Re: [AFMUG] CAT5e/6 tower grounding

2016-12-05 Thread Paul McCall
My 2 cents.  Never assume ANYTHING about existing ground at the tower, at the 
shelter, at the service panel.  Measure everything.  If you get a sub-Ohm 
measurement you are tied into a loop which may or MAY NOT actually be 
“effectually” grounded. Remember that CADWelds can break with a strong enough 
strike, so a ground ring around in or outside of a shelter may indeed have poor 
grounds to the actual earth.  We put in inspection boxes (sprinkler boxes) at 
every connection point to be able to come back later and test.

50% of the commercial towers we tested had at least one leg of their tower 
grounds be under spec.  For us, (and the cell guys) spec is <5ohm, but if all 
points were at 8 ohm I wouldn’t freak out.  More than 50% of the electrical 
panels we pull from had poor ground.  We either forced the tower companies to 
fix the problem or if they didn’t, magically it would get fixed in the middle 
of the night.  Pays BIG dividends in Florida.

From: Af [mailto:af-boun...@afmug.com] On Behalf Of Justin Wilson
Sent: Friday, December 2, 2016 1:21 PM
To: af@afmug.com
Subject: Re: [AFMUG] CAT5e/6 tower grounding

http://wirelessestimator.com/content/standards/eia_tia_222/protective-grounding-standard

this is a good start.

https://sites.auburn.edu/admin/facilities/spw-bid-calendar/11-150%20AU%20Regional%20Airport-Construct%20a%20Self-Supporting%20Radio%20Tower/Project%20Documents/1/Motorola_R56_2005_manual.pdf



Justin Wilson
j...@mtin.net<mailto:j...@mtin.net>

---
http://www.mtin.net Owner/CEO
xISP Solutions- Consulting – Data Centers - Bandwidth
http://www.midwest-ix.com  COO/Chairman
Internet Exchange - Peering - Distributed Fabric

On Nov 22, 2016, at 7:54 PM, Dev 
mailto:d...@logicalwebhost.com>> wrote:

I’ve heard it’s good to ground multiple places, like up by the radio, down by 
the turn to the ice bridge and inside the shelter, but how do you that (and is 
it necessary) with CAT5e/6? Do you strip a section off the insulation and tie 
the drain wire to multiple ground lugs? Sounds hard to do and not get water in 
the cable. I just have been running surge suppressors inside the building that 
the cable plugs into before heading to the switches/etc. What should I be doing?



Re: [AFMUG] CAT5e/6 tower grounding

2016-12-02 Thread Justin Wilson
http://wirelessestimator.com/content/standards/eia_tia_222/protective-grounding-standard
 


this is a good start.

https://sites.auburn.edu/admin/facilities/spw-bid-calendar/11-150%20AU%20Regional%20Airport-Construct%20a%20Self-Supporting%20Radio%20Tower/Project%20Documents/1/Motorola_R56_2005_manual.pdf
 




Justin Wilson
j...@mtin.net

---
http://www.mtin.net Owner/CEO
xISP Solutions- Consulting – Data Centers - Bandwidth

http://www.midwest-ix.com  COO/Chairman
Internet Exchange - Peering - Distributed Fabric

> On Nov 22, 2016, at 7:54 PM, Dev  wrote:
> 
> I’ve heard it’s good to ground multiple places, like up by the radio, down by 
> the turn to the ice bridge and inside the shelter, but how do you that (and 
> is it necessary) with CAT5e/6? Do you strip a section off the insulation and 
> tie the drain wire to multiple ground lugs? Sounds hard to do and not get 
> water in the cable. I just have been running surge suppressors inside the 
> building that the cable plugs into before heading to the switches/etc. What 
> should I be doing?



