Schneider uses 1.25 max on an XW for Ac coupling. That would be 1.25 x 6
kw or 7.5kw max from the grid inverter when ac coupling. 

I doubt your
numbers would work well with a 5kw internal powerwall. Maybe if you had 2
poweralls? Better get info from Tesla or the installer on Wrenches. Good
Luck!  

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Wed, 22 Jul 2020 07:24:48 -0400,
r...@solartechvt.com wrote:   

Considering the lack of public info
available for the Powerwall, does anyone have any insight into the AC
coupling limits for a single Powerwall? 

For example, can we AC couple
10kw Solar Edge to a single Powerwall? 

Thanks 

Rich 

FROM: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] ON BEHALF OF Ray
SENT:
Tuesday, July 21, 2020 8:39 PM
TO:
re-wrenches@lists.re-wrenches.org
SUBJECT: Re: [RE-wrenches] Tesla
Powerwall 2.0 - Experience?/Generator charging   

That's going to be long
extension cord for most off grid projects....... 
Ray Walters

Remote
Solar

303 505-8760

On 7/21/20 12:11 PM, Matt Partymiller wrote:   

Jay,


The Tesla Gateway has a 12v input terminal for boot up. To startup my off
grid Powerwall we wired in a 12V power supply to the input terminals and
plugged the other side into a grid-connected outlet.    

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:offgridso...@sti.net
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to