Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)

2020-10-28 Thread Jason Szumlanski
I'm not following you. How is this not at the end of the feeder? The feeder terminates at the main breaker in the subpanel. On Wed, Oct 28, 2020, 6:34 PM Brian Mehalic wrote: > This scenario is certainly allowed, but since it's not at the end of the > feeder, either: > >1. a. > >The fee

Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)

2020-10-28 Thread Brian Mehalic
This scenario is certainly allowed, but since it's not at the end of the feeder, either: 1. a. The feeder ampacity shall be not less than the sum of the primary source overcurrent device and 125 percent of the power-source output circuit current. 2. b. An overcurrent device at

Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)

2020-10-28 Thread Jason Szumlanski
Of course the feeder conductors and bus bar could be subjected to a fault. But we're not talking about faults here. Fault protection is the job of the PV OCPD And primary supply OCPD to protect the downstream busbar and feeders. If that wasn't the case, you would need a new OCPD on BOTH the load an

Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)

2020-10-28 Thread Jason Szumlanski
For further discussion, I don't see how my original scenario is any different from this attached scenario, which I think everyone would agree is allowed. All conductors and busbars are subject to the same potential loads and fault currents. (Image attached). On Wed, Oct 28, 2020 at 5:01 PM Jaso

Re: [RE-wrenches] NEC 2020 - 705.12(B)(6)

2020-10-28 Thread Brian Mehalic
Hey Jason, Here's the 2020 text: 6) Connections shall be permitted on busbars of panelboards that supply lugs connected to feed-through conductors. The feed-through conductors shall be sized in accordance with 705.12(B)(1). Where an overcurrent device is installed at the supply end of the feed-thr

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Christopher Warfel
CMP-4 strikes again!   That one is pretty obvious.  Accessible battery disconnect requirement no so much.  Christopher Warfel On 10/28/2020 12:40 PM, Brian Mehalic wrote: There's very "territorial" language in the 2020 NEC 705.11(D): "For meter socket enclosures or other equipment under the ex

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Brian Mehalic
There's very "territorial" language in the 2020 NEC 705.11(D): "For meter socket enclosures or other equipment under the exclusive control of the electric utility, only connections approved by the electric utility shall be permitted." Brian Mehalic NABCEP Certified Solar PV Installation Professio

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread August Goers
Others have pointed this out, but I thought I'd just add a bit of info based on my experience - the issue is not so much whether you can do a supply side connection or not, as that is allowed in the code. The issue is whether you can do wiring in a section of equipment that is only for the utility.

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread James Jefferson Jarvis
Hopefully Wisconsin is better than Minnesota about this. As a former Wisconsin resident, I doubt it...but here is how some of this works in Minnesota, lest you have any illusion that a PSC or a state cares about you. In Minnesota the state allows the utility to essentially make any interconnec

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Kristopher Schmid
Thanks for all the discussion and insight. I believe the main issue here is them being territorial about the meter socket (they did not install it and they do not own it). My follow up question to them was, "I assume that you allow a 320 A meter socket feeding two main panels. Is this different?

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Kirpal
Hi Kris. Here in Southern Oregon our utility if Pacific Power. They also will not allow us to do any kind of connection of tap inside the meter box even with code approved connection methods. They consider the meter can "their property" We are allowed supply side connections via any other AHJ ap

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Matt Partymiller
Kris, Are they telling you the problem is the connection in the meter base? We get this all the time from local utilities. Even with the listed Milbanks like you describe, they say no and direct us to tap on the load side of the meter base. I agree that you may consider an informal complaint

Re: [RE-wrenches] Supply side denial

2020-10-28 Thread Christopher Warfel
I would think that would be illegal.  They don't have jurisdiction on supply side taps. It's past the meter, and expressly allowed in the NEC.  I would definitely first ask to talk to a higher level person than the one denying it (paper trail important). If that does not work, then the PSC is y