Re: [RE-wrenches] RETURN AMP SETTING

2010-07-23 Thread James Surrette
Hi Dana, Sorry for the delay - been on the road. Not sure if this has already been presented / discussed. The old standby from industrial chargers, is 100% SOC is reached when charge current drops to 2% of capacity (normaly based on 6 or 8 hr rate). Please note, this comes from an era of

Re: [RE-wrenches] calculating DC voltage drop

2010-07-23 Thread Richard L Ratico
All, For longer, underground, array to inverter/charge controller runs, are folks using aluminum or copper? Last time I compared prices, for the same ampacity, Al was 1/3 the cost of Cu. Dick Ratico Solarwind Electric --- You wrote: Hi Dana; I'd say that's a bit overkill for today's market.

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Darryl Thayer
I found similar to Phil, but all the wire had thwn-2 on the spool label but not on the wire.  Execpt for pink it did not have thwn-2 on the spool lable.    Darryl --- On Fri, 7/23/10, Phil Undercuffler solarp...@gmail.com wrote: From: Phil Undercuffler solarp...@gmail.com Subject: Re:

Re: [RE-wrenches] calculating DC voltage drop

2010-07-23 Thread R Ray Walters
I try to keep it in copper for DC, as I had always heard of trouble with Aluminum on DC. (True or Old Wrenches Tale?) We definitely go to Al on long AC runs, as its whats available, and the cost difference becomes remarkable. I've seen small cuts in Al, later corrode completely through the

[RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
We went through a similar problem with some beach communities here in SoCal. Because of the high humidity (all winter and summer mornings) they wanted THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we were charged a premium for THWN-2 compared to THHN. But then we found a

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Nick Soleil
I have specified THWN-2 for years, but occasionally will not be able to source it! Sent from my iPhone On Jul 23, 2010, at 11:37 AM, Peter Parrish peter.parr...@calsolareng.com wrote: We went through a similar problem with some beach communities here in SoCal. Because of the high humidity

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Mick Abraham
I'm sorry to broadcast my ignorance, but: Could someone explain to me the significance of the -2 marking? Reply off-list if you wish to save bandwidth...but other List members may also be wondering... Thanks, Mick Abraham, Proprietor www.abrahamsolar.com Voice: 970-731-4675 On Fri, Jul 23,

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Mark Westbrock
-2 indicates that the insulation is rated for hot wet; that is that it is rated for 90C and wet conditions. See NEC Table 310.13(A). We also use Encore Wire. The sticker on the spool has THHN in big print, but then in small print below it says Type MTW or THHN or THWN-2. The insulation

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread David Brearley
Mick, THWN-2 is 90°C rated per Table 310.16. This is key for conductors in conduit on a roof. On a roof in full sun ambient temperatures are such that a 75°C rated conductor will have a severely diminished allowable ampacity, if any allowable ampacity. Jollily, David On 7/23/10 11:52 AM, Mick

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
The dash-two, as an appendage to THWN indicates that the wire, normally rated for dry and wet locations and 75 deg C, is now rated dry/wet up to 90 deg C. - Peter Peter T. Parrish, Ph.D., President California Solar Engineering, Inc. 820 Cynthia Ave., Los Angeles, CA 90065 CA Lic. 854779, NABCEP

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Allan Sindelar
Mick, -2 means 90 degrees C rather than 75. THWN-2 thus means that it is wet-rated at 90C. That is generally considered Code for arrays, such as if it is run in NM flex conduit to a traditional module j-box. The j-box area may be considered to be able to get hot enough

[RE-wrenches] AL wire with DC

2010-07-23 Thread Dana
The problem with Al is that, IF there is ever a loose connection, associated arcing, that it melts not like copper in the same situation which may arc but not melt. I have come in on OG jobs where Al was employed and found J boxes that were [sometimes wet] and had loose connections and the

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
Just a minor point: the dash-two appendage brings a wet-rated wire from 75 deg C to 90 deg C. If you are not in a locale that argues for wet-rated wire and your specific application does not argue for wet-rated wire, IMHO it is perfectly acceptable to use THHN wire (90 deg C rated for damp

