On Fri, 2 Sep 2022, Pavel Hofman wrote:
blazer_usb reports:
ups.model: WPHVT2K0
ups.productid: 5161
Clearly a bug in blazer_usb
If battery.charge.low is not available, perhaps it is possible to get the
same effect by watching the voltage drop to a critical value. This needs
upssched and a custom upssched-cmd script.
I see. IIUC since I basically want to "override" the LOWBATT event, not to
react to it, I will have to periodically parse upsc output and check for the
current battery.voltage level when OB. It means basically doing all the work
ups-monitor actually does, but with a different threshold (which I do not see
how to change in ups-monitor). Do I assume correctly I cannot force/script
ups-monitor to do that for me since it already has all the parsed data
available?
Can I at least call some ups-monitor feature to start the controlled shutdown
on all the NUTS networked clients?
A lot of what you need is in chapter 7 of
https://rogerprice.org/NUT/ConfigExamples.A5.pdf . Ignore all the stuff about
heartbeat and timers. The EXEC on lines 380 and 381 of upsmon.conf in figure 54
will get you to line 398 in upssched.conf in figure 56.
At line 398, remove the lines "warning-timer" and "failure-timer", and add a
line such as
AT ONBATT <myups> EXECUTE watch-battery-charge
Change line 425 in upssched-cmd to VOLTAGE=$( upsc $UPS battery.voltage ) You
may need to ensure that $VOLTAGE is an integer.
At line 428 in upssched-cmd replace the sections (heart-failure-timer),
(two-minute-warning-timer) and (one-minute-warning-timer) with something like
(watch-battery-charge)
# Compare the $VOLTAGE with say 48 (Bash insists on integers)
if [[ $VOLTAGE > 48 ]]; then continue;
else MSG="Power failure shutdown: Calling upsmon -c fsd, $CHMSG"
/usr/sbin/upsmon -c fsd
fi ;;
Roger_______________________________________________
Nut-upsuser mailing list
[email protected]