OK. So did you run a line 120V up to the box on the roof to energize the coil of the relay up there?

Mark Frye

On 2/2/2015 9:13 AM, Jerry Shafer wrote:
The units we have used have a large contactor inside the combiner box made by AMtec Solar. this was required to control the shut down includes a fire button done on the ground floor
Jerry

On Mon, Feb 2, 2015 at 5:49 AM, Mark Frye <ma...@berkeleysolar.com <mailto:ma...@berkeleysolar.com>> wrote:

    Jerry,

    What unit did you use?

    Mark Frye


    On 2/2/2015 7:43 AM, Jerry Shafer wrote:

    Wrenches
    We have installed some of these rapid shut down units and they
    are always located close to the array and ours kill the DC
    instantly as long as the inverter was running when this accures
    did not test it with inverters already off.
    Jerry

    On Feb 2, 2015 5:34 AM, "Christopher Warfel"
    <cwar...@entech-engineering.com
    <mailto:cwar...@entech-engineering.com>> wrote:

        We have a interpretation problem among some people I work
        with with, and 690.12 Rapid Shut Down and the the 10 second
time for reducing ac and dc conductors to 240ma, and 30V. The word "initiation" seems to indicate that all affected
        conductors need to be at these levels within 10 seconds of
        de-energizing either the ac or dc conductors. If so, then the
        disconnects need to be co-located to meet this requirement if
        this interpretation is correct.

        I have read Mr. Brook's article in Solar Pro, but AHJs may
        feel differently.

        Would anyone care to weigh in on their interpretation?

        Thank you, Chris





-- Christopher Warfel, President
        ENTECH Engineering, Inc.
        PO Box 871, Block Island, RI 02807
        401-466-8978 <tel:401-466-8978>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>




    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to