Re: [AFMUG] CAT5e/6 tower grounding

2016-11-24 Thread Jaime Solorza
OK... Later as I on kitchen duty

On Nov 24, 2016 9:13 AM, "Faisal Imtiaz"  wrote:

> Hi Jamie,
>
> Happy Thanksgiving
>
> I would be interested in seeing some pictures of these that you are
> describing (if possible) and also if you have any ref. / docs/ explanation
> of the 'Franklin Method'
>
> Regards.
>
> Faisal Imtiaz
> Snappy Internet & Telecom
> 7266 SW 48 Street
> Miami, FL 33155
> Tel: 305 663 5518 x 232
>
> Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
>
> --
>
> *From: *"Jaime Solorza" 
> *To: *"Animal Farm" 
> *Sent: *Wednesday, November 23, 2016 4:33:44 PM
> *Subject: *Re: [AFMUG] CAT5e/6 tower grounding
>
> We ground all cables from antennas and/or radios at top by mast/tower and
> before it enters cabinets...we use two or three points depending on length
> of cable runs.   As I have stated before, we use an aerial rod with as a
> direct path to ground rod/ring we can install.
> We use the Franklin method which has worked well for us whether is an MDS,
> Schneider or Freewave radio using Heliax RF cable or a POE powered type
> radio such as Ubiquiti , Mimosa or Cambium using Ethernet cable.
>
> Happy Thanksgiving
>
> Jaime Solorza
> Wireless Systems Architect
> 915-861-1390
>
> On Wed, Nov 23, 2016 at 8:28 AM, Faisal Imtiaz 
> wrote:
>
>> There is a reason for grounding anything ...
>>
>> Just connecting stuff for the sake of connecting to ground is not a good
>> thing, actually is a bad thing.
>>
>> There is a reason why the outer core/conductor shield of LMR cable is
>> connected to the ground using the kits being described, and typically that
>> reason does not apply to the doing the same with Shielded Ethernet cable.
>>
>> I would strongly suggest that folks try to gain an understanding on what
>> they are doing and why they are doing it, rather than hey I see him do this
>> so I am going to do it as well...  :)
>>
>> There are a number of great documents that address what to do and why to
>> do so one such article was / is done by Chris S of Netonix ( posted in
>> the netonix forums), pretty comprehensive, and done with adequate
>> explanations.
>>
>> Regards.
>>
>> Faisal Imtiaz
>> Snappy Internet & Telecom
>> 7266 SW 48 Street
>> Miami, FL 33155
>> Tel: 305 663 5518 x 232
>>
>> Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
>>
>> --
>>
>> *From: *"Adam Moffett" 
>> *To: *af@afmug.com
>> *Sent: *Wednesday, November 23, 2016 10:18:51 AM
>> *Subject: *Re: [AFMUG] CAT5e/6 tower grounding
>>
>> I've never tried those ground kits in real life.  I'm assuming you
>> wouldn't use them on a foil shielded cable but rather one with armor.
>>
>> I don't think I would do it unless the tower owner made me do it.  Even
>> where I was told it had to be R56 the guy doing the inspection was happy
>> with an SS at the bottom for the Ethernet.
>>
>>
>> -- Original Message --
>> From: "That One Guy /sarcasm" 
>> To: "af@afmug.com" 
>> Sent: 11/22/2016 8:17:26 PM
>> Subject: Re: [AFMUG] CAT5e/6 tower grounding
>>
>> [image: Inline image 1][image: Inline image 2]
>>
>> On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:
>>
>>> Lots of opinions about this.  R56 doesn't really apply too well to
>>> things that are Ethernet and POE.
>>> Try to bring all grounds back to a single point.  Bond things together
>>> like the ice bridge to the tower so you are not counting on the mechanical
>>> connection to also be the lightning circuit.
>>>
>>> People using my products use the grounding RJ45 plugs which interconnect
>>> to my surge protectors.
>>> You never know which direction the surge will be coming from either.
>>> Many times it comes in on the power.
>>>
>>>
>>>
>>> -Original Message- From: Dev
>>> Sent: Tuesday, November 22, 2016 5:54 PM
>>> To: af@afmug.com
>>> Subject: [AFMUG] CAT5e/6 tower grounding
>>>
>>>
>>> I’ve heard it’s good to ground multiple places, like up by the radio,
>>> down by the turn to the ice bridge and inside the shelter, but how do you
>>> that (and is it necessary) with CAT5e/6? Do you strip a section off the
>>> insulation and tie the drain wire to multiple ground lugs? Sounds hard to
>>> do and not get water in the cable. I just have been running surge
>>> suppressors inside the building that the cable plugs into before heading to
>>> the switches/etc. What should I be doing?
>>>
>>
>>
>>
>> --
>> If you only see yourself as part of the team but you don't see your team
>> as part of yourself you have already failed as part of the team.
>>
>>
>>
>


Re: [AFMUG] CAT5e/6 tower grounding

2016-11-24 Thread Faisal Imtiaz
Hi Jamie, 

Happy Thanksgiving 

I would be interested in seeing some pictures of these that you are describing 
(if possible) and also if you have any ref. / docs/ explanation of the 
'Franklin Method' 

Regards. 

