[RE-wrenches] SunnyBoy 2500

2024-10-02 Thread Howie Michaelson via RE-wrenches
Hi All, Does anyone have any leads on a replacement for a SunnyBoy 2500. Ideally it would be a direct replacement, but another 120 vAC inverter would be possible as well. Thanks, Howie Michaelson ___ List sponsored by Redwood Alliance Pay optional

Re: [RE-wrenches] Blue Planet Energy

2024-09-16 Thread Howie Michaelson via RE-wrenches
Not surprising given their pricing structure. If this is true, I assume their 15 year warranty is the equivalent of vaporware. And I'm glad I only have 1 installation left with their product. Howie On Mon, Sep 16, 2024, 2:29 PM Brian Mehalic via RE-wrenches < re-wrenches@lists.re-wrenches.org> wro

Re: [RE-wrenches] MN 15-12KW-AIO

2024-08-02 Thread Howie Michaelson via RE-wrenches
system is not testing its limits due to the nature of the existing loads, but after several months, I've seen nothing that gives me pause. I will be installing several more of these systems both on and off grid over the next 1-2 months and will report back my experience here. Howie Michaelso

[RE-wrenches] Legacy SunnyBoy 2700 replacement

2024-07-25 Thread Howie Michaelson via RE-wrenches
Hi all,What are folks' choices for replacing a 16 year old SB2700 (120vAC inverter with a roof mounted array) that let the factory smoke out? I know this has been discussed before, but I'm wondering what the current suggestions might be. Thanks, Howie Michaelson S

Re: [RE-wrenches] have a laugh

2024-07-23 Thread Howie Michaelson via RE-wrenches
And conveniently it is on wheels so you can grid tie it virtually anywhere! It seems appropriately named... Howie Michaelson On Tue, Jul 23, 2024 at 6:10 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > > Same person asking about the pump was also asking about t

Re: [RE-wrenches] have a laugh

2024-07-23 Thread Howie Michaelson via RE-wrenches
Unfortunately it is back ordered, although it looks like you can still order the 2 50A extension cords. Howie Michaelson On Tue, Jul 23, 2024 at 6:10 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > > Same person asking about the pump was also asking about t

Re: [RE-wrenches] Outback in general

2024-07-21 Thread Howie Michaelson via RE-wrenches
-wrenches@lists.re-wrenches.org> wrote: > >> HI Howie, >> >> Does the AIO communicate with other brands of batteries? >> >> I concure about using batteries/inverters from same OEM, its my >> preference. >> >> Jay >> >> On Jul 20, 2024,

Re: [RE-wrenches] Outback in general

2024-07-20 Thread Howie Michaelson via RE-wrenches
issues and firmware headaches, which is why I am sticking to inverters and batteries from the same manufacturer. I will keep you all up to date on my experience with the production model of the Midnite AIO as I install them and with the Midnite LiFePO4 batteries as they become available. Howie Michaels

Re: [RE-wrenches] AES RACK MOUNT

2024-07-17 Thread Howie Michaelson via RE-wrenches
Michael, What do you use to make your evaluation of AES in specific and varying brands of Lithium batteries in general? Thanks Howie Sun Catcher On Wed, Jul 17, 2024 at 9:55 AM Michael Morningstar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I am. EG4=Yugo and AES=Mercedes. > >

[RE-wrenches] Sol-Ark Support

2024-06-05 Thread Howie Michaelson via RE-wrenches
Is anyone else having trouble getting through to Sol-Ark support? Howie Michaelson ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread Howie Michaelson via RE-wrenches
William, We have had this same SOC calibration issue with a dual stack of XW Pro (AC couple with Solaredge) and 2 eVault Max as well (other issues as well). Schneider's solution was to use voltage (open loop), not SOC, for the XW's programming. We weren't very happy about that since trying to do t

