Re: [RE-wrenches] Xfmr's job?
Hello All The VFX/FX inverters does make use of the X240 transformer. The transformer itself could act as a step up, a step down, or a load balancing transformer. Neither the FXR or the Radian inverters require the transformer as a load balancing transformer. The transformer can still be used in its step up or step down configurations. The FXRA does not use the transformer for load balancing therefore each inverter must be sized to handle the loads and any associated surges as required by the ac loads on that leg. What was lost was the ability of the inverter systems to "borrow" from the lessor used ac leg. What was gained. The FXRA can sell back with up to 10 inverters compared to two of the GVFX . The FXRA can have up to 9 inverters in a 3 phase system compared to 3 with the VFX. The FXRA has seven modes of operation allowing on grid or off grid operation. SA capabilities are also available. The question "How much wattage could be supplied by the Radian on a single AC leg" was also asked. I put 6000 watts on L1 leaving no loads connected to the L2 phase. I will add this is not recommended practice. The loads should be balanced at the ac panel as closely as possible. But real life conditions are not always ideal. I hope this helps to clarify. Take Care All -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Angelini Offgrid Solar Sent: Wednesday, May 30, 2018 7:53 AM To: RE-wrenches Subject: Re: [RE-wrenches] Xfmr's job? The 8kw radian still has to have balance! You can't expect it to supply 8kw @ 120vac. It can supply 8kw @ 240 vac. > Does each of the 4 kW 240 volt inverters have a maximum on the > 120-volt power it can supply? for example, can it supply 70% of the 4 > kW on 120 -volts? > This example would leave 5.6 kW of 120-volt? > > On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 > > wrote: > >> The Radian has 2, 4k, 240 volt inverters, so its different but the >> way the computer works it makes the same from the load side of things >> Jerry >> >> >> >> Sent from my Verizon, Samsung Galaxy smartphone >> >> >> Original message >> From: frenergy >> Date: 5/29/18 5:51 PM (GMT-10:00) >> To: re-wrenches@lists.re-wrenches.org >> Subject: [RE-wrenches] Xfmr's job? >> >> Hey folks, >> >> Outback FP2 with Xfrmr shifts power to "other" leg if >> that leg needs more than the one FX can provide, right? Say, you >> need 5.5 KW on leg 1, the Xfrmr pulls some power from the leg 2 >> (inverter) to support that 5.5KW load on leg 1. >> >> My question (assuming above is accurate) is does the 8048 Radian do >> the same? >> >> Thanks, >> >> Bill >> >> Feather River Solar Electric >> Bill Battagin, Owner >> 4291 Nelson St. >> Taylorsville, CA 95983 >> 530.284.7849 >> CA Lic 874049 >> www.frenergy.net >> >> >> --- >> This email has been checked for viruses by Avast antivirus software. >> https://www.avast.com/antivirus >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. >> org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. >> org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist > .html > > List rule
Re: [RE-wrenches] Xfmr's job?
On 5/31/2018 7:09 AM, Drake wrote: That is interesting about Magnum: Tech support told me that the 4024PAE was two separate 2000 W inverters. We had problems with a microwave shutting the system down. That's interesting. I lived off grid for 7 years with a single MS4024PAE. I had one overload shut down in all that time. Microwave (1200 watts @ 120) + well pump (1700 watts @ 240) + vacuum cleaner (1400 watts @ 120) + house loads (200 watts @ 120) + I'm guessing fridge compressor kicked in (600 watts? @ 120). Never had any issues with air compressors, shop tools, 240 volt MIG welder, or anything else. Do you find you have good reliability with Magnum products? I have never had a failure with any MS inverter or ARC or AGS that I've installed. I had one BMK fail after 5 years, but that was during a lightning storm. -James Jefferson Jarvis APRS World, LLC +1-507-454-2727 www.aprsworld.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Xfmr's job?
