Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread Mike Hammett
Yes. 




- 
Mike Hammett 
Intelligent Computing Solutions 

Midwest Internet Exchange 

The Brothers WISP 




- Original Message -

From: "SmarterBroadband" <li...@sbb.net> 
To: af@afmug.com 
Sent: Monday, May 22, 2017 12:20:12 PM 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 



>From the specs it looks like the BCMU360 only supports a 12v battery? 
Is this correct? 



From: Af [mailto:af-boun...@afmug.com] On Behalf Of George Skorup 
Sent: Saturday, May 20, 2017 3:55 PM 
To: af@afmug.com 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe. 

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going. 

On 5/20/2017 4:51 PM, Gino A. Villarini wrote: 



How much are you paying for the Traco and how long does it last? 

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" < af-boun...@afmug.com 
� 
Gino A. Villarini 

President 

Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 
cid:image001.png@01D2D2DA.8BB7D5B0
on behalf of george.sko...@cbcast.com > wrote: 

>Mean Well AD-155B 
>or 
>Mean Well SDR-240-24 + DR-UPS40 
>or 
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W 
>continuous. 
> 
>All this stuff is fine until you start looking to deploy things that are 
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, 
>multiple AF24s or licensed radios, etc. Then you need big-boy 
>rectifiers, which aren't all that expensive, but they aren't cheap 
>either. Add good telco-grade batteries on top and it's easily 10x the 
>cost of what we're used to with the smaller stuff. 
> 
>On 5/20/2017 1:16 PM, Matt wrote: 
>> What is everyone using for switching from AC to battery backup at sites? 
>> 
>> I normally have our other guy take care of that part.� But we normally 
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor 
>> that monitors power supply output and battery voltage and some DIN 
>> mount module that does charging and switching between the two.� Also 
>> have a 24V to 48V converter to power our 450i etc stuff. 
>> 
>> Monitor the site monitor with SNMP and start emailing alarms if power 
>> supply voltage drops.� Also graph power supply and battery voltage 
>> with MRTG. 
>> 
>> Curious what others are using here? 
> 





Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread Jason McKemie
Yes, and management. Along with some amount of redundancy.

On Monday, May 22, 2017, SmarterBroadband <li...@sbb.net> wrote:

> Hi Mark
>
>
>
> We have never used a Rectifier Shelf.  Is it an all in one solution, AC in
> DC out power for equipment and integrated battery charging?
>
>
>
> Thanks
>
>
>
> Adam
>
>
>
> *From:* Af [mailto:af-boun...@afmug.com
> <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>] *On Behalf Of *Mark
> Radabaugh
> *Sent:* Sunday, May 21, 2017 6:48 PM
> *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
>
>
>
> 720W site?   That’s some serious power.   At that point it’s time for a
> real rectifier shelf - call these guys:
>
>
>
> http://telecomsurplus.net/power/rectifiers/
>
>
>
> They have a pretty good collection of Eltek rectifiers that would handle
> that load nicely.
>
>
>
> Mark
>
>
>
>
>
>
>
> On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net
> <javascript:_e(%7B%7D,'cvml','jesse.dup...@celeritycorp.net');>> wrote:
>
>
>
> Well, that is a concern. I think we'll be under 30A after all is said and
> done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate.
> I should note this site will have an automatic standby generator so we
> won't need a huge battery string.
>
>
> --
>
> *From:* Af <af-boun...@afmug.com
> <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of Gino
> A. Villarini <g...@aeronetpr.com
> <javascript:_e(%7B%7D,'cvml','g...@aeronetpr.com');>>
> *Sent:* Sunday, May 21, 2017 4:47:19 AM
> *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
>
>
>
> How do you plan to connect to batteries for this setup ?
>
>
>
> *From: *Af <af-boun...@afmug.com
> <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of
> Jesse Dupont <jesse.dup...@celeritycorp.net
> <javascript:_e(%7B%7D,'cvml','jesse.dup...@celeritycorp.net');>>
> *Reply-To: *"af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>"
> <af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>>
> *Date: *Saturday, May 20, 2017 at 7:07 PM
> *To: *"af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>" <
> af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>>
> *Subject: *Re: [AFMUG] 24V Battery Revert and Charge Module
>
>
>
> The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to
> 8 of those in parallel to have a lot of capacity and N+1 redundancy without
> the DR-RDN20 redundancy module.
>
>
>
> We're getting ready to do a four unit N+1 at a site that has 16-17 Amps
> already and is getting some LTE base stations added to it.
>
>
> --
>
> *From:* Af <af-boun...@afmug.com
> <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>> on behalf of
> George Skorup <george.sko...@cbcast.com
> <javascript:_e(%7B%7D,'cvml','george.sko...@cbcast.com');>>
> *Sent:* Saturday, May 20, 2017 4:55:25 PM
> *To:* af@afmug.com <javascript:_e(%7B%7D,'cvml','af@afmug.com');>
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
>
>
>
> List price on the BCMU360 is about $215 IIRC. I think we pay about $175
> from PSUI. Plus $15 for the temp probe.
>
> Are you asking run time? I have a couple with 40Ah of battery attached. A
> few with about 90W load have ran for over four hours, but they never went
> down, utility came back. A couple others with ~190-220W. Lost utility at
> one of the sites the other day. It was running for about an hour and a half
> before I brought a portable gen out. That site didn't go down either.
> Couldn't let it, too much traffic. And of course utility came back 15
> minutes after I got the generator going.
>
>
>
> *Gino A. Villarini*
>
> President
>
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> 
>
> On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
>
> How much are you paying for the Traco and how long does it last?
>
> On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com
> <javascript:_e(%7B%7D,'cvml','af-boun...@afmug.com');>
>
> ï¿1Ž2
>
> *Gino A. Villarini*
>
> President
>
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> on behalf of george.sko...@cbcast.com
> <javascript:_e(%7B%7D,'cvml','george.sko...@

Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread SmarterBroadband
>From the specs it looks like the BCMU360 only supports a 12v battery?

Is this correct?

 

From: Af [mailto:af-boun...@afmug.com] On Behalf Of George Skorup
Sent: Saturday, May 20, 2017 3:55 PM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

 

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A
few with about 90W load have ran for over four hours, but they never went
down, utility came back. A couple others with ~190-220W. Lost utility at one
of the sites the other day. It was running for about an hour and a half
before I brought a portable gen out. That site didn't go down either.
Couldn't let it, too much traffic. And of course utility came back 15
minutes after I got the generator going.

On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com
<mailto:af-boun...@afmug.com> 


�

Gino A. Villarini


President


Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968



on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> >
wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.� But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.� Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.� Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>

 



Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread SmarterBroadband
Hi Mark

 

We have never used a Rectifier Shelf.  Is it an all in one solution, AC in DC 
out power for equipment and integrated battery charging?

 

Thanks

 

Adam

 

From: Af [mailto:af-boun...@afmug.com] On Behalf Of Mark Radabaugh
Sent: Sunday, May 21, 2017 6:48 PM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

 

720W site?   That’s some serious power.   At that point it’s time for a real 
rectifier shelf - call these guys:  

 

http://telecomsurplus.net/power/rectifiers/

 

They have a pretty good collection of Eltek rectifiers that would handle that 
load nicely.

 

Mark

 

 

 

On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net 
<mailto:jesse.dup...@celeritycorp.net> > wrote:

 

Well, that is a concern. I think we'll be under 30A after all is said and done 
and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should 
note this site will have an automatic standby generator so we won't need a huge 
battery string.

 

  _  

From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of 
Gino A. Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com> >
Sent: Sunday, May 21, 2017 4:47:19 AM
To: af@afmug.com <mailto:af@afmug.com> 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

 

How do you plan to connect to batteries for this setup ?

 

From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of 
Jesse Dupont <jesse.dup...@celeritycorp.net 
<mailto:jesse.dup...@celeritycorp.net> >
Reply-To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com 
<mailto:af@afmug.com> >
Date: Saturday, May 20, 2017 at 7:07 PM
To: "af@afmug.com <mailto:af@afmug.com> " <af@afmug.com <mailto:af@afmug.com> >
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

 

The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of 
those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

 

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already 
and is getting some LTE base stations added to it.

 


  _  


From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com> > on behalf of 
George Skorup <george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> >
Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com <mailto:af@afmug.com> 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

 

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.


