Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-21 Thread Dave Angelini Offgrid Solar
nect at all in 480.7(A)..quite confusing. 

Ray Walters
Remote Solar
303 505-8760
 On 10/19/20 7:06 PM, Jerry Shafer
wrote:  Wrenches Blue planet are fire and UL listed systems both on there
48 Volt and the LX flavors Jerry  
  On Mon, Oct 19, 2020, 5:51 PM Ray 
wrote:   

The notes in the NEC 2020 Handbook for article 706 clearly state
that 706 only covers ESS which is an assembly of components, and that the
total assembly must be listed under UL 9540.  

Further it states: "_ A
group of separate components that includes storage batteries, that is
provided with support systems (racks), charge controllers, and inverters,
and that does NOT have an overall listing as an ESS is a storage battery
system and as such is subject to the requirements of article 480"_ 

and
just in case someone says the notes don't matter, 706.5 says: "_Energy
Storage systems shall be listed"_. 

So, since I have never used an actual
listed ESS, I'm back to 480. Specifically, 480.7 (A) says we need a
disconnect for batteries over 60 vdc (48v should be exempt) and then
480.7(B) says houses need to have an outside disconnect for the batteries
labeled "Emergency Disconnect".  

So here's the real question: Does
480.7(A) exempt us from 480.7(B)?  
Ray Walters
Remote Solar
303 505-8760

On 3/9/19 8:08 PM, Brian Mehalic wrote:  Hi Glenn, I don't completely agree
with your interpretation of ESS systems and the application of Article 706.
Yes, an ESS _could_ provide 120/240 VAC (e.g. the Powerwall), but the
figures in Article 690 show three different configurations where the output
of the ESS is not AC, and where the ESS disconnect comes before any power
electronics (like a multimode inverter, as shown in the AC and DC coupled
systems) or loads (as shown in the stand-alone system). Are those ESS
connected to other systems which utilize stored energy to provide AC power?
Yes, but the key is "connected to other systems" - in many cases the ESS
only provides DC. In fact the definition of ESS clearly states this - it
_can_ have AC or DC output, and it _may_ include power electronics (but may
not).My understanding is that the 60 volt limit (which is
obviously problematic in a world where 48 VDC batteries and ESS are very
common) was inserted in order to exempt other devices that store energy
(such as UPS, or battery backup in fire alarms/exit signage/etc.) from the
706 requirements.   Cheers,   Brian Mehalic 
 NABCEP Certified Solar PV
Installation Professional(tm) R031508-59 National Electrical Code(R) CMP-4
Member (520) 204-6639
 Solar Energy International

http://www.solarenergy.org [7]  SEI Professional Services
http://www.seisolarpros.com [8] 
  On Sat, Mar 9, 2019 at
4:07 PM Glenn Burt  wrote: Hi Ray,

 This is a conversation I have had some
time ago with a number of my fellow inspectors and code experts. When the
2017 NEC came out, I agreed with Mike Holt and Bill Brooks' assessment that
the new article was poorly written and did not apply to most systems being
installed today. After much discussion through my Cadmus network of
authorities, it emerged that indeed 706 apples to the typical residential
systems.
 So Energy Storage Systems (ESS) are the point of article 706, and
I believe that the key point is that the SYSTEM is generating AC voltage of
120VAC or 240VAC, making the system fall under article 706.

 Batteries
themselves are minimally covered by NEC 480, NFPA 1, and the IFC as
applicable locally.
 So, the bottom line is that the new article does cover
the work we do when systems provide or interface with 120VAC or above
(making the system operation exceeding the 60V AC trigger).

 My initial
problem was believing that the article applied to a component (the battery
bank), and not the system (all components taken together as a
generator/storage system). It is an easy misunderstanding to make.

 Hope
this helps!

 -Glenn Burt

 -Original Message-
 From: RE-wrenches 
On Behalf Of Ray
 Sent: Saturday, March 09, 2019 12:41 PM
 To: RE-wrenches

 Cc: Bill Brooks ; Bill Brooks 
 Subject: [RE-wrenches] NEC for Batteries
< 60v ??

 Hi Everyone;

 I'm updating all my verbage on plansets, and I
just realized that the newly created article 706 covering Energy Storage
Systems is only for Over 60 VDC (706.1) Also article 480 for batteries only
requires disconnecting means over 60 VDC ?! (480.7). I'm not about to not
have a disconnect, so now that NEC pulled battery systems out of 690, where
do we go for guidance on normal battery systems: 12, 24, 48 VDC?

