7.6 kW.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
r...@solartechvt.com
Sent: Wednesday, July 22, 2020 7:25 AM
To: 'RE-wrenches' <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Tesla Powerwall 2.0 - AC Coupling

Considering the lack of public info available for the Powerwall, does anyone 
have any insight into the AC coupling limits for a single Powerwall?
For example, can we AC couple 10kw Solar Edge to a single Powerwall?
Thanks
Rich

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Ray
Sent: Tuesday, July 21, 2020 8:39 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Tesla Powerwall 2.0 - Experience?/Generator charging


That's going to be long extension cord for most off grid projects.......

Ray Walters

Remote Solar

303 505-8760
On 7/21/20 12:11 PM, Matt Partymiller wrote:
Jay,

The Tesla Gateway has a 12v input terminal for boot up.  To startup my off grid 
Powerwall we wired in a 12V power supply to the input terminals and plugged the 
other side into a grid-connected outlet.