Re: [AFMUG] 24V Battery Revert and Charge Module
Yes. - Mike Hammett Intelligent Computing Solutions Midwest Internet Exchange The Brothers WISP - Original Message - From: "SmarterBroadband" <li...@sbb.net> To: af@afmug.com Sent: Monday, May 22, 2017 12:20:12 PM Subject: Re: [AFMUG] 24V Battery Revert and Charge Module >From the specs it looks like the BCMU360 only supports a 12v battery? Is this correct? From: Af [mailto:af-boun...@afmug.com] On Behalf Of George Skorup Sent: Saturday, May 20, 2017 3:55 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" < af-boun...@afmug.com � Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 cid:image001.png@01D2D2DA.8BB7D5B0 on behalf of george.sko...@cbcast.com > wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.� But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.� Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.� Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
Yes, and management. Along with some amount of redundancy. On Monday, May 22, 2017, SmarterBroadband <li...@sbb.net> wrote: > Hi Mark > > > > We have never used a Rectifier Shelf. Is it an all in one solution, AC in > DC out power for equipment and integrated battery charging? > > > > Thanks > > > > Adam > > > > *From:* Af [mailto:af-boun...@afmug.com > <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>] *On Behalf Of *Mark > Radabaugh > *Sent:* Sunday, May 21, 2017 6:48 PM > *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');> > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > > > > 720W site? That’s some serious power. At that point it’s time for a > real rectifier shelf - call these guys: > > > > http://telecomsurplus.net/power/rectifiers/ > > > > They have a pretty good collection of Eltek rectifiers that would handle > that load nicely. > > > > Mark > > > > > > > > On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net > <javascript:_e(%7B%7D,'cvml','jesse.dup...@celeritycorp.net');>> wrote: > > > > Well, that is a concern. I think we'll be under 30A after all is said and > done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. > I should note this site will have an automatic standby generator so we > won't need a huge battery string. > > > -- > > *From:* Af <af-boun...@afmug.com > <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of Gino > A. Villarini <g...@aeronetpr.com > <javascript:_e(%7B%7D,'cvml','g...@aeronetpr.com');>> > *Sent:* Sunday, May 21, 2017 4:47:19 AM > *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');> > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > > > > How do you plan to connect to batteries for this setup ? > > > > *From: *Af <af-boun...@afmug.com > <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of > Jesse Dupont <jesse.dup...@celeritycorp.net > <javascript:_e(%7B%7D,'cvml','jesse.dup...@celeritycorp.net');>> > *Reply-To: *"af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>" > <af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>> > *Date: *Saturday, May 20, 2017 at 7:07 PM > *To: *"af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>" < > af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>> > *Subject: *Re: [AFMUG] 24V Battery Revert and Charge Module > > > > The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to > 8 of those in parallel to have a lot of capacity and N+1 redundancy without > the DR-RDN20 redundancy module. > > > > We're getting ready to do a four unit N+1 at a site that has 16-17 Amps > already and is getting some LTE base stations added to it. > > > -- > > *From:* Af <af-boun...@afmug.com > <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of > George Skorup <george.sko...@cbcast.com > <javascript:_e(%7B%7D,'cvml','george.sko...@cbcast.com');>> > *Sent:* Saturday, May 20, 2017 4:55:25 PM > *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');> > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > > > > List price on the BCMU360 is about $215 IIRC. I think we pay about $175 > from PSUI. Plus $15 for the temp probe. > > Are you asking run time? I have a couple with 40Ah of battery attached. A > few with about 90W load have ran for over four hours, but they never went > down, utility came back. A couple others with ~190-220W. Lost utility at > one of the sites the other day. It was running for about an hour and a half > before I brought a portable gen out. That site didn't go down either. > Couldn't let it, too much traffic. And of course utility came back 15 > minutes after I got the generator going. > > > > *Gino A. Villarini* > > President > > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > > > On 5/20/2017 4:51 PM, Gino A. Villarini wrote: > > How much are you paying for the Traco and how long does it last? > > On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com > <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');> > > ï¿1Ž2 > > *Gino A. Villarini* > > President > > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > on behalf of george.sko...@cbcast.com > <javascript:_e(%7B%7D,'cvml','george.sko...@
Re: [AFMUG] 24V Battery Revert and Charge Module
>From the specs it looks like the BCMU360 only supports a 12v battery? Is this correct? From: Af [mailto:af-boun...@afmug.com] On Behalf Of George Skorup Sent: Saturday, May 20, 2017 3:55 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com <mailto:af-boun...@afmug.com> � Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> > wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.� But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.� Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.� Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