 

Gino A. Villarini


President


Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968



On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com 
<mailto:af-boun...@afmug.com> 


ï¿1Ž2

Gino A. Villarini


President


Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com> > wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.ï¿1Ž2 But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.ï¿1Ž2 Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>

 



Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread Chuck McCown
Depends on money.  If you have plenty of money I try for many days of autonomy 
on batts.  How many days to you expect to be out of power and then double it.  
If you have enough batts, you don’t even need the genset.  

If you are scrimping, a genset with a few batts is the best value for providing 
backup energy.  

From: Adam Moffett 
Sent: Monday, May 22, 2017 8:34 AM
To: af@afmug.com ; af@afmug.com 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

Eventually you run out of space for them :)


-- Original Message --
From: "Lewis Bergman" <lewis.berg...@gmail.com>
To: af@afmug.com
Sent: 5/21/2017 12:29:08 PM
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

  Yea...i lean towards putting mow batteries in with the money you would have 
spent on a genset. 



  On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote:

You can always 100% rely on a standby generator not starting when you need 
it the most.

From: Jesse Dupont 
Sent: Sunday, May 21, 2017 7:02 AM
To: af@afmug.com 
    Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
Well, that is a concern. I think we'll be under 30A after all is said and 
done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I 
should note this site will have an automatic standby generator so we won't need 
a huge battery string.




From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini 
<g...@aeronetpr.com>
Sent: Sunday, May 21, 2017 4:47:19 AM
To: af@afmug.com
    Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 

How do you plan to connect to batteries for this setup ?

From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont 
<jesse.dup...@celeritycorp.net>
Reply-To: "af@afmug.com" <af@afmug.com>
Date: Saturday, May 20, 2017 at 7:07 PM
    To: "af@afmug.com" <af@afmug.com>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module


The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 
8 of those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps 
already and is getting some LTE base stations added to it.




From: Af <af-boun...@afmug.com> on behalf of George Skorup 
<george.sko...@cbcast.com>
    Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 
from PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A 
few with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.





  Gino A. Villarini
 
  President 
  Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 



On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

  How much are you paying for the Traco and how long does it last?

  On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com


ï¿1Ž2

Gino A. Villarini
   
President 
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 



  on behalf of george.sko...@cbcast.com> wrote:

  >Mean Well AD-155B
  >or
  >Mean Well SDR-240-24 + DR-UPS40
  >or
  >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
  >or 48) - I use this combo most often. The BCMU360 is only good for ~240W
  >continuous.
  >
  >All this stuff is fine until you start looking to deploy things that are
  >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
  >multiple AF24s or licensed radios, etc. Then you need big-boy
  >rectifiers, which aren't all that expensive, but they aren't cheap
  >either. Add good telco-grade batteries on top and it's easily 10x the
  >cost of what we're used to with the smaller stuff.
  >
  >On 5/20/2017 1:16 PM, Matt wrote:
  >> What is everyone using for switching from AC to battery backup at 
sites?
  >>
  >> I normally have our other guy take care of that part.ï¿1Ž2 But we 
normally
  >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
  &

Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-22 Thread Adam Moffett

Eventually you run out of space for them :)


-- Original Message --
From: "Lewis Bergman" <lewis.berg...@gmail.com>
To: af@afmug.com
Sent: 5/21/2017 12:29:08 PM
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

Yea...i lean towards putting mow batteries in with the money you would 
have spent on a genset.



On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote:
You can always 100% rely on a standby generator not starting when you 
need it the most.


From:Jesse Dupont
Sent: Sunday, May 21, 2017 7:02 AM
To:af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
Well, that is a concern. I think we'll be under 30A after all is said 
and done and the DR-UPS40 handles 40A. Downside would be the 2A 
charging rate. I should note this site will have an automatic standby 
generator so we won't need a huge battery string.



From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini 
<g...@aeronetpr.com>

Sent: Sunday, May 21, 2017 4:47:19 AM
To:af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

How do you plan to connect to batteries for this setup ?

From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont 
<jesse.dup...@celeritycorp.net>

Reply-To: "af@afmug.com" <af@afmug.com>
Date: Saturday, May 20, 2017 at 7:07 PM
To: "af@afmug.com" <af@afmug.com>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

The Meanwell SDR-480P-24 and -48 do current sharing so you can stack 
up to 8 of those in parallel to have a lot of capacity and N+1 
redundancy without the DR-RDN20 redundancy module.


