RE: EN 61000-3-3 compliant heater controller

2002-01-21 Thread Pettit, Ghery

So rather than educating the public on the cause of flicker, we get saddled
with a useless design requirement.  Typical bureaucracy - don't fix the
problem, make it LOOK like you're doing something, at someone else's
expense.  Just like the harmonics standard - fix a problem that doesn't
exist.

Ghery Pettit
Opinions expressed are my own and may not necessarily reflect those of my
employer...


-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Monday, January 21, 2002 2:28 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: EN 61000-3-3 compliant heater controller



I read in !emc-pstc that Ken Javor ken.ja...@emccompliance.com wrote
(in 20020121193650.LDSV11289.femail7.sdc1.sfba.home.com@[65.11.150.27]
) about 'EN 61000-3-3 compliant heater controller', on Mon, 21 Jan 2002:

I have some questions which are just for my own education.  I understand
Mr.
Woodgate's comments and they make sense to me.  But I wonder why there is a
problem in the first place. 

I assumed that the lack of compliance was certain, because I have no up-
front evidence to sustain a doubt.
 
 I believe all power in Europe is at 200 Volts
or higher, which makes an 800 Watt heater a four Amp device.  I don't
believe inrush on a heater is greatly in excess of steady-state current,

Suppose, just as an example, it's an 800 W IR lamp, used as a heater?

therefore the mechanism is switching a four Amp load on and off every few
minutes.  Why is this a problem requiring specification control in the
first
place?

Because lamp flicker is a disturbance that worries people and they often
complain to the electricity suppliers. Some elderly people get very
worried about the supply breaking down or causing a fire.

The reference single-phase supply impedance used for IEC/EN61000-3-3 is
0.47 ohms (actually 0.4 + j0.25 ohms). So switching a 4 A load causes a
dmax (maximum relative voltage drop, based on 230 V) of 0.8%. That is
not likely to result in a Pst or Plt failure to comply, so there IS
something we don't know - maybe a high inrush current or a faulty
measurement.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

After swimming across the Hellespont, I felt like a Hero.
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Pacemaker

2002-01-21 Thread Ted Rook

 cecil.gitt...@kodak.com 18-Jan-02 1:20:16 PM 

From: Cecil A. Gittens

If someone has a pacemaker and wants to use a APS Camera with an internal
clock 8MHz
on the main CPU circuit board.
My question is it safe for that person to use the APS Camera



Reply: 

APS camera is a traditional 35mm system camera. 

APS is a magnetic code stripe on the film which records exposure data for use 
by the color paper printing machine. It has the added benefit of drop in 
loading.

There may be a clock in the autofocus mechanism but the camera is not a digital 
camera, it does not generate an image file, so why the 8MHz clock?

Or was this a trick question from Kodak?





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: EN 61000-3-3 compliant heater controller

2002-01-21 Thread John Woodgate

I read in !emc-pstc that Ken Javor ken.ja...@emccompliance.com wrote
(in 20020121193650.LDSV11289.femail7.sdc1.sfba.home.com@[65.11.150.27]
) about 'EN 61000-3-3 compliant heater controller', on Mon, 21 Jan 2002:

I have some questions which are just for my own education.  I understand Mr.
Woodgate's comments and they make sense to me.  But I wonder why there is a
problem in the first place. 

I assumed that the lack of compliance was certain, because I have no up-
front evidence to sustain a doubt.
 
 I believe all power in Europe is at 200 Volts
or higher, which makes an 800 Watt heater a four Amp device.  I don't
believe inrush on a heater is greatly in excess of steady-state current,

Suppose, just as an example, it's an 800 W IR lamp, used as a heater?

therefore the mechanism is switching a four Amp load on and off every few
minutes.  Why is this a problem requiring specification control in the first
place?

Because lamp flicker is a disturbance that worries people and they often
complain to the electricity suppliers. Some elderly people get very
worried about the supply breaking down or causing a fire.

The reference single-phase supply impedance used for IEC/EN61000-3-3 is
0.47 ohms (actually 0.4 + j0.25 ohms). So switching a 4 A load causes a
dmax (maximum relative voltage drop, based on 230 V) of 0.8%. That is
not likely to result in a Pst or Plt failure to comply, so there IS
something we don't know - maybe a high inrush current or a faulty
measurement.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero.
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Zero Crossing Question

2002-01-21 Thread jrbarnes



John,
Or another example where different companies' equivalent parts are not
equivalent-- this is one that I ran into in 1977.  I had designed a
Power-On-Reset (POR) circuit using a 555 timer, and had tested the circuit on a
solderless breadboard.  I was being sneaky in my design, and used the RESET,
TRIGGER, and THRESHOLD inputs as three separate inputs to the 555.  When we
built the first tester the POR circuit didn't work.  I then discovered that
there were two flavors of 555 timers-- TI's and most companies 555's obeyed
TRIGGER if(TRIGGER  1/3*VCC) AND (THRESHOLD  2/3*VCC).  But the National
Semiconductor LM555, which we used when we built the tester, obeyed THRESHOLD
instead...  Since this is an undefined input state for the 555, the chip
designers did as they pleased.

I have heard of many other cases  where engineers have used components outside
the published specifications, and gotten burned for their trouble.  Bob Pease
has written several Pease Porridge columns in Electronic Design about
specmanship, and about how Design Engineers and Applications Engineers at chip
manufacturers *try* to write honest datasheets over the objections of the
marketeers.  His best advice was:
1.  If in doubt, try it out.
2.  If an unspecified characteristic is important to you, contact the
manufacturer and get them to guarantee it in
 writing.

You may find yourself having to retest your design every time the chip
manufacturer does a die shrink or moves the chip to a different process or
plant.  But you are much better off to find this out early, and have time to
find a suitable alternative part or make a lifetime buy of the older (working)
part than to suddenly have 100% of your products fail in production.

 John Barnes  Advisory Engineer
 Lexmark International

 (soon to be   Chief Engineer, dBi
Corporation)



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


SV: Company close down due to EMC phenomena

2002-01-21 Thread amund

To all of you who responded, here is the latest info.

I have picked up the following:
1. 15000 units have been placed on the marked and 2 complains have been
reported to the Telecommunications Authorities. They could not produce any
evidence that the PLC made the problems, but they were unfortunately
installed close by the victim. The victim might have had poor immunity .
who knows 
2. The conducted emission is far above the limits (50-60dB) in the
transmission band so it do not fulfil EN55022 or any other emission
standard.
3. Finally, the telecommunications Authorities will do a more thorough
investigation next time a problem/complain pops up.

So, from this it seems that they are not closing down yet ..

I agree 100% about your statements that you have to be aware the technical
regulations before you start up any type of electrical/electronic business.
I do not know these PLC folks, but they might have followed this doctrine
If it is allowed in US, then it must be allowed in EU ...

... in good faith

Amund







-Opprinnelig melding-
Fra: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]På vegne av
am...@westin-emission.no
Sendt: 16. januar 2002 21:17
Til: emc-p...@majordomo.ieee.org
Emne: Company close down due to EMC phenomena



Well, this might be the reality in a case I have been introduced to lately.

Case:
A company are manufacturing PowerLine Communication products. They
communicate via the power lines and a typical link is between a consumer
residence and the nearest power station. The products can of course also
communicate inside the consumers residence. The communication protocol is
called CEBus http://www.cebus.org/which and make use of the frequency band
100kHz-400kHz and the amplitude is approximate 2-5V. A typical length of a
transmission is 25ms and occurs approximate one time pr hour.

First of all, AFAIK PowerLine Communication and PowerLine Transmission
(broadband 1.6MHz-30MHz) are now coming will full force in EU and
CENELEC/ETSI are working together regulate this type of transmission path
and also coming up with standards.

The problem for the manufacturer is the conducted emission requirements in
EU. According to the EN55022B levels the maximum quasi-peak emission is
66dBuV@150kHz, and a typical PLC (under transmission) which has been
measured, showed the value of 120dBuV (peak). With no transmission it had a
margin of 10dB (quasi-peak) and 30dB (average). The radiated emission had a
margin of 10dB.

Well, conducted emission is the problem when transmitting. But, as I said,
the transmission occurs only 25ms/hour.

The national authority will not allowed this product to be placed into the
marked because it do not fulfil the EN55022B limits (100kHz-400kHz) under
transmission mode. No way.

Other national authorities have other approaches on this case, they say  as
long as you do not disturb other equipment, install it. If you do disturb,
we will come and remove it. They also say  install it even if it does not
fulfil EN550022B, but we will remove it if it disturb others.

Two completely different approaches as you see.

Questions:
1. Is it possible to have different approaches within EU ?
2. Since PLC/PLT is quite new technology and since we do not have any EU
product standard (no standard for whose who are using 100kHz-400kHz band), I
like the approach as long as you do not disturb other equipment, install
it. If you do disturb, we will come and remove it. What is your opinion
about this?
3. The transmission occurs very seldom. 25ms/hour, that is 7e-6 and
approximate 0,001% transmission rate. Can this seldom transmission rate be
an argument to not test the PLC product under continuous transmission ? I
would say yes, but which rate is acceptable / reasonable ?

So, why should the company close down ? Because if the national authority
gets what they want, there will be one sale. Logical, but is it a correct
prohibition the authority call?


Best regards
Amund Westin, Oslo/Norway







---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site 

Re: EN 61000-3-3 compliant heater controller

2002-01-21 Thread Ken Javor

I have some questions which are just for my own education.  I understand Mr.
Woodgate's comments and they make sense to me.  But I wonder why there is a
problem in the first place.  I believe all power in Europe is at 200 Volts
or higher, which makes an 800 Watt heater a four Amp device.  I don't
believe inrush on a heater is greatly in excess of steady-state current,
therefore the mechanism is switching a four Amp load on and off every few
minutes.  Why is this a problem requiring specification control in the first
place?

--
From: Leszek Langiewicz leszek_langiew...@phogenix.com
To: emc-p...@majordomo.ieee.org
Subject: EN 61000-3-3 compliant heater controller
Date: Mon, Jan 21, 2002, 12:01 PM



 Dear list-members,

 Would anybody know of the shelf controller design to meet EN61000-3-3
 for 500W heater.
 Thanks in advance for your support.


 Best Regards,
 Leszek M. Langiewicz
 Homologation / Power Distribution
 Phogenix Imaging, LLC
 A joint venture of Kodak and HP
 Phogenix Imaging LLC   16275 Technology Dr. San Diego, CA 92127-1815
 www.phogenix.com
 Phone: (858) 798-8004  Cell: (858) 722-8004  Fax: (858) 798-8113
 E-mail: leszek_langiew...@phogenix.com

  -Original Message-
 From:  John Woodgate [mailto:j...@jmwa.demon.co.uk]
 Sent: Sunday, January 20, 2002 6:30 AM
 To: emc-p...@majordomo.ieee.org
 Subject: Re: Corrective Actions for EN 61000-3-3 Plt; Pst
 Failures


 I read in !emc-pstc that IEEE-EMC User Group ieee-...@itl.co.il wrote
 (in 2D1037012914D4118DB8204C4F4F5020275AB4@ITLLTD01) about 'Corrective
 Actions for EN 61000-3-3 Plt; Pst Failures', on Sun, 20 Jan 2002:
A product (800W input power) having a heating element that is
 controlled by
ON/OFF action (1-2 sec. interval) of a thermostat failed the subject
requirements due to large input current variation resulting from the
 above
action.

 It's unusual to have such a powerful heater in a product with such a low
 thermal inertia that the thermostat cycle is as short as 1 to 2 s.

What will be a practical corrective action in this case?

 To answer properly, more details about the product would be required. It
 might be possible to split the heating element into two parts, not
 necessarily of equal powers, and to have one permanently on (apart from
 an over-temperature cut-out) while the other one is switched in and out
 by the thermostat. The cycle time should then become much longer, and
 the 'dmax' value is reduced.

 Another solution is to use the electronic control method known as 'burst
 firing', in which the thermostat switches on a control circuit that
 sends trains of complete cycles of the supply current to the heater.
 With different designs, the switching of the load is either very fast
 (e.g. 5-cycle bursts of current, lasting 100 ms on 50 Hz mains) or very
 slow. In either case, the Pst value is low.
 --
 Regards, John Woodgate, OOO - Own Opinions Only.
 http://www.jmwa.demon.co.uk
 After swimming across the Hellespont, I felt like a Hero.

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
  

RE: Zero Crossing Question

2002-01-21 Thread Allen, John

Hi Folks
 
Could this ON Semiconductors problem be something to do with: 
 
a) The fact that the neutral is generally not at ground potential, but has
floated up due the current flowing in it?
 
or 
 
b) The actual PSU has a filtering arrangement that is non-symmetrical wrt
true ground?
 (Often evidenced by the leakage current differing when Line and Neutral
are reversed)
 
John Allen

-Original Message-
From: Bouse, John [mailto:john.bo...@perkinelmer.com]
Sent: 21 January 2002 14:20
To: emc-p...@majordomo.ieee.org
Subject: Zero Crossing Question



Hi Group, 

Our manufacturing personnel encountered a strange problem:  when the mains
plug used on a 
230V/50Hz equipment that has an internal zero crossing reference integrated
circuit (specifically, 
a CA3059) is reversed (this can occur in countries such as Germany, Italy,
France and Switzerland),  
the zero crossing pulses appear with a 20 millisecond spacing,  rather than
the expected 10 millisecond 
spacing. 

Harris or Intersil IC's work properly regardless of the mains polarity. ON
Semiconductor IC's appear 
to be polarity sensitive. They will produce the proper number of pulses with
only one mains polarity. 
The incorrect spacing of these zero crossing pulses affects the normal
operation of the equipment. 

Has anyone encountered and, hopefully, solved this problem? 

Regards, 
John Bouse 
PKI 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Zero Crossing Question

2002-01-21 Thread Scott Lacey
Zero Crossing QuestionJohn,
I think you already have the answer to the problem. You stated that Harris
or Intersil IC's work properly regardless of the mains polarity. Some years
back I had an issue where another manufacturer's replacement was substituted
for a Sprague ULN2003 Darlington Array that I had specified in a design. I
was using the ULN2003 to buffer a reset pulse distributed in a system. The
other brand was not capable of switching quickly enough in this application.
Replacing the ICs with the specified part solved the problem.

I would not waste valuable engineering time resolving an issue that only
occurs with one vendor's part.

Just one man's opinion,
Scott Lacey

Simplicate, don't complicate!

  -Original Message-
  From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Bouse, John
  Sent: Monday, January 21, 2002 9:20 AM
  To: emc-p...@majordomo.ieee.org
  Subject: Zero Crossing Question


  Hi Group,

  Our manufacturing personnel encountered a strange problem:  when the mains
plug used on a
  230V/50Hz equipment that has an internal zero crossing reference
integrated circuit (specifically,
  a CA3059) is reversed (this can occur in countries such as Germany, Italy,
France and Switzerland),
  the zero crossing pulses appear with a 20 millisecond spacing,  rather
than the expected 10 millisecond
  spacing.

  Harris or Intersil IC's work properly regardless of the mains polarity. ON
Semiconductor IC's appear
  to be polarity sensitive. They will produce the proper number of pulses
with only one mains polarity.
  The incorrect spacing of these zero crossing pulses affects the normal
operation of the equipment.

  Has anyone encountered and, hopefully, solved this problem?

  Regards,
  John Bouse
  PKI



RE: pacemakers

2002-01-21 Thread richwoods

It is well known in the medical device community that the immunity standards
for implanted medical devices and the emissions standards for electrical
devices are not compatible. Pacemakers have an operations mode that is used
when excessive noise is detected. That mode goes by several names including
fixed rate pacing, noise mode and reversion. The FDA is well aware of the
issue and finds that the reversion mode is safe. Nevertheless, in some noise
cases the PM may not properly detect the noise situation and operation may
become affected including loss of a pacing pulse or an extra pulse may be
generated. In the case of rate adaptive PMs, the pulse rate may increase. In
some cases, the patient may become aware of the affected operation and find
the effect to be undesirable. This is why the patient manual warns to avoid
many types of field sources or specifies how the patient should not linger
near other types of sources. Again, the FDA is well aware of the noise issue
but has concluded that the PM design is acceptable when accompanied by the
user warnings. No patient should be overly concerned, but should discuss the
situation with their doctor in consultation with the medical device
manufacturer. In all cases, they should follow the advice of their doctor.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: geor...@lexmark.com [mailto:geor...@lexmark.com]
Sent: Friday, January 18, 2002 4:26 PM
To: emc-p...@ieee.org
Subject: pacemakers





A few observations..

APS--An APS camera is one that uses Kodak's patented Advanced
Photo System film cartridge.  The only big difference from other
35mm film cartridges is that you just pop it in and close the lid.
It self winds.  No film trailer to fool with.

Electronics--An APS camera's electronics is not that much different
from any other electronic camera.  All such devices must operate at
very low power levels to avoid changing batteries every month.  My
wife's APS can go a year or more on a battery, and that's including
use of the built in flash.

Pacemakers--My father-in-law had one of these twenty years ago.  The
early models were (or were thought to be) susceptible to higher than
ambient electromagnetic waves.  Wearers were warned to avoid microwave
ovens and the like. However, note that microwave ovens operate at
100s of watts, not microwatts, like consumer portable electronics.

Opinion--It is my opinion that any electrical appliance that falls
under FCC (and similar) guidelines will not produce adequate EMF to
interfere with today's pacemakers.  I think I'd be more cautious of
non-regulated appliances which one might have near their chest cavity,
e.g. electric blankets, electric razors, hairdryers, etc.

George Alspaugh



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Zero Crossing Question

2002-01-21 Thread Bouse, John
Hi Group, 

Our manufacturing personnel encountered a strange problem:  when the
mains plug used on a 
230V/50Hz equipment that has an internal zero crossing reference
integrated circuit (specifically, 
a CA3059) is reversed (this can occur in countries such as Germany,
Italy, France and Switzerland),  
the zero crossing pulses appear with a 20 millisecond spacing,  rather
than the expected 10 millisecond 
spacing. 

Harris or Intersil IC's work properly regardless of the mains polarity.
ON Semiconductor IC's appear 
to be polarity sensitive. They will produce the proper number of pulses
with only one mains polarity. 
The incorrect spacing of these zero crossing pulses affects the normal
operation of the equipment. 

Has anyone encountered and, hopefully, solved this problem? 

Regards, 
John Bouse 
PKI 



IEE Guide to EMC and Functional Safety

2002-01-21 Thread CherryClough
Dear all
Following comments made in the correspondence on 'EMC-related safety issues' 
early in January I asked for everyone who was interested to read at least the 
beginning of the IEE's guide and let me know their opinions. 
Also to ask their colleagues and anyone else who might be interested.

I was hoping for a good response from a number of knowledgeable and 
experienced  people which would help me to get the guide improved in future.

But so far, after about 2 weeks, I have had just two replies on this from 
US-based engineers. Neither of them complained about the engineering guidance 
in the guide, both complained about the way it is presented but without (so 
far) being specific or offering any alternatives so I can't (yet) tell if it 
is simply a UK-US cultural or language thing that is the cause of their 
complaints.

Please consider this a last reminder (in this forum, anyway) to have your 
say. 
But please don't merely complain, please try to be constructive to help us 
improve the guide.

Just to remind you of the basic engineering guidance at the heart of this 
guide, it recommends:
QUOTE:

To control EMC correctly for functional safety reasons, hazard and risk 
assessments must take EM environment, emissions, and immunity into account. 
The following should be addressed:

1) The EM disturbances, however infrequent, to which the apparatus might be 
exposed;

2) The foreseeable effects of such disturbances on the apparatus

3) How the EM disturbances emitted by the apparatus might affect other 
apparatus (existing or planned)?

4) The foreseeable safety implications of the above mentioned disturbances 
(what is the severity of the hazard, the scale of the risk, and the 
appropriate safety integrity level?)

5) The level of confidence required to verify that the above have been fully 
considered and all necessary actions taken to achieve the desired level of 
safety.

UNQUOTE

Please note that the word addressed in the above simply means: seriously 
considered or, if you prefer: seriously thought about.

You can download the IEE's guide from www.iee.org.uk/Policy/Areas/Electro in 
Word or PDF formats (note: the URL may be case sensitive). 

I suggest you download the 'Core' document and at least read the first few 
sections of it, pass it around, etc. etc.

I look forward to your inputs.
Regards, Keith Armstrong


Re: EMC-related safety issues

2002-01-21 Thread CherryClough
Dear John
Sorry to be so late replying.

