[RE-wrenches] Looking for insulated #6 bare standoff

2018-04-18 Thread Matthew Sirum
Greetings Dana,

You may consider sheathing the bare copper wire in a product
appropriately rated for the outdoors and UV etc...  Possibly
Liquidtight Flexible Nonmetallic Conduit (LFNC), electronics
insulating sheathing, continuous grommet channel, heat shrink tubing,
or some type of weather stripping product.

Stainless steel cable clamps ("p" clips); bare, coated, or with EPDM
bushing/lining may also be a possible solution.

Heyco Products may be a good source to search for a solution:
https://www.heyco.com/

If time and budget allows you may like to consider using an
appropriately rated insulated wire with a green outer finish.  #6 AWG
USE-2 with green insulation may be an option.  The insulation can be
removed where needed for connection to the ground lugs etc.

Hope you find a good solution for the project.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


 --  Original Message Below  --

[RE-wrenches] Looking for insulated #6 bare standoff

Dana dana at solarwork.com
Wed Apr 18 09:00:27 PDT 2018

Good Morning Wrenches,

I am required to keep the bare #6 copper from touching the aluminum frame
work of a Array Technologies tracker where it is not mechanically connected
by a pass-through ground clamp on a tracking array [dissimilar metals] and
am looking for a lead on an insulated standoff or strap to hold the #6 bare
copper as it passes from panel to panel and rail to rail. The plans examiner
would accept pass through clamps & this is a worst case-spendy solution to
this.

I have searched the inquired at local electrical warehouse &on the internet
and to no avail under "insulated strap" & "insulated cable standoff".

Has anyone else encountered his & what did you use? Where did you source
this strap?

I remember seeing something like this in the fuzzy past & cannot recall
where I saw it or what it was for.

Thanks for any suggestions.
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] TJI rafters

2018-03-07 Thread Matthew Sirum
Greetings Jerry,

I believe I remember reading some Trus Joist technical documentation
which indicated no more than one hole should be drilled or lag
screw/bolt driven into any cross sectional area of the top flange.  If
using the Quick Mount Q-Base with two lag screws/bolts, will you be
orienting the Q-Base so that the two lags are in line vertically with
each other or side by side?...  Seems like side by side (straddling
the web) may not be a good approach.  Staggered vertically (straddling
the web) may be alright if the size of the holes and lags are
appropriate for the top flange dimensions and can be installed where
allowed by the rafter/joist manufacturer's specifications.

I hope you are able to accurately identify the rafter/joist
manufacturer and the rafter/joist model so you can reach out to them
for guidance on what are and are not acceptable attachment methods for
their product.

Other thoughts:
If access to the underside of the roof structure allows, installing
appropriate blocking with proper hangers and fasteners would likely be
a more robust way to go.
I have looked into using stainless steel j-bolts to hook the underside
of the rafter members in situations like this as well; the rest of the
install from the top side is just like working with hanger bolts.
If the roof decking/sheathing and its attachment fasteners and
schedule are all known and sufficient, a multi-fastener deck mount
type mounting product may possibly be an appropriate and labor/time
saving option.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below  --

[RE-wrenches] TJI rafters
Jerry Caldwell solarcowboy at yahoo.com
Tue Mar 6 15:57:04 PST 2018

Bill,
Mineral bitumen roll roofing. 2:12 slope.
Everyone who gave input below, thanks for the suggestions.
I've decided to go with the Quick Mount Q-Base product. It allows you
to get 2 lag bolts into the top chord on either side of the OSB web.
Cheers,Jerry Caldwell
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Interstate battery charging info

2017-12-18 Thread Matthew Sirum
Greetings Jay,

If you aren't having any success getting the Interstate Battery
information you are searching for these contacts may be of help...

Interstate Battery, Dallas, TX 800.541.8419

Here are a couple of names of Interstate Battery ProClinic trainers
from the Power Management Group:
Gale Kimbrough (Gale was the Technical Services Manager when I trained
with him and has taught many of their battery classes over the years.
He may be retired by now?)
Jim Powell

Sorry, I can't seem to find an email address for either of these folks
at the moment.

These gentlemen worked on the heavy-duty truck and industrial battery
training service department at Interstate Battery, but were tied in
with engineering... So, if you can reach them they should be able to
get you what you are looking for or at least connect you with someone
who can.

If all else fails I hope these contacts may be helpful.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


  --Original Message Below--

[RE-wrenches] Interstate battery charging info

Jay jay.peltz at gmail.com
Mon Dec 18 18:17:56 PST 2017

Hi all

I can’t seem to find much information at all on the interstate web site.

I’m trying to find out charging information and maybe cycle curves for
someone with interstate L-16 HCL.

Any ideas?

Thx
Jay
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Breaker trip

2017-12-07 Thread Matthew Sirum
Greetings Mac,

If you haven't already done so it may be interesting to check the
actual current when the circuit breaker trips.  Put a reliable DC
clamp-on current meter on one of the charge controller's output
conductors, set it to log the maximum current, and operate the load in
question.  See what the max current is when the circuit breaker trips.

Also; I am curious if the existing charge controller output circuit
breaker is a model which is rated for 100% continuous duty?   If it is
not and the max current measured is not too great it may be possible
to swap it out for one which is 100% continuous duty rated and still
maintain the same amperage circuit breaker.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


  --  Original Message Below  --

[RE-wrenches] Breaker trip

Mac Lewis maclewis1 at gmail.com
Wed Dec 6 04:18:11 PST 2017

Hello wrenches,

I've got a mysterious breaker tripping that I need some ideas on how to fix.

Original system:
Array 6 x 235W Kyocera modules
1 x Outback FM60 charge controller
1 x Magnum MS 4024 PAE inverter

Upgraded system we stacked a second inverter to accommodate an air
compressor:
Array 6 x 235W Kyocera modules
1 x Outback FM60 charge controller
*2 x Magnum MS 4024 PAE inverter*

There have been no changes to the solar array, just to the inverter side of
the system.  We have been getting intermittent breaker tripping (a couple
of weeks between) on the battery breaker side of the charge controller.
The basics have been checked and rechecked.  Torque is good on all sides of
the breaker all the way to the battery bussing.

The only thing that I can think of is that during a surge on the AC side
its sucking enough current out of the charge controller caps to trip this
breaker occasionally.

Has anyone experienced this?  The only way I can see to fix it is to go
with a larger breaker ampacity, but maybe there is something better.  Does
anyone no how quickly the max current setting in the Outback can respond,
would dropping this help?

