The standard 35A or so breakage capacity glass fuses
may fulfill your needs in a household situation with relative low prospective 
short circuit currents.
If used on branches with higher currents (say 64A or even more) the prospective 
short
circuit current will be even higher (50 kA) leading to the failure you 
mentioned.
Small glass fuses can be obtained with 1500 A safe breaking capacity.
If you need even more you need other type (large in general) of fuses and fuse 
holder.
Not that the wiring diameter in the protected circuit should keep up with that.

Regards,

Ing.  Gert Gremmen, BSc



g.grem...@cetest.nl
www.cetest.nl

Kiotoweg 363
3047 BG Rotterdam
T 31(0)104152426
F 31(0)104154953

 Before printing, think about the environment. 



-Oorspronkelijk bericht-
Van: emc-p...@ieee.org [mailto:emc-p...@ieee.org] Namens Boštjan Glavic
Verzonden: Thursday, August 08, 2013 6:21 AM
Aan: EMC-PSTC@LISTSERV.IEEE.ORG
Onderwerp: RE: [PSES] breakage of the fuse

Dear all,

Thank you for your comments.

The below mentioned construction was rejected. The client needs to use high 
breaking fuse and not enhanced fuse.

The problem is that in every switch mode power supply you can get high short 
circuit current which is causing non-high breaking fuse to burst (there is a 
resistance 1ohm even with power supply cord). This happens during fault 
condition testing in primary circuit right after the fuse (e.g. across the 
varistor or diode bridge). But test has to be performed on the correct branch 
circuit and in peak of input voltage. But the problem is that standard does not 
define precisely how to conduct the abnormal condition (e.g. IEC 60950-1).

There are many power supplies on the market with low breaking or enhanced 
breaking type of fuse and they are approved by different certification bodies. 
Some power supplies have only TR5 low breaking fuse. That's why I decided to 
ask you experts for 2nd opinion.

UL has a PAG about this issue and does not allow it. However in the past many 
such construction were acceptable also by UL.

Best regards,

Boštjan Glavič
Head of Laboratory, Laboratory of Electronic Engineering www.siq.si SIQ 
Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678 t +386 
(0)1 4778 265, m +386 (0)41 391 283, f +386 (0)1 4778 444


-Original Message-
From: Pete Perkins [mailto:peperkin...@cs.com]
Sent: Wednesday, August 07, 2013 11:33 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Cc: Boštjan Glavič
Subject: RE: [PSES] breakage of the fuse

Bostjan commented:  During the abnormal tests in primary circuit,
internal input fuse operates and glass breaks. However, fuse is inside the 
tubing and broken glass does not spread around.

Would you accept such construction?

- - - - -

Bostjan,

Such a question can have several answers, among other things it
depends upon who the 'you' is.   

If the 'you' is a party who suffered personal injury or financial 
damage they probably wouldn't be willing to accept such construction  you will 
hear from them.  

If the 'you' is a test house or regulator they probably would be 
looking closely for a way to not accept such construction.  

If the 'you' is a tinkerer who likes to solve difficult problems they 
probably would accept such construction  be happy that they could fix it and 
get on with using the product. 

Perhaps the question you should ask is 'would your mother accept such 
construction?' or would she be all over you because of what happened.  

Would the general public know how to clear out the mess in the 
fuseholder and insert a new fuse to get back in operation?  

Think about it; not all questions have one simple answer.  

:) br, Pete

 

Peter E Perkins, PE

Principal Product Safety Engineer

PO Box 23427

Tigard, ORe  97281-3427

 

503/452-1201 fone/fax

p.perk...@ieee.org

 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list

Re: [PSES] breakage of the fuse

2013-08-08 Thread Peter Tarver
 -Original Message-
 From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
 Sent: Wednesday, August 07, 2013 21:41

 Peter,

 Fuse is not replaceable. It needs to be sleeved (tubed)
 and only manufacturer can repair the power supply.

 Due to the tubing, there is not likely that vaporized
 metal would affect other parts and decrease safety
 distances.

Boštjan -

Don't be too hasty in that tubing assessment, simply because it's there.
The pressures involved can be substantial and the sealing ability of the
tubing would need to be carefully reviewed, as well as application
methodology (work instructions and craftsmanship).  After a fuse opens the
circuit involved, the tubing needs to be cut open to look for evidence of
metal vapor deposition.  Assume nothing.

During my employ at a well known NRTL, I was responsible for testing glass
tube and other fuses, as well as having seen glass tube fuses crack,
ferrules become dislodged (even on solder in place fuses), when the
interrupting (breaking) capacity was too low for an application in
end-product equipment.

I'm glad the fuse will be replaced with another, more approriate type.


