RE: Australia Safety

2000-10-11 Thread Kevin Richardson
Hi Richard, I am afraid I led you astray a little for NZ. This type of power supply does NOT require any form of approval presently in NZ. A little history These types of devices have not been required to be approved in NZ in the past. NZ is presently completely revamping their electrical

Re: DC circuits /+60 V

2000-10-11 Thread Rich Nute
Hi Chris: In other words: don't test if you know already the result before the test is made. A good safety engineer can predict the result (not pass-fail but the measured value) of each and every safety test. For example, a good safety engineer can predict leakage current to

RE: Neutral/Earth connections

2000-10-11 Thread rbusche
Another possibility is that the US equipment may have been designed for a three phase Y input with a neutral and was used on a European three phase delta circuit. Someone could have then tied the neutral terminal to ground creating a serious hazard as well as a voltage imbalance. Just a

RE: Neutral/Earth connections

2000-10-11 Thread O'Shaughnessy, Paul
He's right. Tying neutral directly to the chassis is just WRONG, even if you could be sure it would always be neutral (not guaranteed at all). Sounds like somebody got neutral and the safety ground mixed up. I'd send the unit back to the manufacturer with a nasty note. I would also question

RE: Neutral/Earth connections

2000-10-11 Thread Crane, Lauren
Dave, It is my understanding, as you state, that earth ground and neutral should not be tied together in a piece of equipment except to ground reference the output of a transformer that is part of the equipment, although I can not quote chapter and verse from the NEC or 1950 on this. I suspect

Re: Neutral/Earth connections

2000-10-11 Thread Rich Nute
Hi Richard and Dave: In answer to Richard's comment: The neutral is never to be tied to the chassis of equipment. It is not allowed by any safety standard nor the National Electrical Code. The neutral is to be tied to earth at one and only one point and that is that the service

RE: Label Rub test per IEC60950

2000-10-11 Thread Massey, Doug C.
THANKS TO ALL FOR THE REPLIES - THANKS, NED, FOR THE EXACT ANSWER !! -Original Message- From: Ned Devine [mailto:ndev...@entela.com] Sent: Tuesday, October 10, 2000 10:01 AM To: emc-p...@majordomo.ieee.org Subject: RE: Label Rub test per IEC60950 Hi, The requirement is for The

RE: Neutral/Earth connections

2000-10-11 Thread WOODS
The neutral is never to be tied to the chassis of equipment. It is not allowed by any safety standard nor the National Electrical Code. The neutral is to be tied to earth at one and only one point and that is that the service entrance or the electrical box fed by an on-premises transformer. I

RE: PCB temp ratings, etc...

2000-10-11 Thread WOODS
Let me see if I understand. The board without the resist coating has a UL certified temperature rating. We don't know the temperature rating of the coating; but if it does ignite, at least we know the certified burn rate. Well, perhaps the ignition temperature is high enough so that we don't have

RE: DoC TCF

2000-10-11 Thread Bailey, Jeff
Ooops I meant to say I can't guarantee you that NOT I won't provide you with Maybe I should stop using my cell phone so much... :-) Jeff -Original Message- From: Bailey, Jeff [mailto:jbai...@mysst.com] Sent: Wednesday, October 11, 2000 12:35 PM To: 'emc-pstc' Subject: RE: DoC TCF

Neutral/Earth connections

2000-10-11 Thread k3row
The company that I work for in the U.K has recentlyreceived from the USA an item of test equipment, provided to us under contract, in which, we discovered, the 240v neutral line was connected to earth/unit chassis. This became apparent when the unit was plugged into a U.K 120-0-120 supply and

RE: Standards hierarchy

2000-10-11 Thread Maxwell, Chris
In the instance of EN 61000-3-2 and EN 61000-3-3, we MUST look to regulatory authorities to make the decision. I think the basis of the whole argument is this: For many products covered by these standards, the essential requirements as listed by many competent EMC engineers would not include

RE: PCB temp ratings, etc...

2000-10-11 Thread Peter Tarver
Richard - Then the answer is no. The MOT, as Pete Perkins pointed out, establishes the test points for thermal conditioning, but solder resists are then tested in conjunction with the PWB only for flammability classification. Regards, Peter L. Tarver, PE ptar...@nortelnetworks.com

DC circuits /+60 V

2000-10-11 Thread Scott Lemon
Hello Group, I have a good idea (first hand knowledge) of what UL looks for with respect to dc supply circuitry /= 60 Vdc (e.g. telecom equip supply). UL considers (with caveats on the supply) that it is SELV secondary with operational insulation requiring 500 Vac/707 Vdc dielectric withstand

RE: PCB temp ratings, etc...

2000-10-11 Thread WOODS
You are correct. I used the wrong term. I should have said the solder resist coating. Is this coating included in the temperature ratings? Richard Woods -- From: mike harris [SMTP:tecco...@i-cafe.net] Sent: Wednesday, October 11, 2000 11:25 AM To:

RE: DoC TCF

2000-10-11 Thread Bailey, Jeff
Hi Richard, AB uses the TCF route quite frequently and they list their DoC's online. Try going to http://www.ab.com/certification/ce/docs/index.html and look at a couple of DoC's through the links found there. It won't provide you with the rules for wording are adhered to or not but it may give

Re: PCB temp ratings, etc...

