You could probably SELL that. People have asked me if it's possible to jam
smart meter communications.
Seriously, though, isn't there some FCC rule about devices accepting
interference from other devices as part of their approval? Maybe smart
meters would be covered under that.
Jason Szumlanski
I have one system out there with a Mitsu mini-split unit on four VFX3648
inverters, and no reported issues.
Jason Szumlanski
Fafco Solar
Jason Szumlanski
On Tue, Oct 21, 2014 at 10:54 AM, d...@foxfire-energy.com wrote:
Anyone else had issues with Mitsubishi Mini Split heat pumps fighting
a thriving and profitable service department, but until
consumer expectations are brought back to reality, its not fun work.
Jason Szumlanski
On Thu, Oct 16, 2014 at 3:40 PM, Steve McCarney stevemccarne...@gmail.com
wrote:
Warranty-related service calls and related issues are compounded for off
they install. We have been picking up service business as a
result (we have a reputation for doing so and manufacturers call us), but
it's still not steady enough to handle well.
Jason Szumlanski
On Oct 15, 2014 4:41 PM, Rebecca Lundberg
rebecca.lundb...@powerfullygreen.com wrote:
We are starting
people, but ultimately solar is a tiny sliver of what they do.
Jason Szumlanski
On Thu, Oct 9, 2014 at 2:23 PM, penobscotso...@midmaine.com wrote:
Does anyone have a number for Schneider's solar tech support? It seems
impossible to reach people there with a direct question, without having
about other trades engaging in these tiny PV systems that range from
5-40W.
Jason Szumlanski
Fafco Solar
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address settings:
http://lists.re
Array. In fact, in the text an Array is defined as components forming a
direct-current power-producing unit. In a microinverter-based system, how
can any group of modules be considered an array given that definition?
Jason Szumlanski
Fafco Solar
___
List
are mounted.
Jason Szumlanski
Fafco Solar
On Mon, Sep 29, 2014 at 2:19 PM, Ray Walters r...@solarray.com wrote:
Definitely could use some clarification. The 690 definition of an array
says mechanically integrated, which sort of implies each roof plane is
its own array.
However in terms
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski
*Sent:* Monday, September 29, 2014 11:54 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] PV Array Definition and 690.47(D) (2008)
We are 100% on the same page. That is the technique we use and the
argument I
of Florida downpours and found no issues.
Jason Szumlanski
Fafco Solar
On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch solar1onl...@charter.net
wrote:
Bruce, August, et al,
This is but one more example of confusing terminology. A plumbing vent is
not an exhaust vent!
A plumbing vent (what
always get into the attic right from the j-box location. I think I'd use
the QuickMount solution if we had to do this.
Jason Szumlanski
Fafco Solar
On Mon, Sep 22, 2014 at 7:57 PM, Chris Mason cometenergysyst...@gmail.com
wrote:
In a hurricane region, we can't use glued supports.
Caddy supports
Just got this from Zilla. This might be just what you are looking for...
https://www.zillarac.com/Store/Product-Details/ProductID/25.aspx
On Tue, Sep 16, 2014 at 9:32 AM, Will White william.wh...@rgsenergy.com
wrote:
We've used Ecofasten ECO-65 successfully on both SIP roofs and membrane
ultimate design wind speed (ASCE 7-10). Because of the number of fasteners
per attachment point, even OSB should provide enough pull-out strength to
meet your engineering requirements.
http://www.ecofastensolar.com/store/pc/viewCategories.asp?idCategory=10
Jason Szumlanski
Fafco Solar
, as
there seems to be evidence that a higher module rating/inverter rating
ratio results in more energy harvest, presumably in part due to inverter
efficiency increasing as the input power increases. That's why I have been
reluctant to put 250-265W modules on the M250.
Jason Szumlanski
Fafco Solar
Enphase's is similarly flat. I guess it's really a
non-issue other than very low light situations.
[image: Inline image 1]
Jason Szumlanski
Fafco Solar
On Tue, Aug 26, 2014 at 2:10 AM, Marco Mangelsdorf ma...@pvthawaii.com
wrote:
Look, guys, what’s beyond dispute is that
when we size
on many contracts in the
area, selling installed systems below our material costs, and even beating
us on a large government contract.
Ugh. How do you explain to a homeowner that they now have 5kw worth of
fancy shingle protectors on their roof?
Jason Szumlanski
Fafco Solar
On Mon, Jun 30
, and how do inverter manufacturers determine the
recommended and/or maximum rating of the connected module or array? Also,
why do some manufacturers have a simple recommendation while others have a
maximum rating?
