RE: Fiber and AC mains wire runs

2003-04-25 Thread John Allen

Hi Folks

I second Richard Hughes' comments, but would also add the following:

- The IEC 60634/HD 384/ BS7671 etc documents are aimed at wiring
installation designers - and they certainly differ from country to country
in many respects, notably in the sections on special locations, and in some
of the national wiring requirements (e.g. local cables, sockets, plugs and
over-current protection requirements).

- In addition, each country has its own sets of national and /or electrical
contractors installation and verification guides which give the local
interpretations. However, most of the guides are only available in the
national language!
(Done a bit of that over the years!)

Therefore, you would have to identify one or more sample countries and put
in some considerable work to investigate those in detail to get the
flavours being sought.

John Allen
ERA Technology Ltd


From: richhug...@aol.com [mailto:richhug...@aol.com]
Sent: 22 April 2003 15:29
To: richwo...@tycoint.com; emc-p...@majordomo.ieee.org
Subject: re: Fiber and AC mains wire runs



Richard,
 
As I mentioned in my original reply, the building wiring rules vary from one
country within the EU to another.  While it is true that the UK Wiring
Regulations (BSI 7671) are based on the CENELEC Harmonised Document HD384,
which is itself based on the IEC 60364 series of standards, it would be
wrong of someone to think that if they purchased a copy of BS 7671 and then
based their whole European installation strategy on this UK document that
they would be certain not to have difficulties elsewhere in Europe.
 
Of course, if someone wanted to know what the requirements are in the UK and
thereby get a 'flavour' of the requirements elsewhere, then that would be a
different matter and BS 7671 (also known as the IEE Wiring Regulations)
would be a good place to start.  They may also wish to look at the IEE web
site (www.iee.org) for books that provide aditional guidance when applying
the IEE Wiring Regulations.
 
Regards,
 
Richard Hughes.


From: richwo...@tycoint.com [mailto:richwo...@tycoint.com] 
Sent: 22 April 2003 13:57
To: emc-p...@majordomo.ieee.org
Subject: RE: Fiber and AC mains wire runs





The EU wiring rules are based upon HD384 which is based upon IEC 60364. You
can purchase a single part copy as BSI 7671.

Richard Woods
Sensormatic Electronics
Tyco International



From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, April 16, 2003 5:26 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: Fiber and AC mains wire runs



I read in !emc-pstc that Cereceres, David dcerece...@pelco.com wrote
(in b2cc0e0f2c10d511b86600b0d06898420541f...@localhost.pelco.dns)
about 'Fiber and AC mains wire runs' on Wed, 16 Apr 2003:

Is there a European equivalent of the NEC that I could possibly reference?

An *international* standard, IEC 60364, a huge multi-part standard.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
   http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
   http://www.ieeecommunities.org/emc-pstc
http://www.ieeecommunities.org/emc-pstc 






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p

Re: Fiber and AC mains wire runs

2003-04-23 Thread John Woodgate

I read in !emc-pstc that richwo...@tycoint.com wrote (in 846BF526A205F8
4BA2B6045BBF7E9A6A04675EB8@flbocexu05) about 'Fiber and AC mains wire
runs' on Tue, 22 Apr 2003:

The EU wiring rules are based upon HD384 which is based upon IEC 60364. You
can purchase a single part copy as BSI 7671.

BS 7671 is a *UK interpretation* of HD384 and IEC 60364. Other
interpretations, significantly different, apply in other European
countries.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Fiber and AC mains wire runs

2003-04-23 Thread Juhasz, John (IndSys, GE Interlogix)

David,

Be careful here. While fiber itself is non-conductive, and
the outer jacket is non-conductive, there are fiber cables
that have metal sheaths below the outerjacket - these are
used for mechanical strength.
Should the outer jacket become damaged, and there is cross-over
you could have a problem.

I'd look into this further if I were you.

John A. Juhasz
Compliance Engr.

GE Interlogix
Fiber Options Div.
Bohemia, NY 



From: Cereceres, David [mailto:dcerece...@pelco.com]
Sent: Wednesday, April 16, 2003 4:11 PM
To: emc-p...@ieee.org
Cc: Toste, David
Subject: Fiber and AC mains wire runs 



Hello Group,
Does anyone know of any European or North American restrictions against
running 
fiber and high voltage (115-230v ac) through the same conduit entry of a
product? 
I am aware of certain standards that allow running high and low voltage
wiring together, 
provided the wiring has sufficient insulation.  I am also aware that fiber
jacketing is 
electrically non-conductive. So would it follow that there are no
restrictions running high 
voltage wiring and fiber optics together through the same conduit entry? 