Magnum is a no go for me for several reasons. First one is until they have a decent web based system data view/configure I can't help my remote clients as I do with Outback and Schneider. The second is they did not have a charge controller until 3 or so years ago:( The 8 KW radian and its mppts or an XW+ and the hi voltage mppt just works too well. XW+ can be configured for 6.8 KW @ 120vac if needed. I am going to use alot of skyboxes if they release it in November! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 > Hi all i have great respect for Magnum, it seems to have greater surge > capacity, and i have 120 volt draws greater thsn 2500 watts on one leg. I > never had a to much load one one leg problem. With Magnum, so please give > more information > > On Thu, May 31, 2018, 7:09 AM Drake > wrote: > >> That is interesting about Magnum: Tech support >> told me that the 4024PAE was two separate 2000 W >> inverters. We had problems with a microwave shutting the system down. >> >> Do you find you have good reliability with Magnum products? >> >> Drake >> >> >> At 03:53 PM 5/30/2018, you wrote: >> >HI Dave and everyone, Its interesting because >> >there is a great deal of difference between >> >OEMââ¬â¢s. Outback says 4kw at 120v for 8kw >> >radian. ( tech support) Magnum says 27 amps at >> >120v, 16.7 amps at 240 for MS4024PAE ( from the >> >manual) Schneider says 4200 watts at 120v on >> >XW-6848 ( from the manual) Also I know that the >> >Magnum allows you to charge with just 120v and I >> >think the XW is the same, OB you have to have >> >240v. Cheers jay > On May 30, 2018, at 7:52 AM, >> >Dave Angelini Offgrid Solar >> > wrote: > > The 8kw radian >> >still has to have balance! You can't expect it >> >to supply > 8kw @ 120vac. It can supply 8kw @ >> >240 vac. > > >> Does each of the 4 kW 240 volt >> >inverters have a maximum on the 120-volt >> >> >power it can supply? for example, can it supply >> >70% of the 4 kW on 120 >> -volts? >> This >> >example would leave 5.6 kW of 120-volt? >> >> On >> >Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >> >> > >> wrote: >> >>> The >> >Radian has 2, 4k, 240 volt inverters, so its >> >different but the way >>> the >>> computer works >> >it makes the same from the load side of >> >things >>> Jerry >>> >>> >>> >>> Sent from my >> >Verizon, Samsung Galaxy smartphone >>> >>> >>> >> > Original message >>> From: >> >frenergy >>> Date: 5/29/18 >> >5:51 PM (GMT-10:00) >>> To: >> >re-wrenches@lists.re-wrenches.org >>> Subject: >> >[RE-wrenches] Xfmr's job? >>> >>> Hey >> >folks, >>> >>>Outback FP2 with Xfrmr >> >shifts power to "other" leg if that >>> leg >> >needs more than the one FX can provide, >> >right? Say, you need 5.5 KW >>> on leg 1, the >> >Xfrmr pulls some power from the leg 2 (inverter) >> >to >>> support that 5.5KW load on leg 1. >>> >>> >> >My question (assuming above is accurate) is does >> >the 8048 Radian do the >>> same? >>> >>> >> >Thanks, >>> >>> Bill >>> >>> Feather River Solar >> >Electric >>> Bill Battagin, Owner >>> 4291 >> >Nelson St. >>> Taylorsville, CA 95983 >>> >> >530.284.7849 >>> CA Lic 874049 >>> >> >www.frenergy.net >>> >>> >>> --- >> >___ >> >List sponsored by Redwood Alliance List Address: >> >RE-wrenches@lists.re-wrenches.org Change >> >listserver email address & settings: >> >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >List-Archive: >> > >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >List rules & etiquette: >> >www.re-wrenches.org/etiquette.htm Check out or >> >update participant bios: www.members.re-wrenches.org >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___
Re: [RE-wrenches] Xfmr's job?