We're getting ready to do a four unit N+1 at a site that has 16-17 
Amps already and is getting some LTE base stations added to it.



From: Af <af-boun...@afmug.com> on behalf of George Skorup 
<george.sko...@cbcast.com>

Sent: Saturday, May 20, 2017 4:55:25 PM
To:af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

List price on the BCMU360 is about $215 IIRC. I think we pay about 
$175 from PSUI. Plus $15 for the temp probe.


Are you asking run time? I have a couple with 40Ah of battery 
attached. A few with about 90W load have ran for over four hours, but 
they never went down, utility came back. A couple others with 
~190-220W. Lost utility at one of the sites the other day. It was 
running for about an hour and a half before I brought a portable gen 
out. That site didn't go down either. Couldn't let it, too much 
traffic. And of course utility came back 15 minutes after I got the 
generator going.





Gino A. Villarini

PresidentMetro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" 
<af-boun...@afmug.com


ï¿1Ž2

Gino A. Villarini

PresidentMetro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

on behalf of george.sko...@cbcast.com> wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 
24
>or 48) - I use this combo most often. The BCMU360 is only good for 
~240W

>continuous.
>
>All this stuff is fine until you start looking to deploy things that 
are

>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x 
the

>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at 
sites?

>>
>> I normally have our other guy take care of that part.ï¿1Ž2 But we 
normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site 
monitor

>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the 
two.ï¿1Ž2 Also

>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if 
power
>> supply voltage drops.ï¿1Ž2 Also graph power supply and battery 
voltage

>> with MRTG.
>>
>> Curious what others are using here?
>



Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-21 Thread Mark Radabaugh
720W site?   That’s some serious power.   At that point it’s time for a real 
rectifier shelf - call these guys:  

http://telecomsurplus.net/power/rectifiers/ 
<http://telecomsurplus.net/power/rectifiers/>

They have a pretty good collection of Eltek rectifiers that would handle that 
load nicely.

Mark



> On May 21, 2017, at 9:02 AM, Jesse Dupont <jesse.dup...@celeritycorp.net> 
> wrote:
> 
> Well, that is a concern. I think we'll be under 30A after all is said and 
> done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I 
> should note this site will have an automatic standby generator so we won't 
> need a huge battery string.
> 
> From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of 
> Gino A. Villarini <g...@aeronetpr.com <mailto:g...@aeronetpr.com>>
> Sent: Sunday, May 21, 2017 4:47:19 AM
> To: af@afmug.com <mailto:af@afmug.com>
> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
>  
> How do you plan to connect to batteries for this setup ?
> 
> From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of 
> Jesse Dupont <jesse.dup...@celeritycorp.net 
> <mailto:jesse.dup...@celeritycorp.net>>
> Reply-To: "af@afmug.com <mailto:af@afmug.com>" <af@afmug.com 
> <mailto:af@afmug.com>>
> Date: Saturday, May 20, 2017 at 7:07 PM
> To: "af@afmug.com <mailto:af@afmug.com>" <af@afmug.com <mailto:af@afmug.com>>
> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
> 
> The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 
> of those in parallel to have a lot of capacity and N+1 redundancy without the 
> DR-RDN20 redundancy module.
> 
> We're getting ready to do a four unit N+1 at a site that has 16-17 Amps 
> already and is getting some LTE base stations added to it.
> 
> From: Af <af-boun...@afmug.com <mailto:af-boun...@afmug.com>> on behalf of 
> George Skorup <george.sko...@cbcast.com <mailto:george.sko...@cbcast.com>>
> Sent: Saturday, May 20, 2017 4:55:25 PM
> To: af@afmug.com <mailto:af@afmug.com>
> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
>  
> List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
> PSUI. Plus $15 for the temp probe.
> 
> Are you asking run time? I have a couple with 40Ah of battery attached. A few 
> with about 90W load have ran for over four hours, but they never went down, 
> utility came back. A couple others with ~190-220W. Lost utility at one of the 
> sites the other day. It was running for about an hour and a half before I 
> brought a portable gen out. That site didn't go down either. Couldn't let it, 
> too much traffic. And of course utility came back 15 minutes after I got the 
> generator going.
> 
>  
> 
> Gino A. Villarini
> 
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
> 
> 
> On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
>> How much are you paying for the Traco and how long does it last?
>> 
>> On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com 
>> <mailto:af-boun...@afmug.com>
>> ï¿1Ž2
>> 
>> Gino A. Villarini
>> 
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>> 
>> 
>> on behalf of george.sko...@cbcast.com <mailto:george.sko...@cbcast.com>> 
>> wrote:
>> 
>> >Mean Well AD-155B
>> >or
>> >Mean Well SDR-240-24 + DR-UPS40
>> >or
>> >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>> >or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>> >continuous.
>> >
>> >All this stuff is fine until you start looking to deploy things that are
>> >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>> >multiple AF24s or licensed radios, etc. Then you need big-boy
>> >rectifiers, which aren't all that expensive, but they aren't cheap
>> >either. Add good telco-grade batteries on top and it's easily 10x the
>> >cost of what we're used to with the smaller stuff.
>> >
>> >On 5/20/2017 1:16 PM, Matt wrote:
>> >> What is everyone using for switching from AC to battery backup at sites?
>> >>
>> >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally
>> >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> >> that monitors power supply output and battery voltage and some DIN
>> >> mount module that does charging and switching between the two.ï¿1Ž2 Also
>> >> have a 24V to 48V converter to power our 450i etc stuff.
>> >>
>> >> Monitor the site monitor with SNMP and start emailing alarms if power
>> >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
>> >> with MRTG.
>> >>
>> >> Curious what others are using here?
>> >



Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-21 Thread Lewis Bergman
Yea...i lean towards putting mow batteries in with the money you would have
spent on a genset.

On Sun, May 21, 2017, 9:50 AM Chuck McCown <ch...@wbmfg.com> wrote:

> You can always 100% rely on a standby generator not starting when you need
> it the most.
>
> *From:* Jesse Dupont
> *Sent:* Sunday, May 21, 2017 7:02 AM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
> Well, that is a concern. I think we'll be under 30A after all is said and
> done and the DR-UPS40 handles 40A. Downside would be the 2A charging rate.
> I should note this site will have an automatic standby generator so we
> won't need a huge battery string.
>
> --
> *From:* Af <af-boun...@afmug.com> on behalf of Gino A. Villarini <
> g...@aeronetpr.com>
> *Sent:* Sunday, May 21, 2017 4:47:19 AM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
>
> How do you plan to connect to batteries for this setup ?
>
> From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont <
> jesse.dup...@celeritycorp.net>
> Reply-To: "af@afmug.com" <af@afmug.com>
> Date: Saturday, May 20, 2017 at 7:07 PM
> To: "af@afmug.com" <af@afmug.com>
> Subject: Re: [AFMUG] 24V Battery Revert and Charge Module
>
> The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to
> 8 of those in parallel to have a lot of capacity and N+1 redundancy without
> the DR-RDN20 redundancy module.
>
> We're getting ready to do a four unit N+1 at a site that has 16-17 Amps
> already and is getting some LTE base stations added to it.
>
> --
> *From:* Af <af-boun...@afmug.com> on behalf of George Skorup <
> george.sko...@cbcast.com>
> *Sent:* Saturday, May 20, 2017 4:55:25 PM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] 24V Battery Revert and Charge Module
>
> List price on the BCMU360 is about $215 IIRC. I think we pay about $175
> from PSUI. Plus $15 for the temp probe.
>
> Are you asking run time? I have a couple with 40Ah of battery attached. A
> few with about 90W load have ran for over four hours, but they never went
> down, utility came back. A couple others with ~190-220W. Lost utility at
> one of the sites the other day. It was running for about an hour and a half
> before I brought a portable gen out. That site didn't go down either.
> Couldn't let it, too much traffic. And of course utility came back 15
> minutes after I got the generator going.
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
>
> How much are you paying for the Traco and how long does it last?
>
> On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com
>
> ï¿1Ž2
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> on behalf of george.sko...@cbcast.com> wrote:
>
> >Mean Well AD-155B
> >or
> >Mean Well SDR-240-24 + DR-UPS40
> >or
> >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
> >or 48) - I use this combo most often. The BCMU360 is only good for ~240W
> >continuous.
> >
> >All this stuff is fine until you start looking to deploy things that are
> >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
> >multiple AF24s or licensed radios, etc. Then you need big-boy
> >rectifiers, which aren't all that expensive, but they aren't cheap
> >either. Add good telco-grade batteries on top and it's easily 10x the
> >cost of what we're used to with the smaller stuff.
> >
> >On 5/20/2017 1:16 PM, Matt wrote:
> >> What is everyone using for switching from AC to battery backup at sites?
> >>
> >> I normally have our other guy take care of that part.ï¿1Ž2 But we
> normally
> >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
> >> that monitors power supply output and battery voltage and some DIN
> >> mount module that does charging and switching between the two.ï¿1Ž2 Also
> >> have a 24V to 48V converter to power our 450i etc stuff.
> >>
> >> Monitor the site monitor with SNMP and start emailing alarms if power
> >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
> >> with MRTG.
> >>
> >> Curious what others are using here?
> >
>
>
>


Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-21 Thread Chuck McCown
You can always 100% rely on a standby generator not starting when you need it 
the most.

From: Jesse Dupont 
Sent: Sunday, May 21, 2017 7:02 AM
To: af@afmug.com 
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

Well, that is a concern. I think we'll be under 30A after all is said and done 
and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should 
note this site will have an automatic standby generator so we won't need a huge 
battery string.




From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini 
<g...@aeronetpr.com>
Sent: Sunday, May 21, 2017 4:47:19 AM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 

How do you plan to connect to batteries for this setup ?

From: Af <af-boun...@afmug.com> on behalf of Jesse Dupont 
<jesse.dup...@celeritycorp.net>
Reply-To: "af@afmug.com" <af@afmug.com>
Date: Saturday, May 20, 2017 at 7:07 PM
To: "af@afmug.com" <af@afmug.com>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module


The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of 
those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already 
and is getting some LTE base stations added to it.




From: Af <af-boun...@afmug.com> on behalf of George Skorup 
<george.sko...@cbcast.com>
Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module 

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.




  Gino A. Villarini
 
  President 
  Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 




On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

  How much are you paying for the Traco and how long does it last?

  On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" <af-boun...@afmug.com

ï¿1Ž2

Gino A. Villarini
   
President 
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 




  on behalf of george.sko...@cbcast.com> wrote:

  >Mean Well AD-155B
  >or
  >Mean Well SDR-240-24 + DR-UPS40
  >or
  >Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
  >or 48) - I use this combo most often. The BCMU360 is only good for ~240W
  >continuous.
  >
  >All this stuff is fine until you start looking to deploy things that are
  >power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
  >multiple AF24s or licensed radios, etc. Then you need big-boy
  >rectifiers, which aren't all that expensive, but they aren't cheap
  >either. Add good telco-grade batteries on top and it's easily 10x the
  >cost of what we're used to with the smaller stuff.
  >
  >On 5/20/2017 1:16 PM, Matt wrote:
  >> What is everyone using for switching from AC to battery backup at sites?
  >>
  >> I normally have our other guy take care of that part.ï¿1Ž2 But we normally
  >> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
  >> that monitors power supply output and battery voltage and some DIN
  >> mount module that does charging and switching between the two.ï¿1Ž2 Also
  >> have a 24V to 48V converter to power our 450i etc stuff.
  >>
  >> Monitor the site monitor with SNMP and start emailing alarms if power
  >> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
  >> with MRTG.
  >>
  >> Curious what others are using here?
  >





Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-21 Thread Jesse Dupont
Well, that is a concern. I think we'll be under 30A after all is said and done 
and the DR-UPS40 handles 40A. Downside would be the 2A charging rate. I should 
note this site will have an automatic standby generator so we won't need a huge 
battery string.


From: Af <af-boun...@afmug.com> on behalf of Gino A. Villarini 
<g...@aeronetpr.com>
Sent: Sunday, May 21, 2017 4:47:19 AM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

How do you plan to connect to batteries for this setup ?

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Jesse 
Dupont <jesse.dup...@celeritycorp.net<mailto:jesse.dup...@celeritycorp.net>>
Reply-To: "af@afmug.com<mailto:af@afmug.com>" 
<af@afmug.com<mailto:af@afmug.com>>
Date: Saturday, May 20, 2017 at 7:07 PM
To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of 
those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already 
and is getting some LTE base stations added to it.


From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of 
George Skorup <george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>>
Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.




Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]

On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" 
<af-boun...@afmug.com<mailto:af-boun...@afmug.com>

ï¿1Ž2

Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:part1.95843274.3D23CEA5@cbcast.com]

on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.ï¿1Ž2 But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.ï¿1Ž2 Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>




Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-21 Thread Gino A. Villarini
How do you plan to connect to batteries for this setup ?

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of Jesse 
Dupont <jesse.dup...@celeritycorp.net<mailto:jesse.dup...@celeritycorp.net>>
Reply-To: "af@afmug.com<mailto:af@afmug.com>" 
<af@afmug.com<mailto:af@afmug.com>>
Date: Saturday, May 20, 2017 at 7:07 PM
To: "af@afmug.com<mailto:af@afmug.com>" <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of 
those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already 
and is getting some LTE base stations added to it.


From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> on behalf of 
George Skorup <george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>>
Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.




Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]

On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" 
<af-boun...@afmug.com<mailto:af-boun...@afmug.com>

ï¿1Ž2

Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:part1.95843274.3D23CEA5@cbcast.com]

on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.ï¿1Ž2 But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.ï¿1Ž2 Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.ï¿1Ž2 Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>




Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread Jesse Dupont
The Meanwell SDR-480P-24 and -48 do current sharing so you can stack up to 8 of 
those in parallel to have a lot of capacity and N+1 redundancy without the 
DR-RDN20 redundancy module.

We're getting ready to do a four unit N+1 at a site that has 16-17 Amps already 
and is getting some LTE base stations added to it.


From: Af <af-boun...@afmug.com> on behalf of George Skorup 
<george.sko...@cbcast.com>
Sent: Saturday, May 20, 2017 4:55:25 PM
To: af@afmug.com
Subject: Re: [AFMUG] 24V Battery Revert and Charge Module

List price on the BCMU360 is about $215 IIRC. I think we pay about $175 from 
PSUI. Plus $15 for the temp probe.

Are you asking run time? I have a couple with 40Ah of battery attached. A few 
with about 90W load have ran for over four hours, but they never went down, 
utility came back. A couple others with ~190-220W. Lost utility at one of the 
sites the other day. It was running for about an hour and a half before I 
brought a portable gen out. That site didn't go down either. Couldn't let it, 
too much traffic. And of course utility came back 15 minutes after I got the 
generator going.

On 5/20/2017 4:51 PM, Gino A. Villarini wrote:
How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup" 
<af-boun...@afmug.com<mailto:af-boun...@afmug.com>

�

Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:part1.95843274.3D23CEA5@cbcast.com]

on behalf of george.sko...@cbcast.com<mailto:george.sko...@cbcast.com>> wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.� But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.� Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.� Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>




Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread George Skorup
List price on the BCMU360 is about $215 IIRC. I think we pay about $175 
from PSUI. Plus $15 for the temp probe.


Are you asking run time? I have a couple with 40Ah of battery attached. 
A few with about 90W load have ran for over four hours, but they never 
went down, utility came back. A couple others with ~190-220W. Lost 
utility at one of the sites the other day. It was running for about an 
hour and a half before I brought a portable gen out. That site didn't go 
down either. Couldn't let it, too much traffic. And of course utility 
came back 15 minutes after I got the generator going.


On 5/20/2017 4:51 PM, Gino A. Villarini wrote:

How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup"  wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at 
sites?

>>
>> I normally have our other guy take care of that part.  But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.  Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.  Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>





Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread Gino A. Villarini
How much are you paying for the Traco and how long does it last?

On 5/20/17, 4:44 PM, "Af on behalf of George Skorup"  wrote:

>Mean Well AD-155B
>or
>Mean Well SDR-240-24 + DR-UPS40
>or
>Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24
>or 48) - I use this combo most often. The BCMU360 is only good for ~240W
>continuous.
>
>All this stuff is fine until you start looking to deploy things that are
>power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each,
>multiple AF24s or licensed radios, etc. Then you need big-boy
>rectifiers, which aren't all that expensive, but they aren't cheap
>either. Add good telco-grade batteries on top and it's easily 10x the
>cost of what we're used to with the smaller stuff.
>
>On 5/20/2017 1:16 PM, Matt wrote:
>> What is everyone using for switching from AC to battery backup at sites?
>>
>> I normally have our other guy take care of that part.  But we normally
>> have a DIN mount 24V power supply, a DIN mount packetflux site monitor
>> that monitors power supply output and battery voltage and some DIN
>> mount module that does charging and switching between the two.  Also
>> have a 24V to 48V converter to power our 450i etc stuff.
>>
>> Monitor the site monitor with SNMP and start emailing alarms if power
>> supply voltage drops.  Also graph power supply and battery voltage
>> with MRTG.
>>
>> Curious what others are using here?
>



Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread George Skorup

Mean Well AD-155B
or
Mean Well SDR-240-24 + DR-UPS40
or
Mean Well SDR-240-24 (or 48) + Traco BCMU360 (jumper selectable for 24 
or 48) - I use this combo most often. The BCMU360 is only good for ~240W 
continuous.


All this stuff is fine until you start looking to deploy things that are 
power hungry like 450m's @ 70W, LTE eNB's that pull 60-100W each, 
multiple AF24s or licensed radios, etc. Then you need big-boy 
rectifiers, which aren't all that expensive, but they aren't cheap 
either. Add good telco-grade batteries on top and it's easily 10x the 
cost of what we're used to with the smaller stuff.


On 5/20/2017 1:16 PM, Matt wrote:

What is everyone using for switching from AC to battery backup at sites?

I normally have our other guy take care of that part.  But we normally
have a DIN mount 24V power supply, a DIN mount packetflux site monitor
that monitors power supply output and battery voltage and some DIN
mount module that does charging and switching between the two.  Also
have a 24V to 48V converter to power our 450i etc stuff.

Monitor the site monitor with SNMP and start emailing alarms if power
supply voltage drops.  Also graph power supply and battery voltage
with MRTG.

Curious what others are using here?




Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread Bill Prince
If you are using a DC UPS, there is no switching required on your part. 
The load, batteries and AC line in are all separate from each other. If 
AC line voltage is active, power comes from there. If AC line voltage is 
not active, then power comes from the batteries. If the controller has 
LVD, it will maintain until the batteries get to the LVD. If it doesn't 
have LVD, then the controller  will maintain until the batteries are 
depleted.


If you are just using a smart charger, you hook the load directly to the 
batteries, and hang tough. No switching required here either.



bp


On 5/20/2017 11:16 AM, Matt wrote:

What is everyone using for switching from AC to battery backup at sites?

I normally have our other guy take care of that part.  But we normally
have a DIN mount 24V power supply, a DIN mount packetflux site monitor
that monitors power supply output and battery voltage and some DIN
mount module that does charging and switching between the two.  Also
have a 24V to 48V converter to power our 450i etc stuff.

Monitor the site monitor with SNMP and start emailing alarms if power
supply voltage drops.  Also graph power supply and battery voltage
with MRTG.

Curious what others are using here?




Re: [AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread Chuck McCown
Not totally sure what you are asking here.  Normally there is no switching. 
Everything is running the DC bus.  When AC fails the rectifier/power supply 
just stops supplying DC power to the bus.  So the batts supply the current. 
Power comes back on and the rectifier once again powers the loads and 
charges the batts.


-Original Message- 
From: Matt

Sent: Saturday, May 20, 2017 12:16 PM
To: af@afmug.com
Subject: [AFMUG] 24V Battery Revert and Charge Module

What is everyone using for switching from AC to battery backup at sites?

I normally have our other guy take care of that part.  But we normally
have a DIN mount 24V power supply, a DIN mount packetflux site monitor
that monitors power supply output and battery voltage and some DIN
mount module that does charging and switching between the two.  Also
have a 24V to 48V converter to power our 450i etc stuff.

Monitor the site monitor with SNMP and start emailing alarms if power
supply voltage drops.  Also graph power supply and battery voltage
with MRTG.

Curious what others are using here? 



[AFMUG] 24V Battery Revert and Charge Module

2017-05-20 Thread Matt
What is everyone using for switching from AC to battery backup at sites?

I normally have our other guy take care of that part.  But we normally
have a DIN mount 24V power supply, a DIN mount packetflux site monitor
that monitors power supply output and battery voltage and some DIN
mount module that does charging and switching between the two.  Also
have a 24V to 48V converter to power our 450i etc stuff.

Monitor the site monitor with SNMP and start emailing alarms if power
supply voltage drops.  Also graph power supply and battery voltage
with MRTG.

Curious what others are using here?