I have reviewed the NEC but have been unable to come to a definitive
conclusion. 
Is there a European equivalent of the NEC that I could possibly reference?

Once again, your expert advice is greatly appreciated,
David R. Cereceres
Safety Engineer
Pelco
800-289-9100x3493
559-292-1981x3493
dcerece...@pelco.com mailto:dcerece...@pelco.com 
www.Pelco.com http://www.pelco.com/ 



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



re: Fiber and AC mains wire runs

2003-04-22 Thread richhug...@aol.com

Richard,
 
As I mentioned in my original reply, the building wiring rules vary from one
country within the EU to another.  While it is true that the UK Wiring
Regulations (BSI 7671) are based on the CENELEC Harmonised Document HD384,
which is itself based on the IEC 60364 series of standards, it would be
wrong of someone to think that if they purchased a copy of BS 7671 and then
based their whole European installation strategy on this UK document that
they would be certain not to have difficulties elsewhere in Europe.
 
Of course, if someone wanted to know what the requirements are in the UK and
thereby get a 'flavour' of the requirements elsewhere, then that would be a
different matter and BS 7671 (also known as the IEE Wiring Regulations)
would be a good place to start.  They may also wish to look at the IEE web
site (www.iee.org) for books that provide aditional guidance when applying
the IEE Wiring Regulations.
 
Regards,
 
Richard Hughes.


From: richwo...@tycoint.com [mailto:richwo...@tycoint.com] 
Sent: 22 April 2003 13:57
To: emc-p...@majordomo.ieee.org
Subject: RE: Fiber and AC mains wire runs





The EU wiring rules are based upon HD384 which is based upon IEC 60364. You
can purchase a single part copy as BSI 7671.

Richard Woods
Sensormatic Electronics
Tyco International



From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, April 16, 2003 5:26 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: Fiber and AC mains wire runs



I read in !emc-pstc that Cereceres, David dcerece...@pelco.com wrote
(in b2cc0e0f2c10d511b86600b0d06898420541f...@localhost.pelco.dns)
about 'Fiber and AC mains wire runs' on Wed, 16 Apr 2003:

Is there a European equivalent of the NEC that I could possibly reference?

An *international* standard, IEC 60364, a huge multi-part standard.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
   http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
   http://www.ieeecommunities.org/emc-pstc
http://www.ieeecommunities.org/emc-pstc 






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Fiber and AC mains wire runs

2003-04-22 Thread richwo...@tycoint.com

The EU wiring rules are based upon HD384 which is based upon IEC 60364. You
can purchase a single part copy as BSI 7671.

Richard Woods
Sensormatic Electronics
Tyco International



From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Wednesday, April 16, 2003 5:26 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: Fiber and AC mains wire runs



I read in !emc-pstc that Cereceres, David dcerece...@pelco.com wrote
(in b2cc0e0f2c10d511b86600b0d06898420541f...@localhost.pelco.dns)
about 'Fiber and AC mains wire runs' on Wed, 16 Apr 2003:

Is there a European equivalent of the NEC that I could possibly reference?

An *international* standard, IEC 60364, a huge multi-part standard.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk

Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Fiber and AC mains wire runs

2003-04-22 Thread Evangeline Cometa

David:
The Insulated Conductors Committee of the IEEE has a fiber optic cables
working group that has come up with a document called P1428 - IEEE Guide
for Installation Methods for Fiber Optic Cables in Electric Power Generating
Stations and in Industrial Facilities.
You can also check the fiber optic section of the IEEE ICC web site:
http://www.ewh.ieee.org/soc/pes/icc/ for more information as to whether this
guide has been published.

In power cable engineering, the term high voltage is used for cables rated
above 69 kV and above. Those cables employ a semiconductive jacket over the
insulation for installations that are in proximity to communications cables.
Not sure what the practice is for low voltage (115-230V ac)but the ICC
working group on fiber optic cables should be able to give you some
guidelines.

Hope it helps.

