On Jul 20, 2012, at 11:25 PM, Daniel O'Connor wrote:

> I have an Eaton/MGE EX 11 RT UPS (uses the mge-shut driver) and while I was 
> testing it I found that it would turn back on straight after power was 
> restored.
> 
> I had a look but I couldn't find a setting which would let me tell it to 
> charge to (say) 50% before turning the load back on.
> 
> Does anyone know if this is possible? A setting like this would provide some 
> hysteresis for successive power failures which would be handy to have :)

I don't know about that specific hardware, but the variables which would 
control this are battery.charge.restart ("Minimum battery level for UPS restart 
after power-off") and ups.delay.start ("Interval to wait before restarting the 
load (seconds)"). Check the output of "upsrw <ups>" to see if that variable is 
supported with your combination of UPS and driver.

Which version of NUT are you using? There might be a newmge-shut driver 
included as well.

-- 
Charles Lepple