Hi all i have great respect for Magnum, it seems to have greater surge capacity, and i have 120 volt draws greater thsn 2500 watts on one leg. I never had a to much load one one leg problem. With Magnum, so please give more information On Thu, May 31, 2018, 7:09 AM Drake wrote: > That is interesting about Magnum: Tech support > told me that the 4024PAE was two separate 2000 W > inverters. We had problems with a microwave shutting the system down. > > Do you find you have good reliability with Magnum products? > > Drake > > > At 03:53 PM 5/30/2018, you wrote: > >HI Dave and everyone, Its interesting because > >there is a great deal of difference between > >OEM’s. Outback says 4kw at 120v for 8kw > >radian. ( tech support) Magnum says 27 amps at > >120v, 16.7 amps at 240 for MS4024PAE ( from the > >manual) Schneider says 4200 watts at 120v on > >XW-6848 ( from the manual) Also I know that the > >Magnum allows you to charge with just 120v and I > >think the XW is the same, OB you have to have > >240v. Cheers jay > On May 30, 2018, at 7:52 AM, > >Dave Angelini Offgrid Solar > > wrote: > > The 8kw radian > >still has to have balance! You can't expect it > >to supply > 8kw @ 120vac. It can supply 8kw @ > >240 vac. > > >> Does each of the 4 kW 240 volt > >inverters have a maximum on the 120-volt >> > >power it can supply? for example, can it supply > >70% of the 4 kW on 120 >> -volts? >> This > >example would leave 5.6 kW of 120-volt? >> >> On > >Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >> > > >> wrote: >> >>> The > >Radian has 2, 4k, 240 volt inverters, so its > >different but the way >>> the >>> computer works > >it makes the same from the load side of > >things >>> Jerry >>> >>> >>> >>> Sent from my > >Verizon, Samsung Galaxy smartphone >>> >>> >>> > > Original message >>> From: > >frenergy >>> Date: 5/29/18 > >5:51 PM (GMT-10:00) >>> To: > >re-wrenches@lists.re-wrenches.org >>> Subject: > >[RE-wrenches] Xfmr's job? >>> >>> Hey > >folks, >>> >>>Outback FP2 with Xfrmr > >shifts power to "other" leg if that >>> leg > >needs more than the one FX can provide, > >right? Say, you need 5.5 KW >>> on leg 1, the > >Xfrmr pulls some power from the leg 2 (inverter) > >to >>> support that 5.5KW load on leg 1. >>> >>> > >My question (assuming above is accurate) is does > >the 8048 Radian do the >>> same? >>> >>> > >Thanks, >>> >>> Bill >>> >>> Feather River Solar > >Electric >>> Bill Battagin, Owner >>> 4291 > >Nelson St. >>> Taylorsville, CA 95983 >>> > >530.284.7849 >>> CA Lic 874049 >>> > >www.frenergy.net >>> >>> >>> --- > >___ > >List sponsored by Redwood Alliance List Address: > >RE-wrenches@lists.re-wrenches.org Change > >listserver email address & settings: > >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > >List-Archive: > > > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > >List rules & etiquette: > >www.re-wrenches.org/etiquette.htm Check out or > >update participant bios: www.members.re-wrenches.org > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Xfmr's job?
That is interesting about Magnum: Tech support told me that the 4024PAE was two separate 2000 W inverters. We had problems with a microwave shutting the system down. Do you find you have good reliability with Magnum products? Drake At 03:53 PM 5/30/2018, you wrote: HI Dave and everyone, Its interesting because there is a great deal of difference between OEMâs. Outback says 4kw at 120v for 8kw radian. ( tech support) Magnum says 27 amps at 120v, 16.7 amps at 240 for MS4024PAE ( from the manual) Schneider says 4200 watts at 120v on XW-6848 ( from the manual) Also I know that the Magnum allows you to charge with just 120v and I think the XW is the same, OB you have to have 240v. Cheers jay > On May 30, 2018, at 7:52 AM, Dave Angelini Offgrid Solar wrote: > > The 8kw radian still has to have balance! You can't expect it to supply > 8kw @ 120vac. It can supply 8kw @ 240 vac. > > >> Does each of the 4 kW 240 volt inverters have a maximum on the 120-volt >> power it can supply? for example, can it supply 70% of the 4 kW on 120 >> -volts? >> This example would leave 5.6 kW of 120-volt? >> >> On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >> >> wrote: >> >>> The Radian has 2, 4k, 240 volt inverters, so its different but the way >>> the >>> computer works it makes the same from the load side of things >>> Jerry >>> >>> >>> >>> Sent from my Verizon, Samsung Galaxy smartphone >>> >>> >>> Original message >>> From: frenergy >>> Date: 5/29/18 5:51 PM (GMT-10:00) >>> To: re-wrenches@lists.re-wrenches.org >>> Subject: [RE-wrenches] Xfmr's job? >>> >>> Hey folks, >>> >>>Outback FP2 with Xfrmr shifts power to "other" leg if that >>> leg needs more than the one FX can provide, right? Say, you need 5.5 KW >>> on leg 1, the Xfrmr pulls some power from the leg 2 (inverter) to >>> support that 5.5KW load on leg 1. >>> >>> My question (assuming above is accurate) is does the 8048 Radian do the >>> same? >>> >>> Thanks, >>> >>> Bill >>> >>> Feather River Solar Electric >>> Bill Battagin, Owner >>> 4291 Nelson St. >>> Taylorsville, CA 95983 >>> 530.284.7849 >>> CA Lic 874049 >>> www.frenergy.net >>> >>> >>> --- ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Xfmr's job?