Evangeline Cometa
CSA International
Tel. 416-727-2671
 

 -Original Message-
 From: Cereceres, David [mailto:dcerece...@pelco.com]
 Sent: Wednesday, April 16, 2003 4:11 PM
 To: emc-p...@ieee.org
 Cc: Toste, David
 Subject: Fiber and AC mains wire runs 
 
 
 
 Hello Group,
 Does anyone know of any European or North American 
 restrictions against
 running 
 fiber and high voltage (115-230v ac) through the same conduit 
 entry of a
 product? 
 I am aware of certain standards that allow running high and 
 low voltage
 wiring together, 
 provided the wiring has sufficient insulation.  I am also 
 aware that fiber
 jacketing is 
 electrically non-conductive. So would it follow that there are no
 restrictions running high 
 voltage wiring and fiber optics together through the same 
 conduit entry? 
 
 I have reviewed the NEC but have been unable to come to a definitive
 conclusion. 
 Is there a European equivalent of the NEC that I could 
 possibly reference?
 
 Once again, your expert advice is greatly appreciated,
 David R. Cereceres
 Safety Engineer
 Pelco
 800-289-9100x3493
 559-292-1981x3493
 dcerece...@pelco.com mailto:dcerece...@pelco.com 
 www.Pelco.com http://www.pelco.com/ 
 
 





--IMPORTANT NOTICE-- 
This message is intended only for the use of the person or organization to
which it is addressed, and may contain information that is privileged,
confidential and exempt from disclosure under applicable law. If the reader
of this message is not the intended recipient, or responsible for delivering
the message to the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited. If you have received this communication in error, please notify
the sender immediately by email or telephone and delete the original message
immediately.  Thank you.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Fiber and AC mains wire runs

2003-04-16 Thread richhug...@aol.com
In a message dated 16/04/2003 21:23:18 GMT Daylight Time, dcerece...@pelco.com
writes:




David



The wiring regulations in Europe are based on a CENELEC Harmonised Document
(HD) rather than a European Norm (EN) and, as such, it is permissible for
requirements to vary from country-to-country in Europe to a much greater
extent than is the case for EN 60950, EN 60065, etc.  You may therefore find
that there is no single answer for the whole of Europe.

You say 'high voltage' - but that means different things to a logic designer
vs. a power utility engineer.  Certainly, in the UK it is not uncommon to run
backbone optical fibres in a spiral fashion around the earth return conductor
strung between  extra-high tension pylons.  However, that is a very special
application.

For mains and optical cables run in a single conduit it is necessary to
understand who could access (and damage accidentally) the electrical and
optical cables.  For instance, it is far from uncommon for underground cables
to be damaged by diggers repairing roads etc.  Normally, the repairing of
optical cables and electrical cables falls to two or more organisations who
have operatives specialised in optical safety and electrical safety
respectively.  Even if only one company is involved in maintaining/repairing
both optical and electrical cables, the personnel may well be different. Your
application may just be between two linked buildings or even within a single
room, but you should nevertheless consider this question.

So, are the high voltage cables double-insulated such that they could be
touched by untrained personnel?  If not, then re-splicing an optical fibre
could expose 'optical technicians' to unexpected and unacceptable electrical
safety hazards.

What is the optical power being transmitted down the fibre?  What is the
Hazard Level per IEC 60825-2 and would it be acceptable for the 'electrical
technicians' to be exposed to this radiation from broken fibres?

Within IEC TC76 (responsible for the optical safety standards - IEC 60825
series) and IEC TC 86C (responsible for fibre-optic cable standards) and the
ITU-T there has been discussion regarding potential fire hazards caused by the
transmission of high optical powers (e.g. in the order of 1W) under certain
circumstances. It is a theoretical possibility that a fault in a fibre
carrying high optical powers could burn the insulation off of electrical
cables carrying high electrical powers, thereby causing an electrical
short-circuit.  Whether this is the case for you at the moment is something
for you to determine - as is the possibility that it is relatively easy to
increase the transmitted optical power at some future date.

You also talk of optical fibres being insulating.  That may be so for certain
fibres, but it is also possible to get steel reinforced optical cables.  If
such optical cables are being used, is the insulation from the high voltage
conductors to the (hopefully, earthed) steel reinforcing cables adequate?

Of course, your application could just involve running double-insulated mains
cables and non-metallic fibres at both Class 1 (825-1) and Hazard Level 1
(825-2) in a single channel for a short run.  In such a case you may possible
conclude that the potential safety hazards have been reduced to a sufficiently
low level.

Regards,

Richard Hughes

Safety Answers Ltd.