Hey all,

To close the loop on this, I doesn’t look like its a “Power Save” setting as 
those are available on Grid-Tied FX’s.  I went yesterday and confirmed that 
just Inverter #2 is pushing power when grid-tied ( 21A at 120V  is what I 
tested at the time), however both start inverting (indicated by green LED) when 
grid-goes down.  But it seems to be functioning like the Power Save modes and 
shutting down Inverter #1 when grid-tied.  

My best guess is since the array is only 4.2KW and a shallow roof and never 
really hitting that 4.2KW peak (2.0-3.0KW typical on a sunny day), it’s only 
running the power through 1 of the inverters because it only needs to run 1.   
There are no errors, or warnings on Inverter 1, and what’s weird is even when I 
switch the inverter ports on the Hub (swap 1 and 2), Inverter 2 is still the 
only one that’s inverting typically.  The exception was when I was testing I 
shut off grid power for a few minutes to test the backup function, during which 
the batteries did an absorb charge.  When I reconnected the grid the inverters 
started to sell some of that battery power(for a minute), along with the PV, 
down to the sell voltage.  Then once the voltage leveled out, inverter #1 went 
to sleep again.

If this was Myth Busters I would say “Plausible” because I’m not really sure… :)

Thanks for your brains!
Amos




       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    ienergyVT.com <http://www.ienergyvt.com/>
        Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>