Hi Mark We have never used a Rectifier Shelf. Is it an all in one solution, AC in DC out power for equipment and integrated battery charging? Thanks Adam From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mark Radabaugh Sent: Sunday, May 21, 2017 6:48 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 720W site? That’s some serious power. At that point it’s time for a real rectifier shelf - call these guys: http://telecomsurplus.net/power/rectifiers/ They have a pretty good collection of Eltek rectifiers that would handle that load nicely. Mark On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net <mailto:jesse.dup...@celeritycorp.net> > wrote: Well, that is a concern. I think we'll be under 30A after all is said and done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should note this site will have an automatic standby generator so we won't need a huge battery string. _ From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of Gino A. Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com> > Sent: Sunday, May 21, 2017 4:47:19 AM To: af@afmug.com <mailto:af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net <mailto:jesse.dup...@celeritycorp.net> > Reply-To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. _ From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of George Skorup <george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> > Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com <mailto:af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com <mailto:af-boun...@afmug.com> ï¿1Ž2 Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> > wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
Depends on money. If you have plenty of money I try for many days of autonomy on batts. How many days to you expect to be out of power and then double it. If you have enough batts, you don’t even need the genset. If you are scrimping, a genset with a few batts is the best value for providing backup energy. From: Adam Moffett Sent: Monday, May 22, 2017 8:34 AM To: af@afmug.com ; af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Eventually you run out of space for them :) -- Original Message -- From: "Lewis Bergman" <lewis.berg...@gmail.com> To: af@afmug.com Sent: 5/21/2017 12:29:08 PM Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Yea...i lean towards putting mow batteries in with the money you would have spent on a genset. On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote: You can always 100% rely on a standby generator not starting when you need it the most. From: Jesse Dupont Sent: Sunday, May 21, 2017 7:02 AM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Well, that is a concern. I think we'll be under 30A after all is said and done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should note this site will have an automatic standby generator so we won't need a huge battery string. From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini <g...@aeronetpr.com> Sent: Sunday, May 21, 2017 4:47:19 AM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net> Reply-To: "af@afmug.com" <af@afmug.com> Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com" <af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com> on behalf of George Skorup <george.sko...@cbcast.com> Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com ï¿1Ž2 Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of george.sko...@cbcast.com> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor &
Re: [AFMUG] 24V Battery Revert and Charge Module
Eventually you run out of space for them :) -- Original Message -- From: "Lewis Bergman" <lewis.berg...@gmail.com> To: af@afmug.com Sent: 5/21/2017 12:29:08 PM Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Yea...i lean towards putting mow batteries in with the money you would have spent on a genset. On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote: You can always 100% rely on a standby generator not starting when you need it the most. From:Jesse Dupont Sent: Sunday, May 21, 2017 7:02 AM To:af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Well, that is a concern. I think we'll be under 30A after all is said and done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should note this site will have an automatic standby generator so we won't need a huge battery string. From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini <g...@aeronetpr.com> Sent: Sunday, May 21, 2017 4:47:19 AM To:af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net> Reply-To: "af@afmug.com" <af@afmug.com> Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com" <af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com> on behalf of George Skorup <george.sko...@cbcast.com> Sent: Saturday, May 20, 2017 4:55:25 PM To:af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini PresidentMetro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com ï¿1Ž2 Gino A. Villarini PresidentMetro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of george.sko...@cbcast.com> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
