Re: [RE-wrenches] Finding ground faults

2012-05-24 Thread William Miller

Mike:

Is there such a tool as a DC clamp-on that can reliably measure 10 mA?  My 
experience is any clamp meter is unreliable below 5A.


William


At 10:09 PM 5/23/2012, Mike Sullivan wrote:

Hi Bob,

Sorry if I am duplicating any of the replies you've already received 
regarding the possible ground fault. I think the best way to determine 
whether GFDI is tripping on 1 A ground current or 80 A circuit current is 
to use a sensitive DC clamp-on to check the current on your system ground 
under normal operation. If it is more than about 10 mA when things are 
dry, you probably do have a ground fault issue to resolve. Assuming that's 
true, I recommend that you buy, borrow or rent a megohm tester (like those 
by Megger) to check out your circuit wiring resistance. Once you fully 
isolate your strings at the combiner box, you can quickly zero in on where 
the fault lies -- just divide and conquer. You may need to wet down the 
array and wiring to make the fault more detectable. Often, the fault will 
be in wiring that was damaged when pulled from a splice or combiner box 
into conduit, esp. if there's no bushing on the conduit terminal adapter.


A word of warning -- if you have more than one ground fault, some parts of 
your equipment grounding system will be carrying current, which may be 
sizable. Use precautions when disconnecting any wiring or grounds. A 
clamp-on is really useful here...


Hope that helps!

Cheers,

Mike Sullivan



Wrenches:
?
Sorry to bring up this situation again, but I could not find a previous 
discussion thread that talked about step-by-step procedures for tracking 
down ground faults (I believe it was John Berdner who provided the bulk of 
the writing in that regard and it related to high voltage strings?not that 
75-85 volts per string is all that low).

?
We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon 
Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner 
with breakers.? The cables from the array are routed to two different 
Wiley 4-string pass-through boxes (located under the two center strings) 
and then off of the roof and into the PV combiner.

?
Up until this week the system has seen several weeks of awesome power 
production.? Yesterday, the rains came and the GFDI breaker tripped.? 
Every time it rains, the little green breaker on the GFDI trips off. ?That 
tells me that the ground fault is occurring in a place where at least one 
of the conductors on one of the strings (possibly more) is getting wet and 
conducting current to ground.

?
It would seem to me that the most likely place for moisture to cause a 
ground fault to occur in this system would be in the pass-through boxes.? 
This would mean removing the central modules to access the pass-through boxes.

?
Any of you who have mounted the Silicon Energy modules know that the 
cables are contained in trays along the side of the modules until they are 
routed through conduit to the pass-through boxes.? So, if there is current 
going to ground from any of these cables, it could even be occurring in 
any of the 9 trays along side of the modules.? I do not like the idea of 
tracking down a ground fault in one of these trays as they are all 
interconnected.

?
How best (and safely) to track down where the ground fault is occurring?? 
Any advice as to the best and safest way to track down the ground fault(s) 
would be greatly appreciated.

?
Bob Clark
SolarWind Energy Systems, LLC


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5018 - Release Date: 05/23/12 
18:41:00


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-24 Thread James Jarvis

Yes. Look for 4-20mA loop clamp on meters. Fluke 77x series is an example:

http://www.fluke.com/Fluke/usen/Clamp-Meters/Fluke-771-Milliamp-Process-Clamp-Meter.htm?PID=69415

0 to 100mA with 1% accuracy worst case over the whole range.

-James Jarvis
APRS World, LLC

On 05/24/2012 12:49 AM, William Miller wrote:

Mike:

Is there such a tool as a DC clamp-on that can reliably measure 10 mA?
My experience is any clamp meter is unreliable below 5A.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Dave Click

Here's the Paul Mync / John Berdner article from SolarPro 2.5:
http://solarprofessional.com/article/?file=SP2_5_pg60_Mync

-David Brearley... er... Click

On 2012/5/22 22:36, Bob Clark wrote:

Wrenches:

Sorry to bring up this situation again, but I could not find a previous
discussion thread that talked about step-by-step procedures for tracking
down ground faults (I believe it was John Berdner who provided the bulk
of the writing in that regard and it related to high voltage strings—not
that 75-85 volts per string is all that low).