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Howie Michaelson via RE-wrenches
Yes, output not input. Thanks for clarifying that William... Howie *Sun Catcher* *Solar Electric Systems Sales & Service802-272-0004* On Tue, May 7, 2024 at 2:55 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Andrew: > > > > I see no problem paralleling the Ch

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Howie Michaelson via RE-wrenches
Andrew, As long as you have proper over current and wire sizing, there shouldn't be a problem with paralleling C60s. Of course, keeping the batteries at 12v for a 2kw array makes everything else bigger and more expensive. And they won't get the MPPT advantages of even 20 year old charge controller

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-24 Thread Howie Michaelson via RE-wrenches
then. Easier maintenance and operation for the client, less headache for you. I've definitely gravitated toward the KISS concept of the years, for both my and my clients' sanity... Howie Michaelson Sun Catcher On Wed, Apr 24, 2024 at 8:26 AM Jason Szumlanski via RE-wrenches < re-wren

Re: [RE-wrenches] speaking of batteries

2024-04-23 Thread Howie Michaelson via RE-wrenches
I had the same experience as Jay as far as being marketed three idea that managed lithium batteries can jane several year age differences and still play well together, only to be told, after telling my clients the same, that most manufacturers don't recommend more than a year age differential (alth

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Howie Michaelson via RE-wrenches
king to Outback support, after checking for appropriate input and output voltages, if there aren't any other obvious issues, they've told me the units are toast. Howie Michaelson Sun Catcher On Tue, Apr 23, 2024 at 2:45 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote:

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread Howie Michaelson via RE-wrenches
John, If you are thinking of pairing the Envy with lead-acid batteries, I would strongly suggest not doing it. Even though Fortress sales advertises the Envy to be compatible with lead-acid, after trying it in my off-grid home, I would emphatically say that it is not. The programming is inadequate,

Re: [RE-wrenches] midnite new inverter

2024-04-09 Thread Howie Michaelson via RE-wrenches
The last I heard, they are shipping this month or early next month. The pricing is supposed to be comparable to the other all in ones (Envy, Sol-Ark, EG4, etc.) deportment on your distributor. Howie On Tue, Apr 9, 2024, 6:55 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi

Re: [RE-wrenches] Good tech support

2024-03-27 Thread Howie Michaelson via RE-wrenches
heir support team, their sales team and their higher level tech, with absolutely no response. Crickets. Now I am frustrated, hence this missive. I will be replacing the Envy with another more appropriately designed inverter. Hopefully, I will be able to do something useful with it. Howie Michaels

[RE-wrenches] Reroofing grandfathering

2024-03-20 Thread Howie Michaelson via RE-wrenches
it with add on Tigo or APSMART equipment as opposed to replacing the whole system. In any case, before we explore the options, I'm trying to determine if putting it back up without RSD is (1) code compliant and (2) reasonable. Thanks for any insight, Howie Mi

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Howie Michaelson via RE-wrenches
interpretation of what they do and don't cover. Howie Michaelson Sun Catcher On Mon, Mar 11, 2024 at 8:02 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Dave: > > > > I have thought about this dilemma pretty carefully in the past. I have

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-10 Thread Howie Michaelson via RE-wrenches
According to my agent, general liability does not cover design problems, whether we wrench it or not. That is what an Errors and Omissions policy would cover, and what a previous agent mentioned to me in passing after selling me general liability for 10 years! They could offer me an E&O policy for

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Howie Michaelson via RE-wrenches
does anyone know about the built in signal generator in the Envy (or others?) continue to work if the inverter has shut down on LBCO? If not, wouldn't using the built in signal generators cause a significant headache in those circumstances? Howie Michaelson On Tue, Feb 20, 2024 at 12

Re: [RE-wrenches] EG4 Equipment

2024-02-18 Thread Howie Michaelson via RE-wrenches
thing and everything, but many of these stories (including ones on the wrenches) are fairly specific and disheartening. I assume by the fact that you continue to install their batteries, that that has not been your experience? Howie Michaelson On Sun, Feb 18, 2024 at 3:16 PM Carl Hansen v

