I've seen that same issue too. I assumed that the battery charging, house
base loads, and the microwave were too much power for the small generator.
The voltage drops big time which I assume is what was causing the issue
with the microwave and most likely with the dryer too.

On Sat, Aug 15, 2020 at 11:51 AM Dan Fink <danbo...@gmail.com> wrote:

> I have the same problem at my place, and a couple client's systems, with
> Magnum inverter/chargers and small ~2-3kw generators (not just Honda). But
> the problem appliance is microwave ovens, doesn't matter which microwave
> brand. They run fine straight from the generator, and fine from the
> inverter with no generator running, but make a strange, loud hum, dim
> internal light, and food doesn't heat if the generator is also charging the
> battery bank. I'll try to figure out how to capture a waveform photo with
> my scopemeter and post it.
> Dan Fink
> Executive Director, Buckville Energy Consulting
> NABCEP PV Associate
> NABCEP Certified PV System Inspector
> IREC Certified Instructorâ„¢ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP Registered Continuing Education Providers
> d <dan.f...@greendustrialtraining.com>anbo...@gmail.com
> 970-672-4342
>
>
>
>
> On Sat, Aug 15, 2020 at 9:37 AM Kent Osterberg <k...@coveoregon.com>
> wrote:
>
>> Matt,
>>
>> I haven't looked at what the FXR does to the waveform of a 3000-watt
>> Honda, but I have used an oscilloscope to look at the waveform of a small
>> generator while an FX inverter is charging batteries -- it pretty much
>> makes an ugly mess of the voltage waveform. Not surprised to hear that some
>> loads don't like to operate when the FXR is charging batteries from a small
>> generator. The FX charger has a poor power factor and little filtering of
>> the current waveform, it is a tough load on a small generator. The
>> generator responds with lots of harmonic voltages and high frequency noise.
>>
>> Kent Osterberg
>> Blue Mountain Solar
>>
>>
>> On 8/15/2020 8:06 AM, Matt Sherald wrote:
>>
>> Hello All,
>>
>> My curiosity was piqued by a recent customer complaint.  I'm hoping
>> someone has bumped up against this issue before.
>>
>> The customer has a OB FXR2812 and a 3,000W Honda gen.
>> Her gas clothes dryer runs just fine off the OB inverter.
>> It runs properly on the Honda gen (when the inverter is bypassed)
>> It will not run when the gen is on and battery charging is taking place.
>>
>> All the other AC loads (including the washing machine) run properly
>> during battery charging with the gen.
>> The OB inverter replaced an old Trace unit.  The dryer worked as it
>> should with the Trace during battery charging.
>>
>> Any thoughts are greatly appreciated.  Thanks in advance!
>>
>> --
>> Matt Sherald
>> PIMBY Energy, LLC
>> NABCEP Certified Solar PV Installer®
>> 304-704-5943
>>
>> www.getpimby.blogspot.com
>> www.getpimby.com
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
*Will White*
Curriculum Developer


e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092

NABCEP Certified PV Installation Professional
# 093006-34
Do you envision a world powered by renewable energy? Be the change
<http://solarenergy.org/donate>.
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to