 Overall,
I welcome most of the changes in NEC 2017, like separating off grid systems
into articles 706, and 710, but it seems us off grid installers need some
more clarification.

 Thanks,

 --
 Ray Walters
 Remote Solar
 303
505-8760

 ___
 List sponsored
by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org
[14]

 Change listserver email a

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-20 Thread Kent Osterberg
ency Disconnect".

So here's the real question:   Does 480.7(A) exempt us from
480.7(B)?

Ray Walters
Remote Solar
303 505-8760

On 3/9/19 8:08 PM, Brian Mehalic wrote:

Hi Glenn, I don't completely agree with your interpretation of
ESS systems and the application of Article 706.  Yes, an ESS
/could/ provide 120/240 VAC (e.g. the Powerwall), but the
figures in Article 690 show three different configurations
where the output of the ESS is not AC, and where the ESS
disconnect comes before any power electronics (like a
multimode inverter, as shown in the AC and DC coupled systems)
or loads (as shown in the stand-alone system). Are those ESS
connected to other systems which utilize stored energy to
provide AC power? Yes, but the key is "connected to other
systems" - in many cases the ESS only provides DC.  In fact
the definition of ESS clearly states this - it /can/ have AC
or DC output, and it /may/ include power electronics (but may
not).
My understanding is that the 60 volt limit (which is obviously
problematic in a world where 48 VDC batteries and ESS are very
common) was inserted in order to exempt other devices that
store energy (such as UPS, or battery backup in fire
alarms/exit signage/etc.) from the 706 requirements.
Cheers,
Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com <http://www.seisolarpros.com>

On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt
mailto:glenn.b...@glbcc.com>> wrote:

Hi Ray,

This is a conversation I have had some time ago with a
number of my fellow inspectors and code experts. When the
2017 NEC came out, I agreed with Mike Holt and Bill
Brooks' assessment that the new article was poorly written
and did not apply to most systems being installed today.
After much discussion through my Cadmus network of
authorities, it emerged that indeed 706 apples to the
typical residential systems.
So Energy Storage Systems (ESS) are the point of article
706, and I believe that the key point is that the SYSTEM
is generating AC voltage of 120VAC or 240VAC, making the
system fall under article 706.

Batteries themselves are minimally covered by NEC 480,
NFPA 1, and the IFC as applicable locally.
So, the bottom line is that the new article does cover the
work we do when systems provide or interface with 120VAC
or above (making the system operation exceeding the 60V AC
trigger).

My initial problem was believing that the article applied
to a component (the battery bank), and not the system (all
components taken together as a generator/storage system).
It is an easy misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches
mailto:re-wrenches-boun...@lists.re-wrenches.org>> On
Behalf Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks
mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just
realized that the newly created article 706 covering
Energy Storage Systems is only for Over 60 VDC (706.1) 
Also article 480 for batteries only requires disconnecting
means over 60 VDC ?! (480.7).   I'm not about to not have
a disconnect, so now that NEC pulled battery systems out
of 690,  where do we go for guidance on normal battery
systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710,
but it seems us off grid installers need some more
clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

 

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-20 Thread Kent Osterberg
enches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks
mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just
realized that the newly created article 706 covering
Energy Storage Systems is only for Over 60 VDC (706.1) 
Also article 480 for batteries only requires
disconnecting means over 60 VDC ?! (480.7).   I'm not
about to not have a disconnect, so now that NEC pulled
battery systems out of 690,  where do we go for guidance
on normal battery systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710,
but it seems us off grid installers need some more
clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org
<http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org
<http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Ch

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-20 Thread Ray
of article 480"/

and just in case someone says the notes don't matter, 706.5
says: "/Energy Storage systems shall be listed"/.

So, since I have never used an actual listed ESS, I'm back to
480. Specifically, 480.7 (A) says we need a disconnect for
batteries over 60 vdc (48v should be exempt) and then 480.7(B)
says houses need to have an outside disconnect for the
batteries labeled "Emergency Disconnect".

So here's the real question:   Does 480.7(A) exempt us from
480.7(B)?

