We use this 3M wire numbering dispenser. They don't stick as well as
I'd like, but it can solve some very weird problems later.
3M STD Wire Marker Dispenser with #0-9 H-5223 - Uline
I'm also a fiend for color coding, and have had numerous discussion here
on the list about the need to color code wire. Crossed wiring as Jason
has illustrated to us, can be very dangerous and lead to issues none of
us could have predicted. Once again, this situation would have easily
been prevented by good old labeling and color coding by the original
installer Every time I open a box and see unmarked black wires running
every where, or inconsistent colors, I know the entire installation is
suspect.
Ray Walters
Remote Solar
303 505-8760
On 1/23/20 2:28 PM, Jason Szumlanski wrote:
What made this installation (again, by others) a bit more complicated
was that all branch circuit line conductors were black. I make it a
point on my installations to require black for L1 and red for L2 up to
#6 wire size. It's not a failsafe by any means but does reduce risk.
*
*
On Thu, Jan 23, 2020 at 2:41 PM August Goers <aug...@luminalt.com
<mailto:aug...@luminalt.com>> wrote:
Jason -
Thanks for sharing - this is a good lesson for all Wrenches. Years
ago we had a dual string inverter installation where the DC
positives and negatives were mixed between the two interters.
String 1 positive went to inverter 1, string 1 negative went to
inverter 2 and vice versa. The inverters tested out and ran for
about two weeks and then one of them literally caught on fire.
Since then, we implemented a policy of checking wiring coming from
the roof down individually. In the case of microinverter branch
circuits, this means checking each branch circuit voltage on the
roof with the other breakers off one branch at a time.
Not to get too far off on a tangent, but as we're installing more
and more energy storage with lots of onsite wiring work, it is
clear that fully testing wiring is of utmost importance. We have a
procedure for checking voltage at each piece of equipment (such as
a backup loads panel, etc) prior to turning on branch breakers.
We've run into a couple of scenarios where hots and neutrals were
mixed up causing 240 v to go to a 120 v circuit. Not good.
August
On Wed, Jan 22, 2020 at 2:58 PM Jason Szumlanski
<ja...@floridasolardesigngroup.com
<mailto:ja...@floridasolardesigngroup.com>> wrote:
I discovered the issue I believe, so I thought I'd update all
of you who gave me ideas on what to look for (thank you).
And this is something that I stress the importance of all the
time...
The branch circuit pairs were not properly paired up! All of
the L1 conductors went to L1 on the bus and all of the L2 to
L2. However, for example, circuit 1 L1 and circuit 2 L2 were
on a single 2-pole breaker. And circuit 2 L1 and circuit 1 L2
were on another breaker. Everything worked because it was
electrically connected to the right bus bar. However, when
there was a previous fault one of the breakers probably didn't
trip when it should have as a result of the improper pairings.
It was reset a few times and just kept heating up and heating up.
This isn't conclusive, but it sure makes sense. It wasn't fun
tracking this down with 5 strings and 5 junction boxes on the
roof, but once we started continuity testing and finding
strange results, it became clear.
Jason Szumlanski
On Tue, Jan 21, 2020 at 12:10 PM Jason Szumlanski
<ja...@floridasolardesigngroup.com
<mailto:ja...@floridasolardesigngroup.com>> wrote:
(System installed by another contractor...)
I have been tasked with assisting in the investigation of
damage in a subpanel used to combine inverter output
circuits (5 strings of microinverters). There appears to
be no damage to conductors or other system components. It
looks like the damage started at the stabs of the bus bar
where the breakers connect. Picture attached. Here are a
few clues:
* Monitoring indicates that damage occurred overnight a
few weeks ago. That night we had rain as a winter
front came through Florida, possibly lightning. The
prior day everything was fine.
* The next morning, only 2 of 5 strings started
producing power, but 4 of 5 strings were reporting
data to the Envoy. The two strings that were reporting
but not producing power reported 0Vac and Voc on the
DC side of the microinverters.
* A couple of weeks later, 1 of the 2 strings that was
producing power quit doing so, but continued reporting
data.
* Customer discovered damage yesterday.
* About a week before the initial damage apparently
manifested itself, another contractor installed a
whole house generator transfer switch on the line side
of the PV interconnection. The generator has never
been run (there is not even a LP fuel source on site
yet). I pointed out that the solar interconnection,
which was previously on the supply side, would need to
be moved to the supply side of the generator transfer
switch's main breaker before operation. During the
transfer switch installation, the contractor also
switched line 1 and line 2, but that shouldn't
really matter, except for Enphase consumption
monitoring, which was messed up by the swapping of the
lines.
So I'm looking for ideas. I'm wondering if the OCPD would
be a likely place for lightning damage to manifest itself.
I can't visually detect any other damage anywhere else. I
can't imagine that the transfer switch installation would
have anything to do with it, but the timing is
interesting. Other than replacing the subpanel and OCPD
and firing it back up (no pun intended), I'm not sure how
to approach further investigation.
Jason Szumlanski
Florida Solar Design Group
*
*
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/0630738790020bf17b7774ad6ed4464425204c4b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=636f6272fa7ddeb8>
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
<https://mailtrack.io/trace/link/723f771ba6190c7b8fc2fd06f31ea7a6b6ab41c0?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f6676786e8e04410>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/d7ea9ae3eaf8765631db5d80b47f3267e01120c0?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=7b3d598ee513f514>
Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/01c37be05208c0de420580d892b553f82dfadc19?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=01eb85f151b00d5d>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
<https://mailtrack.io/trace/link/36360340e428b3c123126012a4fa231afa4d6f05?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ed994c188e79c2d3>
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
<https://mailtrack.io/trace/link/6cd516775bc1800cf14b878dba3290cc3ab86de6?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1c8f4f1539e9183a>
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<https://mailtrack.io/trace/link/9c3fae629a074d4c8ae47e0eaf0c5201471c0b1d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=6fda5140d3ecc484>
Check out or update participant bios:
www.members.re-wrenches.org
<https://mailtrack.io/trace/link/ad276d8b16d068c12a6ea6c0cd4c11cbd1f413a5?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=92016f985d4b96d5>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org