Jason Szumlanski
Fafco Solar
___
List
Does anyone know if the HiS-S265MG and HiS-S270MG modules are FSEC
approved? The FSEC website only lists models up to 255 watts. I'm hoping
it's just not up to date.
Jason Szumlanski
Fafco Solar
___
List sponsored by Redwood Alliance
List
It's been a solid brand for us for a few years. Soligent and Affordable
Solar stock them, although supplies are a bit tight and the prices are
creeping back up.
Jason Szumlanski
Fafco Solar
On Fri, Jul 11, 2014 at 2:52 PM, Kristopher Schmid sol...@legacysolar.com
wrote:
Hi All,
I have
going to guess your 3/4HP well pump will be a breeze to start with this
inverter.
Jason Szumlanski
Fafco Solar
On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar al...@sindelarsolar.com
wrote:
Drake,
As a normal CYA, I'll always gently let a customer know that this (or any)
particular
the
limitations and possibilities, you may be just fine.
Jason Szumlanski
Fafco Solar
On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski ja...@fafcosolar.com
wrote:
For what it's worth, I've run a single speed 1.5HP pool pump with a
MS4448PAE in a mobile application on a 38.4kWh battery bank (sixteen
that.
Jason Szumlanski
Fafco Solar
On Wed, Jul 2, 2014 at 2:35 PM, Roy Butler r...@four-winds-energy.com
wrote:
I haven't seen anyone mention the battery bank. If I understand
correctly, there's a single string of sealed
L16 batteries on this inverter. I have my doubts as to whether
Sorry, typo - that's a 48V string (one string of 8 batteries).
Jason Szumlanski
Fafco Solar
On Wed, Jul 2, 2014 at 3:15 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:
Even at 9600W, which is above the 5 second surge rating of the inverter,
we're looking at about 200A on the DC side
for the
utility to turn off the PV system. I didn't go into the fact that they
don't require utility externally accessible disconnects anymore for Tier 1
interconnections. I don't need him to understand... just to allow. :)
Jason Szumlanski
Fafco Solar
On Fri, Jun 27, 2014 at 8:44 AM, Jason
systems in 2011, whereas 690.64(B)(1)-(7) in 2008 clearly applied to
load-side connections only.
Are you saying 705.12(D)(1)-(7) in 2011 apply to load-side connections
only? That's not the way I interpret it.
Jason Szumlanski
Fafco Solar
On Fri, Jun 27, 2014 at 8:12 PM, Bill Brooks
our first service call is going to be the first of many in our area. We're
implementing a policy that we won't work on the inverters if the system has
the fraudulent UL labels on the PV panels. That should be interesting...
Jason Szumlanski
Fafco Solar
out that dual
200A load panels are commonly fed this way and this was no different
because I could just backfeed each 200A panel with two 20A breakers, my
comment was met with blank stares.
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 6:11 PM, Corey Shalanski
cshalan...@joule
(i.e. 15A center and 20A outer breakers). They are not readily
stocked and not cheap. We stuck with Sq D QO load centers for that reason.
Am I missing something?
Jason Szumlanski
Fafco Solar
On Fri, Jun 27, 2014 at 11:32 AM, Dave Click davecl...@fsec.ucf.edu wrote
of a dedicated enclosure. There would be some material and labor
savings.
If the inverter has a maximum OCPD rating, you will be limited by that.
Microinverters get around that by the wire and inverter being
sized/rated for the entire maximum string.
Jason Szumlanski
Fafco Solar
On Wed, Jun 25
I use this site when I need a quick answer. Use RHH (covered) with one
conductor. You get the same answer.
http://www.electrician2.com/calculators/rf_calculator.html
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 1:46 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:
0.0437435 per
Yeah, 1k/2k wire shows a diameter of 0.26 on the spec sheet, or 0.053093
in^2.
Jason Szumlanski
Fafco Solar
On Thu, Jun 26, 2014 at 2:06 PM, Kirk k...@vtsolar.com wrote:
Nice calculator. RHH may be equivalent to 600 volt pv wire, but 1k/2k pv
wire is thicker.
Kirk Herander
VSE
What about an Ideal Push-In Model 39 dipped in liquid electrical tape? You
can see through the case to ensure the wire is pushed all the way in, and
it accepts stranded and solid wire. The cases are rated to 105C and they
are UL 467. We use these for AC wiring sometimes, but mostly inside pool
,
gables, etc. It even does dutch gables and other less-common roof features.