Re: [RE-wrenches] EG4 Equipment

2024-02-18 Thread Howie Michaelson via RE-wrenches
happy to hear about them on or off list. Howie Michaelson Sun Catcher On Sat, Feb 17, 2024 at 1:16 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Drake: > > > > I prefer the UnigyII VRLA batteries. Full river 2 volt L-16s are pretty > go

[RE-wrenches] EG4 Equipment

2024-02-16 Thread Howie Michaelson via RE-wrenches
blems, but it certainly will help in the troubleshooting process by hopefully having less of the "not my problem" or "we haven't seen that problem" responses from tech support. I really don't like making forays into bleeding-edge technologies, so I'm hop

[RE-wrenches] Automatic load control

2023-12-14 Thread Howie Michaelson via RE-wrenches
pieces of equipment that work specifically with the Sol-Ark? I'd also be open to considering Fortress's Envy, if there is an option that would work well specifically with it. I'm interested in the range of options from simple to complicated, as long as it is automated. All automated

Re: [RE-wrenches] Home grid stacked battery heating

2023-11-05 Thread Howie Michaelson via RE-wrenches
Daryl, Being in Vermont and dealing with lots of off-grid, occasional use systems, I'm definitely interested in others' experience with cold weather installations. Howie Michaelson Sun Catcher On Sun, Nov 5, 2023 at 3:03 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re

Re: [RE-wrenches] Aging Batteries

2023-10-27 Thread Howie Michaelson via RE-wrenches
Hey Will, At the risk of being overly simplistic and obvious, have you kept good specific gravity records over the years? Are they showing lowered or uneven readings? I've often been able to get some more life out of flooded batteries by raising the charge and equalize voltages, particularly if t

Re: [RE-wrenches] Wattnode AC Coupling Monitoring on Insight Cloud

2023-10-26 Thread Howie Michaelson via RE-wrenches
tion match device value. > • AC coupled power flow on InsightCloud & InsightMobile will be coming > soon. > > > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" ><http://members.sti.net/offgridsolar/>https://offgridsolar1.com/

[RE-wrenches] Wattnode AC Coupling Monitoring on Insight Cloud

2023-10-26 Thread Howie Michaelson via RE-wrenches
a "Home" device) which is causing this issue. Just wondering if anyone has been successful at implementing this feature so that it shows up on the Cloud. Thanks, Howie Michaelson Sun Catcher ___ List sponsored by Redwood Alliance Pay optional me

[RE-wrenches] Pytes Batteries

2023-10-11 Thread Howie Michaelson via RE-wrenches
Does anyone have any experience with using Pytes LiFePO4 batteries? They appear to be a solid option, but have little to no direct knowledge of them. TIA, Howie Michaelson Sun Catcher ___ List sponsored by Redwood Alliance Pay optional member dues here

[RE-wrenches] Solar World 285

2023-09-25 Thread Howie Michaelson via RE-wrenches
t and look)? Thanks, Howie Michaelson Sun Catcher ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http:/

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-24 Thread Howie Michaelson via RE-wrenches
Hi Mick, Unlike others in the list, I am still mostly happily using SolarEdge for my straight grid tied roof mounted arrays. There have been significant hiccups with service, although not so much recently, and the failure rate is higher than I like, but it hasn't been dramatic for me. For systems t

[RE-wrenches] Silfab

2023-08-21 Thread Howie Michaelson via RE-wrenches
Hi All, I have heard mixed comments about Silfab modules. If anyone has experience with these panels, I would appreciate any feedback available. Thanks, *Howie Michaelson**Sun Catcher* ___ List sponsored by Redwood Alliance Pay optional member dues

[RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread Howie Michaelson via RE-wrenches
Hi All, I have never installed the SolarEdge car charger, and even though it seems to have some capacity advantages over a standalone charger, for some reason I've stayed away from them. I'd be interested to hear others' takes on the advantages/disadvantages of going that route. Thanks, Howie