Peter Tarver


This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-07 Thread Tyra, John
What is the breaking capacity of the fuse? Sounds like it may be a low breaking 
capacity fuse. If it is you should change it to a high breaking capacity fuse.

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Boštjan Glavic
Sent: Tuesday, August 06, 2013 12:46 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: breakage of the fuse

Dear safety experts,

During the abnormal tests in primary circuit, internal input fuse operates and 
glass breaks. However, fuse is inside the tubing and broken glass does not 
spread around.

Would you accept such construction?

Best regards,
Bostjan
SIQ
-


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.orgmailto:emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.netmailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.orgmailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.orgmailto:j.bac...@ieee.org
David Heald dhe...@gmail.commailto:dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-07 Thread Pete Perkins
Bostjan commented:  During the abnormal tests in primary circuit,
internal input fuse operates and glass breaks. However, fuse is inside the
tubing and broken glass does not spread around.

Would you accept such construction?

- - - - -

Bostjan,

Such a question can have several answers, among other things it
depends upon who the 'you' is.   

If the 'you' is a party who suffered personal injury or financial
damage they probably wouldn't be willing to accept such construction  you
will hear from them.  

If the 'you' is a test house or regulator they probably would be
looking closely for a way to not accept such construction.  

If the 'you' is a tinkerer who likes to solve difficult problems
they probably would accept such construction  be happy that they could fix
it and get on with using the product. 

Perhaps the question you should ask is 'would your mother accept
such construction?' or would she be all over you because of what happened.  

Would the general public know how to clear out the mess in the
fuseholder and insert a new fuse to get back in operation?  

Think about it; not all questions have one simple answer.  

:) br, Pete

 

Peter E Perkins, PE

Principal Product Safety Engineer

PO Box 23427

Tigard, ORe  97281-3427

 

503/452-1201 fone/fax

p.perk...@ieee.org

 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-07 Thread Peter Tarver
When a fuse's interrupting (breaking) capacity is too low for an
application and the fuse opening interrupts current in a manner that
causes the glass to crack or break, the temperature gradient across the
glass and the internal pressure created by the plasma when the fusible
element vaporized can and will push some of the vaporized metal out of the
confines of the glass and contaminate the surrounding area.  Sometimes the
deposited metal is not readily visible and even if visible does not always
clean up easily or well.  The Creepage Distances may be compromised.
Depending on the overall design, this can cause increases in touch current
(leakage current) and otherwise increase the risk of electric shock with
continued product use.

Replacement of the fuse can become more frequently necessary due to the
contamination allowing unintentional current flow to keep the product
operating.  If each successive fuse replacement uses the same fuse, more
of the same may result.  If the product isn't returned for replacement or
discarded, the fuse might eventually be replaced with a larger rated fuse
with possible further degradation of safety.


Peter Tarver


This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-07 Thread Boštjan Glavič
Dear all,

Thank you for your comments.

The below mentioned construction was rejected. The client needs to use high 
breaking fuse and not enhanced fuse.

The problem is that in every switch mode power supply you can get high short 
circuit current which is causing non-high breaking fuse to burst (there is a 
resistance 1ohm even with power supply cord). This happens during fault 
condition testing in primary circuit right after the fuse (e.g. across the 
varistor or diode bridge). But test has to be performed on the correct branch 
circuit and in peak of input voltage. But the problem is that standard does not 
define precisely how to conduct the abnormal condition (e.g. IEC 60950-1).

There are many power supplies on the market with low breaking or enhanced 
breaking type of fuse and they are approved by different certification bodies. 
Some power supplies have only TR5 low breaking fuse. That's why I decided to 
ask you experts for 2nd opinion.

UL has a PAG about this issue and does not allow it. However in the past many 
such construction were acceptable also by UL.

Best regards,

Boštjan Glavič
Head of Laboratory, Laboratory of Electronic Engineering
www.siq.si
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678
t +386 (0)1 4778 265, m +386 (0)41 391 283, f +386 (0)1 4778 444


-Original Message-
From: Pete Perkins [mailto:peperkin...@cs.com] 
Sent: Wednesday, August 07, 2013 11:33 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Cc: Boštjan Glavič
Subject: RE: [PSES] breakage of the fuse

Bostjan commented:  During the abnormal tests in primary circuit,
internal input fuse operates and glass breaks. However, fuse is inside the 
tubing and broken glass does not spread around.

Would you accept such construction?

- - - - -

Bostjan,

Such a question can have several answers, among other things it
depends upon who the 'you' is.   

If the 'you' is a party who suffered personal injury or financial 
damage they probably wouldn't be willing to accept such construction  you will 
hear from them.  

If the 'you' is a test house or regulator they probably would be 
looking closely for a way to not accept such construction.  

