Dave,

I would first suspect the generator, not the inverter. Check its output voltage and Hz under load. If it's overloading, either (or both) voltage and frequency will drop below the acceptable range and the inverter will unlatch its input relays, wait for a bit, relatch and ramp up input amps until it again overloads and the cycle repeats. You may reduce either (or both) charging amps and overall input amps, broaden the frequency and minimum voltage acceptance ranges (I don't recommend this), adjust the AC output voltage of the generator, or advise them to get a better gennie.

Allan

On 12/15/2020 11:14 AM, Dave Tedeyan wrote:
Hi All,

I am going to service a system where the homeowner is telling me that their Conext SW4048 had been working fine for 14 months, and then all of a sudden recently stopped being able to charge the batteries from the generator. It is an off grid system.

The inverter would start charging the batteries, but then about a minute later they would hear a relay click and the charging would stop. Then it would just keep cycling. If they turned everything off for a while, they could then turn it back on and charge for maybe 10 minutes before it would start cycling. They just have a crappy 4kw generator from Harbor Freight.

I have not laid my own eyes on it yet, but will be there in the next day or two. Just wondering if anyone has experienced these symptoms and have a good idea of what to look for first.

Thanks!
-Dave

*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. _607.277.1118 x121_  f. 607.277.2119
www.taitem.com <http://www.taitem.com>

Solar •Sustainability • Energy • Design
Certified B-Corporation since 2013

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--

*Allan Sindelar*
al...@sindelarsolar.com <mailto:al...@sindelarsolar.com>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to