Subject: Re: [RE-wrenches] Conext SW4048 not charging from generator

 

Definitely the generator.  Harbor Freight?  4 kW into a 4 kW charger?  What's 
the altitude?   I believe that 4 kW generator is actually only 3.5 kW 
continuous rated.   By the time you derate for altitude, and then account for 
the generator not being built to be a prime power unit, its probably reasonable 
to derate it 50%.  Then yet another thing,  those gennies are 240/120 so you 
only get half the rated power at 120 vac, and it unbalances the load on the 
generator.  Is that Conext 240/ 120 or just 120vac ?   

Its just going to be a head ache for everyone until they buy something much 
better.  They really need something in the 6.5 kW to 9 kW range, and 240 to 120 
transformer if the Conext is not the 240/120 model, so that the generator is 
loaded evenly. 

Ray Walters
Remote Solar
303 505-8760

On 12/15/20 1:57 PM, Sindelar Solar wrote:

Dave,

I would first suspect the generator, not the inverter. Check its output voltage 
and Hz under load. If it's overloading, either (or both) voltage and frequency 
will drop below the acceptable range and the inverter will unlatch its input 
relays, wait for a bit, relatch and ramp up input amps until it again overloads 
and the cycle repeats. You may reduce either (or both) charging amps and 
overall input amps, broaden the frequency and minimum voltage acceptance ranges 
(I don't recommend this), adjust the AC output voltage of the generator, or 
advise them to get a better gennie.

Allan

On 12/15/2020 11:14 AM, Dave Tedeyan wrote:

Hi All,  

 

I am going to service a system where the homeowner is telling me that their 
Conext SW4048 had been working fine for 14 months, and then all of a sudden 
recently stopped being able to charge the batteries from the generator. It is 
an off grid system. 

 

The inverter would start charging the batteries, but then about a minute later 
they would hear a relay click and the charging would stop. Then it would just 
keep cycling. If they turned everything off for a while, they could then turn 
it back on and charge for maybe 10 minutes before it would start cycling. They 
just have a crappy 4kw generator from Harbor Freight.

 

I have not laid my own eyes on it yet, but will be there in the next day or 
two. Just wondering if anyone has experienced these symptoms and have a good 
idea of what to look for first.

 

Thanks!

-Dave


 

Dave Tedeyan, PE

Senior Engineer | Taitem Engineering, PC



110 South Albany Street | Ithaca, NY 14850

o. 607.277.1118 x121  f. 607.277.2119

www.taitem.com <http://www.taitem.com> 

 

Solar • Sustainability • Energy • Design

Certified B-Corporation since 2013





_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
http://www.members.re-wrenches.org
 

-- 



Allan Sindelar
 <mailto:al...@sindelarsolar.com> al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 





_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
http://www.members.re-wrenches.org
 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to