Ray Walters
Remote Solar
303 505-8760

On 3/9/19 8:08 PM, Brian Mehalic wrote:

Hi Glenn, I don't completely agree with your interpretation of
ESS systems and the application of Article 706.  Yes, an ESS
/could/ provide 120/240 VAC (e.g. the Powerwall), but the
figures in Article 690 show three different configurations
where the output of the ESS is not AC, and where the ESS
disconnect comes before any power electronics (like a
multimode inverter, as shown in the AC and DC coupled systems)
or loads (as shown in the stand-alone system). Are those ESS
connected to other systems which utilize stored energy to
provide AC power? Yes, but the key is "connected to other
systems" - in many cases the ESS only provides DC.  In fact
the definition of ESS clearly states this - it /can/ have AC
or DC output, and it /may/ include power electronics (but may
not).
My understanding is that the 60 volt limit (which is obviously
problematic in a world where 48 VDC batteries and ESS are very
common) was inserted in order to exempt other devices that
store energy (such as UPS, or battery backup in fire
alarms/exit signage/etc.) from the 706 requirements.
Cheers,
Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639
Solar Energy International
http://www.solarenergy.org
SEI Professional Services
http://www.seisolarpros.com <http://www.seisolarpros.com>

On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt
mailto:glenn.b...@glbcc.com>> wrote:

Hi Ray,

This is a conversation I have had some time ago with a
number of my fellow inspectors and code experts. When the
2017 NEC came out, I agreed with Mike Holt and Bill
Brooks' assessment that the new article was poorly written
and did not apply to most systems being installed today.
After much discussion through my Cadmus network of
authorities, it emerged that indeed 706 apples to the
typical residential systems.
So Energy Storage Systems (ESS) are the point of article
706, and I believe that the key point is that the SYSTEM
is generating AC voltage of 120VAC or 240VAC, making the
system fall under article 706.

Batteries themselves are minimally covered by NEC 480,
NFPA 1, and the IFC as applicable locally.
So, the bottom line is that the new article does cover the
work we do when systems provide or interface with 120VAC
or above (making the system operation exceeding the 60V AC
trigger).

My initial problem was believing that the article applied
to a component (the battery bank), and not the system (all
components taken together as a generator/storage system).
It is an easy misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches
mailto:re-wrenches-boun...@lists.re-wrenches.org>> On
Behalf Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks
mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just
realized that the newly created article 706 covering
Energy Storage Systems is only for Over 60 VDC (706.1) 
Also article 480 for batteries only requires disconnecting
means over 60 VDC ?! (480.7).   I'm not about to not have
a disconnect, so now that NEC pulled battery systems out
of 690,  where do we go for guidance on normal battery
systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710,
but it seems us off grid installers need some more
clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-20 Thread Dave Angelini Offgrid Solar
EP Certified Solar PV
Installation Professional(tm) R031508-59 National Electrical Code(R) CMP-4
Member (520) 204-6639
 Solar Energy International

http://www.solarenergy.org [4]  SEI Professional Services
http://www.seisolarpros.com [5] 
  On Sat, Mar 9, 2019 at
4:07 PM Glenn Burt  wrote: Hi Ray,

 This is a conversation I have had some
time ago with a number of my fellow inspectors and code experts. When the
2017 NEC came out, I agreed with Mike Holt and Bill Brooks' assessment that
the new article was poorly written and did not apply to most systems being
installed today. After much discussion through my Cadmus network of
authorities, it emerged that indeed 706 apples to the typical residential
systems.
 So Energy Storage Systems (ESS) are the point of article 706, and
I believe that the key point is that the SYSTEM is generating AC voltage of
120VAC or 240VAC, making the system fall under article 706.

 Batteries
themselves are minimally covered by NEC 480, NFPA 1, and the IFC as
applicable locally.
 So, the bottom line is that the new article does cover
the work we do when systems provide or interface with 120VAC or above
(making the system operation exceeding the 60V AC trigger).

 My initial
problem was believing that the article applied to a component (the battery
bank), and not the system (all components taken together as a
generator/storage system). It is an easy misunderstanding to make.

 Hope
this helps!

 -Glenn Burt

 -Original Message-
 From: RE-wrenches 
On Behalf Of Ray
 Sent: Saturday, March 09, 2019 12:41 PM
 To: RE-wrenches

 Cc: Bill Brooks ; Bill Brooks 
 Subject: [RE-wrenches] NEC for Batteries
< 60v ??