If the 'you' is a tinkerer who likes to solve difficult problems they 
probably would accept such construction  be happy that they could fix it and 
get on with using the product. 

Perhaps the question you should ask is 'would your mother accept such 
construction?' or would she be all over you because of what happened.  

Would the general public know how to clear out the mess in the 
fuseholder and insert a new fuse to get back in operation?  

Think about it; not all questions have one simple answer.  

:) br, Pete

 

Peter E Perkins, PE

Principal Product Safety Engineer

PO Box 23427

Tigard, ORe  97281-3427

 

503/452-1201 fone/fax

p.perk...@ieee.org

 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-06 Thread John Woodgate
In message f3471a52242d724da04c8a85ac1ca33a91c8a...@ser-ex01.siq.si, 
dated Tue, 6 Aug 2013, =?iso-8859-2?Q?Bo=B9tjan_Glavi=E8?= 
bostjan.gla...@siq.si writes:


During the abnormal tests in primary circuit, internal input fuse 
operates and glass breaks. However, fuse is inside the tubing and 
broken glass does not spread around.


This indicates that the fuse is being used beyond its safe interrupting 
current rating. To meet most safety standards, components must be used 
within their ratings, so your scenario is not allowed. What happens to 
the glass is irrelevant.


How can the fuse be safely replaced? The tubing must be damaged by the 
explosion (yes, it IS an explosion).

--
OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk
Why is the stapler always empty just when you want it?

John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-06 Thread Brian Oconnell
No

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Boštjan
Glavic
Sent: Monday, August 05, 2013 9:46 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: breakage of the fuse

Dear safety experts,
 
During the abnormal tests in primary circuit, internal input fuse operates
and glass breaks. However, fuse is inside the tubing and broken glass does
not spread around.
 
Would you accept such construction?
 
Best regards,
Bostjan
SIQ

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-06 Thread Peter Merguerian
Yes do the test 3 times to check for repeatable results 

Sent from my iPhone

Peter S. Merguerian
pe...@goglobalcompliance.com
Go Global Compliance Inc.
www.goglobalcompliance.com
(408) 931-3303

On Aug 6, 2013, at 8:31 AM, Brian Oconnell oconne...@tamuracorp.com wrote:

 No
 
 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Boštjan
 Glavic
 Sent: Monday, August 05, 2013 9:46 PM
 To: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: breakage of the fuse
 
 Dear safety experts,
  
 During the abnormal tests in primary circuit, internal input fuse operates
 and glass breaks. However, fuse is inside the tubing and broken glass does
 not spread around.
  
 Would you accept such construction?
  
 Best regards,
 Bostjan
 SIQ
 
 -
 
 This message is from the IEEE Product Safety Engineering Society emc-pstc 
 discussion list. To post a message to the list, send your e-mail to 
 emc-p...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieee-pses.org/emc-pstc.html
 
 Attachments are not permitted but the IEEE PSES Online Communities site at 
 http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
 formats), large files, etc.
 
 Website:  http://www.ieee-pses.org/
 Instructions:  http://listserv.ieee.org/request/user-guide.html
 List rules: http://www.ieee-pses.org/listrules.html
 
 For help, send mail to the list administrators:
 Scott Douglas emcp...@radiusnorth.net
 Mike Cantwell mcantw...@ieee.org
 
 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] breakage of the fuse

2013-08-06 Thread Richard Nute


Hello Bostjan:


I agree with John Woodgate.  The fuse is being
used beyond its ratings.  It cannot be relied
upon to interrupt the fault current.


Rich



On 8/5/2013 9:46 PM, Boštjan Glavič wrote:


Dear safety experts,

During the abnormal tests in primary circuit, internal input fuse 
operates and glass breaks. However, fuse is inside the tubing and 
broken glass does not spread around.


Would you accept such construction?

Best regards,

Bostjan

SIQ

-


This message is from the IEEE Product Safety Engineering Society 
emc-pstc discussion list. To post a message to the list, send your 
e-mail to emc-p...@ieee.org mailto:emc-p...@ieee.org


All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html


Attachments are not permitted but the IEEE PSES Online Communities 
site at http://product-compliance.oc.ieee.org/ can be used for 
graphics (in well-used formats), large files, etc.


Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net mailto:emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org mailto:mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org mailto:j.bac...@ieee.org
David Heald dhe...@gmail.com mailto:dhe...@gmail.com




-

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


[PSES] breakage of the fuse

2013-08-05 Thread Boštjan Glavič
Dear safety experts,

During the abnormal tests in primary circuit, internal input fuse operates and 
glass breaks. However, fuse is inside the tubing and broken glass does not 
spread around.

Would you accept such construction?

Best regards,
Bostjan
SIQ

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com