The 8kw radian still has to have balance! You can't expect it to supply 8kw @ 120vac. It can supply 8kw @ 240 vac. > Does each of the 4 kW 240 volt inverters have a maximum on the 120-volt > power it can supply? for example, can it supply 70% of the 4 kW on 120 > -volts? > This example would leave 5.6 kW of 120-volt? > > On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 > > wrote: > >> The Radian has 2, 4k, 240 volt inverters, so its different but the way >> the >> computer works it makes the same from the load side of things >> Jerry >> >> >> >> Sent from my Verizon, Samsung Galaxy smartphone >> >> >> Original message >> From: frenergy >> Date: 5/29/18 5:51 PM (GMT-10:00) >> To: re-wrenches@lists.re-wrenches.org >> Subject: [RE-wrenches] Xfmr's job? >> >> Hey folks, >> >> Outback FP2 with Xfrmr shifts power to "other" leg if that >> leg needs more than the one FX can provide, right? Say, you need 5.5 KW >> on leg 1, the Xfrmr pulls some power from the leg 2 (inverter) to >> support that 5.5KW load on leg 1. >> >> My question (assuming above is accurate) is does the 8048 Radian do the >> same? >> >> Thanks, >> >> Bill >> >> Feather River Solar Electric >> Bill Battagin, Owner >> 4291 Nelson St. >> Taylorsville, CA 95983 >> 530.284.7849 >> CA Lic 874049 >> www.frenergy.net >> >> >> --- >> This email has been checked for viruses by Avast antivirus software. >> https://www.avast.com/antivirus >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. >> org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. >> org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Xfmr's job?
Does each of the 4 kW 240 volt inverters have a maximum on the 120-volt power it can supply? for example, can it supply 70% of the 4 kW on 120 -volts? This example would leave 5.6 kW of 120-volt? On Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 wrote: > The Radian has 2, 4k, 240 volt inverters, so its different but the way the > computer works it makes the same from the load side of things > Jerry > > > > Sent from my Verizon, Samsung Galaxy smartphone > > > Original message > From: frenergy > Date: 5/29/18 5:51 PM (GMT-10:00) > To: re-wrenches@lists.re-wrenches.org > Subject: [RE-wrenches] Xfmr's job? > > Hey folks, > > Outback FP2 with Xfrmr shifts power to "other" leg if that > leg needs more than the one FX can provide, right? Say, you need 5.5 KW > on leg 1, the Xfrmr pulls some power from the leg 2 (inverter) to > support that 5.5KW load on leg 1. > > My question (assuming above is accurate) is does the 8048 Radian do the > same? > > Thanks, > > Bill > > Feather River Solar Electric > Bill Battagin, Owner > 4291 Nelson St. > Taylorsville, CA 95983 > 530.284.7849 > CA Lic 874049 > www.frenergy.net > > > --- > This email has been checked for viruses by Avast antivirus software. > https://www.avast.com/antivirus > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Xfmr's job?
The Radian has 2, 4k, 240 volt inverters, so its different but the way the computer works it makes the same from the load side of thingsJerry Sent from my Verizon, Samsung Galaxy smartphone Original message From: frenergy Date: 5/29/18 5:51 PM (GMT-10:00) To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Xfmr's job? Hey folks, Outback FP2 with Xfrmr shifts power to "other" leg if that leg needs more than the one FX can provide, right? Say, you need 5.5 KW on leg 1, the Xfrmr pulls some power from the leg 2 (inverter) to support that 5.5KW load on leg 1. My question (assuming above is accurate) is does the 8048 Radian do the same? Thanks, Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 www.frenergy.net --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org