Hi Roger,
Thanks a lot for your hints.
Dne 29. 08. 22 v 15:14 Roger Price napsal(a):
On Mon, 29 Aug 2022, Pavel Hofman wrote:
blazer_usb reports:
ups.model: WPHVT2K0
ups.productid: 5161
The Fortron site
https://energy.fsp-europe.com/uninterruptible-power-supply/ has no
mention of these references. I wonder where blazer_usb found them?
It just (auto)magically works :-)
ups.status: OL
If you unplug the UPS from the wall, and run it down, maybe with a dummy
load, do you see OB, LB, other statuses?
Yes, OB -> OL
battery.voltage.high/nominal/low: 52.00/48.0/41.60
Does the battery.voltage drop regularly as the UPS exhausts itself?
Yes, the voltage drops as the battery discharges.
If battery.charge.low is not available, perhaps it is possible to get
the same effect by watching the voltage drop to a critical value. This
needs upssched and a custom upssched-cmd script.
I see. IIUC since I basically want to "override" the LOWBATT event, not
to react to it, I will have to periodically parse upsc output and check
for the current battery.voltage level when OB. It means basically doing
all the work ups-monitor actually does, but with a different threshold
(which I do not see how to change in ups-monitor). Do I assume correctly
I cannot force/script ups-monitor to do that for me since it already has
all the parsed data available?
Can I at least call some ups-monitor feature to start the controlled
shutdown on all the NUTS networked clients?
The alternative is to shutdown after a fixed time in status OB. Its my
preferred solution since I live in an area with a lot of lightning
strikes, but few people seem to do it.
Thanks. I do not know the times exactly, checking the battery voltage
with a standalne script will probably work fine.
Best regards,