I would slide 3" of 3/4" 600 volt heat shrink over the end of a stainless steel 
hose clamp and secure the wire to the rail where it comes out of the conduit at 
each end. Chris Worcester chris@solarwindworks.com530-448-9692Sent from my 
Samsung Galaxy s9.
-------- Original message --------From: Dave Tedeyan <d...@sungineersolar.com> 
Date: 3/22/22  1:44 PM  (GMT-08:00) To: RE-wrenches 
<re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Wires between arrays 
Hi All, I have an inspector giving me a hard time about wire management between 
two ground mounted arrays. The racking is Unirac GFT, and the system was too 
large to have one continuous array. So there are two arrays, side by side, with 
only a 1' gap between the rails and modules from the two separate arrays. We 
jumped the PV wire between the arrays through a short section of PVC for 
protection, and the wires are secured to the rails about a foot past the PVC on 
either end. The inspector is citing the following:----Array conductors found 
disconnected or
improperly connected, which may be
causing portions of the array to be
inoperable and/or pose a shock hazard.----They say that they are citing this 
because there is no strain relief as the wires enter and exit the 18" piece of 
conduit. My question to you all is, do you know of any code reference that says 
that this setup is or is not okay? I would also be curious to hear what others 
do to span a 1' gap on a ground mount. It almost seems as if I just left the 
conductors exposed for that gap, there would have been no problem.I attached a 
couple of photos to help with my written description.I appreciate the knowledge 
of this hive mind!Cheers, Dave-- Dave Tedeyan, P.E.Owner | Sungineer Solarp: he 
| him | hisa: 1653 Slaterville Rd. | Ithaca, NY 14850w: 
www.sungineersolar.comc: (607) 288-2898
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to