Re: [RE-wrenches] Inverter output fluctuations

2023-07-24 Thread Howie Michaelson via RE-wrenches
; http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > > On 2023-07-23 9:37 pm, Howie Michaelson via RE-wrenches wrote: > > Don, > Thanks, but this is not the issue here. The fluctuati

Re: [RE-wrenches] Inverter output fluctuations

2023-07-23 Thread Howie Michaelson via RE-wrenches
s energy. > Tell the customer to turn the hot tub up high, or something like that. > Heat up a bathtub in a greenhouse and plant bananas. > > DonBarch > Energy Solar > > From: Howie Michaelson > To: Dave Angelini , RE-wrenches > > Subject: Re: [RE-wrenches] In

Re: [RE-wrenches] Inverter output fluctuations

2023-07-23 Thread Howie Michaelson via RE-wrenches
orked fine for years it would appear that the XW+ has an > issue. > > I don’t see how the SE could cause this. > > Is it still under warranty? What does Schneider say about the issue. > > Jay > > > > On Jul 22, 2023, at 10:33 PM, Howie Michaelson via RE-wrench

Re: [RE-wrenches] Inverter output fluctuations

2023-07-22 Thread Howie Michaelson via RE-wrenches
;>> This is off an old list I got from Support many years ago and combined >>> with my findings over the years. Really rare for this kind of weirdness and >>> why it would be getting worse without visual evidence. >>> >>> Good Luck Howie! >>> >>> &g

Re: [RE-wrenches] Inverter output fluctuations

2023-07-22 Thread Howie Michaelson via RE-wrenches
k Howie! > > > > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > > > > On 2023-07-03 12:42 pm

[RE-wrenches] SolarEdge and Schneider Conext

2023-07-05 Thread Howie Michaelson via RE-wrenches
Hi all, Had anyone successfully established communications between a SolarEdge single phase inverter and a Schneider Gateway? I have a client with a battery backup system which included a dual stack of XW pros and 2 AC coupled SolarEdge inverters. He would really like to be able to use one monitori

[RE-wrenches] Inverter output fluctuations

2023-07-03 Thread Howie Michaelson via RE-wrenches
Hi All, I upgraded an old clients' off-grid system about five years ago to a Schneider XW6848+ and 2 Blue Ion 2.0 cabinets (32kWh). When the batteries were moving toward full, if the charge rate was on the higher side via generator or solar (AC coupled w/SolarEdge 6kW and DC coupled with an FM 80),

Re: [RE-wrenches] Need detailed help with Pytee battery

2023-06-04 Thread Howie Michaelson via RE-wrenches
Daryl, I purchased some Pytes batteries for my brother-in-law this spring, as I had some contact with them, and he wanted to try their batteries. I've had no contact with their support team at all, and the only real contact I have is the sales person I dealt with, Austin Li (austin...@pytesgroup.c

Re: [RE-wrenches] Fortress LFPs & ENVY 12kw inverter

2023-06-01 Thread Howie Michaelson via RE-wrenches
Kirk, I have not tried the new Envy inverter, and at the moment am slightly reluctant to do so, mostly because I have gone all in on Sol-Ark/eVault Max setups for battery based systems and I hate having more and more different products to stay on top of. That being said, I attended an Envy webinar

Re: [RE-wrenches] Schneider Conext SCP

2023-05-26 Thread Howie Michaelson via RE-wrenches
Thanks for the heads up, Kevin! However I seem to have missed the memo that xantrex and Schneider are separate entities? How far out of the loop am I? Howie Sun Catcher On Fri, May 26, 2023, 1:28 PM Kevin Pegg via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Not sure if it’s quite pu

[RE-wrenches] Solar direct water pumping

2023-05-08 Thread Howie Michaelson via RE-wrenches
Hi, I have a friend/client that is looking to keep his pond filled with water pumped from a spring downhill from the pond. He's happy to have the pond filled just when there is enough sun to pump, so no batteries are desired. I have little to no experience with water solar direct pumping, so I'm a