Faisal Imtiaz 
Snappy Internet & Telecom 
7266 SW 48 Street 
Miami, FL 33155 
Tel: 305 663 5518 x 232 

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net 

> From: "Jaime Solorza" 
> To: "Animal Farm" 
> Sent: Wednesday, November 23, 2016 4:33:44 PM
> Subject: Re: [AFMUG] CAT5e/6 tower grounding

> We ground all cables from antennas and/or radios at top by mast/tower and 
> before
> it enters cabinets...we use two or three points depending on length of cable
> runs. As I have stated before, we use an aerial rod with as a direct path to
> ground rod/ring we can install.
> We use the Franklin method which has worked well for us whether is an MDS,
> Schneider or Freewave radio using Heliax RF cable or a POE powered type radio
> such as Ubiquiti , Mimosa or Cambium using Ethernet cable.

> Happy Thanksgiving

> Jaime Solorza
> Wireless Systems Architect
> 915-861-1390

> On Wed, Nov 23, 2016 at 8:28 AM, Faisal Imtiaz < fai...@snappytelecom.net >
> wrote:

>> There is a reason for grounding anything ...

>> Just connecting stuff for the sake of connecting to ground is not a good 
>> thing,
>> actually is a bad thing.

>> There is a reason why the outer core/conductor shield of LMR cable is 
>> connected
>> to the ground using the kits being described, and typically that reason does
>> not apply to the doing the same with Shielded Ethernet cable.

>> I would strongly suggest that folks try to gain an understanding on what they
>> are doing and why they are doing it, rather than hey I see him do this so I 
>> am
>> going to do it as well... :)

>> There are a number of great documents that address what to do and why to do
>> so one such article was / is done by Chris S of Netonix ( posted in the
>> netonix forums), pretty comprehensive, and done with adequate explanations.

>> Regards.

>> Faisal Imtiaz
>> Snappy Internet & Telecom
>> 7266 SW 48 Street
>> Miami, FL 33155
>> Tel: 305 663 5518 x 232

>> Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net

>>> From: "Adam Moffett" < dmmoff...@gmail.com >
>>> To: af@afmug.com
>>> Sent: Wednesday, November 23, 2016 10:18:51 AM
>>> Subject: Re: [AFMUG] CAT5e/6 tower grounding

>>> I've never tried those ground kits in real life. I'm assuming you wouldn't 
>>> use
>>> them on a foil shielded cable but rather one with armor.

>>> I don't think I would do it unless the tower owner made me do it. Even 
>>> where I
>>> was told it had to be R56 the guy doing the inspection was happy with an SS 
>>> at
>>> the bottom for the Ethernet.

>>> -- Original Message --
>>> From: "That One Guy /sarcasm" < thatoneguyst...@gmail.com >
>>> To: " af@afmug.com " < af@afmug.com >
>>> Sent: 11/22/2016 8:17:26 PM
>>> Subject: Re: [AFMUG] CAT5e/6 tower grounding

>>>> On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown < ch...@wbmfg.com > wrote:

>>>>> Lots of opinions about this. R56 doesn't really apply too well to things 
>>>>> that
>>>>> are Ethernet and POE.
>>>>> Try to bring all grounds back to a single point. Bond things together 
>>>>> like the
>>>>> ice bridge to the tower so you are not counting on the mechanical 
>>>>> connection to
>>>>> also be the lightning circuit.

>>>>> People using my products use the grounding RJ45 plugs which interconnect 
>>>>> to my
>>>>> surge protectors.
>>>>> You never know which direction the surge will be coming from either. Many 
>>>>> times
>>>>> it comes in on the power.