 Hi Everyone;

 I'm updating all my verbage on plansets, and I
just realized that the newly created article 706 covering Energy Storage
Systems is only for Over 60 VDC (706.1) Also article 480 for batteries only
requires disconnecting means over 60 VDC ?! (480.7). I'm not about to not
have a disconnect, so now that NEC pulled battery systems out of 690, where
do we go for guidance on normal battery systems: 12, 24, 48 VDC?

 Overall,
I welcome most of the changes in NEC 2017, like separating off grid systems
into articles 706, and 710, but it seems us off grid installers need some
more clarification.

 Thanks,

 --
 Ray Walters
 Remote Solar
 303
505-8760

 ___
 List sponsored
by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org
[11]

 Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [12]


List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[13]

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [14]


Check out or update participant bios:
 www.members.re-wrenches.org [15]


___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [16]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [17]


List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[18]

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm [19]


Check out or update participant bios:
 www.members.re-wrenches.org
[20]

___
List sponsored by
Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
[21]

Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[22]

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[23]

List rules & etiquette:
www.re-wrenches.org/etiquette.htm [24]

Check
out or update participant bios:
www.members.re-wrenches.org [25]

  
___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [26]

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [27]


There are two list archives for searching. When one doesn't work, try the
other:
 https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[28]
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[29]

 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm
[30]

 Check out or update participant bios:

http://www.members.re-wrenches.org
[31]

___
List sponsored by
Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
[32]

Change listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[33]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
[34]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.o

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-19 Thread Kent Osterberg
, I agreed with Mike Holt and Bill Brooks'
assessment that the new article was poorly written and did
not apply to most systems being installed today. After much
discussion through my Cadmus network of authorities, it
emerged that indeed 706 apples to the typical residential
systems.
So Energy Storage Systems (ESS) are the point of article
706, and I believe that the key point is that the SYSTEM is
generating AC voltage of 120VAC or 240VAC, making the system
fall under article 706.

Batteries themselves are minimally covered by NEC 480, NFPA
1, and the IFC as applicable locally.
So, the bottom line is that the new article does cover the
work we do when systems provide or interface with 120VAC or
above (making the system operation exceeding the 60V AC
trigger).

My initial problem was believing that the article applied to
a component (the battery bank), and not the system (all
components taken together as a generator/storage system). It
is an easy misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> On
Behalf Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks
mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just realized
that the newly created article 706 covering Energy Storage
Systems is only for Over 60 VDC (706.1)  Also article 480
for batteries only requires disconnecting means over 60 VDC
?! (480.7).   I'm not about to not have a disconnect, so now
that NEC pulled battery systems out of 690, where do we go
for guidance on normal battery systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710, but
it seems us off grid installers need some more clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http:/

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-19 Thread Ray
is an easy misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf
Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks
mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just realized
that the newly created article 706 covering Energy Storage
Systems is only for Over 60 VDC (706.1)  Also article 480 for
batteries only requires disconnecting means over 60 VDC ?!
(480.7).   I'm not about to not have a disconnect, so now
that NEC pulled battery systems out of 690,  where do we go
for guidance on normal battery systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710, but
it seems us off grid installers need some more clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There 

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-19 Thread Jerry Shafer
Wrenches
Blue planet are fire and UL listed systems both on there 48 Volt and the LX
flavors
Jerry

On Mon, Oct 19, 2020, 5:51 PM Ray  wrote:

