Am 03.02.2012 um 04:50 schrieb Kirk Wallace:
I am able to modpoll the proper registers now, but I have a problem with
Do you mean 'modpoll the proper registers' to mean 'read several holding
registers in one operation'?
If so: I had that problem with the Toshiba VFS-11. See the note in my
On Fri, 2012-02-03 at 11:36 +0100, Michael Haberler wrote:
Am 03.02.2012 um 04:50 schrieb Kirk Wallace:
I am able to modpoll the proper registers now, but I have a problem
with
Do you mean 'modpoll the proper registers' to mean 'read several
holding registers in one operation'?
If so:
On Fri, 2012-02-03 at 19:13 +1100, Frank Tkalcevic wrote:
I've taken the existing gs2_vfd.c from src/hal/user_comps and made an
sj200_vfd.c
I don't like writing code that isn't modular and reusable, so I started to
write the module so it could be configured by a table of values. I only got
On Thu, 2012-02-02 at 19:50 -0800, Kirk Wallace wrote:
I'm trying to get my SJ200 VFD connected with Modbus. In preparation for
this I ported a MVX9000 which I had on the shelf. It turned out to be a
slam dunk, almost.
http://www.wallacecompany.com/machine_shop/EMC2/mvx9000/
I've noticed on
On Fri, 2012-02-03 at 11:38 -0800, Kirk Wallace wrote:
On Thu, 2012-02-02 at 19:50 -0800, Kirk Wallace wrote:
I'm trying to get my SJ200 VFD connected with Modbus. In preparation for
this I ported a MVX9000 which I had on the shelf. It turned out to be a
slam dunk, almost.
On 02/03/2012 12:20 PM, Kirk Wallace wrote:
I have some more thoughts on VFD components. My plan for my SJ200
component was to have a bare-bones version that let one operate speed,
direction and maybe a fault signal, then a more complete version with
more features, but still only those
I haven't considered a generic VFD or Modbus device driver, because not
only do the device functions vary widely, but so do implementations of the
Modbus standard.
Yes, I found that too. I built my code based on the GS2 module and
Michael's code.
Early on, I avoided using the GS2
On Fri, 2012-02-03 at 14:58 -0800, Karl Cunningham wrote:
On 02/03/2012 12:20 PM, Kirk Wallace wrote:
I have some more thoughts on VFD components. My plan for my SJ200
component was to have a bare-bones version that let one operate speed,
direction and maybe a fault signal, then a more
Am 04.02.2012 um 00:30 schrieb Frank Tkalcevic:
I haven't considered a generic VFD or Modbus device driver, because not
only do the device functions vary widely, but so do implementations of the
Modbus standard.
Yes, I found that too.
Amen. I had that grandiose plan too, despite advice
I'm trying to get my SJ200 VFD connected with Modbus. In preparation for
this I ported a MVX9000 which I had on the shelf. It turned out to be a
slam dunk, almost.
http://www.wallacecompany.com/machine_shop/EMC2/mvx9000/
The SJ200 is a different story. It turns out Hitachi made a rev. 1 and 2
So which version do you need? I've made my own revision 2 driver.
-Original Message-
From: Kirk Wallace [mailto:kwall...@wallacecompany.com]
Sent: Friday, 3 February 2012 2:51 PM
To: LinuxCNC Users List
Subject: [Emc-users] SJ200 VFD and Modbus
I'm trying to get my SJ200 VFD
On Fri, 2012-02-03 at 16:12 +1100, Frank Tkalcevic wrote:
So which version do you need? I've made my own revision 2 driver.
I have rev. 2, or rather SJ200subscript2. If your component is GPL'd
then I'd appreciate getting a copy, although my problem seems to be with
libmodbus. I'm planning on
12 matches