Oh I forgot to mention the inverters are side x side on 2 individual Panels….


       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    ienergyVT.com <http://www.ienergyvt.com/>
        Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>

> On May 12, 2025, at 12:48 PM, jay via RE-wrenches 
> <[email protected]> wrote:
> 
> good point.  
> For GT OB systems I have removed the side screens for better air flow and 
> I’ve also taken the covers off and used external fans to cool them.
> 
> They just were not designed to run anywhere near rated capacity for long 
> periods of time, they don’t have enough air cooling.
> 
>> On May 12, 2025, at 10:41 AM, Ray Walters via RE-wrenches 
>> <[email protected]> wrote:
>> 
>> Is inverter 2 on top?  The top inverter in an Outback dual stack always runs 
>> hotter, because the heat from the bottom inverter is adding to its own heat. 
>>  I used to see that consistently cause board failures on the top inverter 
>> more often, if the whole system was running close to capacity.
>> 
>> Ray Walters 
>> 
>> On 5/12/2025 7:56 AM, Amos Post via RE-wrenches wrote:
>>> UPDATE:
>>> 
>>> So far so good and since replacing the fuse holder, fuse #3 has not blown 
>>> again.
>>> 
>>> ANOTHER ISSUE:
>>> 
>>> Inverter 2 runs hotter than inverter 1.   Reminder this is grid-tied system 
>>> with 2-GVFX3648’s in series for 120/240V.   The fan on inverter #2 had 
>>> malfunctioned, but I was able to replace it and get that going again.  Even 
>>> with the replaced fan, inverter #2 is still running noticeably hotter.  My 
>>> understanding is that both inverters in this system are essentially 
>>> “Masters”, since this is grid-tied.  Shouldn’t the load/generation be split 
>>> between the two and hence they run equally as hot?  I did check the 
>>> stacking and they were both set to “Master” which is I think what they 
>>> recommended for grid-tie.  I tried switching the ports on the Hub that they 
>>> are plugged into to see if that would change anything, but no change.  I 
>>> did also noticed while I was there last week that while both inverters had 
>>> the solid yellow “AC IN” light on, inverter #2’s green “Inverter” light was 
>>> always on, while inverter #1’s green “Inverter” seemed to come and go…
>>> 
>>> Any ideas?
>>> 
>>> Thanks as always,
>>> Amos
>>> 
>>> 
>>> 
>>> 
>>> 
>>> <IE LOGO 150x78.jpg>
>>> 
>>>        Amos Post
>>>    Integrity Energy
>>>   W 802.763.7023
>>>    C 802.291.2188
>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>> 
>>>> On Apr 15, 2025, at 8:40 AM, Amos Post <[email protected] 
>>>> <mailto:[email protected]>> wrote:
>>>> 
>>>> Hi all,
>>>> 
>>>> I decided to start with the simple stuff.  While I don’t have a string 
>>>> curve tester (I should have one), yesterday I tested strings 1,2,3 
>>>> individually under load.  String 3 is the one that’s been blowing the 
>>>> fuse.  I did not test strings 4-6 which are on a separate charge 
>>>> controller and combiner.  Here are the results:
>>>> 
>>>> String 1- 7.1A at 76V
>>>> String 2- 7.77Aat 79V
>>>> String 3-7.13A at 78.3V
>>>> 
>>>> I did notice that the second charge controller with strings 4-6 was 
>>>> running about 100watts more (1800w vs 1700w).  The conditions were clear 
>>>> blue skies.  I replaced the fuse holder and fuse.  If it blows again I’ll 
>>>> try switching strings to see if it follows…
>>>> 
>>>> Thanks for your feedback and I’ll keep ya’ll posted.
>>>> 
>>>> Amos
>>>> 
>>>> 
>>>> <IE LOGO 150x78.jpg>
>>>> 
>>>>        Amos Post
>>>>    Integrity Energy
>>>>   W 802.763.7023
>>>>    C 802.291.2188
>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>> 
>>>>> On Apr 11, 2025, at 4:07 PM, Jerry Shafer via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> 
>>>>> Wrenches, Amos, blowing of a 15 amp fuse is not a ghost in the machine, 
>>>>> it is an actual issue no way around it, shorted modules, shorted diodes, 
>>>>> in most cases it's a home run, way back when USE-2 white wure was failing 
>>>>> and would crack and break off mostly this would result in a GFI trip. The 
>>>>> fuse is blowing because of over current and a single string of your 
>>>>> vintage will max out at far less than 10 amps but the other two strings 
>>>>> will back feed this fuse with close to 20 then pop.
>>>>> Sharp had module failures resulting in cell shorts, look very close 
>>>>> there. I have inspected arrays with extreme exposure differences, this 
>>>>> will effect performance but should not pop a fuse. Do you have a module 
>>>>> string curve tester, this very well may show an issue of the string but 
>>>>> eyes on the array is required to located the cause.
>>>>> I have seen nails through wires, conduit, racking in contact with the 
>>>>> back of the module but this will trip the GFI breaker not the string fuse.
>>>>> Fun times.