> The notes in the NEC 2020 Handbook for article 706 clearly state that 706
> only covers ESS which is an assembly of components, and that the total
> assembly must be listed under UL 9540.
>
> Further it states: "* A group of separate components that includes
> storage batteries, that is provided with support systems (racks), charge
> controllers, and inverters, and that does NOT have an overall listing as an
> ESS is a storage battery system and as such is subject to the requirements
> of article 480"*
>
> and just in case someone says the notes don't matter, 706.5 says: "*Energy
> Storage systems shall be listed"*.
>
> So, since I have never used an actual listed ESS, I'm back to 480.
> Specifically, 480.7 (A) says we need a disconnect for batteries over 60 vdc
> (48v should be exempt) and then 480.7(B) says houses need to have an
> outside disconnect for the batteries labeled "Emergency Disconnect".
>
> So here's the real question:   Does 480.7(A) exempt us from 480.7(B)?
>
> Ray Walters
> Remote Solar
> 303 505-8760
>
> On 3/9/19 8:08 PM, Brian Mehalic wrote:
>
> Hi Glenn, I don't completely agree with your interpretation of ESS systems
> and the application of Article 706.  Yes, an ESS *could* provide 120/240
> VAC (e.g. the Powerwall), but the figures in Article 690 show three
> different configurations where the output of the ESS is not AC, and where
> the ESS disconnect comes before any power electronics (like a multimode
> inverter, as shown in the AC and DC coupled systems) or loads (as shown in
> the stand-alone system). Are those ESS connected to other systems which
> utilize stored energy to provide AC power? Yes, but the key is "connected
> to other systems" - in many cases the ESS only provides DC.  In fact the
> definition of ESS clearly states this - it *can* have AC or DC output,
> and it *may* include power electronics (but may not).
>
> My understanding is that the 60 volt limit (which is obviously problematic
> in a world where 48 VDC batteries and ESS are very common) was inserted in
> order to exempt other devices that store energy (such as UPS, or battery
> backup in fire alarms/exit signage/etc.) from the 706 requirements.
>
> Cheers,
>
> Brian Mehalic
> NABCEP Certified Solar PV Installation Professional™ R031508-59
> National Electrical Code® CMP-4 Member
> (520) 204-6639
>
> Solar Energy International
> http://www.solarenergy.org
>
> SEI Professional Services
> http://www.seisolarpros.com
>
>
>
> On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt  wrote:
>
>> Hi Ray,
>>
>> This is a conversation I have had some time ago with a number of my
>> fellow inspectors and code experts. When the 2017 NEC came out, I agreed
>> with Mike Holt and Bill Brooks' assessment that the new article was poorly
>> written and did not apply to most systems being installed today. After much
>> discussion through my Cadmus network of authorities, it emerged that indeed
>> 706 apples to the typical residential systems.
>> So Energy Storage Systems (ESS) are the point of article 706, and I
>> believe that the key point is that the SYSTEM is generating AC voltage of
>> 120VAC or 240VAC, making the system fall under article 706.
>>
>> Batteries themselves are minimally covered by NEC 480, NFPA 1, and the
>> IFC as applicable locally.
>> So, the bottom line is that the new article does cover the work we do
>> when systems provide or interface with 120VAC or above (making the system
>> operation exceeding the 60V AC trigger).
>>
>> My initial problem was believing that the article applied to a component
>> (the battery bank), and not the system (all components taken together as a
>> generator/storage system). It is an easy misunderstanding to make.
>>
>> Hope this helps!
>>
>> -Glenn Burt
>>
>> -Original Message-
>> From: RE-wrenches  On Behalf
>> Of Ray
>> Sent: Saturday, March 09, 2019 12:41 PM
>> To: RE-wrenches 
>> Cc: Bill Brooks ; Bill Brooks > >
>> Subject: [RE-wrenches] NEC for Batteries < 60v ??
>>
>> Hi Everyone;
>>
>> I'm updating all my verbage on plansets, and I just realized that the
>> newly created article 706 covering Energy Storage Systems is only for Over
>> 60 VDC (706.1)  Also article 480 for batteries only requires disconnecting
>> means over 60 VDC ?! (480.7).   I'm not about to not have a disconnect, so
>> now that NEC pulled battery systems out of 690,  where do we go for

Re: [RE-wrenches] NEC for Batteries < 60v ??

2020-10-19 Thread Ray
The notes in the NEC 2020 Handbook for article 706 clearly state that 
706 only covers ESS which is an assembly of components, and that the 
total assembly must be listed under UL 9540.


Further it states: "/A group of separate components that includes 
storage batteries, that is provided with support systems (racks), charge 
controllers, and inverters, and that does NOT have an overall listing as 
an ESS is a storage battery system and as such is subject to the 
requirements of article 480"/


and just in case someone says the notes don't matter, 706.5 says: 
"/Energy Storage systems shall be listed"/.


So, since I have never used an actual listed ESS, I'm back to 480. 
Specifically, 480.7 (A) says we need a disconnect for batteries over 60 
vdc (48v should be exempt) and then 480.7(B) says houses need to have an 
outside disconnect for the batteries labeled "Emergency Disconnect".


So here's the real question:   Does 480.7(A) exempt us from 480.7(B)?