Thanks

-- 

Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] battery buss bar stock

2017-12-01 Thread Matthew Sirum
Greetings Jay,

I second the Storm Power Components (formerly Storm Copper)
recommendation   https://stormpowercomponents.com/

In addition to Storm you may also like to take a look at:

Farmers Copper http://www.farmerscopper.com/

Watteredge Products (now renamed as parent company Southwire)
http://www.watteredge.com/

Electric Equipment & Engineering Company (EEE) http://eeeusa.com/
EEE manufactures interconnects, bus bars, terminal plates, and etc for
some of the industrial battery system companies.  If you are looking
for cell interconnects for stringing 2-volt cells together they may be
a resource.

You may remember the custom DC bus system pictures I shared with you a
while back; I sourced the large DC battery system circuit breakers
from EEE and the C11000 copper bar stock and insulators came from
Storm.  Here is the last contact I had with EEE: Mike Morroni, phone:
303.296.1476 ext: 21, email: mike.morr...@eeeusa.com

As Tump mentioned, McMaster-Carr as well as Grainger and MSC also sell
copper stock.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


  --  Original Message Below  --

[RE-wrenches] battery buss bar stock

jay jay.peltz at gmail.com
Fri Dec 1 08:06:00 PST 2017

HI All,

I’m wondering if anyone has a good source for battery buss bar stock.
Either pre made ones or stock I can use to make myself.

It would be for larger Rolls GEL 2v in this case but other battery
sizes/types as well.

thanks

jay

peltz power
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Outdoor rated insulation covering for Solar Water Heating Systems

2017-11-04 Thread Matthew Sirum
Greetings Chris,

I used to do a lot of solar thermal installations and rehabs on older
systems.  I tried not to use elastomeric type pipe insulation (such as
Armacell/Armaflex and Rubatex Insul-Tube 180) outdoors, because of all
the unsightly and deterioration issues I observed on air conditioning
and refrigeration installations.  When I did need to use the
elastomeric type pipe insulation outdoors I coated it with the
specific manufacturer supplied UV resistant paint product.  I
pre-painted the lengths to be used before installation and then
touched up with more paint as needed once installed.

My preferred outdoor exposed-run pipe insulation is extruded rigid
urethane jacketed with either UV rated PVC or aluminum
jackets/sheathes.  The extruded rigid urethane insulation was
available in straight lengths as well as 45° and 90° elbows.  All was
available split in halves for ease of installation.  The PVC
jackets/sheathes were also available in 45° and 90° elbows.  I would
secure the insulation in place with a ripstop tape strip product and
then install the jacket/sheathe over it.  Thermocouple/sensor wires
and tray cable for PV direct powered pumps could be hidden between the
insulation and outer jacket/sheath.  I have tried a number of methods
for securing and closing the PVC jackets/sheathes; glue/cement,
stainless steel tacks, aluminum tacks, aluminum rivets.  The push in
tacks with serrated shank and white flat heads were decent for a
while, but I had the best long term success with rivets.  They took a
little longer to install and need to be cut or drilled out for service
access to the pipe, but held well for the long term and helped create
the best aesthetic installation.  I have also used the PVC and
aluminum jackets/sheathes over elastomeric insulation products with
the same method for closing and securing the jacket/sheath.

The majority of my solar thermal installs were in the Northeast U.S.
and the PVC jacket/sheath over extruded rigid urethane pipe insulation
installs are expected to last and look decent for 10-20 years before
requiring rework.  Having rehabbed systems which were 20-30+ years old
I know the PVC jacket/sheath and insulation degrade and breakdown with
heat and Sunlight over time.  I expect the functional and
aesthetically acceptable lifetime of the jacket/sheath and insulation
is likely much less in regions with exposure to higher prolonged
ambient temperatures and greater Sun/UV intensity over time.  I
believe different jacket/sheath mil thickness is available, with the
thicker mil products being more suitable for harsher environments.


Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com



--   Original Message Below   --

[RE-wrenches] Outdoor rated insulation covering for Solar Water Heating Systems

cwarfel cwarfel at entech-engineering.com
Fri Nov 3 08:06:58 PDT 2017

I would like to add a covering to the Armorflex insulation we installed
on a solar water heating system. Can anyone recommend a manufacturer's
product that a reasonably competent person can install?  Right now we
have wrapped the insulation in UV resistant tape, but it doesn't look
all that great.  Thank you, Chris

-- 
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Defective UFOs

2017-10-11 Thread Matthew Sirum
Greetings Andrew,

Besides failing during installation, what are the indicators of having
a bad item in hand?  Is/are there any visible characteristic(s) or
item coding indicating which UFOs are defective?  Do you know about
how many defective units made their way onto the distribution market?

Thank you for sharing this issue with us.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below  --

[RE-wrenches] Defective UFOs
Solar Energy Solutions Tue, 10 Oct 2017 18:21:07 -0700

Dear Wrenches,We were at a project yesterday and were quite perplexed as to why
we were breaking so many Iron Ridge UFOs.. 15 on a 10kW.  Had it not been for
us attending an IR workshop today it would still be a mystery and the problem
would continue to plague us for the next several installation.
Below is the IronRidge reply.
A couple batches of black ufo made it out in the market place due to a machine
calibration issue that has been identified and fixed. The customers are to send
an email tosupp...@ironridge.com If they come across any bad product and will
be taken care of with new product and a return address to send the bad ones
back to the factory. Smiles,

Andrew KoyaanisqatsiPresidentSolar Energy Solutions, Inc.
The BRIGHT CHOICE
Since 1987, helping you and your Portland neighbors
move towards an environmentally sustainable future.503-238-4502
www.SolarEnergyOregon.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] OutBack Power MATE3 to MATE3S Upgrade

2017-09-20 Thread Matthew Sirum
Greetings All,

I'm preparing to replace an existing OutBack Power MATE3 System
Display/Controller with the new MATE3S.  The system is a grid tied 5
stack of Radian GS8048A Inverter/Chargers.  I am interested to know if
any of you may have done this and if you encountered any issues or
have any insights to pass along.  This system does have a generator
and uses the Advanced Generator Start (AGS) function to control
generator start/stop and battery charging while the generator is
running.  I believe this is the only Display/Controller based function
the system is using, so it will likely need to be programed and setup
in the new MATE3S.  I am hopeful that all other programing is stored
in the Radians and will not need to be reprogramed/entered to the new
MATE3S.  The system is connected to OpticsRE (OutBack Power's system
monitoring website/service).  I assume we may need to do some
programing from the new MATE3S and/or from the system's OpticsRE site
to enable communication since the new MATE3S may have a different IP
address, MAC Address, and etc than the MATE3 we are removing.

We are hopeful the new MATE3S will allow the system to function better
with its OpticsRE site and not need to be reset every couple months.