[RE-wrenches] HomeGrid Battery Experience

2023-04-14 Thread Howie Michaelson via RE-wrenches
2k inverter. If anyone has any experience with the HomeGrid (positive or negative), or experience with both brands, I'd love to hear any feedback. I hate installing equipment I haven't used before! 😕 Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Sol

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread Howie Michaelson via RE-wrenches
rrange the bank into 2 strings of 8, keeping the others for replacement of future potential failures. This will give you some breathing room to propare to make the investment into a full replacement bank, be it Lead-Acid or Lithium. Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV

Re: [RE-wrenches] Intermittent

2023-03-16 Thread Howie Michaelson via RE-wrenches
Hilton, Can you give more details about the inverter? And when the DC was reading 0 volts, did you try turning off the disconnect at the array to see if isolating it from the inverter, it would show voltage? Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Howie Michaelson via RE-wrenches
Does anyone know of any bypass switch/breaker setup for anything greater than 60 amps for 2 poles, other than large DPDT switches which get pricey and hard to source especially for 200 amps? Howie On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote:

Re: [RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Howie Michaelson via RE-wrenches
d. And to set up the charge algorithm to bring the batteries up higher every now and then. So far, things have worked better. Howie Michaelson Sun Catcher On Thu, Feb 9, 2023, 8:10 PM Chris Sparadeo via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Ray, > > Establ

[RE-wrenches] VillaGrid Lithium Titanium Batteries

2023-01-23 Thread Howie Michaelson via RE-wrenches
hought I'd ask. Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenche

Re: [RE-wrenches] Sola-ark cold morning

2022-12-06 Thread Howie Michaelson via RE-wrenches
t tweaking, but it sounds like they are at least open to getting feedback and suggestions from wrenches that are interested in doing so. Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Sun, Dec 4, 2022

Re: [RE-wrenches] Sola-ark cold morning

2022-12-04 Thread Howie Michaelson via RE-wrenches
Dana, Sounds like potentially the same issue I've been dealing with in a new Sol-Ark 15 paired with Fortress eVault Maxs. Apparently, Sol-Ark did a recent firmware update that caused erratic closed loop communication between the inverter and batteries. I don't know if the Sol-Ark firmware update ef

[RE-wrenches] Fortress support call

2022-12-01 Thread Howie Michaelson via RE-wrenches
Jeremy, I would love to have an opportunity to talk with Fortress about their support process. I am just in the tail end of installing 2 Sol-Ark/Fortress off grid systems (one 15k with 2 eVaults and two 15ks with 5 eVaults). I've been very impressed with both pieces of equipment so far. However, I

[RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-16 Thread Howie Michaelson via RE-wrenches
t is a settings issue, as several technicians have gone through them, I have gone over them many times using the Fortress/Sol-Ark integration white papers. Hoping to get higher level tech involved ASAP, since I don't feel like the lower level techs know enough to provide useful ideas. Thank

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Howie Michaelson via RE-wrenches
, which again takes days for them to respond to. Very unsatisfactory and frustrating after having invested in 7 eVault Max for a long time client. Don't have any suggestions for you. *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & S

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
phone. Do you still have the email response from George? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches < re-wrenches@lists.re-wr

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
efore. Could you possibly elaborate? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Fri, Oct 21, 2022 at 2:46 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > On

[RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
Hi folks, I have a client that I'm doing a larger inverter and battery upgrade. We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The client is wanting manufacturer certification that the equipment is "qualified solar electric property". I don't know that I've ever run acros

[RE-wrenches] Sol-Ark phase imbalances

2022-09-10 Thread Howie Michaelson via RE-wrenches
Is there a white paper or a thorough explanation of the issue Sol-Ark had with large imbalances between phases. I am looking at a large residential off-grid system using potentially (2)15 kw Sol-Arks. What are the concerns specifically around unbalanced inductive loads. Also, I have not installed m

[RE-wrenches] Do Sunny Islands and Fortress batteries play well together?

