August,

The current Tesla (AC coupled only) would be a challenge for sure! I do
like the 13KWH for the price. I hope they do something as everything I
have looked at beside the LG is over $1,000 (wholesale) per ueable KWH.
Hope this changes.  --Dave


> As I mentioned on a related post, Tesla's Powerwall has an active heating
> feature where it will use some of its own energy to raise cell
> temperature.
> Obviously this means that it will need to be charged throughout the cold
> season using some amount of PV energy to do so (I think I heard 250 Wh per
> heating cycle depending on temps?). I understand that Tesla's offgrid
> Powerwall isn't ready for prime time yet.
>
> August
>
> *August Goers*
>
> Luminalt Energy Corporation
>
>
> On Wed, Feb 28, 2018 at 8:55 AM, Bill Hoffer <suneng...@gmail.com> wrote:
>
>> Daniel
>>
>> Why are we having to deal with low temp charging?  Litium batteries
>> already have cell temp monitoring and relays to shut down individual
>> cells
>> when they over temp.  How hard would it be to open the relay at low
>> temps
>> too?  Seems like something the lithium battery folks should have already
>> thought of?
>>
>> Bill hoffer
>>
>>
>> On Feb 28, 2018 8:15 AM, "Daniel Young" <dyo...@dovetailsolar.com>
>> wrote:
>>
>> These issues are not lost on me for sure. I have to plan out a new
>> protective setup to try to ensure that if the temperatures drop and the
>> battery bank hits LVD, that the array cannot just charge the battery
>> back
>> up
>> on it's own. Possibly some sort of temperature dependent relay or shunt
>> trip
>> breaker on the battery bank to ensure that below 35F the battery must be
>> manually warmed to resume operation, or the system waits until the
>> battery
>> warms on it's own before allowing the CC's or even a generator to charge
>> them.
>>
>> My understanding is that the lithium's can go below freezing easily, but
>> they just cannot be charged when below freezing. They can sit down to
>> -5F
>> if
>> not being charged, they can even be under discharge down to that in some
>> cases. But adding controls to allow discharge, but not charge is likely
>> a
>> bit too much, best to just isolate the battery bank if below 32-35F in
>> my
>> opinion, which is what I plan to try to accomplish.
>>
>> Ideally someone is there to watch the batteries, but that simply is not
>> an
>> option. And the client is not likely to want a new AGM bank. But they
>> will
>> have to decide between the pro's and con's. All I can do is give them
>> the
>> info, and the choice.
>>
>> With Regards,
>>
>> Daniel Young,
>> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>>
>> -----Original Message-----
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
>> Behalf Of Dave Angelini Offgrid Solar
>> Sent: Tuesday, February 27, 2018 1:14 PM
>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>> Subject: Re: [RE-wrenches] heating a lithium battery bank
>>
>> The LG RESU series will trip it's breaker at around 10% Soc. It will
>> require
>> a human unless the LVD on the inverter is set higher than the battery.
>> Yes
>> Sir it is our responsibility to educate our users or have plane tickets
>> (:
>>
>> Will be installing the Discover battery soon into Xanbus.
>>
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/
>> e-mail  offgridso...@sti.net
>> text 209 813 0060
>>
>> > Hi Drake,
>> >
>> > I agree. Li-ion batteries, like lead batteries, should always have a
>> > human overseer. This is a difficult reality to convey in our
>> > set-it-forget it, automated world.
>> >
>> > One function of a Li-ion battery EMS or BMS is to prevent over
>> discharge.
>> > Once any battery cell reaches the lower limit, the battery will turn
>> off.
>> > For many systems, once charge current is again detected, the battery
>> > will turn on. Some will not and require a user to turn the battery
>> > back on. You can also install an external LVD device to stop power use
>> at
>> a higher SoC.
>> >
>> > As wrenches, its our responsibility to know our product and educate
>> > the customer. Too often, this does not happen.
>> >
>> > Larry Crutcher
>> > Starlight Solar Power Systems
>> >
>> >
>> >
>> >
>> >
>> >
>> > On Feb 27, 2018, at 7:11 AM, drake.chamber...@redwoodalliance.org
>> wrote:
>> >
>> > Snow on the array could be a very big problem with the heater load,
>> > inverter idle current and anything else that might be left on.
>> > Extended periods of heavy clouds can reduce power generation to be
>> > less than system's internal losses. It seems like a pretty big gamble
>> > to leave an expensive battery bank unattended, that can not go below
>> > freezing, and is dependent on array power to prevent freezing.
>> >
>> > If AGMs survive in this application, it might be better to stay with
>> > this technology.