> On May 12, 2025, at 12:53 PM, Amos Post <[email protected]> wrote:
> 
> Oh I forgot to mention the inverters are side x side on 2 individual Panels….
> <IE LOGO 150x78.jpg>
> 
>        Amos Post
>    Integrity Energy
>   W 802.763.7023
>    C 802.291.2188
>     ienergyVT.com <http://www.ienergyvt.com/>
>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
> 
>> On May 12, 2025, at 12:48 PM, jay via RE-wrenches 
>> <[email protected] 
>> <mailto:[email protected]>> wrote:
>> 
>> good point.  
>> For GT OB systems I have removed the side screens for better air flow and 
>> I’ve also taken the covers off and used external fans to cool them.
>> 
>> They just were not designed to run anywhere near rated capacity for long 
>> periods of time, they don’t have enough air cooling.
>> 
>>> On May 12, 2025, at 10:41 AM, Ray Walters via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> 
>>> Is inverter 2 on top?  The top inverter in an Outback dual stack always 
>>> runs hotter, because the heat from the bottom inverter is adding to its own 
>>> heat.  I used to see that consistently cause board failures on the top 
>>> inverter more often, if the whole system was running close to capacity.
>>> 
>>> Ray Walters 
>>> 
>>> On 5/12/2025 7:56 AM, Amos Post via RE-wrenches wrote:
>>>> UPDATE:
>>>> 
>>>> So far so good and since replacing the fuse holder, fuse #3 has not blown 
>>>> again.
>>>> 
>>>> ANOTHER ISSUE:
>>>> 
>>>> Inverter 2 runs hotter than inverter 1.   Reminder this is grid-tied 
>>>> system with 2-GVFX3648’s in series for 120/240V.   The fan on inverter #2 
>>>> had malfunctioned, but I was able to replace it and get that going again.  
>>>> Even with the replaced fan, inverter #2 is still running noticeably 
>>>> hotter.  My understanding is that both inverters in this system are 
>>>> essentially “Masters”, since this is grid-tied.  Shouldn’t the 
>>>> load/generation be split between the two and hence they run equally as 
>>>> hot?  I did check the stacking and they were both set to “Master” which is 
>>>> I think what they recommended for grid-tie.  I tried switching the ports 
>>>> on the Hub that they are plugged into to see if that would change 
>>>> anything, but no change.  I did also noticed while I was there last week 
>>>> that while both inverters had the solid yellow “AC IN” light on, inverter 
>>>> #2’s green “Inverter” light was always on, while inverter #1’s green 
>>>> “Inverter” seemed to come and go…
>>>> 
>>>> Any ideas?
>>>> 
>>>> Thanks as always,
>>>> Amos
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> <IE LOGO 150x78.jpg>
>>>> 
>>>>        Amos Post
>>>>    Integrity Energy
>>>>   W 802.763.7023
>>>>    C 802.291.2188
>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>> 
>>>>> On Apr 15, 2025, at 8:40 AM, Amos Post <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> 
>>>>> Hi all,
>>>>> 
>>>>> I decided to start with the simple stuff.  While I don’t have a string 
>>>>> curve tester (I should have one), yesterday I tested strings 1,2,3 
>>>>> individually under load.  String 3 is the one that’s been blowing the 
>>>>> fuse.  I did not test strings 4-6 which are on a separate charge 
>>>>> controller and combiner.  Here are the results:
>>>>> 
>>>>> String 1- 7.1A at 76V
>>>>> String 2- 7.77Aat 79V
>>>>> String 3-7.13A at 78.3V
>>>>> 
>>>>> I did notice that the second charge controller with strings 4-6 was 
>>>>> running about 100watts more (1800w vs 1700w).  The conditions were clear 
>>>>> blue skies.  I replaced the fuse holder and fuse.  If it blows again I’ll 
>>>>> try switching strings to see if it follows…
>>>>> 
>>>>> Thanks for your feedback and I’ll keep ya’ll posted.
>>>>> 
>>>>> Amos
>>>>> 
>>>>> 
>>>>> <IE LOGO 150x78.jpg>
>>>>> 
>>>>>        Amos Post
>>>>>    Integrity Energy
>>>>>   W 802.763.7023
>>>>>    C 802.291.2188
>>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>>> 
>>>>>> On Apr 11, 2025, at 4:07 PM, Jerry Shafer via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>> 
>>>>>> Wrenches, Amos, blowing of a 15 amp fuse is not a ghost in the machine, 
>>>>>> it is an actual issue no way around it, shorted modules, shorted diodes, 
>>>>>> in most cases it's a home run, way back when USE-2 white wure was 
>>>>>> failing and would crack and break off mostly this would result in a GFI 
>>>>>> trip. The fuse is blowing because of over current and a single string of 
>>>>>> your vintage will max out at far less than 10 amps but the other two 
>>>>>> strings will back feed this fuse with close to 20 then pop.
>>>>>> Sharp had module failures resulting in cell shorts, look very close 
>>>>>> there. I have inspected arrays with extreme exposure differences, this 
>>>>>> will effect performance but should not pop a fuse. Do you have a module 
>>>>>> string curve tester, this very well may show an issue of the string but 
>>>>>> eyes on the array is required to located the cause.
>>>>>> I have seen nails through wires, conduit, racking in contact with the 
>>>>>> back of the module but this will trip the GFI breaker not the string 
>>>>>> fuse.
>>>>>> Fun times.
>>>>>> 
>>>>>> 