>>>>> -Original Message- From: Dev
>>>>> Sent: Tuesday, November 22, 2016 5:54 PM
>>>>> To: af@afmug.com
>>>>> Subject: [AFMUG] CAT5e/6 tower grounding

>>>>> I’ve heard it’s good to ground multiple places, like up by the radio, 
>>>>> down by
>>>>> the turn to the ice bridge and inside the shelter, but how do you that 
>>>>> (and is
>>>>> it necessary) with CAT5e/6? Do you strip a section off the insulation and 
>>>>> tie
>>>>> the drain wire to multiple ground lugs? Sounds hard to do and not get 
>>>>> water in
>>>>> the cable. I just have been running surge suppressors inside the building 
>>>>> that
>>>>> the cable plugs into before heading to the switches/etc. What should I be
>>>>> doing?

>>>> --
>>>> If you only see yourself as part of the team but you don't see your team 
>>>> as part
>>>> of yourself you have already failed as part of the team.


Re: [AFMUG] CAT5e/6 tower grounding

2016-11-23 Thread Jaime Solorza
We ground all cables from antennas and/or radios at top by mast/tower and
before it enters cabinets...we use two or three points depending on length
of cable runs.   As I have stated before, we use an aerial rod with as a
direct path to ground rod/ring we can install.
We use the Franklin method which has worked well for us whether is an MDS,
Schneider or Freewave radio using Heliax RF cable or a POE powered type
radio such as Ubiquiti , Mimosa or Cambium using Ethernet cable.

Happy Thanksgiving

Jaime Solorza
Wireless Systems Architect
915-861-1390

On Wed, Nov 23, 2016 at 8:28 AM, Faisal Imtiaz 
wrote:

> There is a reason for grounding anything ...
>
> Just connecting stuff for the sake of connecting to ground is not a good
> thing, actually is a bad thing.
>
> There is a reason why the outer core/conductor shield of LMR cable is
> connected to the ground using the kits being described, and typically that
> reason does not apply to the doing the same with Shielded Ethernet cable.
>
> I would strongly suggest that folks try to gain an understanding on what
> they are doing and why they are doing it, rather than hey I see him do this
> so I am going to do it as well...  :)
>
> There are a number of great documents that address what to do and why to
> do so one such article was / is done by Chris S of Netonix ( posted in
> the netonix forums), pretty comprehensive, and done with adequate
> explanations.
>
> Regards.
>
> Faisal Imtiaz
> Snappy Internet & Telecom
> 7266 SW 48 Street
> Miami, FL 33155
> Tel: 305 663 5518 x 232
>
> Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net
>
> --
>
> *From: *"Adam Moffett" 
> *To: *af@afmug.com
> *Sent: *Wednesday, November 23, 2016 10:18:51 AM
> *Subject: *Re: [AFMUG] CAT5e/6 tower grounding
>
> I've never tried those ground kits in real life.  I'm assuming you
> wouldn't use them on a foil shielded cable but rather one with armor.
>
> I don't think I would do it unless the tower owner made me do it.  Even
> where I was told it had to be R56 the guy doing the inspection was happy
> with an SS at the bottom for the Ethernet.
>
>
> -- Original Message --
> From: "That One Guy /sarcasm" 
> To: "af@afmug.com" 
> Sent: 11/22/2016 8:17:26 PM
> Subject: Re: [AFMUG] CAT5e/6 tower grounding
>
> [image: Inline image 1][image: Inline image 2]
>
> On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:
>
>> Lots of opinions about this.  R56 doesn't really apply too well to things
>> that are Ethernet and POE.
>> Try to bring all grounds back to a single point.  Bond things together
>> like the ice bridge to the tower so you are not counting on the mechanical
>> connection to also be the lightning circuit.
>>
>> People using my products use the grounding RJ45 plugs which interconnect
>> to my surge protectors.
>> You never know which direction the surge will be coming from either.
>> Many times it comes in on the power.
>>
>>
>>
>> -Original Message- From: Dev
>> Sent: Tuesday, November 22, 2016 5:54 PM
>> To: af@afmug.com
>> Subject: [AFMUG] CAT5e/6 tower grounding
>>
>>
>> I’ve heard it’s good to ground multiple places, like up by the radio,
>> down by the turn to the ice bridge and inside the shelter, but how do you
>> that (and is it necessary) with CAT5e/6? Do you strip a section off the
>> insulation and tie the drain wire to multiple ground lugs? Sounds hard to
>> do and not get water in the cable. I just have been running surge
>> suppressors inside the building that the cable plugs into before heading to
>> the switches/etc. What should I be doing?
>>
>
>
>
> --
> If you only see yourself as part of the team but you don't see your team
> as part of yourself you have already failed as part of the team.
>
>
>


