Jerry,
I don't think that QOs or QOUs would work. I believe that all are rated only to 50V DC, unless that longtime dual rating has recently changed. As the Radian is only available in 48V, any DC conductors would exceed this.
Allan

*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 10/10/2016 8:40 PM, Jerry Shafer wrote:

You might want to look at the square D QO breaker line some are dc rated and voltage rated and are panel mounted.
Jerry


On Oct 10, 2016 3:00 PM, "jay" <jay.pe...@gmail.com <mailto:jay.pe...@gmail.com>> wrote:

    I”ll chime in here.

    Yes the GSLC is a piece of junk.
    However it is UL listed for the job. And while you could put
    together something that would work with Airpax breakers together,
    but it wouldn’t be UL.

    What I do is to swap out all the wires to Arctic ultra flex.  This
    allows much better movement of the wires with significantly less
    stress on the terminals. And if you want to not attach wires to
    the back of the breakers then you can and I’ve seen outback do it,
    install lay in lugs facing outwards so you can use a screwdriver
    or allen key on them.  Allows for installation and removal of wire
    without removal of the breaker or the plate/breakers.  With
    thimbles of course. And I can’t find them but I know they make
    them, shields that fit between each breaker so the lay in lugs are
    insulated.

    jay
    peltz power


    On Oct 10, 2016, at 4:40 PM, William Miller
    <will...@millersolar.com <mailto:will...@millersolar.com>> wrote:

    Chris:

    Thank you for the reply.  I think you misunderstand me.  We
    always use the GSLC cabinets.  I just don’t like the design
    concept that clutters the cabinet with AC and DC breakers that
    are difficult to access and block other components.  See photo
    below of a prewired GSLC Cabinet we were asked to work in.  Not a
    good scenario.

    We have created an installation standard using the GSLC that
    minimizes the problems inherent with the design.  We run all AC
    leads to adjacent load centers and we try to minimize the DC
    breakers in the cabinet.  It is our goal to completely eliminate
    all breakers from the removable dead-front.  I think it is pretty
    self-explanatory why one would not prefer to make connections in
    a hard to reach location.

    Our goal is to constantly improve our installation procedures to
    create better, safer and more efficient installations.

    Also, I don’t need someone to instruct me on how to make a
    “finished” looking install. If you are familiar with my work you
    know it is as clean as it gets.  Review my web site. Below is but
    one example of one of our installs.

And lastly, “suck it up” is not a very complimentary phrase. Please, let’s keep it professional.

    Sincerely,

    William Miller

    <image007.jpg>

    Figure 1 Factory wired GSLC

    <image008.jpg>

    Figure 2 Miller Solar installed GSLC..

    <image009.jpg>
    Lic 773985
    millersolar.com <http://www.millersolar.com/>
    805-438-5600 <tel:805-438-5600>

    *From:*RE-wrenches
    [mailto:re-wrenches-boun...@lists.re-wrenches.org
    <mailto:re-wrenches-boun...@lists.re-wrenches.org>]*On Behalf
    Of*Chris Mason
    *Sent:*Monday, October 10, 2016 3:40 PM
    *To:*RE-wrenches <re-wrenches@lists.re-wrenches.org
    <mailto:re-wrenches@lists.re-wrenches.org>>
    *Subject:*Re: [RE-wrenches] PV Recombiner

    The GSLC gives the system a nice finished appearance that the
    customer will understand. Suck it up and live with the imperfect
    world we function in.

    On Mon, Oct 10, 2016 at 5:55 PM, William Miller
    <will...@millersolar.com <mailto:will...@millersolar.com>> wrote:
    Friends:

    I am looking for a PV recombiner.  I need to accept the outputs
    from 3 remote PV Combiners, send those outputs through GFP
    circuit breakers, into charge controllers, back thorough
    breaker, into a bus bar, through a main breaker and onto a large
    battery bank.

    I am using 2 Outback Radian inverters, but I refuse to install
    DC breakers on their dead-front because wiring to studs facing
    away from the front is an inferior design.  Furthermore, I see
    no need to run PV circuits through the GSLC cabinets.

    I looked at the Midnite MNDC15 but again, these use panel
    mounted breakers with studs on the back.

    Anyone know of a more thoughtfully designed PV recombiner?

    Thanks in advance,

    William Miller

    <image003.jpg>
    Lic 773985
    millersolar.com <http://www.millersolar.com/>
    805-438-5600 <tel:805-438-5600>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org/>



    --
    Chris Mason
    NABCEP Certified Solar PV Installer™
    Solar Design Engineer
    Generac Generators Industrial technician

    www.cometsolar.com <http://www.cometenergysystems.com/>
    264.235.5670 <tel:264.235.5670>
    869.662.5670 <tel:869.662.5670>
    Skype: netconcepts
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to