Please let me know if you have any experience or thoughts to offer.

Have any of you installed and setup the new MATE3S?  Any Issues,
insights, or comparisons to the MATE3 to report?

Thank you!

Best regards,

----MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] 1,000 volt-rated connectors

2017-09-12 Thread Matthew Sirum
Greetings Marco,

It sounds like you are likely looking for a 1000V version of something
like the Polaris insulated tap connectors and insulated multi cable
connector blocks or the Burndy insulated multiple tap connectors
(Unitap)...  I believe these all are only 600V rated.  There are still
some gaps in the product offerings available for the 600V to 2kV PV
balance of system needs.  There are some products we may be tempted to
use which may have a 1000V rating, but are only for 1000V use in sign
and fixture circuits.  Other items with sufficient voltage ratings may
be designed for use in the generation and transmission segment of
medium voltage work.  Some of this gear will be made for isolation,
not insulated and likely far from appropriate and workable for our
needs.

Depending on the types, gauges, and quantities of conductors you are
working with as well as the required ampacity and intended
installation location some of these products/links may be helpful:

Erico/Pentair makes some useful options including 1000V AC/DC UL din
rail mountable power distribution blocks.  Some of these are being
specifically marketed to the solar PV industry.
https://www.erico.com/catalog/literature/P1215C-WWEN.pdf

Mersen/Ferraz Shawmut offers some 1000V AC/DC power distribution
blocks, some rated for fine strand conductors.
http://ep-us.mersen.com/products/catalog/line/mpdb-series-ul-1953-open-style-power-distribution-blocks/

Marathon Special Products has a variety of offerings including 1500V
AC/DC power distribution blocks and markets to the PV industry.
http://www.marathonsp.com/index.php

TE Connectivity/Raychem (Tyco) 1000V GTAP products
http://www.te.com/usa-en/product-566427-000.html#guest-click

Some Easy-Splice products are 1000V rated. (These look like the TE
Connectivity GTAP products.)
http://www.nsiindustries.com/catalog/nsiproducts/insulating-splicing-id-products-and-panel-channel/easy-splice™-gel-splicing-kits

SolarBOS (http://www.solarbos.com/), Bentek (http://www.bentek.com/),
and Shoals Technologies Group (http://shoals.com/) all offer 1000V PV
wire connectors, "Y", "T", & "X" harnesses, and inline fuse holders.

Depending on the specific circumstances of the project you may be able
to use 1000V or 1500V PV lead branch connectors to make up the
connection detail you are working on.  Many of the PV lead connector
manufacturers offer these to mate up with the commonly used
connectors.

I hope some of this information may be helpful.  Let us know if you
find 1000V rated insulated multi port tap/splice type connectors or
anything else interesting and useful.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below  --

[RE-wrenches] 1,000 volt-rated connectors
Marco Mangelsdorf marco at pvthawaii.com
Mon Sep 11 16:58:03 PDT 2017


Aloha.

Does anyone know of any 1,000 volt-rated insulated connectors?

I checked the Polaris line but they're only rated to 600V.

Mahalo,

marco

provision_highres_solar_logo2 with C-26351

Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
 <http://www.provisiontechnologies.com> www.provision-solar.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] ] Dusty off -grid conditions

2017-09-05 Thread Matthew Sirum
Greetings William,

Regarding a sealed charge controller; may the OutBack FLEXmax Extreme
Charge Controller be an option?...  Its spec sheet identifies it as
being IP54 rated (dust protected) and there is an optional fan kit to
help it run cooler.  Just a thought, if they are still being produced
and available.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


-- Original Message Below --

[RE-wrenches] ] Dusty off -grid conditions
William Miller william at millersolar.com
Tue Sep 5 08:35:33 PDT 2017

Friends:

Thanks for the input on this topic.  A few thoughts:

1. I could change the design from a vented 8k Radian to 4 sealed FX
inverters.  However the Outback charge controllers will still be vented.
This makes me think the best plan is an actively vented cabinet.  This
cabinet has a fan with filtration:
http://millersolar.com/MillerSolar/Portfolio/Commercial/Cal_Trans/Pase_2/Phase_B_Caboinet_2.jpg

2. We have tried in vain to keep rodents out of a building or even a room.
Our best successes are in critter-proofing as small a space as possible.
Attached is a photo of an Outback installation with screen wire to keep out
wood rats that destroyed the previous installation by urinating on the SW
circuit boards.

William

Lic 773985
millersolar.com
805-438-5600
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Over voltage error message

2017-07-18 Thread Matthew Sirum
Greetings Drake,

If this hasn't already been done; "Acknowledge" the Event (Fault) via
the MATE3 in the Event History and the indicator light should switch
"off", as long as the Event/Fault is not actively occurring.
Hopefully it is as simple as this to calm the client's concern.

Best of luck.  Please let us know if you are able to learn any details
about the cause of the issue.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below  --

[RE-wrenches] Over voltage error message

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Tue Jul 18 16:12:20 PDT 2017

Hi Matt,

There is no additional data monitoring. I haven't been able to make it
out there yet to check the parameters.

The main reason the client is so worried is that she got a  message
that I'm not familiar with that said something to the effect that the
problem  had to be solved before the event light could be turned off.
I did not see this personally, and haven't encountered this message
before. I will need to see if the manual can shed any light on how to
turn off the light. .

Thanks,

Drake

- Original Message -

From: "RE-wrenches" 
To:"re-wrenches" 
Sent:Tue, 18 Jul 2017 05:56:15 -0400
Subject:[RE-wrenches] Over voltage error message

 Greetings Drake,

 This is interesting. I have Grid-tied OutBack Radian GS8048A with
 MidNite Classic 200 systems in the field, but don't believe I've seen
 this issue before. (But certainly have seen many strange MATE3 &
 OpticsRE issues)

 Here are a few questions that come to mind:

 What is the Radian "Sell" voltage set at? Has this setting been
 checked since this issue was reported? Have the Classic 200 settings
 been checked to make sure they are set where they should be?

 Does the system have any data monitoring on the charge controller
 and/or battery system independent of the Radian inverter? If so, any
 information similar to the Events logged on the MATE3?

 Does this system have the OutBack FLEXnet DC installed? There could
 be more data to review to try and get a sense of what the issue may
 be. (shunt data, historical VDC data, any battery charging via grid?)

 If the system has more than one Classic 200 are they connected and
set
 up in "Follow Me" mode?

 Any chance the charge controller or inverter/charger tried to
initiate
 an equalization charge?

 Does the system have any DC loads or generation sources (other than
 the charge controller and inverter/charger) connected directly to the
 battery system or anywhere on the DC bus?