>>>>>> On Fri, Apr 11, 2025, 12:49 PM david quattro via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>> One time I had similar, but different problem:  1 Amp ground fault fuse 
>>>>>> consistently blowing, sometimes after 1 day sometimes after 
>>>>>> weeks/months.  I tried everything - replaced home runs, checked VOC, 
>>>>>> VMP, swapped DC input into a different inverter, etc. it kept coming 
>>>>>> back to this one string. I checked every module VOC, ISC, every 
>>>>>> connection, no pinched wires, no discernible problem, but fuse blowing.
>>>>>>    Luckily it was a medium size commercial job (on a fire station) so I 
>>>>>> was able to scatter all the modules of this suspect string all over the 
>>>>>> roof, and carefully track where I had put them. That’s when the problem 
>>>>>> went away and never came back..😂
>>>>>>   Best I could figure was a slight manufacturing error that had a 
>>>>>> compounding/cumulative effect. So once I got those consecutive serial 
>>>>>> numbers away from each other no more problem. Either that or the fire 
>>>>>> chief was fucking with me and he was burning out the fuses, which I 
>>>>>> doubt 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> On Fri, Apr 11, 2025 at 8:05 AM Mac Lewis via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>> Hello Amos,
>>>>>> 
>>>>>> Have you checked for voltage imbalance for each string?  If you have a 
>>>>>> bad diode, that string may run low on voltage and be trying to send 
>>>>>> current toward the weak string (this is the reason you have these 
>>>>>> breakers).  I'd run each string independently and see what Vmp is.  If 
>>>>>> you are missing some voltage that may be a clue.  You can also 
>>>>>> independently clamp each string during operation.
>>>>>> 
>>>>>> I like IR cameras for this type of thing.  It may just be a bad 
>>>>>> connection, heat build up, fuse holder issue.
>>>>>> 
>>>>>> Let us know what you find out
>>>>>> 
>>>>>> On Fri, Apr 11, 2025 at 8:07 AM Amos Post via RE-wrenches 
>>>>>> <[email protected] 
>>>>>> <mailto:[email protected]>> wrote:
>>>>>> Hi Wrenches,
>>>>>> 
>>>>>> I have a bit of a puzzler that I’m trying to get sorted out.  I’ve been 
>>>>>> servicing a Grid-Tied Battery Backup system that’s about 17-18 years 
>>>>>> old.  The system comprises of 2-GVFX3648s in series, with 2-MX60(at 
>>>>>> least I think they are 60s) CC’s.  Each CC has 3 strings of 3 tied to 
>>>>>> it, and each string has a 15A in-line 600V fuse.  The modules are I 
>>>>>> believe are like 230/240Watt 60 cell modules (sorry I don’t have 
>>>>>> pictures/specifics).   We replaced the flooded batteries with AGMs about 
>>>>>> a year and a half ago.  
>>>>>> 
>>>>>> The situation is one of the 15A string fuses keeps blowing.  It’s now 
>>>>>> happened 3 times and its the same fuse every time.  First we just 
>>>>>> replaced the fuse and under the surge/lightning assumption.  Fuse blew 
>>>>>> again.  Then I thought I found the culprit.  The #6 PV output from the 
>>>>>> combiner to the PV input breaker for the CC was a bit darkened and very 
>>>>>> warm to the touch when I replaced the fuse the first time.   So I though 
>>>>>> maybe it was a loose connection on that lug and that caused everything 
>>>>>> to heat up and eventually blow the fuse.  I cut and stripped the wire 
>>>>>> back and cleaned the lug and re-seated the wire in the lug.  Fuse blew 
>>>>>> again within a few months time.  I then checked the Junction box on the 
>>>>>> roof where the USE-2 wire connects to THHN, and did a visual inspection 
>>>>>> of all the wiring on the roof.  All of the Jbox connections and 
>>>>>> everything on the roof “looked” ok.  I have also check all of the 
>>>>>> connections inside the Outback DC load center, and they look ok.  Fuse 
>>>>>> replaced 3rd time and then it blew again.  
>>>>>> 
>>>>>> Before I take all of the panels off the rack, check panels, re-check 
>>>>>> string wiring on the roof, is there anything else I should be checking?  
>>>>>> Seems like that warm wire in the Combiner box is telling me something 
>>>>>> but I can’t figure out what...I believe this is a new problem in the 
>>>>>> last 2-3 years but we are not 100% sure when the problem first came up…
>>>>>> 
>>>>>> As always, thanks for your help/ suggestions!
>>>>>> Amos
>>>>>> 
>>>>>> 
>>>>>> <IE LOGO 150x78.jpg>
>>>>>> 
>>>>>>        Amos Post
>>>>>>    Integrity Energy
>>>>>>   W 802.763.7023
>>>>>>    C 802.291.2188
>>>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> -- 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> Mac Lewis
>>>>>> 
>>>>>> "Yo solo sé que no sé nada." -Sócrates
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>>> <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: [email protected] 
>>>>>> <mailto:[email protected]>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>> 
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> <http://re-wrenches.org/>
>>>> 
>>>> List Address: [email protected] 
>>>> <mailto:[email protected]>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other:
>>>> https://www.mail-archive.com/[email protected]/ 
>>>> <https://www.mail-archive.com/[email protected]/>
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm 
>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to