Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread david quattro via RE-wrenches
in their installation manuals, SolArk indicates black and red colors for PV conductors. ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Eric Smiley via RE-wrenches
SolArk arrays are ungrounded. However, because they are transformerless, when the inverter is operating, there is a reference to ground on the DC side via the AC side neutral bond to ground. So, a ground fault on the AC side will also cause a GF error. Many transformerless interactive inverters ar

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Brian Mehalic via RE-wrenches
2020 NEC® identification requirements in 690.31(B)(2) state that "Only solidly grounded PV system dc circuit conductors shall be marked in accordance with 200.6." (200.6 is Means of Identifying Grounded Conductors") If the circuit is nonsolidly grounded, then positive conductors can be identified

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Bryan Norkunas via RE-wrenches
White PV wire was something we used to sell often, but that demand has dropped off in the last 5 years or so and always wondered why. Thanks for sharing William Sunny Regards, [Description: Description: PV-Cables_Logo_Transparent_Bkgnd_140x140] Bryan Norkunas PV-Cables Inc. 989 Milton Ave Ste 1D

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Glenn Burt via RE-wrenches
Arent you really working with an EGC though?This would make it bare or green insulated.-GlennSent from my 'smart'phone, so please excuse typos and spelling errors.-- Original message--From: William Miller via RE-wrenchesDate: Wed, Jun 5, 2024 4:08 PMTo: RE-wrenches;Cc: William Miller;Sub

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread William Miller via RE-wrenches
Friends: On a related subject, I was researching the question: What color should my grounded PV conductor be? History: In the beginning, negative leads were always black. When it became apparent that negative PV leads were indeed grounded, the requirement to have them white or grey beca

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread Dave Angelini Offgrid Solar via RE-wrenches
Optics was down again last weekend and I read this comment below from the Outback forum. Day 11….without communication with our Sol Ark 15k inverter….Thanks Sol-Ark Solar * Quote [4] Post [5] Mon Jun 03, 2024 4:07 pm Who would have known? A conspiracy theorist that is right??? So i

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread Lloyd Hoffstatter via RE-wrenches
Hi Howie, Text from FB user Scott Shadle Sol-Ark owners Information network: Migration update (edit at 10 am central...my plant is now populating the new solark app. So...hang in there) Just had a very nice call with Sol Ark tech support. He suggested that perhaps my Facebook update would he

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread david quattro via RE-wrenches
Today they tried launching their monitoring migration from Inteless/PVPro to Mysolark/solarkcloud.com I had several sites throwing multiple bogus error codes and concerned homeowners calling my staff all morning. SolArk tech support probably drowning in that Error codes:: F49 Backup_Battery_Fault

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread Lloyd Hoffstatter via RE-wrenches
They are swamped with calls while they work to transition, and partially depends on a third party per user comments on Sol-ark users FB group after talking to tech support. Best regards, Lloyd Get Outlook for iOS From: RE-wrenches on behal

[RE-wrenches] Sol-Ark Support

2024-06-05 Thread Howie Michaelson via RE-wrenches
Is anyone else having trouble getting through to Sol-Ark support? Howie Michaelson ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email addr

[RE-wrenches] IRS Audit

2024-06-05 Thread Hilton Dier, III via RE-wrenches
I had to look into this once and it really isn't any more complex than the statement. It's not about UL listing or whatever. Does it generate electricity from solar? Is it installed on or connected to an occupied residential home? The restriction is that it has to be just the system itself. If yo

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Jason Szumlanski via RE-wrenches
This is a partial backup scenario and the main service panel has a solid neutral to ground bond. I have not been able to find anywhere else where there is a bond, but there is always the chance that there is a neutral wire in a switch box or outlet box somewhere in the house that is touching an equ

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Mac Lewis via RE-wrenches
Hi Jason, You should be able to land your PV EGC in the inverter ground bar. You could do a quick resistance check to verify the +, - PV Is there a bond somewhere (upstream service panel or in the Sol-Ark itself) between ground and neutral? If not, this can cause this fault. On Wed, Jun 5, 202

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Maverick Brown via RE-wrenches
I usually get the 08 GFDI error when I haven’t bonded neutral to ground downstream. (Typically because I booted up the inverter after DC connection but before any AC wires are landed.) That goes away once it is fully commissioned. I get the F23 - Tz_GFCI_OC_Fault If is related to the PV array,

[RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Jason Szumlanski via RE-wrenches
Can anybody clarify the following instruction from the manual? "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire" Does this mean do not connect the array equipment grounding conductor to the grounding terminal in the inverter? Where would be the suggested place to connect