2022-09-01 Thread Howie Michaelson via RE-wrenches
Has anyone put Fortress batteries into a Sunny Island off grid system, either an E flex or an E vault? I have a client with older 2 volt Rolls batteries that need replacing. Currently about 55 kwhs. Or any experience with other LiFEPO4 batteries with Sunny Island off grid systems? Thanks Howie Sin

Re: [RE-wrenches] off-grid AC coupling feasibility

2022-07-30 Thread Howie Michaelson via RE-wrenches
Hey Kirk, This is something I've done a few times with success, although I've used an XW pro instead of the Radian, with OB charge controllers. Having the mix of DC and AC coupled is ideal, as the solaredge will do the bulk of the charging, but then charge controllers will do the finish taper charg

Re: [RE-wrenches] Dark Starting Simpliphi PHI3.5 batteries

2022-07-27 Thread Howie Michaelson via RE-wrenches
pted a charge and > have apparently functioned well for the customer. Job was installed by > others. > > I hope that helps. > Wallace Stahle > Future Electric Energy Co > PO Box 236 > Willits, CA 95490 > 707-459-0474 > Lic.#C10-762093 > fut...@pacific.net > > O

[RE-wrenches] Dark Starting Simpliphi PHI3.5 batteries

2022-07-27 Thread Howie Michaelson via RE-wrenches
one has an easier way to restart the batteries I'd love to hear it. Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* ___ List sponsored by Redwood All

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-10 Thread Howie Michaelson via RE-wrenches
We typically do not require UL listing, but that is always good for insurance reasons... *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Sun, Jul 10, 2022 at 12:53 PM Tump via RE-wrenches < re-wrenches@l

Re: [RE-wrenches] Outback Radian transfer time

2022-02-04 Thread Howie Michaelson
t the bottom end, the inverters will potentially drop the generator connection before the voltage output gets too low as the generator shuts down. Hope this helps, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004*

Re: [RE-wrenches] Radian Glitch

2022-01-16 Thread Howie Michaelson
ate is several years old, and the only way I've been able to fix the problem is to replace the mate, and then the system works fine. (Sorry to sort of hijack this thread). Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service8

Re: [RE-wrenches] Radian Glitch

2022-01-13 Thread Howie Michaelson
Thanks for the update Lines. While it seems from turning off the soc gen control, the generator is running as it should, I don't understand how that explains the charging behavior, or why the inverter continued to ruin the generator without using it's output. Howie Howie Michaelson S

[RE-wrenches] RytEnergy batteries and system

2022-01-11 Thread Howie Michaelson
Does anyone have any experience with RytEnergy? Their pricing looks well below market for reputable companies... Thanks, Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-

Re: [RE-wrenches] Aurora solar design software?

2022-01-05 Thread Howie Michaelson
, specifically Aurora or SolarEdge? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Wed, Jan 5, 2022 at 12:01 PM Rebekah Hren wrote: > Hi all, > Are there any other wrenches out there using auroraso

Re: [RE-wrenches] BP HI / Namaka with Sol-ark inverters

2022-01-05 Thread Howie Michaelson
g for the expense to be able to build up my own experience with the rapidly expanding options, and I'd rather not spend the money necessary to replace a set of Lithium batteries that don't meet expectations... Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar P

[RE-wrenches] Kilovault

2021-12-16 Thread Howie Michaelson
Hi all, Anyone have any experience with the Kilovault HLX+ 12 volt batteries? How does the paralleling and series configuration work? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-

[RE-wrenches] Weather sealing between panels

2021-12-12 Thread Howie Michaelson
amed. There must be at least several options out there given the number of carports. I have never had a call for this as the carpets and sheds I've done to date have had an integral roof that provided the weather sealing. Any products, leads, creative ideas that anyone has would be most welc