We have an Outback FLEXpower Two system with 8, 3-module strings
(Silicon Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar
MNPV12 combiner with breakers. The cables from the array are routed to
two different Wiley 4-string pass-through boxes (located under the two
center strings) and then off of the roof and into the PV combiner.

Up until this week the system has seen several weeks of awesome power
production. Yesterday, the rains came and the GFDI breaker tripped.
Every time it rains, the little green breaker on the GFDI trips off.
That tells me that the ground fault is occurring in a place where at
least one of the conductors on one of the strings (possibly more) is
getting wet and conducting current to ground.

It would seem to me that the most likely place for moisture to cause a
ground fault to occur in this system would be in the pass-through boxes.
This would mean removing the central modules to access the pass-through
boxes.

Any of you who have mounted the Silicon Energy modules know that the
cables are contained in trays along the side of the modules until they
are routed through conduit to the pass-through boxes. So, if there is
current going to ground from any of these cables, it could even be
occurring in any of the 9 trays along side of the modules. I do not like
the idea of tracking down a ground fault in one of these trays as they
are all interconnected.

How best (and safely) to track down where the ground fault is occurring?
Any advice as to the best and safest way to track down the ground
fault(s) would be greatly appreciated.

*Bob Clark*

*/SolarWind Energy Systems, LLC/*



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Kent Osterberg

Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts that 
do not have an over-current trip mechanism. IMHO, the fact that they can 
trip on over-current and unnecessarily interrupt the dc system bond is a 
serious design flaw.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com


On 5/23/2012 9:27 AM, Steve Higgins wrote:

Bob,
Be careful with that GFDI... It's most likely wired on the output of 
the controllers, on the battery side.
This can trip if a ground fault is occurring, or if you are exceeding 
80 amps of current.   With 8, 3 module strings, an edge of cloud event 
you could have the 80amp portion of that breaker tripping rather than 
the GFDI.

Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223


*From:* re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Bob 
Clark

*Sent:* Tuesday, May 22, 2012 7:37 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* [RE-wrenches] Finding ground faults

Wrenches:

Sorry to bring up this situation again, but I could not find a 
previous discussion thread that talked about step-by-step procedures 
for tracking down ground faults (I believe it was John Berdner who 
provided the bulk of the writing in that regard and it related to high 
voltage strings---not that 75-85 volts per string is all that low).


We have an Outback FLEXpower Two system with 8, 3-module strings 
(Silicon Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar 
MNPV12 combiner with breakers.  The cables from the array are routed 
to two different Wiley 4-string pass-through boxes (located under the 
two center strings) and then off of the roof and into the PV combiner.


Up until this week the system has seen several weeks of awesome power 
production.  Yesterday, the rains came and the GFDI breaker tripped.  
Every time it rains, the little green breaker on the GFDI trips off. 
 That tells me that the ground fault is occurring in a place where at 
least one of the conductors on one of the strings (possibly more) is 
getting wet and conducting current to ground.


It would seem to me that the most likely place for moisture to cause a 
ground fault to occur in this system would be in the pass-through 
boxes.  This would mean removing the central modules to access the 
pass-through boxes.


Any of you who have mounted the Silicon Energy modules know that the 
cables are contained in trays along the side of the modules until they 
are routed through conduit to the pass-through boxes.  So, if there is 
current going to ground from any of these cables, it could even be 
occurring in any of the 9 trays along side of the modules.  I do not 
like the idea of tracking down a ground fault in one of these trays as 
they are all interconnected.


How best (and safely) to track down where the ground fault is 
occurring?  Any advice as to the best and safest way to track down the 
ground fault(s) would be greatly appreciated.


*Bob Clark*

*/SolarWind Energy Systems, LLC/*



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread William Miller

Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:

Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts that do 
not have an over-current trip mechanism. IMHO, the fact that they can trip 
on over-current and unnecessarily interrupt the dc system bond is a 
serious design flaw.


Kent Osterberg
Blue Mountain Solar, Inc.
http://www.bluemountainsolar.comwww.bluemountainsolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Steve Higgins

From what I understand, future controllers from Outback Power will incorporate 
the Ground Fault detection into the controller.


Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Wednesday, May 23, 2012 11:22 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Finding ground faults

Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:
Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts that do not 
have an over-current trip mechanism. IMHO, the fact that they can trip on 
over-current and unnecessarily interrupt the dc system bond is a serious design 
flaw.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.comhttp://www.bluemountainsolar.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Darryl Thayer
Bob I had a tough find one time, when it rained I would have GF when it would 
dry out no GF 
I turned off main DC disconnect, I turned off each circuit breakers for the 
strings, I opened the grounded conductor of the strings, I connected my Megger 
at 500 volts I think It might have been maybe 1000 volts, after the fault 
cleared, the megger found one string that was bad and I located the problem in 
a J box 
 


 From: Steve Higgins shigg...@outbackpower.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Wednesday, May 23, 2012 11:27 AM
Subject: Re: [RE-wrenches] Finding ground faults
  

 
Bob,  
  
Be careful with that GFDI... It's most likely wired on the output of the 
controllers, on the battery side.   
  
This can trip if a ground fault is occurring, or if you are exceeding 80 amps 
of current.   With 8, 3 module strings, an edge of cloud event you could have 
the 80amp portion of that breaker tripping rather than the GFDI.  
  
Steve Higgins 
Sales Application Engineering Mgr 
Direct 360-618-4313 
Outback Power Technologies  
5917 195th Street NE Arlington, Washington 98223 
   




 From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob Clark
Sent: Tuesday, May 22, 2012 7:37 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Finding ground faults

  
Wrenches: 
  
Sorry to bring up this situation again, but I could not find a previous 
discussion thread that talked about step-by-step procedures for tracking down 
ground faults (I believe it was John Berdner who provided the bulk of the 
writing in that regard and it related to high voltage strings—not that 75-85 
volts per string is all that low). 
  
We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon 
Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner with 
breakers.  The cables from the array are routed to two different Wiley 4-string 
pass-through boxes (located under the two center strings) and then off of the 
roof and into the PV combiner. 
  
Up until this week the system has seen several weeks of awesome power 
production.  Yesterday, the rains came and the GFDI breaker tripped.  Every 
time it rains, the little green breaker on the GFDI trips off.  That tells me 
that the ground fault is occurring in a place where at least one of the 
conductors on one of the strings (possibly more) is getting wet and conducting 
current to ground. 
  
It would seem to me that the most likely place for moisture to cause a ground 
fault to occur in this system would be in the pass-through boxes.  This would 
mean removing the central modules to access the pass-through boxes. 
  
Any of you who have mounted the Silicon Energy modules know that the cables are 
contained in trays along the side of the modules until they are routed through 
conduit to the pass-through boxes.  So, if there is current going to ground 
from any of these cables, it could even be occurring in any of the 9 trays 
along side of the modules.  I do not like the idea of tracking down a ground 
fault in one of these trays as they are all interconnected. 
  
How best (and safely) to track down where the ground fault is occurring?  Any 
advice as to the best and safest way to track down the ground fault(s) would be 
greatly appreciated. 
  
Bob Clark 
SolarWind Energy Systems, LLC   
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Darryl Thayer
I sure do not like the way the X brand installed their charge controller, Also 
the code says that all strings must open if one string is faulted.  your 
breaker does this up to 4 strings.  
DT 
 


 From: Steve Higgins shigg...@outbackpower.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org 
Sent: Wednesday, May 23, 2012 2:18 PM
Subject: Re: [RE-wrenches] Finding ground faults
  

 
  
From what I understand, future controllers from Outback Power will incorporate 
the Ground Fault detection into the controller.  
  
  
Steve Higgins 
Sales Application Engineering Mgr 
Direct 360-618-4313 
Outback Power Technologies  
5917 195th Street NE Arlington, Washington 98223 
   




 From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Wednesday, May 23, 2012 11:22 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Finding ground faults

 
Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:

Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts that do not 
have an over-current trip mechanism. IMHO, the fact that they can trip on 
over-current and unnecessarily interrupt the dc system bond is a serious 
design flaw.