Ray Walters
Remote Solar
303 505-8760

On 3/9/19 8:08 PM, Brian Mehalic wrote:
Hi Glenn, I don't completely agree with your interpretation of ESS 
systems and the application of Article 706.  Yes, an ESS /could/ 
provide 120/240 VAC (e.g. the Powerwall), but the figures in Article 
690 show three different configurations where the output of the ESS is 
not AC, and where the ESS disconnect comes before any power 
electronics (like a multimode inverter, as shown in the AC and DC 
coupled systems) or loads (as shown in the stand-alone system). Are 
those ESS connected to other systems which utilize stored energy to 
provide AC power? Yes, but the key is "connected to other systems" - 
in many cases the ESS only provides DC.  In fact the definition of ESS 
clearly states this - it /can/ have AC or DC output, and it /may/ 
include power electronics (but may not).


My understanding is that the 60 volt limit (which is obviously 
problematic in a world where 48 VDC batteries and ESS are very common) 
was inserted in order to exempt other devices that store energy (such 
as UPS, or battery backup in fire alarms/exit signage/etc.) from the 
706 requirements.


Cheers,

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com <http://www.seisolarpros.com>



On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt <mailto:glenn.b...@glbcc.com>> wrote:


Hi Ray,

This is a conversation I have had some time ago with a number of
my fellow inspectors and code experts. When the 2017 NEC came out,
I agreed with Mike Holt and Bill Brooks' assessment that the new
article was poorly written and did not apply to most systems being
installed today. After much discussion through my Cadmus network
of authorities, it emerged that indeed 706 apples to the typical
residential systems.
So Energy Storage Systems (ESS) are the point of article 706, and
I believe that the key point is that the SYSTEM is generating AC
voltage of 120VAC or 240VAC, making the system fall under article 706.

Batteries themselves are minimally covered by NEC 480, NFPA 1, and
the IFC as applicable locally.
So, the bottom line is that the new article does cover the work we
do when systems provide or interface with 120VAC or above (making
the system operation exceeding the 60V AC trigger).

My initial problem was believing that the article applied to a
component (the battery bank), and not the system (all components
taken together as a generator/storage system). It is an easy
misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Bill Brooks mailto:bi...@energy808.com>>; Bill Brooks mailto:billbroo...@yahoo.com>>
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just realized that
the newly created article 706 covering Energy Storage Systems is
only for Over 60 VDC (706.1)  Also article 480 for batteries only
requires disconnecting means over 60 VDC ?! (480.7).   I'm not
about to not have a disconnect, so now that NEC pulled battery
systems out of 690,  where do we go for guidance on normal battery
systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like
separating off grid systems into articles 706, and 710, but it
seems us off grid installers need some more clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List 

Re: [RE-wrenches] NEC for Batteries < 60v ??

2019-03-09 Thread Brian Mehalic
Hi Glenn, I don't completely agree with your interpretation of ESS systems
and the application of Article 706.  Yes, an ESS *could* provide 120/240
VAC (e.g. the Powerwall), but the figures in Article 690 show three
different configurations where the output of the ESS is not AC, and where
the ESS disconnect comes before any power electronics (like a multimode
inverter, as shown in the AC and DC coupled systems) or loads (as shown in
the stand-alone system). Are those ESS connected to other systems which
utilize stored energy to provide AC power? Yes, but the key is "connected
to other systems" - in many cases the ESS only provides DC.  In fact the
definition of ESS clearly states this - it *can* have AC or DC output, and
it *may* include power electronics (but may not).

My understanding is that the 60 volt limit (which is obviously problematic
in a world where 48 VDC batteries and ESS are very common) was inserted in
order to exempt other devices that store energy (such as UPS, or battery
backup in fire alarms/exit signage/etc.) from the 706 requirements.

Cheers,

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Sat, Mar 9, 2019 at 4:07 PM Glenn Burt  wrote:

