When in doubt .. ask the manufacturer.

Dan


--- On Mon, 8/27/12, Kirpal Khalsa <solarwo...@gmail.com> wrote:

From: Kirpal Khalsa <solarwo...@gmail.com>
Subject: Re: [RE-wrenches] Ilsco SGB bonding lug
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Monday, August 27, 2012, 6:42 PM

Benn...it looks like that lug has "stainless hardware for corrosion 
resistance"  as stated on the brochure....That would be the biggest 
consideration as David Brearly mentioned earlier in regards to rust potential.  
Stainless hardware and tin plating is equivalent to the WEEB lugs....Tin 
plating and stainless hardware is as good as anything else available as far as 
outdoor ratings are concerned.....

I see your point that it is not explicitly stated for outdoor use....however 
being marketed for use with solar panels also seems to imply rather obviously 
that it is outdoor rated.....in my unofficial opinion.  

-- 

Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer



On Mon, Aug 27, 2012 at 4:11 PM, benn kilburn <b...@daystarsolar.ca> wrote:

Thanks for the feedback Wrenches, lots of interesting comments,

However I'm still wondering…..How does one confirm that it is specifically 
approved for outdoor use?  Other than assuming it is implied (because it is 
'marketed' as a solar lug).  As far as I can tell UL 467 does not imply 
"outdoor rated" as the aluminum lug "GBL-4" is also UL467 listed.  See here…GBL 
LAY-IN AL/CU.  

As well, and as Gary pointed out with his second link, for a module 
bonding/grounding method to be acceptable, it must be recognized by the module 
manufacturer, no?Which means that any new bonding product on the market must 
have the blessing  of each mod mfgr.  
(by way of letter or mention in its install manual).  I have come across 
inspectors that actually look for this.
Jason, you wrote "I like the looks of that lug. However, I've been using WEEBs 
too long to go back now." I agree, and i'm not looking to replace weebs with 
these, but these certainly seem to have a place in the What do you use for the 
bonding connection from the ?rails?  
This SGB lug was suggested for this purpose as well.

BennDayStar Renewable Energy Inc. www.daystarsolar.ca  *  Ph: 780-906-7807 
Construction Electrician Solar Photovoltaic Systems CertifiedCertificate # 
0007SHAVE A SUNNY DAY
On 27/08/12 2:35 PM, "Gary Willett" <g...@icarussolarservices.com> wrote:


  
    
  
  
    Here's the Ilsco
        listing from UL, where it's classed as "Grounding and Bonding
        Equipment":
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=KDER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1


        

        The GuideInfo for Grounding & Bonding Equipment lists:

      
      Grounding and Bonding for
            Photovoltaic (PV) Systems — Grounding and bonding
          equipment intended for use in PV systems are additionally
          investigated in combination with the PV module/panel (see
          QIGU) to the applicable requirements for such products.
          Installation instructions provided with the PV system (see
          QIGU) identify the specific grounding and bonding device that
          has been investigated and intended for use with that system.

      
      
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074098839&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1


        

        

      
      
        
        
        
        
        
        
        
        
        
        
        
          Regards,

              

              Gary Willett, PE
        
      
      On 8/27/2012 3:20 PM, David Brearley wrote:

    
    Yes, sorry. I wasn't speaking of this lug...I like the
      redesign. Looks quicker and easier and robust.
      

        
          On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
          

          Yeah, but this one is marketed as a
            solar bonding lug. I think it's safe to say that it
            appropriately rated for outdoor use. It's always good to
            double-check, of course.
            

              Jason Szumlanski
              Fafco Solar
              

              
              

              

              On Mon, Aug 27, 2012 at 4:11 PM,
                David Brearley <david.brear...@solarprofessional.com>
                wrote:

                
                  Some of the aluminum
                    lugs are indoor-rated. They have a set screw will
                    rust in an outdoor environment. That's one of the
                    classic John Wiles slides. I'd just watch out for
                    that....
                    
                      
                        
                          
                            
                              

                                On Aug 27, 2012, at 12:53 PM, Brian
                                Mehalic <br...@solarenergy.org>                 
               wrote:

                                

                              
                              
                                I believe the UL467 listing means
                                  that it is rated for direct
                                  burial/outdoor use.

                                  

                                  
                                  Brian Mehalic 

                                    NABCEP Certified Solar PV
                                    Installer™ R031508-59
                                    
                                      IREC ISPQ Certified Affiliated
                                      Instructor/PV US-0132

                                      

                                      
                                      PV Curriculum Developer and
                                        Instructor
                                        Solar Energy International
                                          http://www.solarenergy.org
                                      
                                    
                                  
                                
                              
                              
                                .org


_______________________________________________

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org









-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to