Kent Osterberg
Blue Mountain Solar, Inc. www.bluemountainsolar.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread b...@midnitesolar.com

On 5/23/2012 4:44 PM, Darryl Thayer wrote:
I sure do not like the way the X brand installed their charge 
controller, Also the code says that all strings must open if one 
string is faulted.  your breaker does this up to 4 strings.

DT




I think that this is the pertinent part of the code regarding this...

In part...

31.1 Inverters or charge controllers with direct photovoltaic inputs 
from a grounded photovoltaic array or


arrays shall be provided with a ground-fault detector/interrupter 
(GFDI). The GFDI shall be capable of


detecting a ground fault, providing an indication of the fault, 
interrupting the flow of fault current, and either


isolating the faulted array section or disabling the inverter to cease 
the export of power.




This may very well change in the 2014 NEC from what I understand.

boB




*From:* Steve Higgins shigg...@outbackpower.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Wednesday, May 23, 2012 2:18 PM
*Subject:* Re: [RE-wrenches] Finding ground faults

From what I understand, future controllers from Outback Power will 
incorporate the Ground Fault detection into the controller.

Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223

*From:* re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*William Miller

*Sent:* Wednesday, May 23, 2012 11:22 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Finding ground faults

Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:

Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts 
that do not have an over-current trip mechanism. IMHO, the fact that 
they can trip on over-current and unnecessarily interrupt the dc 
system bond is a serious design flaw.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com  http://www.bluemountainsolar.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread b...@midnitesolar.com




Ooops !!  Sorry about that one !!That was from 1741...

Still applicable of course but NOT   NEC.

That was applicable from 2007 though.

boB




On 5/23/2012 6:34 PM, b...@midnitesolar.com wrote:

On 5/23/2012 4:44 PM, Darryl Thayer wrote:
I sure do not like the way the X brand installed their charge 
controller, Also the code says that all strings must open if one 
string is faulted.  your breaker does this up to 4 strings.

DT




I think that this is the pertinent part of the code regarding this...

In part...

31.1 Inverters or charge controllers with direct photovoltaic inputs 
from a grounded photovoltaic array or


arrays shall be provided with a ground-fault detector/interrupter 
(GFDI). The GFDI shall be capable of


detecting a ground fault, providing an indication of the fault, 
interrupting the flow of fault current, and either


isolating the faulted array section or disabling the inverter to cease 
the export of power.




This may very well change in the 2014 NEC from what I understand.

boB




*From:* Steve Higgins shigg...@outbackpower.com
*To:* RE-wrenches re-wrenches@lists.re-wrenches.org
*Sent:* Wednesday, May 23, 2012 2:18 PM
*Subject:* Re: [RE-wrenches] Finding ground faults

From what I understand, future controllers from Outback Power will 
incorporate the Ground Fault detection into the controller.

Steve Higgins
Sales Application Engineering Mgr
Direct 360-618-4313
Outback Power Technologies
5917 195th Street NE Arlington, Washington 98223

*From:* re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*William Miller

*Sent:* Wednesday, May 23, 2012 11:22 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Finding ground faults

Steve:

IMHO, a brilliant suggestion.

William Miller


At 11:19 AM 5/23/2012, you wrote:

Steve,

It would be appropriate for the GFDI to have 80-amp rated contacts 
that do not have an over-current trip mechanism. IMHO, the fact that 
they can trip on over-current and unnecessarily interrupt the dc 
system bond is a serious design flaw.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com  http://www.bluemountainsolar.com




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-23 Thread Mike Sullivan
Hi Bob,

Sorry if I am duplicating any of the replies you've already received regarding 
the possible ground fault. I think the best way to determine whether GFDI is 
tripping on 1 A ground current or 80 A circuit current is to use a sensitive DC 
clamp-on to check the current on your system ground under normal operation. If 
it is more than about 10 mA when things are dry, you probably do have a ground 
fault issue to resolve. Assuming that's true, I recommend that you buy, borrow 
or rent a megohm tester (like those by Megger) to check out your circuit wiring 
resistance. Once you fully isolate your strings at the combiner box, you can 
quickly zero in on where the fault lies -- just divide and conquer. You may 
need to wet down the array and wiring to make the fault more detectable. Often, 
the fault will be in wiring that was damaged when pulled from a splice or 
combiner box into conduit, esp. if there's no bushing on the conduit terminal 
adapter.