720W site? That’s some serious power. At that point it’s time for a real rectifier shelf - call these guys: http://telecomsurplus.net/power/rectifiers/ <http://telecomsurplus.net/power/rectifiers/> They have a pretty good collection of Eltek rectifiers that would handle that load nicely. Mark > On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net> > wrote: > > Well, that is a concern. I think we'll be under 30A after all is said and > done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I > should note this site will have an automatic standby generator so we won't > need a huge battery string. > > From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of > Gino A. Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com>> > Sent: Sunday, May 21, 2017 4:47:19 AM > To: af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] 24V Battery Revert and Charge Module > > How do you plan to connect to batteries for this setup ? > > From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of > Jesse Dupont <jesse.dup...@celeritycorp.net > <mailto:jesse.dup...@celeritycorp.net>> > Reply-To: "af@afmug.com <mailto:af@afmug.com>" <af@afmug.com > <mailto:af@afmug.com>> > Date: Saturday, May 20, 2017 at 7:07 PM > To: "af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>> > Subject: Re: [AFMUG] 24V Battery Revert and Charge Module > > The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 > of those in parallel to have a lot of capacity and N+1 redundancy without the > DR-RDN20 redundancy module. > > We're getting ready to do a four unit N+1 at a site that has 16-17 Amps > already and is getting some LTE base stations added to it. > > From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of > George Skorup <george.sko...@cbcast.com <mailto:george.sko...@cbcast.com>> > Sent: Saturday, May 20, 2017 4:55:25 PM > To: af@afmug.com <mailto:af@afmug.com> > Subject: Re: [AFMUG] 24V Battery Revert and Charge Module > > List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from > PSUI. Plus $15 for the temp probe. > > Are you asking run time? I have a couple with 40Ah of battery attached. A few > with about 90W load have ran for over four hours, but they never went down, > utility came back. A couple others with ~190-220W. Lost utility at one of the > sites the other day. It was running for about an hour and a half before I > brought a portable gen out. That site didn't go down either. Couldn't let it, > too much traffic. And of course utility came back 15 minutes after I got the > generator going. > > > > Gino A. Villarini > > President > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > > On 5/20/2017 4:51 PM, Gino A. Villarini wrote: >> How much are you paying for the Traco and how long does it last? >> >> On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com >> <mailto:af-boun...@afmug.com> >> ï¿1Ž2 >> >> Gino A. Villarini >> >> President >> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >> >> >> on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com>> >> wrote: >> >> >Mean Well AD-155B >> >or >> >Mean Well SDR-240-24 + DR-UPS40 >> >or >> >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >> >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >> >continuous. >> > >> >All this stuff is fine until you start looking to deploy things that are >> >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >> >multiple AF24s or licensed radios, etc. Then you need big-boy >> >rectifiers, which aren't all that expensive, but they aren't cheap >> >either. Add good telco-grade batteries on top and it's easily 10x the >> >cost of what we're used to with the smaller stuff. >> > >> >On 5/20/2017 1:16 PM, Matt wrote: >> >> What is everyone using for switching from AC to battery backup at sites? >> >> >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> >> that monitors power supply output and battery voltage and some DIN >> >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> >> have a 24V to 48V converter to power our 450i etc stuff. >> >> >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> >> with MRTG. >> >> >> >> Curious what others are using here? >> >
Re: [AFMUG] 24V Battery Revert and Charge Module
Yea...i lean towards putting mow batteries in with the money you would have spent on a genset. On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote: > You can always 100% rely on a standby generator not starting when you need > it the most. > > *From:* Jesse Dupont > *Sent:* Sunday, May 21, 2017 7:02 AM > *To:* af@afmug.com > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > Well, that is a concern. I think we'll be under 30A after all is said and > done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. > I should note this site will have an automatic standby generator so we > won't need a huge battery string. > > -- > *From:* Af <af-boun...@afmug.com> on behalf of Gino A. Villarini < > g...@aeronetpr.com> > *Sent:* Sunday, May 21, 2017 4:47:19 AM > *To:* af@afmug.com > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > > How do you plan to connect to batteries for this setup ? > > From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont < > jesse.dup...@celeritycorp.net> > Reply-To: "af@afmug.com" <af@afmug.com> > Date: Saturday, May 20, 2017 at 7:07 PM > To: "af@afmug.com" <af@afmug.com> > Subject: Re: [AFMUG] 24V Battery Revert and Charge Module > > The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to > 8 of those in parallel to have a lot of capacity and N+1 redundancy without > the DR-RDN20 redundancy module. > > We're getting ready to do a four unit N+1 at a site that has 16-17 Amps > already and is getting some LTE base stations added to it. > > -- > *From:* Af <af-boun...@afmug.com> on behalf of George Skorup < > george.sko...@cbcast.com> > *Sent:* Saturday, May 20, 2017 4:55:25 PM > *To:* af@afmug.com > *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module > > List price on the BCMU360 is about $215 IIRC. I think we pay about $175 > from PSUI. Plus $15 for the temp probe. > > Are you asking run time? I have a couple with 40Ah of battery attached. A > few with about 90W load have ran for over four hours, but they never went > down, utility came back. A couple others with ~190-220W. Lost utility at > one of the sites the other day. It was running for about an hour and a half > before I brought a portable gen out. That site didn't go down either. > Couldn't let it, too much traffic. And of course utility came back 15 > minutes after I got the generator going. > > > > *Gino A. Villarini* > President > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > On 5/20/2017 4:51 PM, Gino A. Villarini wrote: > > How much are you paying for the Traco and how long does it last? > > On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com > > ï¿1Ž2 > > *Gino A. Villarini* > President > Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 > > on behalf of george.sko...