>>>>> 
>>>>> 
>>>>> On Fri, Apr 11, 2025, 12:49 PM david quattro via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> One time I had similar, but different problem:  1 Amp ground fault fuse 
>>>>> consistently blowing, sometimes after 1 day sometimes after weeks/months. 
>>>>>  I tried everything - replaced home runs, checked VOC, VMP, swapped DC 
>>>>> input into a different inverter, etc. it kept coming back to this one 
>>>>> string. I checked every module VOC, ISC, every connection, no pinched 
>>>>> wires, no discernible problem, but fuse blowing.
>>>>>    Luckily it was a medium size commercial job (on a fire station) so I 
>>>>> was able to scatter all the modules of this suspect string all over the 
>>>>> roof, and carefully track where I had put them. That’s when the problem 
>>>>> went away and never came back..😂
>>>>>   Best I could figure was a slight manufacturing error that had a 
>>>>> compounding/cumulative effect. So once I got those consecutive serial 
>>>>> numbers away from each other no more problem. Either that or the fire 
>>>>> chief was fucking with me and he was burning out the fuses, which I doubt 
>>>>> 
>>>>> 
>>>>> 
>>>>> On Fri, Apr 11, 2025 at 8:05 AM Mac Lewis via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> Hello Amos,
>>>>> 
>>>>> Have you checked for voltage imbalance for each string?  If you have a 
>>>>> bad diode, that string may run low on voltage and be trying to send 
>>>>> current toward the weak string (this is the reason you have these 
>>>>> breakers).  I'd run each string independently and see what Vmp is.  If 
>>>>> you are missing some voltage that may be a clue.  You can also 
>>>>> independently clamp each string during operation.
>>>>> 
>>>>> I like IR cameras for this type of thing.  It may just be a bad 
>>>>> connection, heat build up, fuse holder issue.
>>>>> 
>>>>> Let us know what you find out
>>>>> 
>>>>> On Fri, Apr 11, 2025 at 8:07 AM Amos Post via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> Hi Wrenches,
>>>>> 
>>>>> I have a bit of a puzzler that I’m trying to get sorted out.  I’ve been 
>>>>> servicing a Grid-Tied Battery Backup system that’s about 17-18 years old. 
>>>>>  The system comprises of 2-GVFX3648s in series, with 2-MX60(at least I 
>>>>> think they are 60s) CC’s.  Each CC has 3 strings of 3 tied to it, and 
>>>>> each string has a 15A in-line 600V fuse.  The modules are I believe are 
>>>>> like 230/240Watt 60 cell modules (sorry I don’t have pictures/specifics). 
>>>>>   We replaced the flooded batteries with AGMs about a year and a half 
>>>>> ago.  
>>>>> 
>>>>> The situation is one of the 15A string fuses keeps blowing.  It’s now 
>>>>> happened 3 times and its the same fuse every time.  First we just 
>>>>> replaced the fuse and under the surge/lightning assumption.  Fuse blew 
>>>>> again.  Then I thought I found the culprit.  The #6 PV output from the 
>>>>> combiner to the PV input breaker for the CC was a bit darkened and very 
>>>>> warm to the touch when I replaced the fuse the first time.   So I though 
>>>>> maybe it was a loose connection on that lug and that caused everything to 
>>>>> heat up and eventually blow the fuse.  I cut and stripped the wire back 
>>>>> and cleaned the lug and re-seated the wire in the lug.  Fuse blew again 
>>>>> within a few months time.  I then checked the Junction box on the roof 
>>>>> where the USE-2 wire connects to THHN, and did a visual inspection of all 
>>>>> the wiring on the roof.  All of the Jbox connections and everything on 
>>>>> the roof “looked” ok.  I have also check all of the connections inside 
>>>>> the Outback DC load center, and they look ok.  Fuse replaced 3rd time and 
>>>>> then it blew again.  
>>>>> 
>>>>> Before I take all of the panels off the rack, check panels, re-check 
>>>>> string wiring on the roof, is there anything else I should be checking?  
>>>>> Seems like that warm wire in the Combiner box is telling me something but 
>>>>> I can’t figure out what...I believe this is a new problem in the last 2-3 
>>>>> years but we are not 100% sure when the problem first came up…
>>>>> 
>>>>> As always, thanks for your help/ suggestions!
>>>>> Amos
>>>>> 
>>>>> 
>>>>> <IE LOGO 150x78.jpg>
>>>>> 
>>>>>        Amos Post
>>>>>    Integrity Energy
>>>>>   W 802.763.7023
>>>>>    C 802.291.2188
>>>>>     ienergyVT.com <http://www.ienergyvt.com/>
>>>>>         Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>>> 
>>>>> 
>>>>> -- 
>>>>> 
>>>>> 
>>>>> 
>>>>> Mac Lewis
>>>>> 
>>>>> "Yo solo sé que no sé nada." -Sócrates
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org 
>>>>> <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: [email protected] 
>>>>> <mailto:[email protected]>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/ 
>>>>> <https://www.mail-archive.com/[email protected]/>
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm 
>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/ 
>>> <https://www.mail-archive.com/[email protected]/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org