A word of warning -- if you have more than one ground fault, some parts of your 
equipment grounding system will be carrying current, which may be sizable. Use 
precautions when disconnecting any wiring or grounds. A clamp-on is really 
useful here...

Hope that helps!

Cheers,

Mike Sullivan



Wrenches: 
? 
Sorry to bring up this situation again, but I could not find a previous 
discussion thread that talked about step-by-step procedures for tracking down 
ground faults (I believe it was John Berdner who provided the bulk of the 
writing in that regard and it related to high voltage strings?not that 75-85 
volts per string is all that low). 
? 
We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon 
Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner with 
breakers.? The cables from the array are routed to two different Wiley 4-string 
pass-through boxes (located under the two center strings) and then off of the 
roof and into the PV combiner. 
? 
Up until this week the system has seen several weeks of awesome power 
production.? Yesterday, the rains came and the GFDI breaker tripped.? Every 
time it rains, the little green breaker on the GFDI trips off. ?That tells me 
that the ground fault is occurring in a place where at least one of the 
conductors on one of the strings (possibly more) is getting wet and conducting 
current to ground. 
? 
It would seem to me that the most likely place for moisture to cause a ground 
fault to occur in this system would be in the pass-through boxes.? This would 
mean removing the central modules to access the pass-through boxes. 
? 
Any of you who have mounted the Silicon Energy modules know that the cables are 
contained in trays along the side of the modules until they are routed through 
conduit to the pass-through boxes.? So, if there is current going to ground 
from any of these cables, it could even be occurring in any of the 9 trays 
along side of the modules.? I do not like the idea of tracking down a ground 
fault in one of these trays as they are all interconnected. 
? 
How best (and safely) to track down where the ground fault is occurring?? Any 
advice as to the best and safest way to track down the ground fault(s) would be 
greatly appreciated. 
? 
Bob Clark 
SolarWind Energy Systems, LLC   


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Finding ground faults

2012-05-22 Thread Bob Clark
Wrenches:

 

Sorry to bring up this situation again, but I could not find a previous
discussion thread that talked about step-by-step procedures for tracking
down ground faults (I believe it was John Berdner who provided the bulk of
the writing in that regard and it related to high voltage strings-not that
75-85 volts per string is all that low).

 

We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon
Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner
with breakers.  The cables from the array are routed to two different Wiley
4-string pass-through boxes (located under the two center strings) and then
off of the roof and into the PV combiner.

 

Up until this week the system has seen several weeks of awesome power
production.  Yesterday, the rains came and the GFDI breaker tripped.  Every
time it rains, the little green breaker on the GFDI trips off.  That tells
me that the ground fault is occurring in a place where at least one of the
conductors on one of the strings (possibly more) is getting wet and
conducting current to ground.

 

It would seem to me that the most likely place for moisture to cause a
ground fault to occur in this system would be in the pass-through boxes.
This would mean removing the central modules to access the pass-through
boxes.

 

Any of you who have mounted the Silicon Energy modules know that the cables
are contained in trays along the side of the modules until they are routed
through conduit to the pass-through boxes.  So, if there is current going to
ground from any of these cables, it could even be occurring in any of the 9
trays along side of the modules.  I do not like the idea of tracking down a
ground fault in one of these trays as they are all interconnected.

 

How best (and safely) to track down where the ground fault is occurring?
Any advice as to the best and safest way to track down the ground fault(s)
would be greatly appreciated.

 

Bob Clark

SolarWind Energy Systems, LLC

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-22 Thread Jesse Dahl
A problem I have seen during my work with SiE is getting the tray covers on 
without pinching a wire, if one of the black plastic bolt guards was left off 
or lost, it could pinch, but they seem water-tight.

I haven't run into any fault problems with SiE, but I see the possibilities. 


Keep me informed if you can. I have 3 11kW systems using SiE modules coming up 
this summer so I'm interested in where this is occurring. 


Jesse


Sent from my iPad!!!