 Best regards,

 MATT

 Matthew Sirum
 P.O. Box 1227
 Greenfield, MA 01302-1227 USA
 phone: +1.413.773.0611
 email: MatthewSirum at gmail.com

 -- Original Message Below --

 [RE-wrenches] Over voltage error message
 Drake drake.chamberlin at redwoodalliance.org
 Mon Jul 17 05:36:46 PDT 2017

 Hello Wrenches,

 My client reported seeing an overvoltage error message on her Mate 3
 on a Radian system. The Radian is selling to the grid and is being
 fed by a Midnite Classic 200. It has shown two spikes so far, the
 last one going to 67 volts and lasting 1 second. The batteries are
 Concorde AGM, 305 AH.

 Does this momentary spike seem like a problem or a warning of
problems to come?

 Thanks,

 Drake
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Over voltage error message

2017-07-18 Thread Matthew Sirum
Greetings Drake,

This is interesting.  I have Grid-tied OutBack Radian GS8048A with
MidNite Classic 200 systems in the field, but don't believe I've seen
this issue before.  (But certainly have seen many strange MATE3 &
OpticsRE issues)

Here are a few questions that come to mind:

What is the Radian "Sell" voltage set at?  Has this setting been
checked since this issue was reported?  Have the Classic 200 settings
been checked to make sure they are set where they should be?

Does the system have any data monitoring on the charge controller
and/or battery system independent of the Radian inverter?  If so, any
information similar to the Events logged on the MATE3?

Does this system have the OutBack FLEXnet DC installed?  There could
be more data to review to try and get a sense of what the issue may
be.  (shunt data, historical VDC data, any battery charging via grid?)

If the system has more than one Classic 200 are they connected and set
up in "Follow Me" mode?

Any chance the charge controller or inverter/charger tried to initiate
an equalization charge?

Does the system have any DC loads or generation sources (other than
the charge controller and inverter/charger) connected directly to the
battery system or anywhere on the DC bus?

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below  --

[RE-wrenches] Over voltage error message
Drake drake.chamberlin at redwoodalliance.org
Mon Jul 17 05:36:46 PDT 2017

Hello Wrenches,

My client reported seeing an overvoltage error message on her Mate 3
on a Radian system. The Radian is selling to the grid and is being
fed by a Midnite Classic 200. It has shown two spikes so far, the
last one going to 67 volts and lasting 1 second. The batteries are
Concorde AGM, 305 AH.

Does this momentary spike seem like a problem or a warning of problems to come?

Thanks,

Drake
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Generator choice for Sunny Island

2017-06-16 Thread Matthew Sirum
Greetings August,

Great thoughts and comments from Brian!  I would also suggest speaking
with the generator manufacturers' tech/engineering folks regarding the
120VAC configuration and to confirm 2-wire start set up once you have
a brand and model or two in mind.  Generator parts and service
availability in the region of the project may also drive brand
selection.  If you need to maximize the inverter's battery charging
capabilities (depending on battery system charging requirements) you
may end up needing to look at generators in the 7.5 kW to 8.0 kW
capacity range to allow for headroom in generator output loading.

Also; I am curious how you arrived at an AC coupled design for this
project.  I do not know any of the details or specific projects goals
you are working with, but I would potentially consider a DC coupled
system design...  DC/DC charge controller(s) would keep the battery
system charged (and any DC loads operable) even if the Sunny Island
and/or Sunny Boy(s) have a failure or is taken offline.  If most of
the AC loads are 120VAC I would consider keeping the inverter AC
output circuit 120VAC and install a dedicated transformer solely for
the 240VAC load  Or perhaps consider a 120/240VAC inverter model.
Depending on the overall situation a DC coupled system could be more
resilient.  The dedicated transformer for the 240VAC load could also
potentially help make the system more robust.  Also; I have spoken
with a number of folks who have told me they wish the Sunny Island had
more/better features for generator integration.  I'd like to hear more
from those who have plenty of experience designing and installing
systems with Sunny Islands and generators to learn what the current
thoughts and issues are.

I hope some of these thoughts may be helpful.

Best regards,

----MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


  Original Message Below 

[RE-wrenches] Generator choice for Sunny Island
August Goers august at luminalt.com
Thu Jun 15 09:02:41 PDT 2017

Hi Wrenches, especially those of you who work on off-grid projects,

We have an upcoming off-grid project where we will be powering a storage
container with electronics in it. The loads are mostly 120 volt but there
is a 240 volt heat pump that might occasionally run. We’re AC coupling the
Sunny Island with a Sunny Boy PV inverter. So, we’ll be installing a
Outback PSX-240 autoformer to bump the Sunny Island’s output from 120 to
240 volt.

We need to select a generator for backup. We need a two-wire electric start
(in order to be controlled by the Sunny Island) and preferably a generator
that is okay just running 120 volt loads since the Sunny Islands input is
only 120 volt. Something in the 3 kVA -7 kVA range should be fine.

Does anyone have experience or ideas about what kind of two-wire start
generator we might select?

Thanks,

August

Luminalt
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Third Radian ---> Class T Fuse With/Without Fuse Holder

2017-04-26 Thread Matthew Sirum
Greetings William,

Good point.  This is something I always take into consideration.  I
have used Class T Fuses in many situations with and without their fuse
holders.  In the case of the installation shown in my custom DC Bus
System pictures the wire/cable type and wire management avoid putting
too much physical stress on the Class T Fuses.  The #4 AWG conductors
are supported from above and apply very little stress on the fuses
they connect to.  The 4/0 AWG cabling is Cobra X-Flex (fine stand,
very flexible) and each of these conductors is secured a few inches
from where they connect to their fuses.  Care was taken in making up
these connection and they were all carefully adjusted and inspected to
ensure they would not stress the fuses.  I feel really good about how
it all came together.  The same care and attention will be needed
whenever these connections are serviced and the fasteners are
torqued/tightened.  When well planned and carefully assembled I do not
have concern there will be any issues related to not using the fuse
holder.  I also think about this another way as well...  Using the
Class T Fuse Holder adds another 2 connections to the circuit.  I try
to remind myself that more connections can equal more chance of
issues...  Although, if a manufacturer of a Class T Fuse states the
fuse holder must be used with their fuse there could be an NEC
violation by not using it.