@cbcast.com> wrote: > > >Mean Well AD-155B > >or > >Mean Well SDR-240-24 + DR-UPS40 > >or > >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 > >or 48) - I use this combo most often. The BCMU360 is only good for ~240W > >continuous. > > > >All this stuff is fine until you start looking to deploy things that are > >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, > >multiple AF24s or licensed radios, etc. Then you need big-boy > >rectifiers, which aren't all that expensive, but they aren't cheap > >either. Add good telco-grade batteries on top and it's easily 10x the > >cost of what we're used to with the smaller stuff. > > > >On 5/20/2017 1:16 PM, Matt wrote: > >> What is everyone using for switching from AC to battery backup at sites? > >> > >> I normally have our other guy take care of that part.ï¿1Ž2 But we > normally > >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor > >> that monitors power supply output and battery voltage and some DIN > >> mount module that does charging and switching between the two.ï¿1Ž2 Also > >> have a 24V to 48V converter to power our 450i etc stuff. > >> > >> Monitor the site monitor with SNMP and start emailing alarms if power > >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage > >> with MRTG. > >> > >> Curious what others are using here? > > > > >
Re: [AFMUG] 24V Battery Revert and Charge Module
You can always 100% rely on a standby generator not starting when you need it the most. From: Jesse Dupont Sent: Sunday, May 21, 2017 7:02 AM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module Well, that is a concern. I think we'll be under 30A after all is said and done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should note this site will have an automatic standby generator so we won't need a huge battery string. From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini <g...@aeronetpr.com> Sent: Sunday, May 21, 2017 4:47:19 AM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net> Reply-To: "af@afmug.com" <af@afmug.com> Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com" <af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com> on behalf of George Skorup <george.sko...@cbcast.com> Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com ï¿1Ž2 Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 on behalf of george.sko...@cbcast.com> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
Well, that is a concern. I think we'll be under 30A after all is said and done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should note this site will have an automatic standby generator so we won't need a huge battery string. From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini <g...@aeronetpr.com> Sent: Sunday, May 21, 2017 4:47:19 AM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net<mailto:jesse.dup...@celeritycorp.net>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of George Skorup <george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png] On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> ï¿1Ž2 Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:part1.95843274.3D23CEA5@cbcast.com] on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
How do you plan to connect to batteries for this setup ? From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Jesse Dupont <jesse.dup...@celeritycorp.net<mailto:jesse.dup...@celeritycorp.net>> Reply-To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Date: Saturday, May 20, 2017 at 7:07 PM To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of George Skorup <george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com<mailto:af@afmug.com> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png] On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> ï¿1Ž2 Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:part1.95843274.3D23CEA5@cbcast.com] on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.ï¿1Ž2 Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of those in parallel to have a lot of capacity and N+1 redundancy without the DR-RDN20 redundancy module. We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already and is getting some LTE base stations added to it. From: Af <af-boun...@afmug.com> on behalf of George Skorup <george.sko...@cbcast.com> Sent: Saturday, May 20, 2017 4:55:25 PM To: af@afmug.com Subject: Re: [AFMUG] 24V Battery Revert and Charge Module List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com<mailto:af-boun...@afmug.com> � Gino A. Villarini President Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 [cid:part1.95843274.3D23CEA5@cbcast.com] on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part.� But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two.� Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops.� Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from PSUI. Plus $15 for the temp probe. Are you asking run time? I have a couple with 40Ah of battery attached. A few with about 90W load have ran for over four hours, but they never went down, utility came back. A couple others with ~190-220W. Lost utility at one of the sites the other day. It was running for about an hour and a half before I brought a portable gen out. That site didn't go down either. Couldn't let it, too much traffic. And of course utility came back 15 minutes after I got the generator going. On 5/20/2017 4:51 PM, Gino A. Villarini wrote: How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup"wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part. But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two. Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops. Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
