good point.  
For GT OB systems I have removed the side screens for better air flow and I’ve 
also taken the covers off and used external fans to cool them.

They just were not designed to run anywhere near rated capacity for long 
periods of time, they don’t have enough air cooling.

> On May 12, 2025, at 10:41 AM, Ray Walters via RE-wrenches 
> <[email protected]> wrote:
> 
> Is inverter 2 on top?  The top inverter in an Outback dual stack always runs 
> hotter, because the heat from the bottom inverter is adding to its own heat.  
> I used to see that consistently cause board failures on the top inverter more 
> often, if the whole system was running close to capacity.
> 
> Ray Walters
> 
> On 5/12/2025 7:56 AM, Amos Post via RE-wrenches wrote:
>> UPDATE:
>> 
>> So far so good and since replacing the fuse holder, fuse #3 has not blown 
>> again.
>> 
>> ANOTHER ISSUE:
>> 
>> Inverter 2 runs hotter than inverter 1.   Reminder this is grid-tied system 
>> with 2-GVFX3648’s in series for 120/240V.   The fan on inverter #2 had 
>> malfunctioned, but I was able to replace it and get that going again.  Even 
>> with the replaced fan, inverter #2 is still running noticeably hotter.  My 
>> understanding is that both inverters in this system are essentially 
>> “Masters”, since this is grid-tied.  Shouldn’t the load/generation be split 
>> between the two and hence they run equally as hot?  I did check the stacking 
>> and they were both set to “Master” which is I think what they recommended 
>> for grid-tie.  I tried switching the ports on the Hub that they are plugged 
>> into to see if that would change anything, but no change.  I did also 
>> noticed while I was there last week that while both inverters had the solid 
>> yellow “AC IN” light on, inverter #2’s green “Inverter” light was always on, 
>> while inverter #1’s green “Inverter” seemed to come and go…
>> 
>> Any ideas?
>> 
>> Thanks as always,
>> Amos
>> 
>> 
>> 
>> 
>> 
>> <IE LOGO 150x78.jpg>
>> 
>>        Amos Post
>>    Integrity Energy
>>   W 802.763.7023
>>    C 802.291.2188
>>     ienergyVT.com <http://www.ienergyvt.com/>
>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>> 
>>> On Apr 15, 2025, at 8:40 AM, Amos Post <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> 
>>> Hi all,
>>> 
>>> I decided to start with the simple stuff.  While I don’t have a string 
>>> curve tester (I should have one), yesterday I tested strings 1,2,3 
>>> individually under load.  String 3 is the one that’s been blowing the fuse. 
>>>  I did not test strings 4-6 which are on a separate charge controller and 
>>> combiner.  Here are the results:
>>> 
>>> String 1- 7.1A at 76V
>>> String 2- 7.77Aat 79V
>>> String 3-7.13A at 78.3V
>>> 
>>> I did notice that the second charge controller with strings 4-6 was running 
>>> about 100watts more (1800w vs 1700w).  The conditions were clear blue 
>>> skies.  I replaced the fuse holder and fuse.  If it blows again I’ll try 
>>> switching strings to see if it follows…
>>> 
>>> Thanks for your feedback and I’ll keep ya’ll posted.
>>> 
>>> Amos
>>> 
>>> 
>>> <IE LOGO 150x78.jpg>
>>> 
>>>        Amos Post
>>>    Integrity Energy
>>>   W 802.763.7023
>>>    C 802.291.2188
>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>> 
>>>> On Apr 11, 2025, at 4:07 PM, Jerry Shafer via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>> 
>>>> Wrenches, Amos, blowing of a 15 amp fuse is not a ghost in the machine, it 
>>>> is an actual issue no way around it, shorted modules, shorted diodes, in 
>>>> most cases it's a home run, way back when USE-2 white wure was failing and 
>>>> would crack and break off mostly this would result in a GFI trip. The fuse 
>>>> is blowing because of over current and a single string of your vintage 
>>>> will max out at far less than 10 amps but the other two strings will back 
>>>> feed this fuse with close to 20 then pop.
>>>> Sharp had module failures resulting in cell shorts, look very close there. 
>>>> I have inspected arrays with extreme exposure differences, this will 
>>>> effect performance but should not pop a fuse. Do you have a module string 
>>>> curve tester, this very well may show an issue of the string but eyes on 
>>>> the array is required to located the cause.
>>>> I have seen nails through wires, conduit, racking in contact with the back 
>>>> of the module but this will trip the GFI breaker not the string fuse.
>>>> Fun times.
>>>> 
>>>> 
>>>> On Fri, Apr 11, 2025, 12:49 PM david quattro via RE-wrenches 
>>>> <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>>> One time I had similar, but different problem:  1 Amp ground fault fuse 
>>>>> consistently blowing, sometimes after 1 day sometimes after weeks/months. 
