I”ll chime in here.

Yes the GSLC is a piece of junk.  
However it is UL listed for the job. And while you could put together something 
that would work with Airpax breakers together, but it wouldn’t be UL.

What I do is to swap out all the wires to Arctic ultra flex.  This allows much 
better movement of the wires with significantly less stress on the terminals.   
And if you want to not attach wires to the back of the breakers then you can 
and I’ve seen outback do it, install lay in lugs facing outwards so you can use 
a screwdriver or allen key on them.  Allows for installation and removal of 
wire without removal of the breaker or the plate/breakers.  With thimbles of 
course. And I can’t find them but I know they make them, shields that fit 
between each breaker so the lay in lugs are insulated.

jay
peltz power


> On Oct 10, 2016, at 4:40 PM, William Miller <will...@millersolar.com> wrote:
> 
> Chris:
>  
> Thank you for the reply.  I think you misunderstand me.  We always use the 
> GSLC cabinets.  I just don’t like the design concept that clutters the 
> cabinet with AC and DC breakers that are difficult to access and block other 
> components.  See photo below of a prewired GSLC Cabinet we were asked to work 
> in.  Not a good scenario.
>  
> We have created an installation standard using the GSLC that minimizes the 
> problems inherent with the design.  We run all AC leads to adjacent load 
> centers and we try to minimize the DC breakers in the cabinet.  It is our 
> goal to completely eliminate all breakers from the removable dead-front.  I 
> think it is pretty self-explanatory why one would not prefer to make 
> connections in a hard to reach location. 
>  
> Our goal is to constantly improve our installation procedures to create 
> better, safer and more efficient installations.  
>  
> Also, I don’t need someone to instruct me on how to make a “finished” looking 
> install. If you are familiar with my work you know it is as clean as it gets. 
>  Review my web site.  Below is but one example of one of our installs.
>  
> And lastly, “suck it up” is not a very complimentary phrase.  Please, let’s 
> keep it professional.
>  
> Sincerely,
>  
> William Miller
>  
> <image007.jpg>
> Figure 1 Factory wired GSLC
> 
>  
> <image008.jpg>
> Figure 2 Miller Solar installed GSLC..
> 
>  
> <image009.jpg>
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Chris Mason
> Sent: Monday, October 10, 2016 3:40 PM
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>>
> Subject: Re: [RE-wrenches] PV Recombiner
>  
> The GSLC gives the system a nice finished appearance that the customer will 
> understand. Suck it up and live with the imperfect world we function in. 
>  
> On Mon, Oct 10, 2016 at 5:55 PM, William Miller <will...@millersolar.com 
> <mailto:will...@millersolar.com>> wrote:
>> Friends:
>>  
>> I am looking for a PV recombiner.  I need to accept the outputs from 3 
>> remote PV Combiners, send those outputs through GFP circuit breakers, into 
>> charge controllers, back thorough breaker, into a bus bar, through a main 
>> breaker and onto a large battery bank.
>>  
>> I am using 2 Outback Radian inverters, but I refuse to install DC breakers 
>> on their dead-front because wiring to studs facing away from the front is an 
>> inferior design.  Furthermore, I see no need to run PV circuits through the 
>> GSLC cabinets.
>>  
>> I looked at the Midnite MNDC15 but again, these use panel mounted breakers 
>> with studs on the back.
>>  
>> Anyone know of a more thoughtfully designed PV recombiner?
>>  
>> Thanks in advance,
>>  
>> William Miller
>>  
>>  
>> <image003.jpg>
>> Lic 773985
>> millersolar.com <http://www.millersolar.com/>
>> 805-438-5600 <tel:805-438-5600>
>>  
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org 
>> <mailto:RE-wrenches@lists.re-wrenches.org>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> 
> 
> 
>  
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>  
> www.cometsolar.com <http://www.cometenergysystems.com/>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings: