Re: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread T.Sato


On Fri, 6 Sep 2002 16:19:52 +0900,
  Michael Jang mich...@certitek.com wrote:

 I have a question for Discharge of capacitors in the primary circuit'
 (Related to 60950 standard)
 
 Standard 
 Equipment is considered to comply if any capacitor having a marked or nominal
 capacitance exceeding 0.1 uF and connected to the PRIMARY CIRCUIT has a
 means of discharge resulting in a time constant not exceeding:
 - 1 s for Pluggable equipment type A; and
 - 10 s for Permanently connected equipment and for pluggable equipment type B.
 ---
 
 Why does not consider up to 0.1 uF?

# maybe too late, but...

I think we can apply the limits for Limited Current Circuit to
capacitors connected to the primary circuit, too, and capacitors
up to 0.1uF are considered there.

A capacitor which:

  - capacitance = 0.1uF for voltage = 450V, or
  - stored charge = 45uC for 450V  voltage = 15kV, or
  - stored energy = 350mJ for 15kV  voltage.

will become a Limited Current Circuit (2.4.1).

So, for voltage up to 450V d.c. (i.e. up to 318V a.c.), capacitor
up to 0.1uF will become a Limited Current Circuit, hence the voltage
is not Hazardous Voltage (1.2.8.4) - no additional condition would
be required for the capacitor connected to the primary circuit.

However, capacitor larger than 0.1uF would not comply with the
requirements for Limited Current Circuit, and the voltage could be
thought as Hazardous Voltage.
I think that is why the discharge requirement which, under certain
condition, allow capacitor exceeding 0.1uF connected to the primary
circuit was specified.

Regards,
Tom

--
Tomonori Sato  vef00...@nifty.ne.jp
URL: http://member.nifty.ne.jp/tsato/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Immunity severity levels

2002-09-19 Thread Luke Turnbull

Alan,

You will find that 61000-4-3 only gives you the test method and some suggested 
test levels.  You don't test to any of the 61000-4 series, you test to 
whichever standard calls them up, for example EN 50081,50082, the generic 
standards, or EN 55024, ITE immunity.  These standards call up the methods from 
the 61000-4 series and tell you what level should be applied.

You need to look through the Official Journal of the EC (OJEC) list of 
standards and find the particular immunity standard that applies to your 
product.  One place you can find the list is at www.yorkemc.co.uk.

Luke Turnbull

 alan.hud...@amsjv.com 09/18/02 06:14pm 


With regard to radiated emission immunity and EN61000-4-3 (or IEC 801-3)
I believe there are different field strengths used, depending on the
environment in which the apparatus being tested is to be used.

I believe equipment to be used in a well-protected environment may be
tested at a lower immunity level than equipment to be used in an
unprotected environment.

I've ordered a copy of 61000-4-3, but while I'm waiting I'd like to know
ASAP:

1) What are the definitions of the levels?
2) What field strengths  are used for the various levels? (I think level
2 is 3V/m and level 3 is 10V/m)

Regards,

Alan


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Marking for Passive speakers

2002-09-19 Thread Gordon,Ian

John
By the wider issue I was referring to your assertion that The EMC
Guidelines document explains that having no active components is NOT grounds
for exemption from the EMC Directive.
If this were the case then it would have far reaching implications for many
industries since all Electromagnetically Benign equipment might require
testing.
Furthermore I imagine this would have legal implications for the UK
Government appointed Competent Body which advised my company that benign
equipment is exempt. This Competent Body helped us compile a list of
products within our range to which this exclusion applied. 
Item 17 of the following web page shows this to be the case in UK law: 
  http://www.hmso.gov.uk/si/si1992/Uksi_19922372_en_1.htm

Thanks
Ian Gordon
-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: 18 September 2002 09:47
To: emc-p...@majordomo.ieee.org
Subject: Re: CE Marking for Passive speakers



I read in !emc-pstc that Gordon,Ian ian.gor...@edwards.boc.com wrote
(in E1BA0362B28ED211A1E80008C71EA306018190AA@EXC_EAS01) about 'CE
Marking for Passive speakers' on Wed, 18 Sep 2002:
Thus whilst I agree with your view on loudspeakers, I don't concur with
your
view of the wider issue.

What 'wider issue'? The discussion was about loudspeakers and
headphones. I'm not suggesting that digital watches should be CE-marked.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com

_
This e-mail has been scanned for viruses by the WorldCom Internet Managed 
Scanning Service - powered by MessageLabs. For further information visit 
http://www.worldcom.com

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread John Allen
Hi Charles, Warren
 
Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.
 
The difference between reality and theory!
 
I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
(the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)
 
However before they do try it, I suggest they wear safety boots and also use
a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!
 
Regards
 
John Allen

-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF



Hi All,

 

From personal experience I can tell you that the involuntary reaction to a
shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a PC
from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed off
the caps didn't make it into 
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued and
the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.

 

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com; mailto:charles.gra...@echostar.com;
%20   
Email Alternate: chasgra...@ieee.org mailto:chasgra...@ieee.org 

 

-Original Message-
From: John Allen [mailto:john.al...@era.co.uk] 
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF

 

Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF capacitor
charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum: 

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock may well have much more
seriousconsequences. 

This type of shock is often encountered by people who pick up equipment
which they have just unplugged from the AC mains in order to carry it
elsewhere.  If they then touch the pins of the plug there are numerous
reported incidences of them involuntarily dropping the unit - and that can
possibly be on their own feet - and from a height of about 3ft/1m! If the
unit is more than a couple of pounds (about one kilo) then the injury to t!
he feet can be substantial. 

Worse situations could occur in industrial equipment when a service engineer
opens a cabinet to perform a service operation - the reaction from the
shock could cause him to strike touch other hazardous electrical or
mechanical parts (which probably should also not be there, I do agree!)
which then cause him serious actual injury.

These types of incident do not make the equipment supplier very popular to
say the least, and could result in product liability claims.

The main basis for the claims would be that the supplier had not adequately
assessed the hazards and taken the appropriate simple precautions which are
easily and cheaply available - fit a bleeder resistor across the capacitor,
or use a filter with a resistor already built in (or with
transformer/inductor windings directly across the capacitor - which achieve
the same result) !

Again from personal experience I can say that it is a very embarassing and
un! comfortable experience to have to write to an injured or anno! yed
person, or to his employer, to say sorry, but that is what the safety
standard allows. It is just not good business sense.

Therefore, regardless of the requirements of the various standards and this
argument over capacitor value and/or charging voltage, I firmly believe that
the use of bleeder resistors should be considered effectively mandatory, and
have always recommended it to engineers I have advised on product safety.

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:  +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:  +44 (0) 1372-367102 (Fax)

--
Replies to this message may be posted in the following public forum:
Question:  

Re: Clock frequencies

2002-09-19 Thread Cortland Richmond

Doesn't sound like you're missing anything. We are just talking about
different things. Common disease, here!  Certainly, for the same directive
gain, the aperture of an antenna is smaller at higher frequencies. However,
I'm not holding gain constant, but size. 

If the two antennas are the same physical size (and properly phased) the
size in wavelengths -- and thus directive gain -- will be greater at the
higher frequency. You may have two devices with nominal 30 cm-long
antennas, one for 915 Mhz, two half waves collinear, close spaced, and one
for 2.4 GHz, with 5 half waves. The 2.4 GHz antenna's gain will be about 6
dBd, I think,  more than the 915 Mhz antenna at about 2 dBd.  But this may
not be why the limit levels off.

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Clock frequencies

2002-09-19 Thread Ken Javor

The increase in gain of a fixed length wire antenna is given in the ARRL 
handbook and is less than monotonic with increasing frequency, further it
comes at a high price for a broadcast antenna: the main lobe veers away from
an optimal toroidal pattern and begins to align with the wire.

But I am not sure that has any bearing whatsoever on the issue of deriving a
microwave radiated emission limit.  The issue as I see it is this:

If I build a 900 MHz link, and a 2.4 GHz link, the antennas for the 2.4 GHz
link will be shorter by the ratio of their wavelengths, for the same gain.
That means the shorter antenna's effective aperture has decreased, and it is
less efficient as a receiver.  In turn that means it can stand a higher
level of radiated rfi.  Which means to me, other things equal, that the
radiated rfi limit should increase with increasing frequency.

What am I missing?
--
From: Cortland Richmond 72146@compuserve.com
To: Ken Javor ken.ja...@emccompliance.com, ieee pstc list emc-p...@ieee.org
Subject: Re: Clock frequencies
Date: Wed, Sep 18, 2002, 8:34 PM


 An antenna of some physical size will indeed have gain increasing with
 frequency. There is some justification, a 1 GHz antenna being reasonably
 small, for assuming that antennas will have similar sizes -- and increasing
 gain -- above 960 MHz. However, I suspect that the original limit was
 simply an extrapolation, not many users existing there to be affected by
 Part 15 devices, from the limit _below_ 960 MHz.

 Cortland
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Current from Car 12V cigarette lighter socket / 42 VDC

2002-09-19 Thread Price, Ed



-Original Message-
From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Wednesday, September 18, 2002 1:36 PM
To: 'Ken Javor'; Jim Eichner; 'EMC-PSTC - forum'
Subject: RE: Current from Car 12V cigarette lighter socket



Thanks.

The solution you propose is in the works.  The SAE is working on a
completely different style connector for power connections to 
12Vdc, and 2
other styles for 42Vdc and 120Vac connectors.  This effort is 
just getting
off the ground however.

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 



Pardon the slight topic shift, but when will we be seeing 42 VDC automotive
systems? I understand that there has already been some fleet vehicle
production with the 42 VDC standard, but when will it be introduced to the
consumer market?

Regards,

Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Clock frequencies

2002-09-19 Thread Cortland Richmond

An antenna of some physical size will indeed have gain increasing with
frequency. There is some justification, a 1 GHz antenna being reasonably
small, for assuming that antennas will have similar sizes -- and increasing
gain -- above 960 MHz. However, I suspect that the original limit was
simply an extrapolation, not many users existing there to be affected by
Part 15 devices, from the limit _below_ 960 MHz.

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: USB Immunity Specs??

2002-09-19 Thread Hellflower

When confronted by confused designers, I explain the USB feature I call the 
common-mode noise detector.  USB detects a new device connection via a very 
simple non-differential circuit, even though the communication is otherwise 
differential.

This problem was made noticable by the insistance of the designer to abide by 
the original USB specification of a floated capacitor-coupled shield on the 
peripheral connector, spoiling the effectiveness of an otherwise suitable 
shielded/screened cable.

Anyway, this circuit happily responds to common mode transients, such as 
EFT/ESD and the like.  What happens next is the software, responding to a 
new device signal, becomes confused when it finds a peripheral ALREADY 
enumerated (logged into the driver) and doesn't know what to do (really due 
to poor stress-testing of the software).  Some of the first USB drivers of 
Window95 would do very entertaining things, drop into random sections of the 
communication protocol, or the infamous blue screen of death.

If your test system is still running Windows95, you will have no chance to 
pass.  Microsoft stopped supporting that driver.  I found that Windows98 was 
much better, but not foolproof.

USB (and Firewire) unsuitable as they are, have crept into industrial 
applications that the designers considered primarily from a software 
functionality point of view.

Eric Lifsey

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Clock frequencies

2002-09-19 Thread Ken Javor

Following this thread, I looked up the FCC limits and see they are flat 
above 960 MHz.  I have a question for the forum.  Given that a broadcast
type omni-directional antenna factor increases monotonically with increasing
frequency, why is the limit flat?  The only way I could justify a flat limit
is if antenna gain is presumed to increase with increasing frequency.  This
doesn't seem likely with commercial applications for microwave
communications, such as LANs or cordless phones.  Another possibility is
that receiver sensitivity is increasing with increasing frequency, but that
doesn't seem terribly likely, either.  Why doesn't the limit increase with
increasing frequency, or stair-step as it does below 960 MHz?

--
From: Pettit, Ghery ghery.pet...@intel.com
To: 'John Woodgate' j...@jmwa.demon.co.uk, emc-p...@majordomo.ieee.org
Subject: RE: Clock frequencies
Date: Wed, Sep 18, 2002, 4:51 PM



 John,

 Cable emissions seldom are a significant factor above 1 GHz.  Besides, we're
 supposed to tune for maximum smoke, not minimum grin.

 There are products on the market today that meet the FCC limits, but would
 not meet the tighter limits being proposed.  There are no interference
 complaints from these products.  What problem are we trying to fix with
 limits tighter than the FCC's?

 Ghery


 -Original Message-
 From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
 Sent: Wednesday, September 18, 2002 1:53 PM
 To: emc-p...@majordomo.ieee.org
 Subject: Re: Clock frequencies



 I read in !emc-pstc that Pettit, Ghery ghery.pet...@intel.com wrote
 (in d9223eb959a5d511a98f00508b68c20c12515...@orsmsx108.jf.intel.com)
 about 'Clock frequencies' on Wed, 18 Sep 2002:
CISPR SC I meets next week in Christchurch, New Zealand and this will be a
topic of discussion at the meetings.  We on the US delegation will be
 trying
to keep the voices for tighter limits from being successful.

 It's really not something worth having a big argument about. To change
 the measured result by 6 dB, just move one of the cables a few cm.

 This Emperor really DOESN'T have any clothes.(;-)
 --
 Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

 Interested in professional sound reinforcement and distribution? Then go to
 http://www.isce.org.uk
 PLEASE do NOT copy news posts to me by E-MAIL!

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Current from Car 12V cigarette lighter socket

2002-09-19 Thread Ken Javor

Eichner informed me that indeed, I have been scooped by the SAE and this in
the works.

--
From: John Woodgate j...@jmwa.demon.co.uk
To: emc-p...@majordomo.ieee.org
Subject: Re: Current from Car 12V cigarette lighter socket
Date: Wed, Sep 18, 2002, 4:33 PM



 I read in !emc-pstc that Ken Javor ken.ja...@emccompliance.com wrote
 (in 0h2n005m8hj...@mtaout04.icomcast.net) about 'Current from Car 12V
 cigarette lighter socket' on Wed, 18 Sep 2002:

An excellent post.  Seems like a solution here would be for the newer
electrical outlet to be designed differently and not mate with the older
male cigarette lighter insert, and then provide an adapter that would take
the cigarette lighter insert to the new electrical outlet.  Then the 8 Amp
limit could be relaxed for appliances with the new plug, and any old devices
would still be taken care of.

 And your next question, for $64 000, is, 'Why didn't SAE think of that?'
 (;-)
 --
 Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk
 Interested in professional sound reinforcement and distribution? Then go to
 http://www.isce.org.uk
 PLEASE do NOT copy news posts to me by E-MAIL!

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Immunity severity levels

2002-09-19 Thread Joe P Martin


Alan,

Level 1:  (1V/M)Low-level electromagnetic radiation environment.
Levels typical of local radio/television stations located at more than 1
km, and transmitters/receivers of low power.

Level 2:  (3V/M)Moderate electromagnetic radiation environment.  Low
power portable transceivers (typically less than 1 W rating) are in use,
but with restrictions on use in close proximity to the equipment.  A
typical commercial environment.

Level 3:  (10V/M)   Severe electromagnetic radiation environment.  Portable
transceivers (2 W rating or more) are in use relatively close to the
equipment but not less than 1m.   High power broadcast transmitters are in
close proximity to the equipment and ISM equipment may be located close by.
A typical industrial environment.

Level x:  (Special) Level x is an open level which might be negotiated and
specified in the product standard or equipment specification.

Regards

Joe Martin
Applied Biosystems




  
alan.hud...@amsjv.com   
  
Sent by:   To: 
emc-p...@majordomo.ieee.org
owner-emc-pstc@majordomcc:  
  
o.ieee.org Subject: Immunity 
severity levels  

  

  
09/18/2002 10:14 AM 
  
Please respond to   
  
alan.hudson 
  

  

  






With regard to radiated emission immunity and EN61000-4-3 (or IEC 801-3)
I believe there are different field strengths used, depending on the
environment in which the apparatus being tested is to be used.

I believe equipment to be used in a well-protected environment may be
tested at a lower immunity level than equipment to be used in an
unprotected environment.

I've ordered a copy of 61000-4-3, but while I'm waiting I'd like to know
ASAP:

1) What are the definitions of the levels?
2) What field strengths  are used for the various levels? (I think level
2 is 3V/m and level 3 is 10V/m)

Regards,

Alan


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Medical equipment and EN61000-3-2

2002-09-19 Thread John Woodgate

I read in !emc-pstc that dave.osb...@philips.com wrote (in
of6ce386fe.d271bb0a-on86256c38.0070a...@diamond.philips.com) about
'Medical equipment and EN61000-3-2' on Wed, 18 Sep 2002:

Hospitals, just like large office buildings are rarely directly connected to 
the 
public low-voltage distribution system.  Their electricity is normally 
provided 
by a MV transformer.

This is not necessary true in lesser developed countries.

It's also a matter of how you define 'hospital'. Some equipment may be
used in a health centre or day unit, which is not a large building and
is likely to have no more than a commercial LV supply, maybe 200 A
3-phase in UK.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Immunity severity levels

2002-09-19 Thread Joe P Martin



Alan,

Level 1:  (1V/M)Low-level electromagnetic radiation environment.
Levels typical of local radio/television stations located at more than 1
km, and transmitters/receivers of low power.

Level 2:  (3V/M)Moderate electromagnetic radiation environment.  Low
power portable transceivers (typically less than 1 W rating) are in use,
but with restrictions on use in close proximity to the equipment.  A
typical commercial environment.

Level 3:  (10V/M)   Severe electromagnetic radiation environment.  Portable
transceivers (2 W rating or more) are in use relatively close to the
equipment but not less than 1m.   High power broadcast transmitters are in
close proximity to the equipment and ISM equipment may be located close by.
A typical industrial environment.

Level x:  (Special) Level x is an open level which might be negotiated and
specified in the product standard or equipment specification.

Regards

Joe Martin
Applied Biosystems




  
alan.hud...@amsjv.com   
  
Sent by:   To: 
emc-p...@majordomo.ieee.org
owner-emc-pstc@majordomcc:  
  
o.ieee.org Subject: Immunity 
severity levels  

  

  
09/18/2002 10:14 AM 
  
Please respond to   
  
alan.hudson 
  

  

  






With regard to radiated emission immunity and EN61000-4-3 (or IEC 801-3)
I believe there are different field strengths used, depending on the
environment in which the apparatus being tested is to be used.

I believe equipment to be used in a well-protected environment may be
tested at a lower immunity level than equipment to be used in an
unprotected environment.

I've ordered a copy of 61000-4-3, but while I'm waiting I'd like to know
ASAP:

1) What are the definitions of the levels?
2) What field strengths  are used for the various levels? (I think level
2 is 3V/m and level 3 is 10V/m)

Regards,

Alan


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the 

Re: Breaker panel lockout-tagout

2002-09-19 Thread Warren Birmingham


I'm not an authority, but I would think that this is against both the 
fire code and common sense.  If an emergency developed such as electric 
shock or fire and the breaker could not be manually opened, i see it as 
tantamount to the locking of fire escape doors and many liability 
concerns.  The object of locking out a single breaker is to prevent 
THAT breaker from being energized accidently.

Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com


On Wednesday, Sep 18, 2002, at 10:29 US/Pacific, lcr...@tuvam.com wrote:

 Group,

 Is anyone aware of an authoritative position on the acceptability (or 
 not) of applying a lock to a breaker panel cover (and so affecting 
 access to other, unrelated, breakers behind the same cove) to achieve 
 OSHA compliant Lockout/Tagout rather than applying the lock to breaker 
 directly?

 -Lauren Crane
 TUV America




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Warren Birmingham



Many line filters do indeed have a bleeder resistor built in.  There 
are a few which do not, and I am familiar with one Delta filter that 
does not.  We added the bleeder across the terminals of the filter and 
it was approved by UL.  It just has to be done in accordance with 
accepted construction practices.

This particular filter is and IEC plug type so the leads are not 
saliently exposed unless the cord is left attached.  None the less I 
agree with John that it is not a good idea to ignore because one 
instance will get you a lot of word-of-mouth bad press and sales are 
hard-enough to come by so to speak.

Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com



On Wednesday, Sep 18, 2002, at 10:11 US/Pacific, John Allen wrote:

 Hello Folks

 Tomonori Sato  commented However, I think discharge from 0.1uF 
 capacitor charged to the mains peak voltage can be quite 
 uncomfortable.

 I believe that to be true from personal experience and from having to 
 investigate the results of a number of such incidents, and so would 
 remind member of a point that I made several years ago on this forum:

 The primary shock almost certainly will NOT hurt a person, but the 
 involuntary reaction TO the shock may well have much more 
 seriousconsequences.

 This type of shock is often encountered by people who pick up 
 equipment which they have just unplugged from the AC mains in order to 
 carry it elsewhere.  If they then touch the pins of the plug there are 
 numerous reported incidences of them involuntarily dropping the unit - 
 and that can possibly be on their own feet - and from a height of 
 about 3ft/1m! If the unit is more than a couple of pounds (about one 
 kilo) then the injury to t! he feet can be substantial.

 Worse situations could occur in industrial equipment when a service 
 engineer opens a cabinet to perform a service operation - the reaction 
 from the shock could cause him to strike touch other hazardous 
 electrical or mechanical parts (which probably should also not be 
 there, I do agree!) which then cause him serious actual injury.

 These types of incident do not make the equipment supplier very 
 popular to say the least, and could result in product liability 
 claims.

 The main basis for the claims would be that the supplier had not 
 adequately assessed the hazards and taken the appropriate simple 
 precautions which are easily and cheaply available - fit a bleeder 
 resistor across the capacitor, or use a filter with a resistor already 
 built in (or with transformer/inductor windings directly across the 
 capacitor - which achieve the same result) !

 Again from personal experience I can say that it is a very 
 embarassing and un! comfortable experience to have to write to an 
 injured or anno! yed person, or to his employer, to say sorry, but 
 that is what the safety standard allows. It is just not good 
 business sense.

 Therefore, regardless of the requirements of the various standards and 
 this argument over capacitor value and/or charging voltage, I firmly 
 believe that the use of bleeder resistors should be considered 
 effectively mandatory, and have always recommended it to engineers I 
 have advised on product safety.

 Regards

 John Allen
 Technical Consultant
 Electromagnetics, Safety and Reliability Group
 ERA Technology Ltd
 Cleeve Rd
 Leatherhead
 Surrey KT22 7SA
 Tel:  +44 (0) 1372-367025 (Direct)
 +44 (0) 1372-367000 (Switchboard)
 Fax:  +44 (0) 1372-367102 (Fax)

 --
 Replies to this message may be posted in the following public forum:
 Question: Discharge capacitance 0.1 uF






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy 

Re: Clock frequencies

2002-09-19 Thread Joe P Martin



Neil,

Section 15.33  of FCC Part 15 Frequency Range of Radiated Measurements
provides you with this information.

Regards

Joe Martin
Applied Biosystems




  
Neil Helsby 
  
neilhe@solid-state-logTo: 
emc-p...@majordomo.ieee.org
ic.comcc:  
  
Sent by:   Subject: Clock 
frequencies 
owner-emc-pstc@majordom 
  
o.ieee.org  
  

  

  
09/18/2002 03:53 AM 
  
Please respond to Neil  
  
Helsby  
  

  

  





I read somewhere, and now cannot find, a reference to FCC requirements
with respect to the relationship between clock frequency and highest
emissions scan frequency.

Can anyone help, preferably pointing to the FCC document?

I also seem to remember similar comments being considered by the EU. Can
anyone advise on these?

Many thanks,

Neil Helsby


**
This email and any files transmitted with it are confidential and
intended solely for the use of the individual or entity to whom they
are addressed. If you have received this email in error please notify
the system manager.

This footnote also confirms that this email message has been swept by
MIMEsweeper for the presence of computer viruses.

www.mimesweeper.com
**


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and 

Repeat postings

2002-09-19 Thread Ken Javor

I am getting multiple postings, even I think into the next day.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: safety testing in the USA

2002-09-19 Thread John Shinn

There has been some good responses to this post.  And it is, in general,
true
that a manufacturer is not mandated, by law, to have the product LISTED
by an appropriate Safety Testing Agency (NRTL).  However, it may be
required by the local inspection agency prior to installation. (This was
covered
in other posts).

However, if you, as the customer, requests that the product be tested and
listed by an
applicable NRTL, and the vendor is not willing to have the product tested
for compliance with the appropriate standard(s), then you should RUN
to the nearest exit and find another vendor.

Assume that a vendor, who is not willing to have their product tested and
listed for by an appropriate testing agency, is hiding something and  the
vendor
is aware that the product would not comply if tested.

OO
John Shinn, P.E.
Manager, Lab Operations
Sanmina-SCI


-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of
rob.humph...@reuters.com
Sent: Thursday, September 19, 2002 7:46 AM
To: emc-p...@majordomo.ieee.org
Subject: safety testing in the USA



Group,

I am in discussions with a potential supplier of IT equipment, Its our usual
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this
geography? is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Rich Nute




Hi Tom:


   So, for voltage up to 450V d.c. (i.e. up to 318V a.c.), capacitor
   up to 0.1uF will become a Limited Current Circuit, hence the voltage
   is not Hazardous Voltage (1.2.8.4) - no additional condition would
   be required for the capacitor connected to the primary circuit.

Electric shock (or electrically-stimulated
sensation) is a function of BOTH voltage 
and current.  For an electric shock to 
occur, the source must exceed, say, 30 V
rms and 0.5 mA rms.

As a general rule, we say that any voltage
not exceeding 30 V rms is not hazardous,
regardless of current.  We identify this 
voltage as ELV or SELV.

Likewise, we say that any current not
exceeding 0.5 mA rms is not hazardous,
regardless of voltage.  We identify this 
current as Limited Current.

Furthermore, Limited Current addresses
capacitors charged to voltages exceeding 
42.4 V dc.  In this case, we control the
capacitance, or the charge, or the stored
energy, and deem the transient discharge 
current equivalent to a steady state 
current.

In the case of an across-the-line 
capacitor installed on the supply side of
the power switch, the capacitor can be 
charged to the peak of the line voltage 
if the plug is disconnected at the peak
of the line voltage.

As has already been noted in this forum,
the discharge is not a pleasant sensation,
and may very well result in an involuntary
reaction, depending on the individual.

By comparison, the sensation from 3.5 mA
steady-state leakage current (allowed by
some standards for Class I equipment) is
also not a pleasant sensation and may
result in an involuntary reaction.

The initial discharge current of a 
charged capacitor is limited only by the
body resistance.  Regardless of capacitance
value, the initial current is the same.
The effect of capacitance value  is the 
duration of the current.  If the current 
has a short duration, the body will not 
sense it.  Assuming all bodies have the
same resistances, then the duration of the 
current is a function of the value of the 
capacitance.

The standards happen to draw the line at 
0.1 uF.  Any value less than 0.1 uF is
deemed acceptable.  Any value greater than
0.1 uF is deemed unacceptable.  

Consequently, for capacitors less than 0.1
uF, the discharge time is short and the
body is less likely to sense the current.
If the capacitor is more than 0.1 uF, the
discharge time is long, and body is likely
to sense the current.

Another factor, of course, is the magnitude
of the voltage to which the capacitor is
charged.  If the capacitor is charged to
the peak of the 230 V mains, the discharge
is almost always sensed.  The same 
capacitor charged to the peak of a 120 V
mains is barely detectable.  The lower the
voltage, the lower the initial current.

The fact that the initial discharge 
current is limited only by body resistance
also applies to leakage current through 
Y capacitors.  At the moment the body is
inserted into the circuit, the initial
current is limited only by the body
resistance.  Thereafter, the current is
the steady-state current due to the
capacitive reactance.  However, the Y
capacitors are much smaller in value,
and therefore the discharge is much
shorter in time.  (You can test this by
putting a switch in series with the leakage
current; if the switch closes at the peak
of the line voltage, you will feel an
initial sharp sensation.)

By the way, the sensation of leakage 
current from a Y capacitor is greater 
than the sensation of leakage current 
from a resistor whose value is equal to 
the value of capacitive reactance.  This
is due to the same phenomenon, namely the
initial discharge of the capacitance.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Compliance Engineering Position

2002-09-19 Thread Joe P Martin

Greetings,



The Applied Biosystems Division located in the Houston Texas area has the
following opening in the Compliance Engineering Department:

Duties include leading EMC and product safety engineering functions,
including working with manufacturing and RD to determine requirements for
implementing and monitoring regulations.  Collect and analyze data that
help determine compliance engineering issues, trends and improvements.

This position requires the knowledge and skills normally acquired through
the successful completion of a BSEE degree and/or
electronics background.  3-7 years product safety and/or EMC experience
preferred.  Computer literate.  Understanding of manufacturing
processes.  Minimum 5 years experience demonstrating communication,
organization and engineering skills.

Please forward your resumes directly to:

Joe Martin
Applied Biosystems
marti...@appliedbiosystems.com
850 Lincoln Centre Dr.
Foster City, CA 94404
(650) 638-5695




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: safety testing in the USA

2002-09-19 Thread Sam Davis

Another interesting point that can be made is I didn't say it was law, I
said List it or I won't buy it.  Depending on the product (basically, if
there's a Listed competitor product on the market), you can make it happen.
In the US, often a Listing mark is enforced by marketing more than law.
Many retail stores have the requirement of products they put on the shelf to
be Listed, thereby passing on the liability, and reducing their insurance
costs.

just my 2 cents (I've got the paystub to prove it)
Sam

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of
rob.humph...@reuters.com
Sent: Thursday, September 19, 2002 9:46 AM
To: emc-p...@majordomo.ieee.org
Subject: safety testing in the USA



Group,

I am in discussions with a potential supplier of IT equipment, Its our usual
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this
geography? is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Current from Car 12V cigarette lighter socket / 42 VDC

2002-09-19 Thread Chris Maxwell

The Darnell Group is a market research/publishing/advertising entity that has 
been tracking the automotive industry changeover from 12V to  42V, as well as 
other power supply issues. 

They were offering a free web-newsletter called the power-pulse (or something 
like that).  I subscribed to it. 

The newsletter was interesting; but its main focus was to try to get me to buy 
their marketing reports on the power supply industry.  

One of these reports dealt with the 42V changeover. 

I didn't buy it; since we don't make much automotive equipment.  However, if 
anyone is interested; Darnell Group has the information for a small fee :-)

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: safety testing in the USA

2002-09-19 Thread Rich Nute




Hi Rob:


   I am in discussions with a potential supplier of IT equipment, Its our 
 usual policy to request testing to a listed standard
   such as UL 60950 for safety in North America.
   
   The supplier has replied that this is not mandatory.
   
   Is he correct? what  compels safety testing for IT equipment in this 
 geography? is it mandated by law?

I am going to interpret your statement of safety
testing as meaning safety certification.

In the USA, there are two sets of regulations that
are mandated by law:

1.  Workplace regulations (OSHA).

2.  Electrical installation regulations (NEC).

Between these two sets of regulations, almost 
every sales situation is covered.

Each of these has two alternatives:

1.  Test each unit in place.

2.  Third-party certification.

Technically, your supplier is correct.  Third-party
safety certification is NOT mandatory (because 
testing each unit in place is the alternative).

Practically, your supplier is wrong.  Third-party
safety certification avoids testing each unit in
place.

In the USA, governments cannot mandate testing by
a private party (which is the case of third-party
safety certification houses).  Consequently, the
regulations promulgated under various laws prescribe
testing in place, with an alternative of third-
party certification to a national standard, i.e., 
an ANSI standard.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: EN60065 mains switches

2002-09-19 Thread John Woodgate

I read in !emc-pstc that Tyra, John john_t...@bose.com wrote (in
418fbd441c22d5118d860003470d43160543e...@cupid.bose.com) about
'EN60065 mains switches' on Thu, 19 Sep 2002:
Here is another issue where you will get conflicting opinions but I believe
that just because it is notified in the OJ does not mean every country
will adopt it at the same time. You need to be careful as there are some
countries still working with the 5th edition so if you have a CB certificate
and report done by a NCB it may not be accepted in a country which has not
adopted that particular version of the standard..This is
a particular concern with countries outside the EU, i.e. AsiaAny other
opinions?

Notification causes immediate adoption in all EU countries and the
former EFTA countries simultaneously. Other countries may indeed not
adopt the standard at that time.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE Marking for Passive speakers

2002-09-19 Thread John Woodgate

I read in !emc-pstc that Tyra, John john_t...@bose.com wrote (in
418fbd441c22d5118d860003470d43160543e...@cupid.bose.com) about 'CE
Marking for Passive speakers' on Thu, 19 Sep 2002:
John, the added cost in our case is the fact that we include a copy of the
DoC with every product. Not required I know but done here as a matter of
policy this adds a couple of pennies to each product which adds up in the
long run.

Just print it as part of the instruction leaflet, not as a separate
document.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Gert Gremmen
Hi John,

Even theory has to comply with practice, so i took my soldering iron...

I have to admit that modern capacitors do keep their charge too
long. I did some test with newer Y and X caps of 0.1 uF and they keep their
charge way too long - over 1 minute - without notable loss of
voltage ( 10%) (real life voltages choosen :310V)
Probably the quality of the dielectricum has been improved, or
the use of paper has been abandoned in favor of modern equivalent
plastics. (any one knows ?).
Of course the increased leakage of the older caps was not meant to be
part of the specs, and this is again a good example of how relying on hidden
specifications may in time lead to undesired results: standards ignoring the
effect of  increased leakage resistance.

I also tried the discharge between two fingers, and found the result to
be unpleasant at least.
Time to change standards...

Gert Gremmen

ce-test, qualified testing

  -Original Message-
  From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Allen
  Sent: Thursday, September 19, 2002 9:24 AM
  To: 'Grasso, Charles'; 'Warren Birmingham'
  Cc: emc-p...@majordomo.ieee.org
  Subject: RE: Question: Discharge capacitance 0.1 uF


  Hi Charles, Warren

  Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.

  The difference between reality and theory!

  I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
  (the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)

  However before they do try it, I suggest they wear safety boots and also
use a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!

  Regards

  John Allen
-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi All,



From personal experience I can tell you that the involuntary reaction to
a shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a
PC from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed
off the caps didn't make it into
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued
and the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.



Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;
Email Alternate: chasgra...@ieee.org



-Original Message-
From: John Allen [mailto:john.al...@era.co.uk]
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF



Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF
capacitor charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum:

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock may well have much more
seriousconsequences.

This type of shock is often encountered by people who pick up equipment
which they have just unplugged from the AC mains in order to carry it
elsewhere.  If they then touch the pins of the plug there are numerous
reported incidences of them involuntarily dropping the unit - and that can
possibly be on their own feet - and from a height of about 3ft/1m! If the
unit is more than a couple of pounds (about one kilo) then the injury to t!
he feet can be substantial.

Worse situations could occur in industrial equipment when a service
engineer opens a cabinet to perform a service operation - the reaction from
the shock could cause him to strike touch other hazardous electrical or
mechanical parts (which probably should also not be there, I do agree!)
which then cause him serious actual injury.

These types of incident do not make the equipment supplier very
popular to say the least, and could result in product liability claims.

The main basis for the claims would be that the supplier had not

RE: safety testing in the USA

2002-09-19 Thread richwoods

Here is a very good discussion of the leagalities.

http://www.conformity.com/A02F18.pdf

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: Gary McInturff [mailto:gary.mcintu...@worldwidepackets.com]
Sent: Thursday, September 19, 2002 12:40 PM
To: rob.humph...@reuters.com; EMC-PSTC (E-mail)
Subject: RE: safety testing in the USA



Rob.
Required is an interesting term, and this is a long debate involving
OSHA, National Electrical Code, fire codes and when and if anybody inspects
the equipment before its installed.
There are places that you probably would be alright, some that you
wouldn't probably be caught even if it wasn't right,  and then there are
places like the City of LA that seems to have a pretty rigorous inspection
policy. They by the way can give you a City of LA inspection, but it isn't
of any real value outside of LA.
Then there are customers that use the safety marks in an attempt to
reduce their liability by showing they have done what any reasonable
manufacturer would do to protect customers. 
So short pragmatic answer, in my opinion, yes you need it.
Gary
The debate rages on


-Original Message-
From: rob.humph...@reuters.com [mailto:rob.humph...@reuters.com]
Sent: Thursday, September 19, 2002 7:46 AM
To: emc-p...@majordomo.ieee.org
Subject: safety testing in the USA



Group,

I am in discussions with a potential supplier of IT equipment, Its our usual
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this
geography? is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: EMC immunity requirements in Canada?

2002-09-19 Thread Grasso, Charles

Hi Warren,

As I understand the FCC Part 15 regs there are NO immunity requirements.
Indeed the FCC have in the past allowed the market to dictate the quality
of the EM design. Has there been a change??

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;  
Email Alternate: chasgra...@ieee.org
 

-Original Message-
From: Warren Birmingham [mailto:war...@comfortjets.com] 
Sent: Thursday, September 19, 2002 10:59 AM
To: am...@westin-emission.no
Cc: emc-p...@majordomo.ieee.org
Subject: Re: EMC immunity requirements in Canada?


The Canadians accept FCC data, which DOES include immunity 
requirements.  There are no testing standards for immunity, only that 
the device must accept any interference for normal operation.  See the 
labeling requirements for verification and certification in Part 15.

Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com



On Thursday, Sep 19, 2002, at 05:22 US/Pacific, 
am...@westin-emission.no wrote:


 As far as I remember, US (FCC) do only have emission (radiated / 
 conducted)
 requirements.
 What about Canada (IC)  do they have immunity requirements in 
 addition ?

 Best regards
 Amund Westin, Oslo/ NORWAY





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Looking for good USB EMI suppression techniques

2002-09-19 Thread Grasso, Charles

Hi 

It is my understanding that the USB guidelines provide for EMI filtering
at the output. That is to say: for USB1 - ferrite beads and caps, for USBII
a common mode choke is recommended. Take a look in there.

Also, USB is a differential signal so appropriate design on the board needs
to be considered

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;  
Email Alternate: chasgra...@ieee.org
 

-Original Message-
From: Darrell Locke [mailto:dlo...@advanced-input.com] 
Sent: Thursday, September 19, 2002 11:15 AM
To: 'Dan Pierce'; emc-p...@majordomo.ieee.org
Subject: RE: Looking for good USB EMI suppression techniques


You can't do much filtering on the USB lines due to signal integrity.  We
have achieved good results with careful attention to PCB layout (an adequete
ground plane, don't even try 2-layer) and shielding, especially with the
cable.

Darrell Locke
Advanced Input Devices

-Original Message-
From: Dan Pierce [mailto:dpie...@openglobe.net]
Sent: Wednesday, September 18, 2002 8:17 AM
To: emc-p...@majordomo.ieee.org
Subject: Looking for good USB EMI suppression techniques


Greetings:

I am looking for a good design practice regarding USB transmission lines.  I
commonly have problems with 120.00MHz and 252.00MHz. 

Thanks in advance.

Daniel J. Pierce
Sr. Design Engineer
OpenGlobe, Inc.
 (An Escient Technologies Affiliate)
6325 Digital Way
Indianapolis, IN  46278

mailto:dpie...@openglobe.net
 
P:  (317) 616.6587
F:  (317) 616.6587


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread John Allen
Gert
 
Thanks for that investigation that I have not had the time for recently!
 
Now, maybe, the standards writing committees will begin to take this issue
on board and do something about it as the problem is generally technically
trivial to solve - the major issue then being to ensure that the bleeder
device is always across the capacitor, and is not isolated from it by a
switch or contactor that the operator can put in the open position before
disconnecting the supply.
 
(The latter point can particularly apply to some filtered IEC, or similar,
power inlets with integral switches where the bleeder could be on the
opposite side of the contacts to the capacitor).
John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel: +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax: +44 (0) 1372-367102 (Fax)

-Original Message-
From: Gert Gremmen [mailto:g.grem...@cetest.nl]
Sent: 19 September 2002 11:57
To: John Allen
Cc: emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi John,
 
Even theory has to comply with practice, so i took my soldering iron...
 
I have to admit that modern capacitors do keep their charge too
long. I did some test with newer Y and X caps of 0.1 uF and they keep their
charge way too long - over 1 minute - without notable loss of
voltage ( 10%) (real life voltages choosen :310V)
Probably the quality of the dielectricum has been improved, or
the use of paper has been abandoned in favor of modern equivalent
plastics. (any one knows ?).
Of course the increased leakage of the older caps was not meant to be
part of the specs, and this is again a good example of how relying on hidden

specifications may in time lead to undesired results: standards ignoring the
effect of  increased leakage resistance.
 
I also tried the discharge between two fingers, and found the result to
be unpleasant at least.
Time to change standards...
 
Gert Gremmen
 
ce-test, qualified testing
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Allen
Sent: Thursday, September 19, 2002 9:24 AM
To: 'Grasso, Charles'; 'Warren Birmingham'
Cc: emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi Charles, Warren
 
Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.
 
The difference between reality and theory!
 
I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
(the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)
 
However before they do try it, I suggest they wear safety boots and also use
a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!
 
Regards
 
John Allen

-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF



Hi All,

 

From personal experience I can tell you that the involuntary reaction to a
shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a PC
from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed off
the caps didn't make it into 
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued and
the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.

 

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com; mailto:charles.gra...@echostar.com;
%20   
Email Alternate: chasgra...@ieee.org mailto:chasgra...@ieee.org 

 

-Original Message-
From: John Allen [mailto:john.al...@era.co.uk] 
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF

 

Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF capacitor
charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum: 

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock 

RE: Current from Car 12V cigarette lighter socket / 42 VDC

2002-09-19 Thread Jim Eichner

Well that's the $1M question, isn't it!  

My involvement is tangential at best, but my understanding is that the
effort is not going to be coordinated as a grand simultaneous roll-out.
Rather each mfr of cars, trucks, boats, etc, will get around to it based on
their own needs.  The drivers for this effort vary widely - vehicle
emissions, increased electrical loads, drive-by-wire technology, etc. - and
the 42Vdc agenda for a given mfr is to some extent determined by the agenda
for those features or regulations.  There is much technology still to be
developed and much standardization work still to be done, but the work is
well in progress.

Is there anyone on the forum who has a more inside view of this and can
share some information with us?

In the meantime, have a look at the web.  Searching on 42V can yield a lot
of hits.  Here's one I found that summarizes things a bit:

http://www.sae.org/42volt/dual_higher_sum.pdf

Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






-Original Message-
From: Price, Ed [mailto:ed.pr...@cubic.com]
Sent: Wednesday, September 18, 2002 6:42 PM
To: 'EMC-PSTC - forum'
Subject: RE: Current from Car 12V cigarette lighter socket / 42 VDC

Pardon the slight topic shift, but when will we be seeing 42 VDC automotive
systems? I understand that there has already been some fleet vehicle
production with the 42 VDC standard, but when will it be introduced to the
consumer market?

Regards,

Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis

---

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Pulse Dialing

2002-09-19 Thread JPR3

In a message dated 9/19/2002, Matt Aschenberg writes:


 Our engineering team is looking for a spec that defines U.S pulse dialing. 
 Any suggestions?
 


Hi Matt:

As you may know, there are no regulatory requirements for pulse dialing in 
FCC part 68.  This means that any requirements you apply will be 
self-imposed.

Simply stated, US pulse dialing uses a 60/40 break/make ratio and a nominal 
10 pulses per second.  Thus, each pulse consists of a nominal 60 mS break 
followed by a 40 mS make.  The number of pulses corresponds to the digit 
dialed, except that a 0 is ten pulses.

If you want a detailed specification for pulse dialing, you can use 
TIA/EIA-470-B, Telephone Sets With Loop Signalling.  


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com



RE: Looking for good USB EMI suppression techniques

2002-09-19 Thread Darrell Locke

You can't do much filtering on the USB lines due to signal integrity.  We
have achieved good results with careful attention to PCB layout (an adequete
ground plane, don't even try 2-layer) and shielding, especially with the
cable.

Darrell Locke
Advanced Input Devices

-Original Message-
From: Dan Pierce [mailto:dpie...@openglobe.net]
Sent: Wednesday, September 18, 2002 8:17 AM
To: emc-p...@majordomo.ieee.org
Subject: Looking for good USB EMI suppression techniques


Greetings:

I am looking for a good design practice regarding USB transmission lines.  I
commonly have problems with 120.00MHz and 252.00MHz. 

Thanks in advance.

Daniel J. Pierce
Sr. Design Engineer
OpenGlobe, Inc.
 (An Escient Technologies Affiliate)
6325 Digital Way
Indianapolis, IN  46278

mailto:dpie...@openglobe.net
 
P:  (317) 616.6587
F:  (317) 616.6587


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: EMC immunity requirements in Canada?

2002-09-19 Thread Warren Birmingham


The Canadians accept FCC data, which DOES include immunity 
requirements.  There are no testing standards for immunity, only that 
the device must accept any interference for normal operation.  See the 
labeling requirements for verification and certification in Part 15.


Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com



On Thursday, Sep 19, 2002, at 05:22 US/Pacific, 
am...@westin-emission.no wrote:




As far as I remember, US (FCC) do only have emission (radiated / 
conducted)

requirements.
What about Canada (IC)  do they have immunity requirements in 
addition ?


Best regards
Amund Westin, Oslo/ NORWAY






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list


RE: safety testing in the USA

2002-09-19 Thread richwoods

Some states (e.g., North Carolina), counties (e.g., Orange, CA) and cities
(e.g., Los Angeles and San Francisco)have a legal requirement that all
electrical products for sale must be Listed. Some local electrical codes
(e.g., Oregon) require electrical equipment be Listed. Since my company
sells products virtually everywhere in the USA, we List all of our products
including those powered by Class 2 sources. I recommend that you do the same
unless you know for a fact that your target locality has no legal
requirements for Listing.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: rob.humph...@reuters.com [mailto:rob.humph...@reuters.com]
Sent: Thursday, September 19, 2002 10:46 AM
To: emc-p...@majordomo.ieee.org
Subject: safety testing in the USA



Group,

I am in discussions with a potential supplier of IT equipment, Its our usual
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this
geography? is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Measuring AC Line Impedance

2002-09-19 Thread plawler

Hi Dave:

I had the same question some time back, and came up with the following process.

1) For the resistive component, I applied a resistive load to the AC line, and
calculated R = dV/dI

2) For the inductive component, I measured the transient current through an 'X'
capacitor at the moment it was touched across the AC line.
This requires a storage scope, and a current sense resistor or current probe.
Amplitude accuracy is not important, since you're concerned with the period of
the ringing.
There is a big spike of current, followed by several cycles of ringing.  I
calculated the line inductance from the ringing frequency.

For those who want more precision:
- If you know the resonant frequency of the 'X' capacitor assembly, you can
calculate the stray inductance, and adjust the line inductance accordingly.
- Once you calculate the line inductance, you can correct the steady state
impedance in step 1.


Patrick Lawler
plaw...@west.net

On Thu, 19 Sep 2002 08:06:18 -0400, Spencer, David H
david.spen...@usa.xerox.com wrote:
I'm trying to characterize the 50Hz AC line impedance of my facility, for
comparison to the values specified in IEC61000-3-3.  I've come across
generic short circuit values for the Resistive and Inductive components.
However, I need to determine exactly what these values are ideally through a
combination of measurement and calculation.

So far,  I've taken a large resistive load and measured the voltage drop on
the AC line.  From that I calculated the total impedance of the AC line.
However, as you may suspect, with a resistive load, the power factor is 1.0.
So I can't vectorly, calculate the resistive and inductive components.  

Is anyone familiar with a method to measure and calculate those values.  The
generic values I have for short circuit condition (which include 4 wires in
a magnetic conduit) come out higher than my measured values, and those do
not include the motor generator source.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: safety testing in the USA

2002-09-19 Thread Gary McInturff

Rob.
Required is an interesting term, and this is a long debate involving 
OSHA, National Electrical Code, fire codes and when and if anybody inspects the 
equipment before its installed.
There are places that you probably would be alright, some that you 
wouldn't probably be caught even if it wasn't right,  and then there are places 
like the City of LA that seems to have a pretty rigorous inspection policy. 
They by the way can give you a City of LA inspection, but it isn't of any real 
value outside of LA.
Then there are customers that use the safety marks in an attempt to 
reduce their liability by showing they have done what any reasonable 
manufacturer would do to protect customers. 
So short pragmatic answer, in my opinion, yes you need it.
Gary
The debate rages on


-Original Message-
From: rob.humph...@reuters.com [mailto:rob.humph...@reuters.com]
Sent: Thursday, September 19, 2002 7:46 AM
To: emc-p...@majordomo.ieee.org
Subject: safety testing in the USA



Group,

I am in discussions with a potential supplier of IT equipment, Its our usual 
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this geography? 
is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Cortland Richmond

 (the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!) 


At a former employer, we monitored the wave form with a 'scope, and
repeatedly opened and closed the connection to the power line until
disconnection could be seen to have occurred at (or very near) the
peak of the wave form, then watched the discharge. None of us EVER
felt tempted enough to question the 'scope display and experience
the discharge personally - and we went to some trouble to arrange
things so we would not do.  Anyone who had doubted the necessity
of the test was converted by seeing the potential for trouble. 

Cortland

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: EN60065 mains switches

2002-09-19 Thread Tyra, John

Here is another issue where you will get conflicting opinions but I believe
that just because it is notified in the OJ does not mean every country
will adopt it at the same time. You need to be careful as there are some
countries still working with the 5th edition so if you have a CB certificate
and report done by a NCB it may not be accepted in a country which has not
adopted that particular version of the standard..This is
a particular concern with countries outside the EU, i.e. AsiaAny other
opinions?

-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, September 18, 2002 4:49 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: EN60065 mains switches



I read in !emc-pstc that Tyra, John john_t...@bose.com wrote (in
418fbd441c22d5118d860003470d43160543e...@cupid.bose.com) about
'EN60065 mains switches' on Wed, 18 Sep 2002:

Also be aware that the published 7th edition of IEC60065 eliminates the
need
for a switch which is in line with the current edition of UL6500.
Unfortunately it will probably be several years before all the countries
adopt this edition of the standard

It is already adopted as EN 60065:2002. If it hasn't already been
'notified' in the Official Journal, it soon will be.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Measuring AC Line Impedance

2002-09-19 Thread JPR3
In a message dated 9/19/2002, you write:


 So far,  I've taken a large resistive load and measured the voltage drop on
 the AC line.  From that I calculated the total impedance of the AC line.
 However, as you may suspect, with a resistive load, the power factor is 
 1.0.
 So I can't vectorly, calculate the resistive and inductive components.  
 


Hi Dave:

I am not familiar with the specific measurement you are trying to make, so 
the following may not be applicable to your situation.  However, some of the 
basic concepts may be useful.

In the telecom business it is sometimes necessary to know the complex 
impedance presented by a 2-wire port.  In theory, if you drive the port with 
a voltage source applied through a known resistance, you can calculate the 
complex impedance of the port based on measurements of the following two 
things:

1) The voltage drop across the source resistor
2) The phase of the current through the resistor, relative to the phase of 
the source

I designed a simple fixture to measure the voltage and phase, then derived 
the necessary equations and created a spreadsheet to calculate the complex 
impedance.

Soon after completing my measurements this way, I got a good price on a used 
test instrument that makes this measurement directly.  I was very pleased to 
find that the values measured by the test instrument matched my calculated 
values almost exactly.  This gave me good confidence in my earlier test 
method, even though I no longer need to use it.

It might be possible for you to adapt this method for the test you want to 
make.  If so, I would be happy to send you a copy of the equations and a copy 
of the spreadsheet I used.  Since this was developed internally for my own 
use, the notes are a little sketchy, but I think I could fill in the gaps 
with a telephone conversation.

While I am not familiar with the details of the test you are trying to 
perform, I can see that one possible complication would occur if the test is 
supposed to be performed under a specified load condition.  In that case, you 
would have to find a way to ensure that the AC impedance of your load does 
not affect the measured impedance of the mains.  I think there are ways to 
accomplish this either with a test fixture or by making the spreadsheet 
calculations take the load impedance into account.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com


HTMLFONT FACE=arial,helveticaFONT  SIZE=2In a message dated 9/19/2002, 
you write:BR
BR
BR
BLOCKQUOTE TYPE=CITE style=BORDER-LEFT: #ff 2px solid; MARGIN-LEFT: 5px; 
MARGIN-RIGHT: 0px; PADDING-LEFT: 5pxSo far,nbsp; I've taken a large 
resistive load and measured the voltage drop onBR
the AC line.nbsp; From that I calculated the total impedance of the AC 
line.BR
However, as you may suspect, with a resistive load, the power factor is 1.0.BR
So I can't vectorly, calculate the resistive and inductive components.nbsp; 
BR
/BLOCKQUOTEBR
BR
BR
Hi Dave:BR
BR
I am not familiar with the specific measurement you are trying to make, so the 
following may not be applicable to your situation.nbsp; However, some of the 
basic concepts may be useful.BR
BR
In the telecom business it is sometimes necessary to know the complex impedance 
presented by a 2-wire port.nbsp; In theory, if you drive the port with a 
voltage source applied through a known resistance, you can calculate the 
complex impedance of the port based on measurements of the following two 
things:BR
BR
1) The voltage drop across the source resistorBR
2) The phase of the current through the resistor, relative to the phase of the 
sourceBR
BR
I designed a simple fixture to measure the voltage and phase, then derived the 
necessary equations and created a spreadsheet to calculate the complex 
impedance.BR
BR
Soon after completing my measurements this way, I got a good price on a used 
test instrument that makes this measurement directly.nbsp; I was very pleased 
to find that the values measured by the test instrument matched my calculated 
values almost exactly.nbsp; This gave me good confidence in my earlier test 
method, even though I no longer need to use it.BR
BR
It might be possible for you to adapt this method for the test you want to 
make.nbsp; If so, I would be happy to send you a copy of the equations and a 
copy of the spreadsheet I used.nbsp; Since this was developed internally for 
my own use, the notes are a little sketchy, but I think I could fill in the 
gaps with a telephone conversation.BR
BR
While I am not familiar with the details of the test you are trying to perform, 
I can see that one possible complication would occur if the test is supposed to 
be performed under a specified load condition.nbsp; In that case, you would 
have to find a way to ensure that the AC impedance of your load does not affect 
the measured impedance of the mains.nbsp; I think there are ways to accomplish 
this either with a test fixture or by 

Re: EMC immunity requirements in Canada?

2002-09-19 Thread John Barnes

Amund,
Like the US, Canada has just radiated and conducted emissions
requirements.  The pertinent standard for Digital Apparatus is Industry
Canada's ICES-003 Issue 3, dated November 22, 1997.  This standard may
be downloaded from:
http://strategis.ic.gc.ca/SSG/1/sf00020e.html
and the implementation/interpretation guide from:
http://strategis.ic.gc.ca/SSG/1/sf01006e.html

You may want to refer to three web pages on our company's web site 
about international electromagnetic compatibility (EMC), electromagnetic
interference (EMC), and electrostatic discharge (ESD) requirements:
*  http://www.dbicorporation.com/ite.htm   for information technology
   equipment (ITE).
*  http://www.dbicorporation.com/generic.htm   for generic devices used
   in residential, commercial, and light industrial areas.
*  http://www.dbicorporation.com/industry.htm   for generic devices used
   in industry.

John Barnes KS4GL
dBi Corporation
http://www.dbicorporation.com/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Marking for Passive speakers

2002-09-19 Thread Tyra, John

I wish to thank everyone for taking the time to consider my questions. There
were a many good points brought up and it gave me some new issues to
consider, i.e. immunity testing for intense. As I expected the opinion was
split and I have to admit that I am still not convinced that CE Marking is
required for these type of products. In order to avoid the possibility of
being questioned upon import into the EU I am going to recommend that we CE
Mark our products until told otherwise and continue to pursue further
clarification from the authorities. I will be happy to share any info I
receive.

John, the added cost in our case is the fact that we include a copy of the
DoC with every product. Not required I know but done here as a matter of
policy this adds a couple of pennies to each product which adds up in the
long run.

Best regards,

John

-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Thursday, September 19, 2002 7:04 AM
To: emc-p...@majordomo.ieee.org
Subject: Re: CE Marking for Passive speakers



I read in !emc-pstc that Gordon,Ian ian.gor...@edwards.boc.com wrote
(in E1BA0362B28ED211A1E80008C71EA306018190AE@EXC_EAS01) about 'CE
Marking for Passive speakers' on Thu, 19 Sep 2002:
By the wider issue I was referring to your assertion that The EMC
Guidelines document explains that having no active components is NOT
grounds
for exemption from the EMC Directive.
If this were the case then it would have far reaching implications for many
industries since all Electromagnetically Benign equipment might require
testing.
Furthermore I imagine this would have legal implications for the UK
Government appointed Competent Body which advised my company that benign
equipment is exempt. This Competent Body helped us compile a list of
products within our range to which this exclusion applied. 

'Benign' is NOT the same as 'passive', which is what was asserted. A
torch/flashlight with an incandescent lamp is benign, because it is
inconceivable that it would either emit anything or suffer from lack of
immunity. But even just a *junction box* for high-speed data cable can
both emit stuff and let external disturbances into the cabling. 

I showed how a loudspeaker can both emit and be disturbed by and
external emission. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: EMC immunity requirements in Canada?

2002-09-19 Thread Warren Birmingham


The Canadians accept FCC data, which DOES include immunity 
requirements.  There are no testing standards for immunity, only that 
the device must accept any interference for normal operation.  See the 
labeling requirements for verification and certification in Part 15.

Warren Birmingham
Epsilon-Mu Consultants
(510) 793-4806
email: war...@epsilon-mu.com
website: http://www.epsilon-mu.com



On Thursday, Sep 19, 2002, at 05:22 US/Pacific, 
am...@westin-emission.no wrote:


 As far as I remember, US (FCC) do only have emission (radiated / 
 conducted)
 requirements.
 What about Canada (IC)  do they have immunity requirements in 
 addition ?

 Best regards
 Amund Westin, Oslo/ NORWAY





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Measuring AC Line Impedance

2002-09-19 Thread John Woodgate

I read in !emc-pstc that Spencer, David H david.spen...@usa.xerox.com
wrote (in 052106A55179D611B34300096BB02E3F8B1D@USAMCMS4) about
'Measuring AC Line Impedance' on Thu, 19 Sep 2002:

Is anyone familiar with a method to measure and calculate those values.  The
generic values I have for short circuit condition (which include 4 wires in
a magnetic conduit) come out higher than my measured values, and those do
not include the motor generator source.  

Put a large capacitor (mains voltage rated) across the mains and measure
the voltage change; it may actually increase. You need about 50 uF to
get a decent change on 120 V 60 Hz mains. With that result and the one
with the resistive load, you can calculate the source impedance as an R
and L in series.

I'd be interested to learn the result.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread John Woodgate

I read in !emc-pstc that John Allen john.al...@era.co.uk wrote (in
BFE68AB0084CD311B4FB00508B014C8703CF9BEE@MERCURY) about 'Question:
Discharge capacitance 0.1 uF' on Thu, 19 Sep 2002:

Now, maybe, the standards writing committees will begin to take this issue
on board and do something about it 

Are you saying that the present requirements (e.g. in EN60065) are
unsatisfactory? In what way?
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Medical equipment and EN61000-3-2

2002-09-19 Thread jgriver

Patrick,

I don't know whether or not hospital power systems fall within the 
scope of EN61000-3-2:2001. But in any case, compliance with EN61000-3-
2 is not required under the Medical Devices Directive.

The only harmonized EMC standard under the MDD is EN 60601-1-2:1993, 
which does not have any harmonics requirements. Medical equipment is, 
of course, specifically exempted from the EMC Directive.

Regards,

Jon Griver
http://www.601help.com
The Medical Device Developers Guide to IEC 60601-1.


On 18 Sep 2002 at 12:55, plaw...@west.net wrote:

 
 The scope of EN61000-3-2:2001 says that the standard deals with harmonic
 currents injected into the public low-voltage distribution system.
 
 I can see that residences and offices are connected to the public system.
 However, I don't know about distribution to hospitals.
 
 Are their power requirements specialized enough that their electricity is
 provided by a MV transformer?  This would exempt hospital-only medical 
 products
 from the harmonic current requirements.
 Or are their different levels of hospitals, some fed by LV transformers, some
 fed by MV transformers?
 
 Patrick Lawler
 plaw...@west.net
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Pulse Dialing

2002-09-19 Thread Aschenberg, Mat

Hello all, 
I am certain there are more than a few telecom gurus on this list. 
Maybe you can help me out. 

Our engineering team is looking for a spec that defines U.S pulse dialing. 
Any suggestions?

Thanks for your help, 
Mat Aschenberg


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Peter Tarver

John -

I respectfully disagree that the standards bodies need to do
anything.  It is the designers that must be aware of the
advancements of technology (such as described by Gert) and
update their practices accordingly.  [Low ESR / High Q caps
are a good thing.] While I have no doubt about the potential
effects of reaction hazards (I've put two fingers across a
circuit calibrated to deliver 3.5 mA at 120V line potential;
the infamous Walter Skuggevig apparatus), the safety
standards should not be prescriptive.

Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


-Original Message-
From: John Allen
Sent: Thursday, September 19, 2002 4:13 AM

Gert

Thanks for that investigation that I have not had the time
for recently!

Now, maybe, the standards writing committees will begin to
take this issue on board and do something about it as the
problem is generally technically trivial to solve - the
major issue then being to ensure that the bleeder device is
always across the capacitor, and is not isolated from it by
a switch or contactor that the operator can put in the
open position before disconnecting the supply.


John Allen


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: EMC immunity requirements in Canada?

2002-09-19 Thread richwoods

No.

Richard Woods
Sensormatic Electronics
Tyco International


-Original Message-
From: am...@westin-emission.no [mailto:am...@westin-emission.no]
Sent: Thursday, September 19, 2002 8:22 AM
To: emc-p...@majordomo.ieee.org
Subject: EMC immunity requirements in Canada?



As far as I remember, US (FCC) do only have emission (radiated / conducted)
requirements.
What about Canada (IC)  do they have immunity requirements in addition ?

Best regards
Amund Westin, Oslo/ NORWAY



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


safety testing in the USA

2002-09-19 Thread Rob . Humphrey

Group,

I am in discussions with a potential supplier of IT equipment, Its our usual 
policy to request testing to a listed standard
such as UL 60950 for safety in North America.

The supplier has replied that this is not mandatory.

Is he correct? what  compels safety testing for IT equipment in this geography? 
is it mandated by law?

Thanks in advance for your opinions

Rob




- ---
Visit our Internet site at http://www.reuters.com

Any views expressed in this message are those of  the  individual
sender,  except  where  the sender specifically states them to be
the views of Reuters Ltd.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread John Allen
Hi Charles, Warren
 
Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.
 
The difference between reality and theory!
 
I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
(the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)
 
However before they do try it, I suggest they wear safety boots and also use
a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!
 
Regards
 
John Allen

-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF



Hi All,

 

From personal experience I can tell you that the involuntary reaction to a
shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a PC
from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed off
the caps didn't make it into 
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued and
the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.

 

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com; mailto:charles.gra...@echostar.com;
%20   
Email Alternate: chasgra...@ieee.org mailto:chasgra...@ieee.org 

 

-Original Message-
From: John Allen [mailto:john.al...@era.co.uk] 
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF

 

Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF capacitor
charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum: 

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock may well have much more
seriousconsequences. 

This type of shock is often encountered by people who pick up equipment
which they have just unplugged from the AC mains in order to carry it
elsewhere.  If they then touch the pins of the plug there are numerous
reported incidences of them involuntarily dropping the unit - and that can
possibly be on their own feet - and from a height of about 3ft/1m! If the
unit is more than a couple of pounds (about one kilo) then the injury to t!
he feet can be substantial. 

Worse situations could occur in industrial equipment when a service engineer
opens a cabinet to perform a service operation - the reaction from the
shock could cause him to strike touch other hazardous electrical or
mechanical parts (which probably should also not be there, I do agree!)
which then cause him serious actual injury.

These types of incident do not make the equipment supplier very popular to
say the least, and could result in product liability claims.

The main basis for the claims would be that the supplier had not adequately
assessed the hazards and taken the appropriate simple precautions which are
easily and cheaply available - fit a bleeder resistor across the capacitor,
or use a filter with a resistor already built in (or with
transformer/inductor windings directly across the capacitor - which achieve
the same result) !

Again from personal experience I can say that it is a very embarassing and
un! comfortable experience to have to write to an injured or anno! yed
person, or to his employer, to say sorry, but that is what the safety
standard allows. It is just not good business sense.

Therefore, regardless of the requirements of the various standards and this
argument over capacitor value and/or charging voltage, I firmly believe that
the use of bleeder resistors should be considered effectively mandatory, and
have always recommended it to engineers I have advised on product safety.

Regards

John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel:  +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax:  +44 (0) 1372-367102 (Fax)

--
Replies to this message may be posted in the following public forum:
Question:  

Re: Measuring AC Line Impedance

2002-09-19 Thread JPR3
In a message dated 9/19/2002, you write:


 So far,  I've taken a large resistive load and measured the voltage drop on
 the AC line.  From that I calculated the total impedance of the AC line.
 However, as you may suspect, with a resistive load, the power factor is 
 1.0.
 So I can't vectorly, calculate the resistive and inductive components.  
 


Hi Dave:

I am not familiar with the specific measurement you are trying to make, so 
the following may not be applicable to your situation.  However, some of the 
basic concepts may be useful.

In the telecom business it is sometimes necessary to know the complex 
impedance presented by a 2-wire port.  In theory, if you drive the port with 
a voltage source applied through a known resistance, you can calculate the 
complex impedance of the port based on measurements of the following two 
things:

1) The voltage drop across the source resistor
2) The phase of the current through the resistor, relative to the phase of 
the source

I designed a simple fixture to measure the voltage and phase, then derived 
the necessary equations and created a spreadsheet to calculate the complex 
impedance.

Soon after completing my measurements this way, I got a good price on a used 
test instrument that makes this measurement directly.  I was very pleased to 
find that the values measured by the test instrument matched my calculated 
values almost exactly.  This gave me good confidence in my earlier test 
method, even though I no longer need to use it.

It might be possible for you to adapt this method for the test you want to 
make.  If so, I would be happy to send you a copy of the equations and a copy 
of the spreadsheet I used.  Since this was developed internally for my own 
use, the notes are a little sketchy, but I think I could fill in the gaps 
with a telephone conversation.

While I am not familiar with the details of the test you are trying to 
perform, I can see that one possible complication would occur if the test is 
supposed to be performed under a specified load condition.  In that case, you 
would have to find a way to ensure that the AC impedance of your load does 
not affect the measured impedance of the mains.  I think there are ways to 
accomplish this either with a test fixture or by making the spreadsheet 
calculations take the load impedance into account.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com



Re: EMC immunity requirements in Canada?

2002-09-19 Thread Kevin Keegan

Amund:

Industry Canada does not have immunity requirements for Class A/B products.

Regards

Kevin Keegan
KES  Associates
Ottawa Canada
- Original Message -
From: am...@westin-emission.no
To: emc-p...@majordomo.ieee.org
Sent: Thursday, September 19, 2002 8:22 AM
Subject: EMC immunity requirements in Canada?



 As far as I remember, US (FCC) do only have emission (radiated /
conducted)
 requirements.
 What about Canada (IC)  do they have immunity requirements in addition
?

 Best regards
 Amund Westin, Oslo/ NORWAY



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Radiated Immunity Testing

2002-09-19 Thread Ken Javor

Be careful about using the antenna factor.  The published antenna factor is
a receive antenna factor, and for what you are trying to do you need the
transmit antenna factor.  You can calculate one from the other if you know
the frequency, but they are not identical.  I can provide that derivation.
You should also know how the antenna factor was measured - if any
attenuation was used to reduce vswr.  Usually antennas will have vswr
specified separately from antenna factor, which leads me to believe that
quite a bit of attenuation is used to remove that source of error.  Likely
someone on this forum has direct experience calibrating antennas.  All the
factors you mentioned you can measure or get from a spec sheet, except
chamber effects.  I though the whole point of the chamber was to be anechoic
enough to allow for that quiet zone calibration.  That would mean to me
there are no chamber effects.

--
From: richwo...@tycoint.com
To: emc-p...@majordomo.ieee.org
Subject: Radiated Immunity Testing
Date: Thu, Sep 19, 2002, 7:11 AM



 Using the antenna factor of a particular antenna, one can compute the
 theoretical power required to create a specified E-field at a specified
 distance. Without over specifying the power amplifier (assume Class A), what
 minimum safety factor should be added to the theoretical values to account
 for impedance mismatches, cable loss, directional coupler loss, compact
 anechoic chamber effects (3 m) including loading of the antenna, the allowed
 6 dB field variation and any other effects.

 Richard Woods
 Sensormatic Electronics
 Tyco International


 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


EMC immunity requirements in Canada?

2002-09-19 Thread amund

As far as I remember, US (FCC) do only have emission (radiated / conducted)
requirements.
What about Canada (IC)  do they have immunity requirements in addition ?

Best regards
Amund Westin, Oslo/ NORWAY



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Radiated Immunity Testing

2002-09-19 Thread richwoods

Using the antenna factor of a particular antenna, one can compute the
theoretical power required to create a specified E-field at a specified
distance. Without over specifying the power amplifier (assume Class A), what
minimum safety factor should be added to the theoretical values to account
for impedance mismatches, cable loss, directional coupler loss, compact
anechoic chamber effects (3 m) including loading of the antenna, the allowed
6 dB field variation and any other effects.

Richard Woods
Sensormatic Electronics
Tyco International


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Measuring AC Line Impedance

2002-09-19 Thread Spencer, David H

I'm trying to characterize the 50Hz AC line impedance of my facility, for
comparison to the values specified in IEC61000-3-3.  I've come across
generic short circuit values for the Resistive and Inductive components.
However, I need to determine exactly what these values are ideally through a
combination of measurement and calculation.

So far,  I've taken a large resistive load and measured the voltage drop on
the AC line.  From that I calculated the total impedance of the AC line.
However, as you may suspect, with a resistive load, the power factor is 1.0.
So I can't vectorly, calculate the resistive and inductive components.  

Is anyone familiar with a method to measure and calculate those values.  The
generic values I have for short circuit condition (which include 4 wires in
a magnetic conduit) come out higher than my measured values, and those do
not include the motor generator source.  

Thanks for any information



David Spencer
Xerox Corporation
  


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread John Allen
Gert
 
Thanks for that investigation that I have not had the time for recently!
 
Now, maybe, the standards writing committees will begin to take this issue
on board and do something about it as the problem is generally technically
trivial to solve - the major issue then being to ensure that the bleeder
device is always across the capacitor, and is not isolated from it by a
switch or contactor that the operator can put in the open position before
disconnecting the supply.
 
(The latter point can particularly apply to some filtered IEC, or similar,
power inlets with integral switches where the bleeder could be on the
opposite side of the contacts to the capacitor).
John Allen
Technical Consultant
Electromagnetics, Safety and Reliability Group
ERA Technology Ltd
Cleeve Rd
Leatherhead
Surrey KT22 7SA
Tel: +44 (0) 1372-367025 (Direct)
+44 (0) 1372-367000 (Switchboard)
Fax: +44 (0) 1372-367102 (Fax)

-Original Message-
From: Gert Gremmen [mailto:g.grem...@cetest.nl]
Sent: 19 September 2002 11:57
To: John Allen
Cc: emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi John,
 
Even theory has to comply with practice, so i took my soldering iron...
 
