Mac Is this site on Optics, what is the state of charge when the genny turns on. Did you use the outback white paper to set up the system with the BPE Batteries, this might be helpful. Jerry Jerry
On Sat, Aug 3, 2019, 2:35 PM Mac Lewis <maclew...@gmail.com> wrote: > Hi Wrenches, > > I've got an issue that I'm remotely trying to troubleshoot but I must be > missing something. > Specs: > Off-grid > Dual Outback FXR 3648s recently installed > FM100, with about 4k of solar > 2 x 16 kWh Blue Ion Batteries, installed this past week > Kohler 14 generator > Outback Mate 3s > > The issue is that the FXR inverters aren't charging the batteries when the > generator is running, they are just passing the power through to the > loads. I have verified that AC Input is in "Use" not "Drop" when generator > is running, I have disabled all of the advanced charging (ie Global charge, > float coordination, auto-charge termination and auto grid-tie control) . I > have told it to "start bulk" both remotely and through the owner on site. > I have done a reboot multiple times of the whole system as well as the Mate > 3s. I even had the owner try a factory reset and firmware update on the > Mate 3s. The firmware was successfully updated and it appears the factory > reset on the mate. > > Nothing has changed how it behaves with the generator, generator just > follows the load and no AC charging takes place. Oddly, this was working > fine when we left, we had topped the batteries off with the generator. > > Any ideas what I might be missing? > > Thanks for your suggestions > -- > > > > Mac Lewis > > *"Yo solo sé que no sé nada." -Sócrates* > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org