Often you have to do dormers as a separate roof. No big deal... I did my
video on a home with to distinct roof sections that came together into one.
Jason Szumlanski
Fafco Solar
On Thu, Jun 19, 2014 at 10:02 AM
number of modules and arrive to find out you can only fit x?
William
[image: Gradient Cap_mini]
Lic 773985
millersolar.com http://www.millersolar.com/
805-438-5600
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski
*Sent
Any known source of 230V 50Hz micros in the US?
Jason Szumlanski
Fafco Solar
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address settings:
http://lists.re-wrenches.org/options.cgi/re
off list and I'll email you an actual presentation packet.
https://drive.google.com/a/fafcosolar.com/file/d/0B-Kt4aH7U2BWOXJhRXRoSV82SFE/edit?usp=sharing
Jason Szumlanski
Fafco Solar
On Tue, Jun 17, 2014 at 2:54 PM, August Goers aug...@luminalt.com wrote:
Hi Wrenches,
We are finding
Hybrid rendering in Layout give you
terrific results.
Jason Szumlanski
Fafco Solar
On Tue, Jun 17, 2014 at 3:52 PM, Daniel Young dyo...@dovetailsolar.com
wrote:
We also use Sketchup pro. If you take some time and create highly detailed
templates for your commonly used equipment, then putting
presentations!
Jason Szumlanski
Fafco Solar
On Tue, Jun 17, 2014 at 4:07 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:
To answer August's question regarding plugins, and as a recommendation to
Daniel - you MUST use the Instant Roof plugin by Chuck Vali. It went
subscription based this year
with a safety factor, that would be good for 12 sq ft at 50 spf
uplift per attachment. 250 fasteners would be good for about 5kW of solar.
Jason Szumlanski
Fafco Solar
On Tue, Jun 3, 2014 at 9:06 AM, Dave Click davecl...@fsec.ucf.edu wrote:
Hi all,
Anyone know what this racking system
of
attachments required, and we often exceed their minimum requirement.
Ultimately there may be some significant installation cost advantages to
reducing the need to locate and hit trusses, so exploring this method and
materials as an industry is worth the effort.
Jason Szumlanski
Fafco Solar
, but for
a 10kW system you have to do a supply side connection anyway on as typical
200A service, so combining strings somewhere is necessary, and a single run
from the roof makes sense in many cases.
Jason Szumlanski
Fafco Solar
On Tue, Apr 29, 2014 at 6:40 PM, jay peltz j...@asis.com wrote
failures. There is a reason we keep a good supply of 1A, 15A,
and 20A Littlefuses in a drawer here.
Jason Szumlanski
On Wed, Apr 30, 2014 at 9:56 AM, Drake drake.chamber...@redwoodalliance.org
wrote:
There are good reasons to want to put AC combiners under modules, but
some reasons
€‹ There is a reason we keep a good supply of 1A,
15A, and 20A Littlefuses in a drawer here.
Jason Szumlanski
Â
On Wed, Apr 30, 2014 at 9:56 AM, Drake drake.chamber...@redwoodalliance.org
wrote:
There are good reasons to want to put AC combiners under modules, but
some reasons not to want to.
â
about the screws on the SolaDeck cover itself
requiring a tool to render it accessible is still an issue if the breakers
themselves need to be readily accessible, but that would also apply to a
Midnite MNPV, which also has a cover with a screw.
Jason Szumlanski
On 4/28/2014 5:57 PM, Bill Brooks
inverter
output circuits? Very infrequently in my experience. I think it's good
practice to keep a SolaDeck AC output circuit combiner box out of the
blazing Florida sun, plus it looks a heck of a lot better. I did it at my
home, and I'm happy I did so.
Jason
Szumlanski
On Mon, Apr 28, 2014 at 5
Not just microinverters. This could apply to multiple string inverters with
combined output in a suitable panel under a module. That scenario is
probably rare, but I have seen it on a commercial flat/low-pitched roof
installation.
Jason Szumlanski
On Tue, Apr 29, 2014 at 12:43 PM, Bill Hoffer
, Jason Szumlanski
lt;a href=mailto:ja...@fafcosolar.com;
target=_blankja...@fafcosolar.com/agt;
wrote:br
/divdl
ddWhile the interior of a raceway in a wet location is considered a wet
location, the interior of a NEMA 3R enclosure is not.. The breakers need
not be listed for use in wet locations
I heard Canadian Solar prices are on the rise, and supply will be tight
and uncertain. Korean made panels were recommended as an alternative.