Re: [AFMUG] CAT5e/6 tower grounding

2016-11-23 Thread chuck
I take part of that back, I once had a noisy telephone cable.  Rules say if 
your bonding is good the noise will go away.  In this case it was opposite.  
Turned out that the noise was not from magnetic coupling which is the reason 
you bond and ground the shields, but our cable was conduct a significant amount 
of neutral/ground current from the primary of the power line.  Their lack of 
grounding and bonding was the problem.  Once they fixed that I went back and 
grounded and bonded everything and we had a nice quiet line.  

From: ch...@wbmfg.com 
Sent: Wednesday, November 23, 2016 9:11 AM
To: af@afmug.com 
Subject: Re: [AFMUG] CAT5e/6 tower grounding

Just connecting stuff for the sake of bonding is always a good thing.  
Doing a PANI style common point ground is a good thing.  
Lightning damage is unpredictable, so no one set of rules or methods will 
always work.
Lightning can be modeled as a high number of sine waves and some of your cables 
and tower elements will form quarter wave transmission lines to certain 
elements of that energy thus not conducting it.  

Every strike has a different frequency distribution.

Lots of things out there on the internet, but most of it is pontificating from 
the point of view of an engineer.
In my opinion the only advise worth reading comes from those that have spend 
decades installing and maintaining gear on mountain tops and high lightning 
areas.  Best if they are the owners of the gear.  

And even those opinions are not totally good for you if they are from a 
different part of the country.  Lightning protection in Florida is different 
than in Utah.  

From: Faisal Imtiaz 
Sent: Wednesday, November 23, 2016 8:28 AM
To: af@afmug.com 
Subject: Re: [AFMUG] CAT5e/6 tower grounding

There is a reason for grounding anything ...

Just connecting stuff for the sake of connecting to ground is not a good thing, 
actually is a bad thing.

There is a reason why the outer core/conductor shield of LMR cable is connected 
to the ground using the kits being described, and typically that reason does 
not apply to the doing the same with Shielded Ethernet cable.

I would strongly suggest that folks try to gain an understanding on what they 
are doing and why they are doing it, rather than hey I see him do this so I am 
going to do it as well...  :)

There are a number of great documents that address what to do and why to do 
so one such article was / is done by Chris S of Netonix ( posted in the 
netonix forums), pretty comprehensive, and done with adequate explanations.

Regards. 

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net




  From: "Adam Moffett" 
  To: af@afmug.com
  Sent: Wednesday, November 23, 2016 10:18:51 AM
  Subject: Re: [AFMUG] CAT5e/6 tower grounding

  I've never tried those ground kits in real life.  I'm assuming you wouldn't 
use them on a foil shielded cable but rather one with armor. 

  I don't think I would do it unless the tower owner made me do it.  Even where 
I was told it had to be R56 the guy doing the inspection was happy with an SS 
at the bottom for the Ethernet.



  -- Original Message --
  From: "That One Guy /sarcasm" 
  To: "af@afmug.com" 
  Sent: 11/22/2016 8:17:26 PM
  Subject: Re: [AFMUG] CAT5e/6 tower grounding




On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:

  Lots of opinions about this.  R56 doesn't really apply too well to things 
that are Ethernet and POE.
  Try to bring all grounds back to a single point.  Bond things together 
like the ice bridge to the tower so you are not counting on the mechanical 
connection to also be the lightning circuit.

  People using my products use the grounding RJ45 plugs which interconnect 
to my surge protectors.
  You never know which direction the surge will be coming from either.  
Many times it comes in on the power.



  -Original Message- From: Dev
  Sent: Tuesday, November 22, 2016 5:54 PM
  To: af@afmug.com
  Subject: [AFMUG] CAT5e/6 tower grounding 


  I’ve heard it’s good to ground multiple places, like up by the radio, 
down by the turn to the ice bridge and inside the shelter, but how do you that 
(and is it necessary) with CAT5e/6? Do you strip a section off the insulation 
and tie the drain wire to multiple ground lugs? Sounds hard to do and not get 
water in the cable. I just have been running surge suppressors inside the 
building that the cable plugs into before heading to the switches/etc. What 
should I be doing? 




-- 

If you only see yourself as part of the team but you don't see your team as 
part of yourself you have already failed as part of the team.



Re: [AFMUG] CAT5e/6 tower grounding

2016-11-23 Thread chuck
Just connecting stuff for the sake of bonding is always a good thing.  
Doing a PANI style common point ground is a good thing.  
Lightning damage is unpredictable, so no one set of rules or methods will 
always work.
Lightning can be modeled as a high number of sine waves and some of your cables 
and tower elements will form quarter wave transmission lines to certain 
elements of that energy thus not conducting it.  

Every strike has a different frequency distribution.

Lots of things out there on the internet, but most of it is pontificating from 
the point of view of an engineer.
In my opinion the only advise worth reading comes from those that have spend 
decades installing and maintaining gear on mountain tops and high lightning 
areas.  Best if they are the owners of the gear.  

And even those opinions are not totally good for you if they are from a 
different part of the country.  Lightning protection in Florida is different 
than in Utah.  

From: Faisal Imtiaz 
Sent: Wednesday, November 23, 2016 8:28 AM
To: af@afmug.com 
Subject: Re: [AFMUG] CAT5e/6 tower grounding

There is a reason for grounding anything ...

Just connecting stuff for the sake of connecting to ground is not a good thing, 
actually is a bad thing.

There is a reason why the outer core/conductor shield of LMR cable is connected 
to the ground using the kits being described, and typically that reason does 
not apply to the doing the same with Shielded Ethernet cable.

I would strongly suggest that folks try to gain an understanding on what they 
are doing and why they are doing it, rather than hey I see him do this so I am 
going to do it as well...  :)

There are a number of great documents that address what to do and why to do 
so one such article was / is done by Chris S of Netonix ( posted in the 
netonix forums), pretty comprehensive, and done with adequate explanations.

Regards. 

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net




  From: "Adam Moffett" 
  To: af@afmug.com
  Sent: Wednesday, November 23, 2016 10:18:51 AM
  Subject: Re: [AFMUG] CAT5e/6 tower grounding

  I've never tried those ground kits in real life.  I'm assuming you wouldn't 
use them on a foil shielded cable but rather one with armor. 

  I don't think I would do it unless the tower owner made me do it.  Even where 
I was told it had to be R56 the guy doing the inspection was happy with an SS 
at the bottom for the Ethernet.



  -- Original Message --
  From: "That One Guy /sarcasm" 
  To: "af@afmug.com" 
  Sent: 11/22/2016 8:17:26 PM
  Subject: Re: [AFMUG] CAT5e/6 tower grounding




On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:

  Lots of opinions about this.  R56 doesn't really apply too well to things 
that are Ethernet and POE.
  Try to bring all grounds back to a single point.  Bond things together 
like the ice bridge to the tower so you are not counting on the mechanical 
connection to also be the lightning circuit.

  People using my products use the grounding RJ45 plugs which interconnect 
to my surge protectors.
  You never know which direction the surge will be coming from either.  
Many times it comes in on the power.



  -Original Message- From: Dev
  Sent: Tuesday, November 22, 2016 5:54 PM
  To: af@afmug.com
  Subject: [AFMUG] CAT5e/6 tower grounding 


  I’ve heard it’s good to ground multiple places, like up by the radio, 
down by the turn to the ice bridge and inside the shelter, but how do you that 
(and is it necessary) with CAT5e/6? Do you strip a section off the insulation 
and tie the drain wire to multiple ground lugs? Sounds hard to do and not get 
water in the cable. I just have been running surge suppressors inside the 
building that the cable plugs into before heading to the switches/etc. What 
should I be doing? 




