Kirpal.

The Ilsco lug GBL-4 also comes with a stainless steel set-screwŠ as stated
hereŠ.GBL LAY-IN AL/CU
<http://ilsco.com/ProductsDetail.aspx?kfjkff=cjiDRFP14PUgtVid3pn1cQ%3d%3d&fj
jfhjhj=nY1wgyVO%2fE%2bFsQNfsmn%2f4OZ3BP5vHo5NcMahtvvHLIc%3d>
if that is all it takes to use the AL lug outdoors (stainless steel
set-screw), then why have we been steered towards the 'direct burial rated'
tin-plated copper lug instead of an AL lug with SS set-screw?

I'm not trying to make a case to not use the SGB lug, I like it and would
like to keep some in stock, as they seem pretty useful, I just want to have
my bases covered if/when an inspector questions me on them being approved
for the application.

Dan,
Agreed!  Been trying to get an answer from Ilsco, just tracking down the
right person with the answers.

Cheers,
benn

DayStar Renewable Energy Inc.
www.daystarsolar.ca  *  Ph: 780-906-7807
Construction Electrician Solar Photovoltaic Systems Certified
Certificate # 0007S
HAVE A SUNNY DAY

On 27/08/12 5:42 PM, "Kirpal Khalsa" <solarwo...@gmail.com> wrote:

Benn...it looks like that lug has "stainless hardware for corrosion
resistance"  as stated on the brochure....That would be the biggest
consideration as David Brearly mentioned earlier in regards to rust
potential.  Stainless hardware and tin plating is equivalent to the WEEB
lugs....Tin plating and stainless hardware is as good as anything else
available as far as outdoor ratings are concerned.....
I see your point that it is not explicitly stated for outdoor use....however
being marketed for use with solar panels also seems to imply rather
obviously that it is outdoor rated.....in my unofficial opinion.

-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer



On Mon, Aug 27, 2012 at 4:11 PM, benn kilburn <b...@daystarsolar.ca> wrote:
> Thanks for the feedback Wrenches, lots of interesting comments,
> 
> However I'm still wonderingŠ..
> How does one confirm that it is specifically approved for outdoor use?
> Other than assuming it is implied (because it is 'marketed' as a solar lug).
> As far as I can tell UL 467 does not imply "outdoor rated" as the aluminum lug
> "GBL-4" is also UL467 listed.  See hereŠGBL LAY-IN AL/CU
> <http://ilsco.com//ProductsDetail.aspx?kfjkff=cjiDRFP14PUgtVid3pn1cQ%3d%3d&fjj
> fhjhj=nY1wgyVO%2fE%2bFsQNfsmn%2f4OZ3BP5vHo5NcMahtvvHLIc%3d> .
> 
> As well, and as Gary pointed out with his second link, for a module
> bonding/grounding method to be acceptable, it must be recognized by the module
> manufacturer, no?
> Which means that any new bonding product on the market must have the blessing
> of each mod mfgr.
> (by way of letter or mention in its install manual).  I have come across
> inspectors that actually look for this.
> 
> Jason, 
> you wrote "I like the looks of that lug. However, I've been using WEEBs too
> long to go back now." I agree, and i'm not looking to replace weebs with
> these, but these certainly seem to have a place in the What do you use for the
> bonding connection from the ?rails?
> This SGB lug was suggested for this purpose as well.
> 
> 
> Benn
> DayStar Renewable Energy Inc.
> www.daystarsolar.ca <http://www.daystarsolar.ca>   *  Ph: 780-906-7807
> <tel:780-906-7807>
> Construction Electrician Solar Photovoltaic Systems Certified
> Certificate # 0007S
> HAVE A SUNNY DAY
> 
> On 27/08/12 2:35 PM, "Gary Willett" <g...@icarussolarservices.com> wrote:
> 
>     
>  
> Here's the Ilsco listing from UL, where it's classed as "Grounding and Bonding
> Equipment":
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?name=K
> DER.E34440&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074099002&cfgi
> d=1073741824&version=versionless&parent_id=1073988940&sequence=1
>  
>  The GuideInfo for Grounding & Bonding Equipment lists:
>   
>> Grounding and Bonding for Photovoltaic (PV) Systems ‹ Grounding and bonding
>> equipment intended for use in PV systems are additionally investigated in
>> combination with the PV module/panel (see QIGU) to the applicable
>> requirements for such products. Installation instructions provided with the
>> PV system (see QIGU) identify the specific grounding and bonding device that
>> has been investigated and intended for use with that system.
>>  
>  
> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=
> KDER.GuideInfo&ccnshorttitle=Grounding+and+Bonding+Equipment&objid=1074098839&
> cfgid=1073741824&version=versionless&parent_id=1073988940&sequence=1
>  
>  
>   
>            
>  
> 
> Regards,
>  
>  Gary Willett, PE
>  
>  
>  On 8/27/2012 3:20 PM, David Brearley wrote:
>  
>  
>> Yes, sorry. I wasn't speaking of this lug...I like the redesign. Looks
>> quicker and easier and robust.
>> 
>>  
>>  
>> On Aug 27, 2012, at 3:17 PM, Jason Szumlanski wrote:
>>  
>>  
>>> Yeah, but this one is marketed as a solar bonding lug. I think it's safe to
>>> say that it appropriately rated for outdoor use. It's always good to
>>> double-check, of course.
>>> 
>>>  Jason Szumlanski
>>> Fafco Solar
>>>  
>>> 
>>>  
>>>  
>>>  
>>>  
>>> On Mon, Aug 27, 2012 at 4:11 PM, David Brearley
>>> <david.brear...@solarprofessional.com> wrote:
>>>  
>>>>  
>>>> Some of the aluminum lugs are indoor-rated. They have a set screw will rust
>>>> in an outdoor environment. That's one of the classic John Wiles slides. I'd
>>>> just watch out for that....
>>>>  
>>>>>  
>>>>>  
>>>>>  
>>>>>  
>>>>> 
>>>>>  On Aug 27, 2012, at 12:53 PM, Brian Mehalic <br...@solarenergy.org>
>>>>> wrote:
>>>>>  
>>>>>  
>>>>>  
>>>>>>  
>>>>>> I believe the UL467 listing means that it is rated for direct
>>>>>> burial/outdoor use.
>>>>>>  
>>>>>> 
>>>>>>  
>>>>>>  
>>>>>> Brian Mehalic
>>>>>>  NABCEP Certified Solar PV Installer R031508-59
>>>>>>  IREC ISPQ Certified Affiliated Instructor/PV US-0132
>>>>>>  
>>>>>> 
>>>>>>  
>>>>>>  
>>>>>> PV Curriculum Developer and Instructor
>>>>>> Solar Energy International
>>>>>>                                           http://www.solarenergy.org
>>>>>> <http://www.solarenergy.org/>
>>>>>>  
>>>>>>  
>>>>>>  
>>>>>>  
>>>>>>  
>>>>>  
>>>>>>  
>>>>>> .org
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
> 
> 



_______________________________________________ List sponsored by Home Power
magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List
rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant
bios: www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org