This may be far fetched but I have encountered good voltage & low amperage =
no amperage from solar arrays that baffled me on T/S on others systems &
ultimately:
We had voltage & low output amperage to no amperage.
Turns out there was a junction box that had been forgotten about in the
crawl space with never tightened split bolts that were crispy black from
arcing.
There was enough contact for voltage readings & not enough for any amps to
flow.
Double check all connections?
___________________________________________________
Dana Orzel c- 2087217003 e - d...@solarwork.com
--- Begin Message ---
Charger Limit is also set to 30 amps. We tried raising the total AC input limit
to max and that may have helped increase the chargeby 200-300watts up to 4.8kw
but thats it. By my math we should be able to see about 6KW+/- of charging
power.
We are using Generator input mode I believe. We will try switching to Support
mode and see if that helps.
By the way batteries are 8- Simpliphi 3.8.
Sent from my Galaxy
-------- Original message --------
From: Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org>
Date: 10/25/23 4:43 PM (GMT-05:00)
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Jay <jay.pe...@gmail.com>
Subject: Re: [RE-wrenches] Outback Radian Generator Charging
What is the charger ac limit set to?
Jay
On Oct 25, 2023, at 2:38 PM, Mac Lewis via RE-wrenches
<re-wrenches@lists.re-wrenches.org> wrote:
Hi Amos,
What input mode are you using?
Try switching to "support" mode and see if the charging current increases.
On Wed, Oct 25, 2023, 1:24 PM Amos Post via RE-wrenches
<re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> >
wrote:
Hello wrenches,
We just installed an GS8048a Radian build with Mate 3SL controller (no Optics).
We are having some with charging from the generator, as the generator charging
seems to be limited to about 4500Watts +/- (20amps AC) when charging through
the Radian. It is a Kohler 8.5RES generator and we have the AC input limit set
to 30amps and the Gen input set to 30amps. The house load is only about
200Watts when we are charging. The system is at 2200ft of elevation, but I
don’t know if that makes enough of a difference.
The Gen output voltage seems pretty good and holds around 234V-236V while
charging.
Any thoughts as to why it may be limiting would be appreciated.
Thanks,
Amos
Amos Post
Integrity Energy
W 802.763.7023
C 802.291.2188
<http://www.ienergyvt.com> ienergyVT.com
Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
<IE LOGO 150x78.jpg>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--- End Message ---
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org