One thing to note about the use of these fuses in this installation is
that they are supplemental over current protection (OCP).  Each
positive (ungrounded) conductor connecting to this DC Bus System has a
means of primary over current protection and disconnect on its
opposite end.  The battery systems, the charge controllers, and the
inverter/chargers all have circuit breaker disconnects on their
respective positive circuit conductors connecting to this DC Bus
System.  I have seen other folks build without having the needed
appropriate means of disconnect and OCP; although most folk are
probably more likely to include the primary OCP, but not consider the
supplemental OCP.  The supplemental OCP (Class T Fuses) provide
protection in the event of a fault or short in a circuit between the
Bus System and the other OCP at the other equipment.

Like many folks I have installed and worked on battery systems where
we install a Class T Fuse directly onto the positive terminal of the
battery bank or via some form of busbar or connector etc.  In these
cases not only do we need to take care not to stress the fuse, but the
fuse itself (and added busbar/connector etc) can act like a lever and
along with the mating cable lug(s) create too much stress on the
battery terminal...  Potentially damaging the terminal, the inner
battery connection to the terminal, and/or the seal between the
battery case and the terminal.  Carelessly tightening the
hardware/fasteners to assemble these items to the battery terminal is
a common way of inflicting damage on the battery as well.  I know I
have been involved in some service situations where there was more
stress on the Class T Fuse than I would like to see, but as best I
know there have not been any fuse failures because of it.

Thanks for bringing up this question!

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


 Original Message Below 

[RE-wrenches] Third Radian

William Miller william at millersolar.com
Tue Apr 25 23:03:03 PDT 2017

Matt:

I have a question for you:  I have often considered mounting Class T fuses
directly to a bus bar as you have done.  Are you ever worried about physical
strain on the fuse itself without a fuse holder?

Thanks again for all of your input.

William Miller

Lic 773985
millersolar.com
805-438-5600
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Polaris gone bad?

2017-04-11 Thread Matthew Sirum
Greetings All,

I too have tried all of the methods discussed so far in this thread.
With regard to multi port tap block type connectors, I have used the
Burndy Unitap product the most and have had good results.  I like that
they come with anti-oxide compound already in them and that the set
screws have hex/allen socket heads.  I may have had one or two of the
set screws strip or come misaligned from the factory over the years,
but have not found any major failures or arcing/burning.  Overall I've
had a good experience with the Burndy Unitap.

I have used the Ideal/Buchanan Splice Cap Crimp Connectors in some
applications, but have not used them outdoors...  I thought at one
time I came across some literature for the nylon Splice Cap Insulators
used on these which indicated there may be an environmental
temperature rating related issue when considering them for PV install
work.  I'm looking for this spec now, but have not found it.  All I
find now regarding temperature is "Temperature Rating: 105° C
(221°F)".  Seems like using the Splice Cap Crimp Connectors with an
appropriately rated quality heat shrink tubing product instead of the
Splice Cap Insulator may also be a potential solution.

I have used electrical rubber insulating tape, electrical silicone
insulating tape, and electrical insulating mastic tapes to insulate
and seal many various uninsulated connectors and etc too...  Always
with an application of  quality electrical tape over them as well.

USE-2/PV Wire with MC Connector connected to THWN-2 with MC Connector
has worked well for me as well in a wire transition/junction box.  The
MC insulator boot sized for PV Wire may have been somewhat oversized
for the THWN-2 conductor.  It's always good to review the specs for
the connector product and the specs for the wire to ensure all will be
appropriately mated up in the field.

I have used butt splice crimp connectors with integrated insulating
shrink tubing such as the Molex Perma-Seal products.  When used with
the appropriate full cycle ratcheting crimping tool these make a very
nice connection.  Some of the butt splice connectors work well for
transitioning from fine stranded wire to standard stranded THWN-2
conductors such as in the case of working with some of the micro
inverter trunk cable systems etc.  I always apply a second layer of
quality heat shrink tubing over the connector and its integrated
shrink.  The use of these products and heat shrink tubing means
bringing a cord and heat gun or torch to the array install area to
seal the heat shrink.  I prefer a heat gun for better control and a
lesser likelihood of burning the connector, shrink, wire, or something
or someone.  Either way I can understand many folks may not want to be
dealing with heat shrink products or having their install crews doing
so, especially up on a pitched roof installation.

Some of the Molex Perma-Seal butt splice products have a connector
barrel made of tined copper and a 600V rating.  Molex identifies some
of these products for use in "consumer" and "industrial" applications.
Some have CSA and UL "certification" on their respective spec sheets,
but I have not researched the certifications by number to say for
certain if use in a PV system wire transition box or junction box is a
truly acceptable and compliant use for the product.

Have any of you researched or worked with these Perma-Seal or similar
products?  I am interested to learn more and fully understand what
their acceptable application are.  Other companies such as 3M and
Power Phase sell similar products, but often what I find are products
intended for the automotive and marine industry.  I absolutely do not
want to be using or suggesting automotive and marine products for use
in professional, code compliant residential and commercial electrical
work.

Link to Molex Perma-Seal Products:
http://www.molex.com/molex/products/family?key=heat_sealable_terminals&channel=products&chanName=family&pageTitle=Introduction&parentKey=solderless_terminals&utm_source=ds&utm_medium=lit&utm_campaign=ipd

Also; glad to see drain/weep holes mentioned too!  Even if water is
not getting in to the box/enclosure/body we want to make sure any
condensation that develops can drain out.  About 10-12 years ago I had
a project with a large outdoor wireway/trough/gutter which would hold
small amounts of water even though a number of drain/weep holes were
drilled in its bottom side...  A seasoned and friendly Electrical
Inspector showed me how to make "wicks" out of single strands of
wire...  Coiled the single strand flat to lay on the bottom inside of
the trough with a straight section of the single strand going through
a weep hole to draw any water out.  I put a few of these in the
trough...  It looked a bit funky but it seemed to help.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.41

[RE-wrenches] Using same PV array for water pump, battery charging

2017-02-16 Thread Matthew Sirum
Greetings Larry,

I can think of a number of ways this may be done.  Not knowing the
details of the existing system configuration, if the switching needs
to be manual or automatic, what (if any) cycle of the NEC is in effect
at the project location, and if the PV array is ground mounted or
mounted on a building I do not know what design thoughts/suggestions
may be most appropriate and helpful.

If I understand the general goal and manual operation is acceptable
this could be as simple as installing an appropriately rated
double-throw switch (on-off-on switch) or transfer switch into the PV
output circuit between the array and the charge controller.  The PV
output circuit would be the feed to the switch and the charge
controller and pump would be the selectable loads.  Some details to
consider for this would include; if the double-throw switch or
transfer switch is load break rated or not, where the array over
current protection device(s) (OCPDs) and disconnect(s) are located,
where the charge controller input disconnect is located, and if and
how this configuration impacts any GFDI (Ground-Fault Detector
Interrupter) and AFCI (Arc-Fault Circuit Interrupter) protection
provided by the charge controller or other components in the system.
Proper labeling and signage for sequence, operation, safety, and
applicable NEC requirements will need to be considered as well.