How much are you paying for the Traco and how long does it last? On 5/20/17, 4:44 PM, "Af on behalf of George Skorup"wrote: >Mean Well AD-155B >or >Mean Well SDR-240-24 + DR-UPS40 >or >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 >or 48) - I use this combo most often. The BCMU360 is only good for ~240W >continuous. > >All this stuff is fine until you start looking to deploy things that are >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, >multiple AF24s or licensed radios, etc. Then you need big-boy >rectifiers, which aren't all that expensive, but they aren't cheap >either. Add good telco-grade batteries on top and it's easily 10x the >cost of what we're used to with the smaller stuff. > >On 5/20/2017 1:16 PM, Matt wrote: >> What is everyone using for switching from AC to battery backup at sites? >> >> I normally have our other guy take care of that part. But we normally >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor >> that monitors power supply output and battery voltage and some DIN >> mount module that does charging and switching between the two. Also >> have a 24V to 48V converter to power our 450i etc stuff. >> >> Monitor the site monitor with SNMP and start emailing alarms if power >> supply voltage drops. Also graph power supply and battery voltage >> with MRTG. >> >> Curious what others are using here? >
Re: [AFMUG] 24V Battery Revert and Charge Module
Mean Well AD-155B or Mean Well SDR-240-24 + DR-UPS40 or Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 or 48) - I use this combo most often. The BCMU360 is only good for ~240W continuous. All this stuff is fine until you start looking to deploy things that are power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, multiple AF24s or licensed radios, etc. Then you need big-boy rectifiers, which aren't all that expensive, but they aren't cheap either. Add good telco-grade batteries on top and it's easily 10x the cost of what we're used to with the smaller stuff. On 5/20/2017 1:16 PM, Matt wrote: What is everyone using for switching from AC to battery backup at sites? I normally have our other guy take care of that part. But we normally have a DIN mount 24V power supply, a DIN mount packetflux site monitor that monitors power supply output and battery voltage and some DIN mount module that does charging and switching between the two. Also have a 24V to 48V converter to power our 450i etc stuff. Monitor the site monitor with SNMP and start emailing alarms if power supply voltage drops. Also graph power supply and battery voltage with MRTG. Curious what others are using here?
Re: [AFMUG] 24V Battery Revert and Charge Module
If you are using a DC UPS, there is no switching required on your part. The load, batteries and AC line in are all separate from each other. If AC line voltage is active, power comes from there. If AC line voltage is not active, then power comes from the batteries. If the controller has LVD, it will maintain until the batteries get to the LVD. If it doesn't have LVD, then the controller will maintain until the batteries are depleted. If you are just using a smart charger, you hook the load directly to the batteries, and hang tough. No switching required here either. bpOn 5/20/2017 11:16 AM, Matt wrote: What is everyone using for switching from AC to battery backup at sites? I normally have our other guy take care of that part. But we normally have a DIN mount 24V power supply, a DIN mount packetflux site monitor that monitors power supply output and battery voltage and some DIN mount module that does charging and switching between the two. Also have a 24V to 48V converter to power our 450i etc stuff. Monitor the site monitor with SNMP and start emailing alarms if power supply voltage drops. Also graph power supply and battery voltage with MRTG. Curious what others are using here?
Re: [AFMUG] 24V Battery Revert and Charge Module
Not totally sure what you are asking here. Normally there is no switching. Everything is running the DC bus. When AC fails the rectifier/power supply just stops supplying DC power to the bus. So the batts supply the current. Power comes back on and the rectifier once again powers the loads and charges the batts. -Original Message- From: Matt Sent: Saturday, May 20, 2017 12:16 PM To: af@afmug.com Subject: [AFMUG] 24V Battery Revert and Charge Module What is everyone using for switching from AC to battery backup at sites? I normally have our other guy take care of that part. But we normally have a DIN mount 24V power supply, a DIN mount packetflux site monitor that monitors power supply output and battery voltage and some DIN mount module that does charging and switching between the two. Also have a 24V to 48V converter to power our 450i etc stuff. Monitor the site monitor with SNMP and start emailing alarms if power supply voltage drops. Also graph power supply and battery voltage with MRTG. Curious what others are using here?
[AFMUG] 24V Battery Revert and Charge Module
What is everyone using for switching from AC to battery backup at sites? I normally have our other guy take care of that part. But we normally have a DIN mount 24V power supply, a DIN mount packetflux site monitor that monitors power supply output and battery voltage and some DIN mount module that does charging and switching between the two. Also have a 24V to 48V converter to power our 450i etc stuff. Monitor the site monitor with SNMP and start emailing alarms if power supply voltage drops. Also graph power supply and battery voltage with MRTG. Curious what others are using here?