-- 

If you only see yourself as part of the team but you don't see your team as 
part of yourself you have already failed as part of the team.



Re: [AFMUG] CAT5e/6 tower grounding

2016-11-23 Thread Faisal Imtiaz
There is a reason for grounding anything ... 

Just connecting stuff for the sake of connecting to ground is not a good thing, 
actually is a bad thing. 

There is a reason why the outer core/conductor shield of LMR cable is connected 
to the ground using the kits being described, and typically that reason does 
not apply to the doing the same with Shielded Ethernet cable. 

I would strongly suggest that folks try to gain an understanding on what they 
are doing and why they are doing it, rather than hey I see him do this so I am 
going to do it as well... :) 

There are a number of great documents that address what to do and why to do 
so one such article was / is done by Chris S of Netonix ( posted in the 
netonix forums), pretty comprehensive, and done with adequate explanations. 

Regards. 

Faisal Imtiaz 
Snappy Internet & Telecom 
7266 SW 48 Street 
Miami, FL 33155 
Tel: 305 663 5518 x 232 

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net 

> From: "Adam Moffett" 
> To: af@afmug.com
> Sent: Wednesday, November 23, 2016 10:18:51 AM
> Subject: Re: [AFMUG] CAT5e/6 tower grounding

> I've never tried those ground kits in real life. I'm assuming you wouldn't use
> them on a foil shielded cable but rather one with armor.

> I don't think I would do it unless the tower owner made me do it. Even where I
> was told it had to be R56 the guy doing the inspection was happy with an SS at
> the bottom for the Ethernet.

> -- Original Message --
> From: "That One Guy /sarcasm" < thatoneguyst...@gmail.com >
> To: "af@afmug.com" < af@afmug.com >
> Sent: 11/22/2016 8:17:26 PM
> Subject: Re: [AFMUG] CAT5e/6 tower grounding

>> On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown < ch...@wbmfg.com > wrote:

>>> Lots of opinions about this. R56 doesn't really apply too well to things 
>>> that
>>> are Ethernet and POE.
>>> Try to bring all grounds back to a single point. Bond things together like 
>>> the
>>> ice bridge to the tower so you are not counting on the mechanical 
>>> connection to
>>> also be the lightning circuit.

>>> People using my products use the grounding RJ45 plugs which interconnect to 
>>> my
>>> surge protectors.
>>> You never know which direction the surge will be coming from either. Many 
>>> times
>>> it comes in on the power.

>>> -Original Message- From: Dev
>>> Sent: Tuesday, November 22, 2016 5:54 PM
>>> To: af@afmug.com
>>> Subject: [AFMUG] CAT5e/6 tower grounding

>>> I’ve heard it’s good to ground multiple places, like up by the radio, down 
>>> by
>>> the turn to the ice bridge and inside the shelter, but how do you that (and 
>>> is
>>> it necessary) with CAT5e/6? Do you strip a section off the insulation and 
>>> tie
>>> the drain wire to multiple ground lugs? Sounds hard to do and not get water 
>>> in
>>> the cable. I just have been running surge suppressors inside the building 
>>> that
>>> the cable plugs into before heading to the switches/etc. What should I be
>>> doing?

>> --
>> If you only see yourself as part of the team but you don't see your team as 
>> part
>> of yourself you have already failed as part of the team.


Re: [AFMUG] CAT5e/6 tower grounding

2016-11-23 Thread Adam Moffett
I've never tried those ground kits in real life.  I'm assuming you 
wouldn't use them on a foil shielded cable but rather one with armor.


I don't think I would do it unless the tower owner made me do it.  Even 
where I was told it had to be R56 the guy doing the inspection was happy 
with an SS at the bottom for the Ethernet.



-- Original Message --
From: "That One Guy /sarcasm" 
To: "af@afmug.com" 
Sent: 11/22/2016 8:17:26 PM
Subject: Re: [AFMUG] CAT5e/6 tower grounding




On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:
Lots of opinions about this.  R56 doesn't really apply too well to 
things that are Ethernet and POE.
Try to bring all grounds back to a single point.  Bond things together 
like the ice bridge to the tower so you are not counting on the 
mechanical connection to also be the lightning circuit.