Re: [RE-wrenches] SolarEdge inverter blowing fuses

2021-11-01 Thread Howie Michaelson
best directed... Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-272-0004 On Mon, Nov 1, 2021, 6:50 PM Dave Tedeyan wrote: > The fuses are Ferraz Shawmut Trionic TR60R. 60A, 250V. I looked them up to > find that

[RE-wrenches] 600 vDC Breakers

2021-08-09 Thread Howie Michaelson
or 40 Amp - preferably - breaker as it will be in a Conext PDP). Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* ___ List sponsored by Redwood Alliance Pay o

Re: [RE-wrenches] Remote AC well pump

2021-07-26 Thread Howie Michaelson
Thanks Jerry, that is what I would certainly suggest first, but I was just curious if there is a way to drive an AC pump with just PV before I suggest pulling the pump. Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Ser

[RE-wrenches] Remote AC well pump

2021-07-26 Thread Howie Michaelson
if there are simpler ways to accomplish this. I don't know any more about the situation, but wanted to see if anyone has idea how to potentially accomplish this without so much infrastructure before I had any more conversations with them. Thanks, Howie Michaelson Sun Catcher NABCEP Certified

Re: [RE-wrenches] schneider xw-Pro issue with genny running

2021-06-29 Thread Howie Michaelson
Chris, Had your client tried running the problematic appliances using generator direct, that is avoiding the xw entirely. That will at least tell you if it is something to do with the generator output or with the interaction of the generator with the xw that is causing the problem. Howie

Re: [RE-wrenches] Surrette Rolls distributors

2021-05-29 Thread Howie Michaelson
Dave, I've been using Hartford Forklift Ron Ramsey, out of Maine. So far, happy with him. (207) 212-4769 rram...@hartfordsforklift.com Stock is limited, but he can get most of what I want usually. Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & H

Re: [RE-wrenches] DC transfer switch

2021-05-08 Thread Howie Michaelson
Kirk, Have you tried IMO (https://www.imoautomation.com/). I haven't seen any ATS units advertised, but they have a pretty extensive and reasonably priced listing of DC control equipment. Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems

Re: [RE-wrenches] Outback_Inverter firmware mismatch

2021-03-29 Thread Howie Michaelson
nding on what you are trying to do, but they are solid both electrically and programmatically from my experience. I also have so far enjoyed using Sol-Ark from my limited experience, although I have yet to use it in an off-grid environment. Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Sol

Re: [RE-wrenches] Residential tax credit

2021-03-16 Thread Howie Michaelson
The last I heard, the residential tax credit could only be rolled forward 1 year - so spread out over 2 years. But I'm not an accountant, so if anyone authoritative knows differently, I'd love to but corrected. Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Sola

Re: [RE-wrenches] Checking Specific Gravity, correct procedure.

2021-02-23 Thread Howie Michaelson
William, How much of a difference did you see in readings after an equalize charge before adding water vs. after adding water and doing a short bulk charge? Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-272-

Re: [RE-wrenches] GVFX3524 fan replacement

2021-02-14 Thread Howie Michaelson
Ron, Easier than board replacement, but you need to open the body up the same way. The fan is attached to the upper part of the housing - 4 screws and a single connection. Trick will be finding the fan, although I think lots of distributors still have it in stock. Howie Howie Michaelson Sun

Re: [RE-wrenches] Battery Specific Gravity versus Electrolyte Level

2021-02-09 Thread Howie Michaelson
William, It certainly is possible I've missed something, but I've never seen any references to not eating batteries before equalizing. If anything, there is statements saying make sure to check levels before equalizing. I'm not sure why you wouldn't bring levels up before

Re: [RE-wrenches] small handheld oscilloscopes

2021-01-24 Thread Howie Michaelson
Having never taken any formal training on using oscilloscopes, but knowing that it might be useful to use one for diagnostics, does anyone have a good resource for explaining how to use one for diagnostics of inverters/generators/grid outputs? Howie Howie Michaelson Sun Catcher NABCEP Certified

