Dne 29. 08. 22 v 12:53 Jim Klimov napsal(a):
The debug_min option is part of NUT 2.8.0, and your driver "screenshot" was from 2.7.4.

With older releases, you should manually ensure several `-D` options on the driver command line to increase verbosity.

Hi Jim,

Thanks a lot. Is there any way to tell upsdrvctl to add the -D option when it starts the specific driver on that older version? I tried adding -D to upsdrvctl (in its systemd unit), to no avail.

Thanks,

Pavel.


On Mon, Aug 29, 2022, 10:18 Pavel Hofman <[email protected] <mailto:[email protected]>> wrote:



    Dne 19. 08. 22 v 12:49 Pavel Hofman napsal(a):
     > Hi,
     >
     > I am trying to configure the shutdown threshold for Fortron UPS
    Champs.
     >
     > upsc reports:
     >
     > Init SSL without certificate database
     > battery.charge: 100
     > battery.voltage: 55.20
     > battery.voltage.high: 52.00
     > battery.voltage.low: 41.60
     > battery.voltage.nominal: 48.0
     > device.mfr:
     > device.model: WPHVT2K0
     > device.type: ups
     > driver.name <http://driver.name>: blazer_usb
     > driver.parameter.pollinterval: 2
     > driver.parameter.port: /dev/hidraw2
     > driver.parameter.synchronous: no
     > driver.version: 2.7.4
     > driver.version.internal: 0.12
     > input.current.nominal: 8.0
     > input.frequency: 50.0
     > input.frequency.nominal: 50
     > input.voltage: 234.5
     > input.voltage.fault: 234.5
     > input.voltage.nominal: 230
     > output.voltage: 229.7
     > ups.beeper.status: enabled
     > ups.delay.shutdown: 30
     > ups.delay.start: 180
     > ups.firmware: 01060.07
     > ups.load: 46
     > ups.mfr:
     > ups.model: WPHVT2K0
     > ups.productid: 5161
     > ups.status: OL
     > ups.temperature: 26.3
     > ups.type: online
     > ups.vendorid: 0665
     >
     >
     > Please note there is no battery.charge.low, the battery.charge is
     > provided by the blazer_usb driver
     >
    
https://networkupstools.org/docs/man/blazer_usb.html#_notes_for_the_previous_user_of_megatec_drivers
    
<https://networkupstools.org/docs/man/blazer_usb.html#_notes_for_the_previous_user_of_megatec_drivers>

     >
     >
     > I tried to configure override.battery.charge.low for the device in
     > ups.conf (after ignorelb), nothing reported in upsc.
     >
     > I do not need any times, just being able to set  charge level or
    voltage
     > level at which NUTS will issue the shutdown command to my servers
     > connected to the UPS a communicating with the nuts-server (their
     > shutdown takes a while). I could not find any info how to do that
    apart
     > of
     >
    https://github.com/networkupstools/nut/issues/561#issuecomment-398791357
    <https://github.com/networkupstools/nut/issues/561#issuecomment-398791357>

     > which did not work for me (no battery.charge.low info appeared in
    upcs
     > after this setting and reloading all nuts-related daemons (server,
     > client, monitor), nothing found in the logs.
     >
     > Thank you very much for any help or hints.
     >

    I tried to increase debug_min = 10 in non-driver/global section of
    ups.conf and no extra logs appeared in /var/log/syslog. Neither did
    with
    debug_min = 0 or 1, no effect. I do not know if the number should be
    high or low, could not find it in any docs online.

    Thanks a lot,

    Pavel.