, this gap widens. This range does not really
> apply to stationery applications, because EV's put more stress on their
> batteries than a home backup solution, for example.
>
>
> > Obviously, when you actually need to use the battery, use it up
> > entirely, that’s what it’s there for. This guideline’s more in general
> > in terms of if you can stop at that point, you really, really should
> > do so.
> >
> > For what it’s worth, I was misremembering the floors slightly. It was
> > 40% and 20% I remember, where stopping discharge at 40% gave you
> > nearly **double** the number of full cycles compared to a 20%
> > discharge. IE say you get 600 if you routinely go to 20%, routinely
> > going to 40% could net you 1500 instead.
> >
>
> The less you give the battery a full charge (so keeping it below 100%),
> the longer it will last. The less you discharge a battery, the longer it
> will last. But the largest capacity loss actually occurs when the
> battery remains at a higher voltage for too long. However, cells can
> only balance when they have a full charge, although once balanced, they
> will remain balanced even at lower voltages for several months before
> they begin to drift and need to be re-balanced.
>
> In practical terms, the battery becomes useless to you with a partial
> discharge because you are limiting the amount of capacity you get out of
> it. And while you will get more cycles from a partial discharge, you are
> still going to have to deal with calendar aging, which is inevitable.
>
> Current research and testing data indicates that the biggest reason for
> capacity loss is calendar aging and maintaining a high voltage for too
> long (100% SoC), rather than cycling.
>
> Mark.
> _______________________________________________
> NANOG mailing list
>
> https://lists.nanog.org/archives/list/[email protected]/message/VQI2SBNIAEZ7NX3LUSYK3Q7R5VX5OHZA/
_______________________________________________
NANOG mailing list 
https://lists.nanog.org/archives/list/[email protected]/message/2NHMSHOVDWZIHPICZBTFNWK5LSC5LFOP/

Reply via email to