On May 22, 2012, at 9:36 PM, Bob Clark bcl...@solar-wind.us wrote:

 Wrenches:
  
 Sorry to bring up this situation again, but I could not find a previous 
 discussion thread that talked about step-by-step procedures for tracking down 
 ground faults (I believe it was John Berdner who provided the bulk of the 
 writing in that regard and it related to high voltage strings—not that 75-85 
 volts per string is all that low).
  
 We have an Outback FLEXpower Two system with 8, 3-module strings (Silicon 
 Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar MNPV12 combiner 
 with breakers.  The cables from the array are routed to two different Wiley 
 4-string pass-through boxes (located under the two center strings) and then 
 off of the roof and into the PV combiner.
  
 Up until this week the system has seen several weeks of awesome power 
 production.  Yesterday, the rains came and the GFDI breaker tripped.  Every 
 time it rains, the little green breaker on the GFDI trips off.  That tells me 
 that the ground fault is occurring in a place where at least one of the 
 conductors on one of the strings (possibly more) is getting wet and 
 conducting current to ground.
  
 It would seem to me that the most likely place for moisture to cause a ground 
 fault to occur in this system would be in the pass-through boxes.  This would 
 mean removing the central modules to access the pass-through boxes.
  
 Any of you who have mounted the Silicon Energy modules know that the cables 
 are contained in trays along the side of the modules until they are routed 
 through conduit to the pass-through boxes.  So, if there is current going to 
 ground from any of these cables, it could even be occurring in any of the 9 
 trays along side of the modules.  I do not like the idea of tracking down a 
 ground fault in one of these trays as they are all interconnected.
  
 How best (and safely) to track down where the ground fault is occurring?  Any 
 advice as to the best and safest way to track down the ground fault(s) would 
 be greatly appreciated.
  
 Bob Clark
 SolarWind Energy Systems, LLC
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Finding ground faults

2012-05-22 Thread b...@midnitesolar.com


Hey Bob !  Hi from the west side of the hill.

This seems like an easy one...  Well, maybe...

One a dry day, take a garden hose and spray different parts of the 
system and see if you can

duplicate the problem and locate where the water makes it trip.

But you may have to wait a while for each spot sprayed to let it fault 
out before spraying

another spot.  That's  how I'd start out.

This also seems kind of weird in a way because of the current necessary 
for that breaker
to trip.  What ?  1/2 amp or 1.0 amp or so  That's not a real small 
amount for rain.
I bet something is rusty or corroded or something like that.  Please let 
us know what

you find !!

boB




On 5/22/2012 7:36 PM, Bob Clark wrote:


Wrenches:

Sorry to bring up this situation again, but I could not find a 
previous discussion thread that talked about step-by-step procedures 
for tracking down ground faults (I believe it was John Berdner who 
provided the bulk of the writing in that regard and it related to high 
voltage strings---not that 75-85 volts per string is all that low).


We have an Outback FLEXpower Two system with 8, 3-module strings 
(Silicon Energy 190W, 25.3Vmp, 7.5 Imp) combined in a Midnite Solar 
MNPV12 combiner with breakers.  The cables from the array are routed 
to two different Wiley 4-string pass-through boxes (located under the 
two center strings) and then off of the roof and into the PV combiner.


Up until this week the system has seen several weeks of awesome power 
production.  Yesterday, the rains came and the GFDI breaker tripped.  
Every time it rains, the little green breaker on the GFDI trips off. 
 That tells me that the ground fault is occurring in a place where at 
least one of the conductors on one of the strings (possibly more) is 
getting wet and conducting current to ground.


It would seem to me that the most likely place for moisture to cause a 
ground fault to occur in this system would be in the pass-through 
boxes.  This would mean removing the central modules to access the 
pass-through boxes.


Any of you who have mounted the Silicon Energy modules know that the 
cables are contained in trays along the side of the modules until they 
are routed through conduit to the pass-through boxes.  So, if there is 
current going to ground from any of these cables, it could even be 
occurring in any of the 9 trays along side of the modules.  I do not 
like the idea of tracking down a ground fault in one of these trays as 
they are all interconnected.


How best (and safely) to track down where the ground fault is 
occurring?  Any advice as to the best and safest way to track down the 
ground fault(s) would be greatly appreciated.


*Bob Clark*

*/SolarWind Energy Systems, LLC/*





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org