Re: [RE-wrenches] Blue planet integration

2020-12-17 Thread Howie Michaelson
Apparently the holdup is on Blue Planets part. Dave, what is the functional difference between integration through there Xanbus or through the gateway? Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-272-0004 On

Re: [RE-wrenches] Remote Alert and Bootstrapping on Sunny Island AC Coupled System

2020-12-17 Thread Howie Michaelson
x27;t shut off on Low Voltage before they do connect. As far as the Sunny Portal, I too haven't messed with it for a few years and SMA had just done a major overhaul of the sites capabilities, so I didn't really explore it. And it probably now has more capability than that upgrade aff

[RE-wrenches] Blue planet integration

2020-12-17 Thread Howie Michaelson
er this is potentially going to happen anytime soon? My clients have been waiting patiently (less so recently)... Thanks for any intel, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Servi

Re: [RE-wrenches] AEE Phones on fritz

2020-11-07 Thread Howie Michaelson
e system is on the > fritz. The IT people are working on it. > > > > > > > > Dana Orzel Great Solar Works, Inc. > > > Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Servi

[RE-wrenches] AEE Solar

2020-11-06 Thread Howie Michaelson
Does anyone know what's going on with AEE Solar? I've been trying to get in touch with anyone there and all the numbers I have used in the past as well as their published numbers get routed to Sunrun and they don't know anything. Thanks, Howie *Howie Michaelson**Sun Catcher* *N

[RE-wrenches] Aurora PVI 4.2 inverter

2020-11-03 Thread Howie Michaelson
ferent inverter? I believe it isn't required to upgrade to RSD equipment since it is just a repair. Any suggestions for a good replacement that will reasonably match the PVI's input DC voltage specs? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Sol

[RE-wrenches] Cedar Shake roofs

2020-10-20 Thread Howie Michaelson
Hi all, Does anyone have any experience mounting on a roof with cedar shakes. I'm most interested in figuring out how you can avoid breaking half the roof apart and still get trail and panels mounted and wired. Thanks for any ideas, Howie Howie Michaelson Sun Catcher NABCEP Certified Sol

[RE-wrenches] Schletter racking

2020-10-16 Thread Howie Michaelson
to go along with the posts. Alternatively, does anyone know of other racking that will work with the schletter post profiles. If nothing can be found, they will have to cut them down and start over. So much for proactively planning ahead... Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified

Re: [RE-wrenches] Optics RE

2020-10-14 Thread Howie Michaelson
Kirk, was that Hughes net that wouldn't recognize the mate? Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-272-0004 On Wed, Oct 14, 2020, 12:23 PM Kirk Herander, VSE wrote: > I have a site with sa

Re: [RE-wrenches] Optics RE

2020-10-12 Thread Howie Michaelson
ernet access. Thanks again, Howie Howie Michaelson Sun Catcher NABCEP Certified Solar PV Installer™ Solar Electric & Heat Pumps Systems Sales & Service 802-272-0004 On Mon, Oct 12, 2020, 7:56 PM Dan Fink wrote: > Howie; I'm pretty satisfied with the current condition of the Opti

[RE-wrenches] Optics RE

2020-10-12 Thread Howie Michaelson
led about putting in systems that need too much fussing or attention to keep operating once they are set up properly. Finally, are there any other comparable monitoring equipment that would work for monitoring such systems? Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV

Re: [RE-wrenches] Disconnects for "ungrounded" arrays

2020-10-08 Thread Howie Michaelson
Chris, This seems to be the feedback I am getting. I guess I daydreamed that change. Thanks, Howie *Howie Michaelson**Sun Catcher* *NABCEP Certified Solar PV Installer™* *Solar Electric Systems Sales & Service802-272-0004* On Thu, Oct 8, 2020 at 6:12 PM Chris Sparadeo wrote: > H