> Hi Ray,
>
> This is a conversation I have had some time ago with a number of my fellow
> inspectors and code experts. When the 2017 NEC came out, I agreed with Mike
> Holt and Bill Brooks' assessment that the new article was poorly written
> and did not apply to most systems being installed today. After much
> discussion through my Cadmus network of authorities, it emerged that indeed
> 706 apples to the typical residential systems.
> So Energy Storage Systems (ESS) are the point of article 706, and I
> believe that the key point is that the SYSTEM is generating AC voltage of
> 120VAC or 240VAC, making the system fall under article 706.
>
> Batteries themselves are minimally covered by NEC 480, NFPA 1, and the IFC
> as applicable locally.
> So, the bottom line is that the new article does cover the work we do when
> systems provide or interface with 120VAC or above (making the system
> operation exceeding the 60V AC trigger).
>
> My initial problem was believing that the article applied to a component
> (the battery bank), and not the system (all components taken together as a
> generator/storage system). It is an easy misunderstanding to make.
>
> Hope this helps!
>
> -Glenn Burt
>
> -Original Message-
> From: RE-wrenches  On Behalf
> Of Ray
> Sent: Saturday, March 09, 2019 12:41 PM
> To: RE-wrenches 
> Cc: Bill Brooks ; Bill Brooks 
> Subject: [RE-wrenches] NEC for Batteries < 60v ??
>
> Hi Everyone;
>
> I'm updating all my verbage on plansets, and I just realized that the
> newly created article 706 covering Energy Storage Systems is only for Over
> 60 VDC (706.1)  Also article 480 for batteries only requires disconnecting
> means over 60 VDC ?! (480.7).   I'm not about to not have a disconnect, so
> now that NEC pulled battery systems out of 690,  where do we go for
> guidance on normal battery systems: 12, 24, 48 VDC?
>
> Overall, I welcome most of the changes in NEC 2017, like separating off
> grid systems into articles 706, and 710, but it seems us off grid
> installers need some more clarification.
>
> Thanks,
>
> --
> Ray Walters
> Remote Solar
> 303 505-8760
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC for Batteries < 60v ??

2019-03-09 Thread Glenn Burt
Hi Ray,

This is a conversation I have had some time ago with a number of my fellow 
inspectors and code experts. When the 2017 NEC came out, I agreed with Mike 
Holt and Bill Brooks' assessment that the new article was poorly written and 
did not apply to most systems being installed today. After much discussion 
through my Cadmus network of authorities, it emerged that indeed 706 apples to 
the typical residential systems.
So Energy Storage Systems (ESS) are the point of article 706, and I believe 
that the key point is that the SYSTEM is generating AC voltage of 120VAC or 
240VAC, making the system fall under article 706.

Batteries themselves are minimally covered by NEC 480, NFPA 1, and the IFC as 
applicable locally.
So, the bottom line is that the new article does cover the work we do when 
systems provide or interface with 120VAC or above (making the system operation 
exceeding the 60V AC trigger).

My initial problem was believing that the article applied to a component (the 
battery bank), and not the system (all components taken together as a 
generator/storage system). It is an easy misunderstanding to make.

Hope this helps!

-Glenn Burt

-Original Message-
From: RE-wrenches  On Behalf Of Ray
Sent: Saturday, March 09, 2019 12:41 PM
To: RE-wrenches 
Cc: Bill Brooks ; Bill Brooks 
Subject: [RE-wrenches] NEC for Batteries < 60v ??

Hi Everyone;

I'm updating all my verbage on plansets, and I just realized that the newly 
created article 706 covering Energy Storage Systems is only for Over 60 VDC 
(706.1)  Also article 480 for batteries only requires disconnecting means over 
60 VDC ?! (480.7).   I'm not about to not have a disconnect, so now that NEC 
pulled battery systems out of 690,  where do we go for guidance on normal 
battery systems: 12, 24, 48 VDC?

Overall, I welcome most of the changes in NEC 2017, like separating off grid 
systems into articles 706, and 710, but it seems us off grid installers need 
some more clarification.

Thanks,

--
Ray Walters
Remote Solar
303 505-8760

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC for Batteries < 60v ??

2019-03-09 Thread Jerry Shafer
Wrenches
Battery voltages in the NEC generally mean Nominal not peak but may also
not to exceed. Blue ion  is UL Listed and as far as less than 60, l think
is the only ones.
Jerry

On Sat, Mar 9, 2019, 9:40 AM Ray  wrote:

> Hi Everyone;
>
> I'm updating all my verbage on plansets, and I just realized that the
> newly created article 706 covering Energy Storage Systems is only for
> Over 60 VDC (706.1)  Also article 480 for batteries only requires
> disconnecting means over 60 VDC ?! (480.7).   I'm not about to not have
> a disconnect, so now that NEC pulled battery systems out of 690,  where
> do we go for guidance on normal battery systems: 12, 24, 48 VDC?
>
> Overall, I welcome most of the changes in NEC 2017, like separating off
> grid systems into articles 706, and 710, but it seems us off grid
> installers need some more clarification.
>
> Thanks,
>
> --
> Ray Walters
> Remote Solar
> 303 505-8760
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org