I installed some double-throw switches manufactured by Eaton not too
long ago.  I believe they were 250VDC rated.  If you are interested in
looking into double-throw switches you may want to call the folks at
the Eaton Flex Center (1-888-329-9272) to get assistance with
specifying an appropriate double-throw switch.  Circuit breaker type
bypass assemblies and transfer switches are available and may be less
expensive than a double-throw switch, but these may not be readily
available with the DC rating this project requires and most I have
seen are only rated for indoor installation.  I am not sure if you
will be looking for a solution which will be installed indoors or
outdoors, but this is a detail to consider.

If you are looking for an automatic or semiautomatic solution I
believe the Magnum PT-100 charge controller does have an auxiliary
relay which can be triggered based on battery system voltage.  I have
not worked with the PT-100, but it is my understanding it needs to be
networked with a Magnum remote control to use the auxiliary relay
based on battery voltage.  This auxiliary relay could signal an
automatic transfer switch system or contactors to perform the needed
switching.

Also; I believe Morningstar has a DC transfer switch for use with
their 600VDC TriStar charge controller...  I do not know if they may
offer this as a separate item, but you may want to reach out for them
to inquire as well.  Learning the details about the switch they use in
their product and sourcing it as a separate item could provide you
with a solution you custom build to suit the project.

I hope you may find some of these thoughts helpful.  Please let us
know how you proceed and how it all works out.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--  Original Message Below --

[RE-wrenches] Using same PV array for water pump, battery charging

Starlight Solar Power Systems larry at starlightsolar.com
Thu Feb 16 14:24:44 PST 2017

Hello Wrenches,

A customer has 3250 Watt PV array @ 139Voc. The PV controller is
Magnum PT100. He wants to install a Grundfos SQFlex pump and be able
to switch the DC from the PV controller to run the pump directly. He
would like to switch midday after the battery (48V) is at a high SoC.

I’m looking for a switching arrangement to do this without arcing
since it will be used a few times each week. Any have a
recommendation?

Thank you,

Larry Crutcher
Starlight Solar Power Systems
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Power Quality Test

2017-01-03 Thread Matthew Sirum
Greetings Corey,

I do not have experience with the specific devices referenced in the
contract language you have cited, but can offer the names of a couple
other manufacturers who make power quality (PQ) analyzers and
loggers/recorders.

Here are three:
Power Monitors, Inc. (PMI), Virginia, USA
Radian Research, Inc., Indiana & Mississippi, USA
AEMC Instruments (Chauvin Arnoux), New Hampshire, USA

These companies produce gear which many utilities and line contractor
firms use in their PQ testing programs.  I have worked with some of
the gear from PMI and Radian Research, but probably not their latest
models.

If it is unlikely that your company would have an ongoing need for a
PQ logger it may consider hiring a local/regional PQ test
company/contractor (or appropriately equipped engineering firm) to
fulfill this requirement in the contract you have mentioned.  They
could potentially perform the testing, review the logged data, and
prepare a report for less than what a new PQ analyzer logger unit and
software would cost your company.  If your company does purchase new
gear some manufacturers or their regional representative may come out
and train/assist/demo the unit with your technician/team.

SEI Professional Services may be of help on this issue too.  They have
members on the RE-wrenches list as well.

On larger or complex projects I like the practice of PQ testing and
data logging at a project site before the system installation as well
as during commissioning activities.  The pre-install data can be
helpful in seeing potential PQ issues before work begins.  The
pre-install data can also be used later for comparative purposes if
there is any concern or dispute regarding PQ issues recognized post
install.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


 Original Message Below 

[RE-wrenches] Power Quality Test

Corey Shalanski corey at joule-energy.com
Tue Jan 3 11:09:50 PST 2017

The contract for one of our upcoming utility-scale projects includes a
requirement for recording/analyzing power quality: "Submit a report that
includes AC voltage, current, impedance, frequency, the maximum and minimum
of ranges continuously during the 72 hour period with intentional and daily
start up and shut down trials. Devices such as a Candura Power Pro or Power
Site can be used to analyze power."

Does anyone have experience with either of these devices and can comment on
their use? Or else can you recommend a similar device that will fulfill
these requirements?

Corey Shalanski
Joule Energy
New Orleans, LA
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Generac EcoGen 6

2016-12-31 Thread Matthew Sirum
Greetings Dave,

Which Generac controller is on this 6kW EcoGen?  Some of the Generac
controller instructions I have seen state that once the controller
control panel fuse is removed and/or the connections to the starting
battery are disconnected the exercise programming will need to be
re-entered.  If you have not already done so, you may want to check
the controller programing and specifically the exercise feature
programming.  I'm wondering if this may be causing the issue you are
observing.  Date and time may need to be set for the controller as
well.  I believe the EcoGen models may come from the factory ready for
2-wire start, so hopefully the start feature programing does not need
to be re-entered as well.  The appropriate Generac controller
instructions for the controller model you are working with should
provide the password and lead you through the necessary steps.

I also like the suggestions of checking the 2-wire start circuit
conductors.  I would remove these 2 wires from their connections at
the generator and see if the issue persists.

Best of luck.  Let us know how this issue works out.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


 Original Message Bellow 

[RE-wrenches] Generac EcoGen 6

Dave Palumbo palumbo131m at gmail.com
Fri Dec 30 06:14:48 PST 2016

Wrenches,

I have a 6 kW Generac EcoGen (1,300 hrs on it) with a new problem.

. After swapping in a new battery the other day  the generator now
starts and runs when its start switch is positioned to Auto.

. The OutBack inverter w Mate2 is not calling for an auto start.

. Even when the EcoGen is disconnected from the off grid house it
still starts and runs every time the start switch is set to Auto.

How do I clear this problem and get this gen back to normal?

Thanks and Happy New Year,

Dave

David Palumbo

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655

802-371-8678 cell

802-888-4917 home
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Retaining Clips

2016-11-29 Thread Matthew Sirum
Greetings Adam,

Here are a couple/few thoughts which may be helpful.  Not knowing the
specific circumstance(s) or goal(s) these may or may not be
appropriate or useful.

Use the 4-8 circuit load center you mentioned with the appropriate
circuit breaker and retainer clip and do not twist out the unneeded
spaces in the dead front or fill them with the appropriate blanks.
Clearly label the load center accordingly and be sure to mark if no
other circuits should be installed in it etc.