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Ryan Mayfield
Peter, There was a change in the 2008 NEC (I know - CA is just getting to this Code cycle) that won't allow THHN inside conduit when the conduit is installed in wet locations, 300.9 (300.5 for underground): 300.9 Raceways in Wet Locations Above Grade. Where raceways are installed in wet

Re: [RE-wrenches] RETURN AMP SETTING

2010-07-23 Thread Dana
James – Thank-you! this is a good start and then monitoring the SG after a rest period w/o loads should help determine the time and SOC. Off to the lab again Igor, we have tests to run. Thanks, Dana Orzel Great Solar Works, Inc E - d...@solarwork.com V - 970.626.5253 F -

Re: [RE-wrenches] RETURN AMP SETTING

2010-07-23 Thread Roy Butler
Darryl, You are probably aware of this but the Endurance machines are 240 VAC induction machines. I had asked about their policy on AC coupling their turbines for off grid use and they were less than enthusiastic. You might want to touch base with

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Kirk Herander, VSE
Dual rated thhn / thwn complies. And every reel I've ever bought is dual rated. I've never seen single-rated thhn. Kirk Herander Vermont Solar Engineering 802.863.1202 NABCEP(tm) Certified Solar Installer NYSERDA-eligible Installer VT Solar Incentive Program Partner -Original Message-

[RE-wrenches] #10 THWN-2

2010-07-23 Thread Marco Mangelsdorf
I've been looking hard to see what manufacturers produce this kinda elusive #10 THHN/THWN-2 wire. United Copper Industries (Texas) does. I have a handy spec sheet from them that I can email anyone who's interested. marco ___ List sponsored by Home

Re: [RE-wrenches] AC Coupling to an Endurance wind machine

2010-07-23 Thread Darryl Thayer
Was Return Amps Thanks Roy I usually leap then look, The customer has it already,   I ran it yesterday, on AC couple into the standalone system, I learned a lot.  But it ran, and I am working out some of the surprises I had.  I am building up two inverter boards with the systems to control

Re: [RE-wrenches] AL wire with DC

2010-07-23 Thread Richard L Ratico
Dana, Thanks for the input. Excuse me please, OG jobs are? If the wire had been copper and didn't melt, but instead continued to arc, would the resultant heat have eventually started a fire? What type of splice was it? Does no one else use Al for DC? Here in rocky Vermont/NH, we use the same

Re: [RE-wrenches] AL wire with DC

2010-07-23 Thread Dana
OG - Off Grid Thanks, Dana Orzel Great Solar Works, Inc E - d...@solarwork.com V - 970.626.5253 F - 970.626.4140 C - 970.209.4076 web - www.solarwork.com Responsible Technologies for Responsible People since 1988 -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] AL wire with DC

2010-07-23 Thread dan
I'm with Dick on this one... Sure, I've seen a few good oopsies involving aluminum, (where the J box does the Salvador Dali thing)... but they're usually installed by "Uncle Larry" types... as long as the install is code compliant (Listed and properly installed), I don't think it maters much.

[RE-wrenches] AL wire with DC

2010-07-23 Thread Dana
I cannot speak for what if. I have seen CU AL bolted in AL mechanical butt splices where someone did not torque it to spec. and it went to arcing. Both were a mess ; The butt splice was pitted / damaged and needed replacement, the AL cable melted and the copper cable did not. It the same

Re: [RE-wrenches] AL wire with DC

2010-07-23 Thread dan
check out NEC 110.14Dan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: [RE-wrenches] AL wire with DC From: "Dana" d...@solarwork.com Date: Fri, July 23, 2010 6:54 pm To: "'RE-wrenches'"

Re: [RE-wrenches] AL wire with DC

2010-07-23 Thread R Ray Walters
I think some of the advantage of the Cu in a bad connection is that it dissipates heat better. That might explain the melting Al, but not the Cu. Cu will melt and cook the insulation if the connection is loose enough at high enough amperage. Again, I have not personally seen a problem with Al on