>>>>>  I tried everything - replaced home runs, checked VOC, VMP, swapped DC 
>>>>> input into a different inverter, etc. it kept coming back to this one 
>>>>> string. I checked every module VOC, ISC, every connection, no pinched 
>>>>> wires, no discernible problem, but fuse blowing.
>>>>>    Luckily it was a medium size commercial job (on a fire station) so I 
>>>>> was able to scatter all the modules of this suspect string all over the 
>>>>> roof, and carefully track where I had put them. That’s when the problem 
>>>>> went away and never came back..😂
>>>>>   Best I could figure was a slight manufacturing error that had a 
>>>>> compounding/cumulative effect. So once I got those consecutive serial 
>>>>> numbers away from each other no more problem. Either that or the fire 
>>>>> chief was fucking with me and he was burning out the fuses, which I doubt 
>>>>> 
>>>>> 
>>>>> 
>>>>> On Fri, Apr 11, 2025 at 8:05 AM Mac Lewis via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>>> Hello Amos,
>>>>>> 
>>>>>> Have you checked for voltage imbalance for each string?  If you have a 
>>>>>> bad diode, that string may run low on voltage and be trying to send 
>>>>>> current toward the weak string (this is the reason you have these 
>>>>>> breakers).  I'd run each string independently and see what Vmp is.  If 
>>>>>> you are missing some voltage that may be a clue.  You can also 
>>>>>> independently clamp each string during operation.
>>>>>> 
>>>>>> I like IR cameras for this type of thing.  It may just be a bad 
>>>>>> connection, heat build up, fuse holder issue.
>>>>>> 
>>>>>> Let us know what you find out
>>>>>> 
>>>>>> On Fri, Apr 11, 2025 at 8:07 AM Amos Post via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>>> Hi Wrenches,
>>>>>>> 
>>>>>>> I have a bit of a puzzler that I’m trying to get sorted out.  I’ve been 
>>>>>>> servicing a Grid-Tied Battery Backup system that’s about 17-18 years 
>>>>>>> old.  The system comprises of 2-GVFX3648s in series, with 2-MX60(at 
>>>>>>> least I think they are 60s) CC’s.  Each CC has 3 strings of 3 tied to 
>>>>>>> it, and each string has a 15A in-line 600V fuse.  The modules are I 
>>>>>>> believe are like 230/240Watt 60 cell modules (sorry I don’t have 
>>>>>>> pictures/specifics).   We replaced the flooded batteries with AGMs 
>>>>>>> about a year and a half ago.  
>>>>>>> 
>>>>>>> The situation is one of the 15A string fuses keeps blowing.  It’s now 
>>>>>>> happened 3 times and its the same fuse every time.  First we just 
>>>>>>> replaced the fuse and under the surge/lightning assumption.  Fuse blew 
>>>>>>> again.  Then I thought I found the culprit.  The #6 PV output from the 
>>>>>>> combiner to the PV input breaker for the CC was a bit darkened and very 
>>>>>>> warm to the touch when I replaced the fuse the first time.   So I 
>>>>>>> though maybe it was a loose connection on that lug and that caused 
>>>>>>> everything to heat up and eventually blow the fuse.  I cut and stripped 
>>>>>>> the wire back and cleaned the lug and re-seated the wire in the lug.  
>>>>>>> Fuse blew again within a few months time.  I then checked the Junction 
>>>>>>> box on the roof where the USE-2 wire connects to THHN, and did a visual 
>>>>>>> inspection of all the wiring on the roof.  All of the Jbox connections 
>>>>>>> and everything on the roof “looked” ok.  I have also check all of the 
>>>>>>> connections inside the Outback DC load center, and they look ok.  Fuse 
>>>>>>> replaced 3rd time and then it blew again.  
>>>>>>> 
>>>>>>> Before I take all of the panels off the rack, check panels, re-check 
>>>>>>> string wiring on the roof, is there anything else I should be checking? 
>>>>>>>  Seems like that warm wire in the Combiner box is telling me something 
>>>>>>> but I can’t figure out what...I believe this is a new problem in the 
>>>>>>> last 2-3 years but we are not 100% sure when the problem first came up…
>>>>>>> 
>>>>>>> As always, thanks for your help/ suggestions!
>>>>>>> Amos
>>>>>>> 
>>>>>>> 
>>>>>>> <IE LOGO 150x78.jpg>
>>>>>>> 
>>>>>>>        Amos Post
>>>>>>>    Integrity Energy
>>>>>>>   W 802.763.7023
>>>>>>>    C 802.291.2188
>>>>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>> 
>>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>>> <http://re-wrenches.org/>
>>>>>>> 
>>>>>>> List Address: [email protected] 
>>>>>>> <mailto:[email protected]>
>>>>>>> 
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>>> the other:
>>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>> 
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> --
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> Mac Lewis
>>>>>> 
>>>>>> "Yo solo sé que no sé nada." -Sócrates
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to