Main Circuit Breaker Disconnect / Circuit Breaker Disconnect:  Usually
not too difficult to source 60A, 100A, or 125A 120/240VAC double pole
main CB disconnects.  Install the appropriate 60A CB you need.
Confirm the design of specific item you are looking at or ordering
meets the retained/fastened in place circuit breaker requirement.
Some designed for the HVACR trade for example may not have the ability
to retain/fasten the circuit breaker in place.  Also; be sure item has
the appropriate isolated or bonded Neutral terminal to meet your
needs, as well as the equipment grounding lug/terminal.  Disconnect
may be designed for use as service equipment and these may be separate
part numbers and/or disconnect may be field convertible.

If acceptable for the project, use a suitable fused disconnect switch
with the required 60A fuses.  Wire line and load sides of switch
accordingly for the circumstances at hand and to meet code and be sure
to label clearly identifying purpose and the hazards of the switch as
installed.  Comment above regarding Neutral and EGC terminals apply
here as well.  May need to order separately.

An appropriately rated panel mount double pole circuit breaker
installed in a small panel mount type enclosure may be an option as
well to meet your requirement.  This may be a good option especially
if you need a solution which will take up as little space as possible.
MidNite Solar may have an appropriate enclosure/box.  The appropriate
double pole circuit breaker may need to be researched with
CBI-electric North America or Safe Circuits, Inc. in Pennsylvania.

I have dealt with this issue in various circumstances before, such as
needing to install backfed circuit breakers.  I do not recall the
specific brands and part numbers used, but the major US market
manufacturers should have a solution to meet your needs.  Hopefully
your local electrical supply company can come up with a solution for
you, but if still in need I suggest calling Schneider/Square D,
Eaton/Cutler-Hammer, or Siemens etc.  Third party retainers may also
be available which could work with a load center and circuit breaker
you may already have, but be aware your local AHJ may not allow a
retainer which is not listed/recognized for use with the load center
and circuit breaker.

Also; we need to remember that in the case of backfeeding a circuit
breaker we must make certain it is rated for backfeed, not marked
"Line" and "Load".

I hope that I understood your question correctly and that some of
these thoughts may be helpful.

Best regards,

----MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


-- Original Message Below --

[RE-wrenches] Retaining Clips

AE Solar autonomousenergies at gmail.com
Tue Nov 29 19:14:45 PST 2016

Wrenchers,

I’m trying to find a 60A 2 Pole Breaker Box that has a compatible
retaining clip. The QO retaining clip (PK2MBCP) seems to only be
compatible with their 4-8 circuit load centers. What are my options?
Thanks!

Thanks

Adam
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SMA Arc-Fault

2016-11-14 Thread Matthew Sirum
Greetings Dave,

Have you considered possibly installing a hybrid type transient
voltage surge suppressor (TVSS), to include filters to remove high
frequency EMI/RFI?  Or possible a straight line filter device?  If
this nuisance arc fault issue is still occurring and it may be related
to an AC issue you may be able to get some technical help and advice
from an engineer at one of the TVSS manufacturers such as Total
Protection Solutions, Richmond, VA 800.647.1911 or Surge Suppression
Incorporated, Destin, FL 888.987.8877.  I would also recommend
reaching out for an application engineer in the SPD division at Eaton.
Eaton Technical Resource Center 800.809.2772.  SSI also has a very
experienced field troubleshooting technician they send all around the
country to help contractors with difficult electrical issues... Of
course that would probably cost $1000-$2000 per day.

I avoid using piercing taps and connectors.  I prefer to use service
entrance tap boxes, insulated multi port connectors, or line side
rated power distribution blocks.  I cannot help but wonder if there
may be an actual arc event occurring at one or more of the piercing
taps which is somehow picked up by the DC AFCI.  In commissioning this
system it would be a good idea to use a non-contact IR thermometer
and/or thermal imaging camera/scope to check the piercing taps for
excessive heating while the conductors are energized and carrying peak
currents.

I hope you are successful in resolving this issue soon.  I will
continue to follow the thread.  Hopefully we can all learn something
from this.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] LG MonoX NeON LG305N1C-B3 Modules Needed

2016-10-19 Thread Matthew Sirum
Greetings All,

I am in search of LG MonoX NeON LG305N1C-B3 PV modules.  I need a few
extra modules for a current project in the US.  Please email me off
list if you know of where I may find some in stock.  Thank you.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Back-up generator/inverter shut-down relay

2016-09-08 Thread Matthew Sirum
Greetings Benn,

There may be another option which would avoid extra controls/devices.
The point of interconnection of the inverter output circuits could be
a supply side connection; the inverter outputs could be combined and
interconnected between the service point/utility meter and the utility
supply connection to the automatic transfer switch.  This may be an
installation option to consider if allowed in the jurisdiction where
your project is located and if practical given the existing electrical
work and nature of the site/building.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


Date: Thu, 8 Sep 2016 11:00:09 -0600
From: Benn Kilburn 
To: RE-wrenches 
Subject: [RE-wrenches] Back-up generator/inverter shut-down relay

Wrenches,
We are installing 2 SolarEdge SE7600A-US inverters in a grid-tied
system that has a 15kw back-up generator on an auto transfer switch.

The generator is located in a shed about 300' or more away and the
feeders to the house are underground. Inverters are located in the
house basement mechanial room along with the house electrical
panelboard.

We are looking for relay options to shut down the inverters when there
is a power interruption, before the generator kicks in.  This could be
a manual reset.

What are some options you have seen/used for something like this?

Thanks,

*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 ? 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Troubleshooting Stumper - Homerun Interference in Conduit/Inverter Turning Off/On Rapidly

2016-09-07 Thread Matthew Sirum
Greetings Matt,

I like the troubleshooting thoughts others have given.  If all else
leaves you with the issue persisting I would also consider checking
for current on the grounding system and on bonded conductive
materials/items on the property.  It may be helpful to see if there is
any current on the Equipment Grounding Conductors, Grounding Electrode
Conductor(s), metallic conduits & raceways, PV mounting system, and
etc.  If the inverter in this system has an AC Neutral connection
intended only for instrumentation and L1 & L2 voltage reference it
would be interesting to measure the actual current on it.  It is good
you have a similar system installed next door, you may need to compare
test measurements and readings.  If you run out of tests and
troubleshooting ideas it may be helpful to open (turn off) all the
circuits in the house/on the service and see how the PV system
performs while being the only item connected to the service.

