>Actually, it is addressed in NFPA 70- the National Electrical Code- which
>is
>ratified by each State's legislature as law in that State. I quote NFPA
>70-2005 Article 620.37, Wiring in Hoistways, Machine Rooms, Control Rooms,
>Machinery Spaces, and Control Spaces in its entirety:

>"(A) Uses Permitted. Only such electric wiring, raceways, and cables used
>directly in connection with the elevator or dumbwaiter, including wiring
>for
>signals, for communication with the car, for lighting, heating, air
>conditioning, and ventilating the elevator car, for fire detecting systems,
>for pit sump pumps, and for heating, lighting, and ventilating the
>hoistway,
>shall be permitted inside the hoistway, machine rooms, control rooms,
>machinery spaces, and control spaces."

>If it wasn't required by the elevator manufacturer, it can't be installed
>in
>the hoistway or the machine room. Period.
 
Well...close.  Fire alarm and control systems vary for elevators and
occupancies a bit.  While mentioned above, they may not be 'required by the
elevator manufacturer' but rather required via code by the AHJ.

In my experience, the elevator inspector is God.  I've seen entire jobs
grind to a halt for a failed elevator inspection.  NO ONE messes with the
elevator inspector in my experience.  You need them to sign off for
occupancy, and if you fail your test it might be 3 weeks before he will come
back and try again.  I've had to change a couple things to pass:

1. One application specified two Cat5e drops to every phone jack, one for
voice and one for data.  In the elevator room we put the data jack on a
faceplate, then ran the phone wire in conduit to the controller for
connection to the car cable.  Since the data jack wasn't integral, we were
forced to pull the data wire back out and cover the box.

2. One installation the electricians had run metal conduit on one wall of
the elevator mechanical room to a GFCI receptacle outside of the room, on an
exterior wall.  Since it was not a circuit for that room, they had to pull
it out and re-route it.

3. One fire alarm installation we had a row of boxes on the wall with
modules in them, basically the box takes an RS-485 data signal and addresses
a relay to do a function.  Six boxes, six modules, one of them actually for
something not directly connected to the elevator circuitry and we had to
pull it out and re-route everything.

I'd never even consider placing radio equipment in there first due to the
obvious code violation, second due to the life safety liability.