This, from a Nov 03, 2017 Powerwall 2 document, makes sense. Generator input in 
place of utility syncs with PV inverters and Powerwall inverter.

Thank you,

Larry Crutcher
Starlight Solar Power Systems






On Jul 20, 2020, at 1:25 PM, August Goers <aug...@luminalt.com> wrote:

Tesla released new offgrid design and installation instructions April of this 
year. As a Powerwall dealer, we're under NDA not to share the document, but the 
Powerwall will now charge from the generator when it hits a certain SOC 
threshold if the PV is not running. I'm not sure about that caveat of not 
allowing the generator to run while the PV is running. It seems like there are 
plenty of times where there is low solar production and you want to fire up the 
generator to top off the batteries. They also have a low state of charge mode 
when SOC reaches 10%, that the Powerwall will turn on during the day for short 
periods of time just to test to see if the PV system will couple up to charge 
the battery. This AC-coupling method of reviving the battery may or not work 
depending on loads and PV sizing / production levels.

One limitation to the NMC battery technology is that it doesn't work well 
particularly in the cold, so offrige Powerwall batteries should be installed in 
the heated envelope of the home. 

August


On Mon, Jul 20, 2020 at 10:09 AM Jason Szumlanski 
<ja...@floridasolardesigngroup.com> wrote:
The Powerwall 2 is now supported by Tesla in an off-grid configuration from 
what I heard. It is AC coupled. It cannot interact with generators whatsoever. 
You can't charge the battery with a generator and you can't AC couple a 
generator to it. If you want a generator, you put a transfer switch on the load 
side of the gateway device. If the battery dies, the generator starts. The 
generator powers loads, but does not recharge the battery because it becomes 
isolated via the transfer switch. The big downside I see with that is there 
would be a loss of power to the loads until the generator fires up. I don't see 
a way around that.

I'm not a Tesla certified installer, but I have seen some of these batteries 
out in the wild and that's just the way it is - it's an integrated unit. I'd 
call it an "AC Battery," kind of like an AC PV Module. To answer another point 
in this thread, if the battery reaches its LBCO it can only recharge with PV in 
an off-grid scenario. It reserves battery capacity to turn on occasionally to 
see if there is PV input. At least that's how I understand it to work. I don't 
know what would happen if the battery actually reached 0%. Seems risky. I'm not 
sure how you would "jump start" it. Publicly available details seem scant on 
this, but there are a few system owners talking about it if you dig deep on the 
Interwebs.

It will be interesting to see what Enphase comes up with. There are generator 
inputs on their Ensemble system, but no software support for this yet. The 
concept is very similar to Tesla in that there is a gateway device, essentially 
a transfer switch with battery controls inside. The Gateway acts as the AC 
point of coupling for everything to tie in together. 

I'm not sure why you couldn't use a generator to charge the Powerwall battery 
the same way you would charge with the grid. However, you would need a way to 
disable PV AC coupling when the generator is running. I can see how Enphase 
would be able to do this pretty easily. But Tesla is clear in that they do not 
allow a generator to interact with the Powerwall in any way.

Jason Szumlanski





On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III <hiltond...@gmail.com> wrote:
Greetings, Wrenches,

I have an off-grid client who has been reading the buzz about the Tesla 
Powerwall 2.0. I have been reading the data sheets and manual for it and it 
appears to be AC coupled only. There was talk of a DC input version, but 
apparently that fell by the wayside. I try to be agnostic about technology, and 
I'd be willing to subcontract a Tesla-approved installer if, in fact, this was 
the best solution.

Does anybody have experience using the Powerwall 2.0 in an off grid PV system? 
Is it AC coupled only? Can it take generator power without barfing? What is the 
lead time on these?

Many Thanks,

Hilton

-- 
Hilton Dier III
Missisquoi River Hydro
Renewable Energy Design

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to