2000-10-11 Thread mike harris
Hi Richard Peter, Richard, I wonder if you are calling the solder resist coating as conformal coating? If so, I expect that the resist coating is ignored for any PWB ratings and insulation properties. My understanding is that conformal coating is a completely other issue from resist

RE: Standards hierarchy

2000-10-11 Thread Wagner, John P (John)
I'd like to throw my two cents worth in here. First, compliance with a national/international standard or regulatory regime does not guarantee adequate product performance or safety. That is the responsibility of the manufacturer. The standard(s) gives guidance to achieve that acceptable level

RE: PCB temp ratings, etc...

2000-10-11 Thread Peter Tarver
You're welcome, Richard. MOTs are developed for a copper clad industrial laminate and verified by certain tests on a finished PWB. Conformal coatings are not a normal part of this process, though I suppose a board house could ask for such considerations to be made for a selection of coatings.

FW: DoC TCF

2000-10-11 Thread Jon Griver
Richard, DoC is the same except that instead of a list of harmonised standards, you list the name and address of the Competent Body, and the serial number and date of the Certificate they issued to you. Regards, Jon Griver VP Quality Assurance Medson Ltd. I have seen several Declarations

RE: EN 475

2000-10-11 Thread dosborn
Hello Massimo, The scope of EN475 is as follows: specifies the characteristics of electrically-generated signals intended for use with medical devices, either individually or as part of a centralized system. This standard applies only if a particular device standard makes reference to it. I

DoC TCF

2000-10-11 Thread WOODS
I have seen several Declarations of Compliance when harmonized standards are used, but I don't recall seeing one where the TCF route was followed for one or more essential requirements. What wording is used on DoC to note that a Competent/Notified Body rendered an opinion that a product complies

RE: PCB temp ratings, etc...

2000-10-11 Thread WOODS
Pete thanks for your reply. I have noticed that the conformal coating on some boards begins to discolor when subjected to continuous high temperatures. In some samples, the coating begins to darken, bubble and delaminate from the surface. Is the conformal coating considered when setting the rated

RE[2]: comparison of ESD per MIL - 1686B to EN61000-4-2

2000-10-11 Thread Geoff Lister
Sorry folks, It seems you cannot go straight to the results screen :-( Try http://astimage.daps.dla.mil/quicksearch/ and insert 1686 in the Document Number box. regards, Geoff Lister Senior Engineer Motion Media Technology Ltd. http://www.motion-media.com -Original Message- From:

Re: Australia Safety

2000-10-11 Thread Barry Esmore
Hi Richard, It's certainly mandatory for Australia, but was not mandatory for NZ last time I looked. The standard should be AS/NZS 3108, or for IT equipment you may use AS/NZS 3260. Let me know if you need further assistance. Regards Barry Esmore AUS-TICK (The Australian Compliance

RE: comparison of ESD per MIL - 1686B to EN61000-4-2

2000-10-11 Thread Geoff Lister
Michael, I could not find revision B of the spec, but revision C is available as a free download from the following address. Regards, Geoff Lister Senior Engineer Motion Media Technology Ltd. http://www.motion-media.com http://assist.daps.mil/eAccess/index.cfm?ident_number=37095

PCB temp ratings, etc...

2000-10-11 Thread Pete Perkins
PSNet, PWB's are one form of plastic insulating materials. They must endure for a long time without giving up the properties that make them good insulators or enclosures for insulators. In the long term the volatiles evaporate away and the molecular structure breaks down giving way to

RE: comparison of ESD per MIL - 1686B to EN61000-4-2

2000-10-11 Thread Brumbaugh, David
I don't know if this is what you are after: MIL-STD-1686B rates ESD sensitivity of class 3 parts, assemblies or equipment at sensitivity levels ranging from 4000 to 15999 volts. I don't see a subclass rating (i.e., 3a) Appendix C of this standard requires testing at 2000 volts for assemblies

Re: PCB temperature ratings

2000-10-11 Thread Rich Nute
Hi Richard: When a PCB is rated 105C or 130C or whatever, what does that really mean? Can I really operate a 130C rated board at a maximum surface temperature of 130C for years without being concerned about reliability or safety? Is there a relationship between de-rating and

Principal Compliance Engineer

2000-10-11 Thread Nazeeh Shaheen
Position: Compliance Engineer ITE Equipment BSEE or equivalent Familiarity with LAN/WAN technologies Product Safety EMI/EMC Network Attachment NEBS Location: Occam Networks 4183 State Street Santa Barbara, CA 93110 Company: Occam Networks is an early stage start up which received initial Series

Job Posting - Compliance Engineer - Santa Barbara, CA

2000-10-11 Thread Michael Garretson
Forwarded for Nazeeh Shaheen nshah...@occamnetworks.com - please do not hit reply to respond - redirect messages to Nazeeh Shaheen nshah...@occamnetworks.com Position: Compliance Engineer ITE Equipment BSEE or equivalent Familiarity with LAN/WAN technologies Product Safety EMI/EMC Network