I have to admit that modern capacitors do keep their charge too
long. I did some test with newer Y and X caps of 0.1 uF and they keep their
charge way too long - over 1 minute - without notable loss of
voltage ( 10%) (real life voltages choosen :310V)
Probably the quality of the dielectricum has been improved, or
the use of paper has been abandoned in favor of modern equivalent
plastics. (any one knows ?).
Of course the increased leakage of the older caps was not meant to be
part of the specs, and this is again a good example of how relying on hidden

specifications may in time lead to undesired results: standards ignoring the
effect of  increased leakage resistance.
 
I also tried the discharge between two fingers, and found the result to
be unpleasant at least.
Time to change standards...
 
Gert Gremmen
 
ce-test, qualified testing
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Allen
Sent: Thursday, September 19, 2002 9:24 AM
To: 'Grasso, Charles'; 'Warren Birmingham'
Cc: emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi Charles, Warren
 
Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.
 
The difference between reality and theory!
 
I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
(the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)
 
However before they do try it, I suggest they wear safety boots and also use
a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!
 
Regards
 
John Allen

-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF



Hi All,

 

From personal experience I can tell you that the involuntary reaction to a
shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a PC
from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed off
the caps didn't make it into 
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued and
the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.

 

Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com; mailto:charles.gra...@echostar.com;
%20   
Email Alternate: chasgra...@ieee.org mailto:chasgra...@ieee.org 

 

-Original Message-
From: John Allen [mailto:john.al...@era.co.uk] 
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF

 

Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF capacitor
charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum: 

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock 

Re: EN60065 mains switches

2002-09-19 Thread John Woodgate

I read in !emc-pstc that Colgan, Chris chris.col...@tagmclaren.com
wrote (in AE0F4BD08FEAD211895900805FE67B1F01425A8B@CAT) about 'EN60065
mains switches' on Thu, 19 Sep 2002:
I'm all for using the 7th edition but it is not mentioned in the LVD List of
Harmonised Standards yet.  Any idea when it will be?

No, but I would have expected to have heard already if there was any
hold-up on technical grounds. It has happened before that notification
has been delayed simply due to a backlog in the Commission's
administration. They shut down for August, I believe.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: CE Marking for Passive speakers

2002-09-19 Thread John Woodgate

I read in !emc-pstc that Gordon,Ian ian.gor...@edwards.boc.com wrote
(in E1BA0362B28ED211A1E80008C71EA306018190AE@EXC_EAS01) about 'CE
Marking for Passive speakers' on Thu, 19 Sep 2002:
By the wider issue I was referring to your assertion that The EMC
Guidelines document explains that having no active components is NOT grounds
for exemption from the EMC Directive.
If this were the case then it would have far reaching implications for many
industries since all Electromagnetically Benign equipment might require
testing.
Furthermore I imagine this would have legal implications for the UK
Government appointed Competent Body which advised my company that benign
equipment is exempt. This Competent Body helped us compile a list of
products within our range to which this exclusion applied. 

'Benign' is NOT the same as 'passive', which is what was asserted. A
torch/flashlight with an incandescent lamp is benign, because it is
inconceivable that it would either emit anything or suffer from lack of
immunity. But even just a *junction box* for high-speed data cable can
both emit stuff and let external disturbances into the cabling. 

I showed how a loudspeaker can both emit and be disturbed by and
external emission. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Question: Discharge capacitance 0.1 uF

2002-09-19 Thread Gert Gremmen
Hi John,

Even theory has to comply with practice, so i took my soldering iron...

I have to admit that modern capacitors do keep their charge too
long. I did some test with newer Y and X caps of 0.1 uF and they keep their
charge way too long - over 1 minute - without notable loss of
voltage ( 10%) (real life voltages choosen :310V)
Probably the quality of the dielectricum has been improved, or
the use of paper has been abandoned in favor of modern equivalent
plastics. (any one knows ?).
Of course the increased leakage of the older caps was not meant to be
part of the specs, and this is again a good example of how relying on hidden
specifications may in time lead to undesired results: standards ignoring the
effect of  increased leakage resistance.

I also tried the discharge between two fingers, and found the result to
be unpleasant at least.
Time to change standards...

Gert Gremmen

ce-test, qualified testing

  -Original Message-
  From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Allen
  Sent: Thursday, September 19, 2002 9:24 AM
  To: 'Grasso, Charles'; 'Warren Birmingham'
  Cc: emc-p...@majordomo.ieee.org
  Subject: RE: Question: Discharge capacitance 0.1 uF


  Hi Charles, Warren

  Seems that a few of us know what DOES happen and the longterm results, but
quite a few others don't believe that it does - and that even it does then
it is not very important.

  The difference between reality and theory!

  I suggest that the non-believers try it for themselves - by unplugging a
suitable piece of equipment and picking it up - AND then touching the pins
of the plug!
  (the unplugging process may need to be repeated a few times until the
capacitor is disconnected when the mains is high at the time of
disconnection and so gets a decent charge!)

  However before they do try it, I suggest they wear safety boots and also
use a piece of equipment which can then be discarded due to the damage it
received when it fell on the foot and/or the ground!

  Regards

  John Allen
-Original Message-
From: Grasso, Charles [mailto:charles.gra...@echostar.com]
Sent: 18 September 2002 19:07
To: 'John Allen'; emc-p...@majordomo.ieee.org
Subject: RE: Question: Discharge capacitance 0.1 uF


Hi All,



From personal experience I can tell you that the involuntary reaction to
a shock can have serious consequences to
the sales of a company. In a former life - a previous employer OEM'd a
PC from a Korean Company. The PC had all
the relevant marks but somehow the resistor that was supposed to bleed
off the caps didn't make it into
production. A customer , moving said model from one location to another,
touched the mains terminals and felt a shock.
The customer fell over, the PC landed on the customer, the customer sued
and the story ended up in the papers.
The sales of PCs essentially died after that. - All for the sake of one
resistor.



Best Regards
Charles Grasso
Senior Compliance Engineer
Echostar Communications Corp.
Tel:  303-706-5467
Fax: 303-799-6222
Cell: 303-204-2974
Email: charles.gra...@echostar.com;
Email Alternate: chasgra...@ieee.org



-Original Message-
From: John Allen [mailto:john.al...@era.co.uk]
Sent: Wednesday, September 18, 2002 11:11 AM
To: emc-p...@majordomo.ieee.org
Subject: Question: Discharge capacitance 0.1 uF



Hello Folks

Tomonori Sato  commented However, I think discharge from 0.1uF
capacitor charged to the mains peak voltage can be quite uncomfortable.

I believe that to be true from personal experience and from having to
investigate the results of a number of such incidents, and so would remind
member of a point that I made several years ago on this forum:

The primary shock almost certainly will NOT hurt a person, but the
involuntary reaction TO the shock may well have much more
seriousconsequences.

This type of shock is often encountered by people who pick up equipment
which they have just unplugged from the AC mains in order to carry it
elsewhere.  If they then touch the pins of the plug there are numerous
reported incidences of them involuntarily dropping the unit - and that can
possibly be on their own feet - and from a height of about 3ft/1m! If the
unit is more than a couple of pounds (about one kilo) then the injury to t!
he feet can be substantial.

Worse situations could occur in industrial equipment when a service
engineer opens a cabinet to perform a service operation - the reaction from
the shock could cause him to strike touch other hazardous electrical or
mechanical parts (which probably should also not be there, I do agree!)
which then cause him serious actual injury.

These types of incident do not make the equipment supplier very
popular to say the least, and could result in product liability claims.

The main basis for the claims would be that the supplier had not

RE: EN60065 mains switches

2002-09-19 Thread Colgan, Chris

I'm all for using the 7th edition but it is not mentioned in the LVD List of
Harmonised Standards yet.  Any idea when it will be?

Cheers

Chris

 -Original Message-
 From: John Woodgate [SMTP:j...@jmwa.demon.co.uk]
 Sent: Wednesday, September 18, 2002 9:47 PM
 To:   emc-p...@majordomo.ieee.org
 Subject:  Re: EN60065 mains switches
 
 
 I read in !emc-pstc that Colgan, Chris chris.col...@tagmclaren.com
 wrote (in AE0F4BD08FEAD211895900805FE67B1F01425A89@CAT) about 'EN60065
 mains switches' on Wed, 18 Sep 2002:
 I know that engineers familiar with EN60065 are rarer than hen's teeth
 but
 maybe someone out there can help me...
 
 Clause 14.6.2 allows for no mains switch to be fitted if the product can
 be
 switched on or off or both automatically.  Do you think that an audio
 amplifier that utilises an input signal detect circuit to automatically
 switch on fulfils the requirements of this clause?
 
 You should be looking at the 2002 edition, in which 14.6.2 is not about
 that. This 14.6 gets re-hashed in every edition, so you must use the up-
 to-date edition. In this case, the relevant text is in 8.9.1! An all-
 pole disconnect device is required, but it can be the mains plug or
 appliance coupler. So your audio amplifier is quite OK - to the 2002
 edition. Do you *really* want to know about how it would fare under the
 previous edition? (;-)
 -- 
 Regards, John Woodgate, OOO - Own Opinions Only.
 http://www.jmwa.demon.co.uk 
 Interested in professional sound reinforcement and distribution? Then go
 to 
 http://www.isce.org.uk
 PLEASE do NOT copy news posts to me by E-MAIL!
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


**  
   Please visit us at www.tagmclaren.com
**

The contents of this E-mail are confidential and for the exclusive
use of the intended recipient. If you receive this E-mail in error,
please delete it from your system immediately and notify us either
by E-mail, telephone or fax. You  should not  copy, forward or 
otherwise disclose the content of the E-mail.

Important Note: Any typographical, clerical or other error in this 
communication is subject to correction without any liability on 
the part of TAG McLaren Audio Limited. Any orders placed shall
be subject to acceptance by TAG McLaren Audio Limited on its 
standard terms and conditions of sale which shall govern the 
contract for the sale and purchase of the products ordered to the
exclusion of any other terms and conditions.

TAG McLaren Audio Ltd
The Summit, 11 Latham Road
Huntingdon, Cambs, PE29 6ZU
Telephone : 01480 415600 (+44 1480 415600)
Facsimile : 01480 52159 (+44 1480 52159)

**  
   Please visit us at www.tagmclaren.com
**

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list