The "smart" modules/optimizers may be making system troubleshooting
more challenging.  I wonder what Trina & Tigo has/can offer(ed) to
assist with troubleshooting?... and if there is an approved/safe
megger (insulation resistance) test for these modules?  This is an
interesting case.  I'll be continuing to follow the thread.  I hope we
can all learn something from this.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com

Date: Wed, 7 Sep 2016 17:45:32 -0400
From: "Matt Partymiller" 
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Troubleshooting Stumper - Homerun Interference
in Conduit/Inverter Turning Off/On Rapidly

Wrenches,

One of our systems is having an issue I have not encountered before
where the inverter switches between nighttime mode and interconnection
every few seconds.  I am hoping for some technical wisdom from the
community.

We have an array of 20 TrinaSmart modules in two strings of 10.  The
array is connected to a Solectria 3.8 kW inverter.  The conduit run is
simple, all four homerun wires (#10 PVwire) in 1" EMT down to the
proximity of the Solectria inverter where the conduit switches to 1"
LFMC before entering the inverter.  The run is about 20', straight
down the side of the wall before hitting the inverter.  A 600V
jacketed communications wire was also in the conduit but has since
been removed and run separately.

Our inverter is starting up, running for a few seconds, giving a low
voltage error, briefly showing nighttime mode, then going into startup
mode again.  Solectria was gracious enough to send us a new inverter
but we have the exact same issue.  They tell us their error codes
(266, 274) indicate 0 volts.  The transition between low voltage error
and startup is almost instant.  Basically we have 20 seconds of start
up, 5 seconds of run, 5 seconds of error then repeat.  This is not a
grid problem, the identical system next door works fine.

In the process of troubleshooting, our technician pulled all four homerun
wires out of our conduit and meggered them.  They all tested fine so he
connected to the inverter.  The inverter worked fine.  The technician
verified grounding of the array and conduit, pulled new homeruns back
through the conduit, and reconnected to the inverter.  He had the same
error as before.

He connected each string separately to the inverter by removing the
string fuses.  Either string will operate fine independently.  With
string one in conduit and either homerun of string two in conduit (but
not both) the inverter operates fine.  With string two in conduit but
string one outside of conduit, the inverter does not operate.

I was certain the error had something to do with homerun roof wiring so I
went out with the technician and removed and checked pretty much every
module.  Everything appears fine, all connections solid, all homeruns
have been remade at least once at this point.  Now I am stumped and
lack the technical knowledge to diagnose the problem.  I would be
extremely grateful if an esteemed wrench can provide technical
support/advice.

Thanks,

Matt

Matthew Partymiller
Solar Energy Solutions LLC
(877) 312-7456
m...@solar-energy-solutions.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid tie with dump load?

2016-09-07 Thread Matthew Sirum
Greetings Kris,

I am curious as to what the utility metering/accounting mechanism is
in the territory serving your client; Net Energy Metering, Sell All,
or ???  And what value is given/paid for excess kWh generation
exported to the grid?  What is the clients goal(s) in considering a
grid-tie PV system?  As utility interconnection rules, grid standards,
and tariffs evolve we may all be dealing with these questions
differently than we had before.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Test procedure for Concorde batteries

2016-09-01 Thread Matthew Sirum
st 4 as a single series
string; so the system owner has some backup capacity while they
consider total battery system replacement.

I hope these thoughts may be helpful.

Best regards,

MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


Date: Thu, 1 Sep 2016 12:51:46 +
From: Gary Bassett 
To: "RE-wrenches (re-wrenches@lists.re-wrenches.org)"

Subject: [RE-wrenches] Test procedure for Concorde batteries
Message-ID:
<4c9022358cd54ad38ff888fd1101fad5@Hosted-MS-3.elcomp.local>
Content-Type: text/plain; charset="us-ascii"

We have a grid tied battery backup system that uses 8 Sun Xtender
PVX-2120L batteries, about 9 years old. The grid has been going out
frequently - about 4 times in the past 3 weeks. When the grid goes
out, the battery voltage gets too low and shuts the system down pretty
quickly. One of the times, this happened within 4 hours. We want to
test the capacity of the batteries and we have a testing procedure
from Concorde that seems like it would take a lot of time. Is there a
quick way to test the battery capacity?

Gary

Date: Thu, 1 Sep 2016 09:31:58 -0400
From: John Blittersdorf 
To: RE-wrenches 
Subject: Re: [RE-wrenches] Test procedure for Concorde batteries

Gary,
   I have just two methods I use to test all batteries.  I do a voltage
check of each battery under load with solar input shut off.  You will
quickly find a battery with a bad cell or two. It is best to do this
test when the batteries are already somewhat discharged to see clearer
results.  When under charge, and even floating or with a light load, a
battery with bad cells can look OK in the voltage check.  Bad cells
can show up as down about 1.5  to 2 volts for each bad cell from
normal.  I have also seen batteries that not only dropped in voltage
but actually changed polarity. Had a 6volt L16 read  -2 VDC.
Thatdropped the string by 8 volts!!!   Typically bad cell problems
will show up after some discharge and if a single string, the string
voltage suddenly drops down.  In parallel strings the numbers get
really random but other batteries in same string will rise high to
compensate for the low battery. I have seen a 6 volt go to +9 volts
and was boiling violently.  (hence why multiple strings are not the
best design). If the above checks are OK, batteries still appearing to
be weak have reached the twilight of their lives and a plan is needed
to retire them.    9 years seems about right from my experience to
see serious decline in output.

   The other quick test for parallel string batteries is to use the DC
clamp meter to check each string as being roughly equal in current
under load or under full charge rate.  This will find bad cells,
different aged batteries, and /or bad connections.  When you lose a
string, that will definitely reduce the coasting time.

I don't check specific gravity for two reasons.  It is time consuming
and moving acid around is not good in my book.  I have found individual
batteries with low specific gravity readings that went on to work OK for
many years,  If the batteries pass my voltage and current checks, I call
them good to go.

John Blittersdorf
Solar Guru
Rob Stubbins Solar (division of Rob Stubbins Electrical and General
Contractors)
280 Quality Lane
Rutland, VT 05701

802-775-1484 ext 512

Date: Thu, 1 Sep 2016 09:43:53 -0400
From: Tump 
To: RE-wrenches 
Subject: Re: [RE-wrenches] Test procedure for Concorde batteries

Gary I would suggest that the battery manufacture?s recommended method
is followed. Yeah it IS time consuming BUT?
Checking w/ a clamp on during a charge or discharge depending on the
# of strings &/or the way the strings are configured will be
misleading.
Your customer is paying by the hour and a the choice is theirs replace
OR pay your tech to watch the voltage/current over the manu?s
discharge time.
These batteries can be run thru an equalization cycle, following the
guide lines recommended by Concord, then do your load test. Full
charge to discharge over time IS the only way.
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org