People using my products use the grounding RJ45 plugs which 
interconnect to my surge protectors.
You never know which direction the surge will be coming from either.  
Many times it comes in on the power.




-Original Message- From: Dev
Sent: Tuesday, November 22, 2016 5:54 PM
To: af@afmug.com
Subject: [AFMUG] CAT5e/6 tower grounding


I’ve heard it’s good to ground multiple places, like up by the radio, 
down by the turn to the ice bridge and inside the shelter, but how do 
you that (and is it necessary) with CAT5e/6? Do you strip a section 
off the insulation and tie the drain wire to multiple ground lugs? 
Sounds hard to do and not get water in the cable. I just have been 
running surge suppressors inside the building that the cable plugs 
into before heading to the switches/etc. What should I be doing?




--
If you only see yourself as part of the team but you don't see your 
team as part of yourself you have already failed as part of the team.

Re: [AFMUG] CAT5e/6 tower grounding

2016-11-22 Thread That One Guy /sarcasm
[image: Inline image 1][image: Inline image 2]

On Tue, Nov 22, 2016 at 7:14 PM, Chuck McCown  wrote:

> Lots of opinions about this.  R56 doesn't really apply too well to things
> that are Ethernet and POE.
> Try to bring all grounds back to a single point.  Bond things together
> like the ice bridge to the tower so you are not counting on the mechanical
> connection to also be the lightning circuit.
>
> People using my products use the grounding RJ45 plugs which interconnect
> to my surge protectors.
> You never know which direction the surge will be coming from either.  Many
> times it comes in on the power.
>
>
>
> -Original Message- From: Dev
> Sent: Tuesday, November 22, 2016 5:54 PM
> To: af@afmug.com
> Subject: [AFMUG] CAT5e/6 tower grounding
>
>
> I’ve heard it’s good to ground multiple places, like up by the radio, down
> by the turn to the ice bridge and inside the shelter, but how do you that
> (and is it necessary) with CAT5e/6? Do you strip a section off the
> insulation and tie the drain wire to multiple ground lugs? Sounds hard to
> do and not get water in the cable. I just have been running surge
> suppressors inside the building that the cable plugs into before heading to
> the switches/etc. What should I be doing?
>



-- 
If you only see yourself as part of the team but you don't see your team as
part of yourself you have already failed as part of the team.


Re: [AFMUG] CAT5e/6 tower grounding

2016-11-22 Thread Chuck McCown
Lots of opinions about this.  R56 doesn't really apply too well to things 
that are Ethernet and POE.
Try to bring all grounds back to a single point.  Bond things together like 
the ice bridge to the tower so you are not counting on the mechanical 
connection to also be the lightning circuit.


People using my products use the grounding RJ45 plugs which interconnect to 
my surge protectors.
You never know which direction the surge will be coming from either.  Many 
times it comes in on the power.




-Original Message- 
From: Dev

Sent: Tuesday, November 22, 2016 5:54 PM
To: af@afmug.com
Subject: [AFMUG] CAT5e/6 tower grounding

I’ve heard it’s good to ground multiple places, like up by the radio, down 
by the turn to the ice bridge and inside the shelter, but how do you that 
(and is it necessary) with CAT5e/6? Do you strip a section off the 
insulation and tie the drain wire to multiple ground lugs? Sounds hard to do 
and not get water in the cable. I just have been running surge suppressors 
inside the building that the cable plugs into before heading to the 
switches/etc. What should I be doing? 



[AFMUG] CAT5e/6 tower grounding

2016-11-22 Thread Dev
I’ve heard it’s good to ground multiple places, like up by the radio, down by 
the turn to the ice bridge and inside the shelter, but how do you that (and is 
it necessary) with CAT5e/6? Do you strip a section off the insulation and tie 
the drain wire to multiple ground lugs? Sounds hard to do and not get water in 
the cable. I just have been running surge suppressors inside the building that 
the cable plugs into before heading to the switches/etc. What should I be doing?