Hi Mac
If you want to contact me off line.
I could give it a look.
Shoot me your phone number
Lones

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Mac 
Lewis
Sent: Saturday, August 3, 2019 2:35 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Pass-through state Dual FXR system

** [EXTERNAL EMAIL] - Please report any suspicious attachments, links, or 
requests for sensitive information to the Help Desk. **
________________________________
Hi Wrenches,

I've got an issue that I'm remotely trying to troubleshoot but I must be 
missing something.
Specs:
Off-grid
Dual Outback FXR 3648s recently installed
FM100, with about 4k of solar
2 x 16 kWh Blue Ion Batteries, installed this past week
Kohler 14 generator
Outback Mate 3s

The issue is that the FXR inverters aren't charging the batteries when the 
generator is running, they are just passing the power through to the loads.  I 
have verified that AC Input is in "Use" not "Drop" when generator is running, I 
have disabled all of the advanced charging (ie Global charge, float 
coordination, auto-charge termination and auto grid-tie control) .  I have told 
it to "start bulk" both remotely and through the owner on site.  I have done a 
reboot multiple times of the whole system as well as the Mate 3s.  I even had 
the owner try a factory reset and firmware update on the Mate 3s.  The firmware 
was successfully updated and it appears the factory reset on the mate.

Nothing has changed how it behaves with the generator, generator just follows 
the load and no AC charging takes place.  Oddly, this was working fine when we 
left, we had topped the batteries off with the generator.

Any ideas what I might be missing?

Thanks for your suggestions
--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to