Jerry,

What unit did you use?

Mark Frye

On 2/2/2015 7:43 AM, Jerry Shafer wrote:

Wrenches
We have installed some of these rapid shut down units and they are always located close to the array and ours kill the DC instantly as long as the inverter was running when this accures did not test it with inverters already off.
Jerry

On Feb 2, 2015 5:34 AM, "Christopher Warfel" <cwar...@entech-engineering.com <mailto:cwar...@entech-engineering.com>> wrote:

    We have a interpretation problem among some people I work with
    with, and  690.12 Rapid Shut Down and the the 10 second time for
    reducing ac and dc conductors to 240ma, and 30V.  The word
    "initiation" seems to indicate that all affected conductors need
    to be at these levels within 10 seconds of de-energizing either
    the ac or dc conductors. If so, then the disconnects need to be
    co-located to meet this requirement if this interpretation is correct.

    I have read Mr. Brook's article in Solar Pro, but AHJs may feel
    differently.

    Would anyone care to weigh in on their interpretation?

    Thank you, Chris





-- Christopher Warfel, President
    ENTECH Engineering, Inc.
    PO Box 871, Block Island, RI 02807
    401-466-8978 <tel:401-466-8978>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to