I am pleased that you now understand the situation that I attempted to 
describe earlier, where an HCMOS inverter with an unterminated input was the 
cause of surprisingly powerful radiated emissions at 200MHz, due to an 
unfortunate, unlikely, but not impossible combination of events.

All the very best!
Keith

In a message dated 14/01/02 18:54:00 GMT Standard Time, j...@jmwa.demon.co.uk 
writes:

 Subj:Re: EMC-related safety issues
 Date:14/01/02 18:54:00 GMT Standard Time
 From:j...@jmwa.demon.co.uk (John Woodgate)
 Sender:owner-emc-p...@majordomo.ieee.org
 Reply-to: A HREF=mailto:j...@jmwa.demon.co.uk;j...@jmwa.demon.co.uk/A 
 (John Woodgate)
 To:emc-p...@majordomo.ieee.org
 
 I read in !emc-pstc that cherryclo...@aol.com wrote (in 14b.7351131.297
 42...@aol.com) about 'EMC-related safety issues', on Mon, 14 Jan 2002:
 I'm sure I said in my original posting on this example, that the HCMOS 
 was 
 'hard switching' and not producing a sine wave. A hot device was, of 
 course, 
 the first thing I looked for, and didn't find any. See the additional 
 information above. 
 
 Yes, you did, BUT I wrote:
 
 
  The absence of harmonics even suggests that this gate was producing 
 a 
  sine-wave, which makes the figures even higher and less credible. 
 
 The presence of the high-Q resonant structure that you describe is
 clearly the real reason why no harmonics were observed. It is not only a
 good antenna *but it very probably cannot radiate odd harmonics*, which
 should be the only ones present if the drive waveform was square.
 -- 
 Regards, John Woodgate, OOO - Own Opinions Only. 
 http://www.jmwa.demon.co.uk 
 After swimming across the Hellespont, I felt like a Hero. 
 


Re: EMC-related safety issues

2002-01-21 Thread CherryClough
Dear Bob
Sorry to be so late replying.

Thank you for this reference, I was unaware of it.
I shall add it to my list of EMC-related safety references.

If anyone wants a copy of my list, I'll be pleased to email it to them in 
Word format.

If anyone knows of any books, articles, or papers on the issue, I'll be 
pleased to hear from them about them.

Regards, Keith

In a message dated 15/01/02 04:08:48 GMT Standard Time, john...@itesafety.com 
writes:

 Subj:RE: EMC-related safety issues
 Date:15/01/02 04:08:48 GMT Standard Time
 From:john...@itesafety.com (Robert Johnson)
 Sender:owner-emc-p...@majordomo.ieee.org
 Reply-to: A HREF=mailto:john...@itesafety.com;john...@itesafety.com/A 
 (Robert Johnson)
 To:emc-p...@ieee.org
 
 The latest IEC Just Published points to an article on this subject
 http://www.iec.ch/etech/etech-live/frames-prod-e.htm
 It discusses the application of IEC 61000-1-2.
 
 Also of related significance when talking about safety of complex
 systems and the impact of outside influences like EMC is IEC 61000-1-2
 FAQs
 http://www.iec.ch/61508/Index.htm 
 
 Bob Johnson


Query for India reguration

2002-01-21 Thread hasimt

Hi,

I would like to know about India reguration for EMC  Radio.
Please give me the information.

Tetsuya Hashimoto
A-PEX International Co., Ltd.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: CE rules

2002-01-21 Thread Paolo Gemma

I think that is possible find something on the directive 99/44/CE
Ciao
Paolo
At 16:42 1/17/02 -0500, Michael Gusel wrote:


Dear Group,

I am looking for CE rules (Directive, Article, ...) for maximum period of
time that the manufacturer must provide repair and service after the
equipment has been discontinued.  Please advise.  Thank you.


Michael Gusel

Datascope Corp. Tel:  201-995-8362
800 MacArthur Blvd.   Fax:  201-995-8614
Mahwah, NJ 07430E-mail: michael_gu...@datascope.com



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



--
Paolo Gemma
Siemens Information and Communication Network spa
Microwave Networks MW RD NSA EMC
SS Padana sup. KM 158 20060 Cassina de'Pecchi (MI) Italy
phone +39 02 9526 6587fax +39 02 9526 6203
mobile +39 348 3690185
e-mail paolo.ge...@icn.siemens.it

--