>> >
>> >
>> > ----- Original Message -----
>> > From: offgridso...@sti.net "RE-wrenches"
>> > <re-wrenches@lists.re-wrenches.org>
>> > To:"RE-wrenches" <re-wrenches@lists.re-wrenches.org>
>> > Cc:
>> > Sent:Mon, 26 Feb 2018 10:36:29 -0800 (PST)
>> > Subject:Re: [RE-wrenches] heating a lithium battery bank
>> >
>> >
>> > Hello Daniel,
>> >
>> > I will give this some thought. What lithium make? The ones I have
>> > looked at log the temperature for warranty so that might negate the
>> value
>> a bit.
>> > The high temp is just as bad in your case here.
>> >
>> > Since this has been working well I am assuming snow on the panels is
>> > not an issue?
>> >
>> > Building a battery box that was cooled (small fan) from conditioned
>> > space is what I have done. The wall between the garage and living
>> > space is perfect. This won't help when the house is cold (unattended)
>> > much. It won't help if the house is allowed to get hot either.
>> >
>> > Some of the Lion batteries are actually listed for living space. The
>> > LG is. I don't do that with mine though. Hmmm
>> >
>> > Dave Angelini Offgrid Solar
>> > "we go where powerlines don't"
>> > http://members.sti.net/offgridsolar/
>> > e-mail offgridso...@sti.net
>> > text 209 813 0060
>> >
>> >> Hello Wrenches, here is a fun one for you all.
>> >>
>> >>
>> >>
>> >> The client you all helped me with earlier this year is now
>> >> considering changing out their AGM off grid bank with a lithium
>> >> battery bank before the next winter. I looked into this, as we have
>> >> been eying the various lithium options for 2+yrs now, but not bit the
>> >> bullet and really designed a bank into a system.
>> >>
>> >>
>> >>
>> >> The main issue I am trying to consider is this. The cabin is not
>> >> occupied during most of the winter, and the batteries are in the
>> >> unconditioned, but attached, garage. They drain the plumbing system
>> >> and shut off all breakers except the ones that power the internet,
>> >> chest freezer, and security system.
>> >> As such, the battery bank has routinely gotten below freezing,
>> >> sometimes staying there for 1-2 weeks. This is not an issue with
>> >> AGM's, within reason.
>> >> The battery bank has never gotten below 20F over the last 2 winters,
>> >> where the site has seen below zero temps for brief periods. But the
>> >> AGMs likely produce more heat during a charge than lithium's, and
>> >> they have significantly more thermal mass to ride through the really
>> >> cold nights.
>> >>
>> >>
>> >>
>> >> Lithium batteries, to the best of my knowledge, can be below freezing
>> >> during storage. But to safely charge, they must be above 32F. So the
>> >> thought was to provide an insulated battery box, and design in some
>> >> small heating system that is set to 40-45F. The first thought was a
>> >> low power fiberglass heating pad like is sometimes used for livestock
>> >> to give them a slightly warmed place to lay down. Then tie that to a
>> >> thermostat with a sensor on the battery bank. I would of course need
>> >> to try to account for the extra load in the battery bank sizing. They
>> >> array is more than is needed right now so I do not worry about it's
>> >> ability to compensate when the sun is shining.
>> >>
>> >>
>> >>
>> >> In theory this could be ok, but I worry about the summer. Will the
>> >> insulated enclosure cause the opposite issue during the summer, the
>> >> batteries getting too hot? I have seen the AGM bank go to 110F at one
>> >> point in Aug 2016.
>> >> But
>> >> with the lower internal resistance of the lithium's, maybe this is
>> >> less likely to be an issue. Do any of you wrenches have any
>> >> experience with this unconditioned setup?
>> >>
>> >>
>> >>
>> >> With Regards,
>> >>
>> >>
>> >>
>> >> Daniel Young,
>> >>
>> >> NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>> >>
>> >> _______________________________________________
>> >> List sponsored by Redwood Alliance
>> >>
>> >> List Address: RE-wrenches@lists.re-wrenches.org
>> >>
>> >> Change listserver email address & settings:
>> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>
>> >> List-Archive:
>> >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis
>> >> t.html
>> >>
>> >> List rules & etiquette:
>> >> www.re-wrenches.org/etiquette.htm
>> >>
>> >> Check out or update participant bios:
>> >> www.members.re-wrenches.org
>> >>
>> >>
>> >
>> >
>> > Dave Angelini Offgrid Solar
>> > "we go where powerlines don't"
>> > http://members.sti.net/offgridsolar/
>> > e-mail offgridso...@sti.net
>> > text 209 813 0060
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches@lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> > .html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches@lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> > .html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches@lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> > .html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>>
>>
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/
>> e-mail  offgridso...@sti.net
>> text 209 813 0060
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
>> g/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
>> g/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to