We had one last year with a bad relay, the customer had been charging a Tesla EV through it (pass through from the grid) and smoked the relay.  It was pretty obvious, the clear relay cover was all covered on the inside with burnt relay bits and smoke coating.

Ray Walters
Remote Solar
303 505-8760

On 3/9/20 12:13 PM, John Blittersdorf wrote:

Hugh,
   I have one at my guest cabin doing the same thing except that the meter on the mate says I have 119 vac but nothing at the AC Out terminal.  I think Kent might be right that it may be the AC output relay.  It is odd though that there is no error message in your case.  This inverter had been tortured by the last tenants of the cabin with bad generators.  I was actually going to go up there and check it out some more as it is warm today. No heat in the cabin.

John Blittersdorf

On Mon, Mar 9, 2020 at 1:00 PM Kent Osterberg <k...@coveoregon.com <mailto:k...@coveoregon.com>> wrote:

    Hugh,

    I've seen these symptoms before. The problem was a failed output
    relay on the ac board.

    Kent Osterberg
    Blue Mountain Solar


    On 3/9/2020 9:25 AM, Hugh Piggott wrote:
    Hi Wrenches,

    I wonder if anyone can tell me what is happening here?

    I have an Outback VFX that I used for my own home from
    2006-2018.  It’s a 50Hz 240V unit, but similar otherwise to any
    other 48V VFX.  It was working well when disconnected.  I needed
    to replace the inverter system for other reasons.

    I installed this for a neighbour recently on his 48V system, and
    it apparently worked when I left the building.

    Now it’s not working.  When “off” it shows a warning for
    temperatures sensor - fair enough I did not install one.  Maybe
    when it gets connected to a generator it will be found a sensor. 
    This is the only error or fault with a yes.

    When “on” it makes a reassuring buzz and both lights come up
    green and there is no error or warning in the Mate.  Just one
    problem - no output.

    Another weird thing.  I go to the status menu and check meters
     STATUS/FX/METER output voltage and it says “4V”.  So it _knows_
    that it is not working but it appears to have no qualms or
    misgivings about this state of affairs.  NO error, no warning,
    two green lights.

    I tried rebooting with the battery fuse.  I tried resetting to
    factory defaults.  No joy.

    I suppose I will take it to pieces and try to figure out a
    hardware failure but I wonder if anyone has seen this and can
    give me a clue?

    cheers
    Hugh


    Hugh Piggott
    Scoraig Wind Electric
    Dundonnell
    Ross shire
    IV23 2RE,  UK
    +44 77 1315 7600
    h...@scoraigwind.co.uk <mailto:h...@scoraigwind.co.uk>
    www.scoraigwind.co.uk <http://www.scoraigwind.co.uk/>





    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to