The WEEB-LUG is great for rail bonding:
http://www.we-llc.com/grounding-lug.html

It is UL467, marked Outdoor Use, made of tin-plated copper. The only
disadvantage is that the stainless steel clip must be sacrificed if the lug
is moved - a disadvantage of all WEEB grounding products.

Jason Szumlanski
Fafco Solar


On Mon, Aug 27, 2012 at 7:11 PM, benn kilburn <b...@daystarsolar.ca> wrote:

> Thanks for the feedback Wrenches, lots of interesting comments,
>
> However I'm still wondering…..
> How does one confirm that it is specifically approved for outdoor use?
> Other than assuming it is implied (because it is 'marketed' as a solar
> lug).  As far as I can tell UL 467 does not imply "outdoor rated" as the
> aluminum lug "GBL-4" is also UL467 listed.  See here…GBL LAY-IN 
> AL/CU<http://ilsco.com//ProductsDetail.aspx?kfjkff=cjiDRFP14PUgtVid3pn1cQ%3d%3d&fjjfhjhj=nY1wgyVO%2fE%2bFsQNfsmn%2f4OZ3BP5vHo5NcMahtvvHLIc%3d>.
>
>
> As well, and as Gary pointed out with his second link, for a module
> bonding/grounding method to be acceptable, it must be recognized by the
> module manufacturer, no?
> Which means that any new bonding product on the market must have the
> blessing  of each mod mfgr.
> (by way of letter or mention in its install manual).  I have come across
> inspectors that actually look for this.
>
> Jason,
> you wrote "I like the looks of that lug. However, I've been using WEEBs
> too long to go back now." I agree, and i'm not looking to replace weebs
> with these, but these certainly seem to have a place in the What do you use
> for the bonding connection from the ?rails?
> This SGB lug was suggested for this purpose as well.
>
>
> Benn
> DayStar Renewable Energy Inc.
> www.daystarsolar.ca  *  Ph: 780-906-7807
> Construction Electrician Solar Photovoltaic Systems Certified
> Certificate # 0007S
> HAVE A SUNNY DAY
>
> On 27/08/12 2:35 PM, "Gary Willett" <g...@icarussolarservices.com> wrote:
>
>  Here's the Ilsco listing from UL, where it's classed as "Grounding and
> Bonding Equipment":
>
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=KDER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
>
> The GuideInfo for Grounding & Bonding Equipment lists:
>
> *Grounding and Bonding for Photovoltaic (PV) Systems *— Grounding and
> bonding equipment intended for use in PV systems are additionally
> investigated in combination with the PV module/panel (see QIGU) to the
> applicable requirements for such products. Installation instructions
> provided with the PV system (see QIGU) identify the specific grounding and
> bonding device that has been investigated and intended for use with that
> system.
>
>
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074098839&cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
>
>
>   Regards,
>
> Gary Willett, PE****
>  On 8/27/2012 3:20 PM, David Brearley wrote:
>
> Yes, sorry. I wasn't speaking of this lug...I like the redesign. Looks
> quicker and easier and robust.
>
>  On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
>
> Yeah, but this one is marketed as a solar bonding lug. I think it's safe
> to say that it appropriately rated for outdoor use. It's always good to
> double-check, of course.
>
> Jason Szumlanski
> Fafco Solar
>
>
>
> On Mon, Aug 27, 2012 at 4:11 PM, David Brearley <
> david.brear...@solarprofessional.com> wrote:
>
>> Some of the aluminum lugs are indoor-rated. They have a set screw will
>> rust in an outdoor environment. That's one of the classic John Wiles
>> slides. I'd just watch out for that....
>>
>>
>> On Aug 27, 2012, at 12:53 PM, Brian Mehalic <br...@solarenergy.org>
>> wrote:
>>
>>  I believe the UL467 listing means that it is rated for direct
>> burial/outdoor use.
>>
>>  Brian Mehalic
>> NABCEP Certified Solar PV Installer™ R031508-59
>> IREC ISPQ Certified Affiliated Instructor/PV US-0132
>>
>>  PV Curriculum Developer and Instructor
>> Solar Energy International
>> http://www.solarenergy.org
>>
>>  .org
>>
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to