Jason Szumlanski
Fafco Solar
On Fri, Apr 25, 2014 at 8:42 AM, William Dorsett wmdors...@sbcglobal.netwrote:
I was recently told by a distributor
If NEMA 3R works, you can also consider a Soladeck combiner on pitched
roofs. They make one for combining up to three microinverter circuits on
the roof, and include circuit protection via DIN rail mounted breakers.
Jason Szumlanski
Fafco Solar
On Wed, Apr 23, 2014 at 11:11 AM, Drake
-sealant-detail.html
Jason Szumlanski
Fafco Solar
On Sat, Apr 12, 2014 at 8:56 AM, Tom Lane t...@ecs-solar.com wrote:
I am only going to refer to primarily to asphalt shingles . PLEASE read
the label on the sealant you are using . Our company has used flexible
polymer rubber - based sealants
I need one, too - same model! Contact me off-list.
Jason
On Tue, Apr 15, 2014 at 5:59 PM, Paul Lyons ly...@zapotecenergy.com wrote:
Hello Re-Wrenches –
Does anyone know where I can purchase a single Evergreen Solar module,
ES-195 Watt?
If yes, please contact me off the list.
flexible than overpriced and overly complicated Autocad. Autocad
light woudl be my first choice, no way you need the full blown version.
Bill
On Wed, Mar 12, 2014 at 4:16 PM, Jason Szumlanski ja...@fafcosolar.comwrote:
Unless there is a compelling reason to use AutoCAD, like interoperability
LT route.
Jason Szumlanski
On Wed, Mar 12, 2014 at 10:37 PM, August Goers aug...@luminalt.com wrote:
Hi William,
We use AutoCAD and AutoCAD LT in our office. Although Sketchup is pretty
awesome for the reasons others have already mentioned, it really doesn't
compare to AutoCAD for heavy
Don't utter the word tap. :)
See:
http://www.soligent.net/documents/HappyLandings_v3.pdf
We usually specify a fusible disconnect for overcurrent protection when
grouping the PV AC combiner with the main premises disconnect is not
practical.
Jason Szumlanski
Fafco Solar
On Wed, Mar 12
The D222NRB General Duty safety switch is service rated. Why do you say it
has to be heavy-duty?
Jason Szumlanski
Fafco Solar
On Wed, Mar 12, 2014 at 5:32 PM, Brian Teitelbaum
bteitelb...@aeesolar.comwrote:
One big omission, in the otherwise fine Soligent white paper, is that the
60A
no time. Note:
Instant Roof, a necessary plugin for roof modeling, has not been updated
for Sketchup 2014, so download 2013 for now. The author is working on it.
Jason Szumlanski
Fafco Solar
On Wed, Mar 12, 2014 at 7:09 PM, William Miller will...@millersolar.comwrote:
Friends:
The 3D CAD
Not that I have an answer for you, but I'm curious, too. You need to
specify voltage to get a good answer.
Jason Szumlanski
Fafco Solar
On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:
Hi wrenches,
I am consulting on a job that requires an 8000 Ahr battery bank
the archives for:
sizing a sub-panel used to combinemultipleinverter outputs
(there are several prior discussions on the subject)
Jason Szumlanski
Fafco Solar
On Wed, Mar 5, 2014 at 10:30 AM, Dave Click davecl...@fsec.ucf.edu wrote:
I think there's plenty of room to interpret the 2008 and 2011 NEC
locate your subpanel adjacent to the main distribution panel,
you may be able to use Exception #3 to 310.15(B)(2) by connecting the
panels with a short nipple. I assume you are just looking at a number of
conductor derate and not an ambient temperature derate.
Jason Szumlanski
Fafco Solar
On Tue
Solar Engineering
NABCEPTM Certified Inaugural Certificant
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202
*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
*Sent:* Tuesday
close our answers are.
Jason Szumlanski
Fafco Solar
On Sun, Feb 16, 2014 at 5:11 PM, Mac Lewis maclew...@gmail.com wrote:
I second Chris's suggestion of Sketchup. Its very easy to use and does a
great job modeling stuff like this. There is a free version from Google
that is more than
refrigeration, but charging computers and
portable electronics works great.
Jason Szumlanski
Fafco Solar
On Thu, Feb 6, 2014 at 11:38 PM, All Solar, Inc. allso...@scswifi.netwrote:
Wrenches
I did a quick search with no luck on, I believe an SMA product that
provides minimal backup
or
parallel connected two-string SunPower systems that should have 20A fuses
per NEC 690.8. The problem does seem to be worse where inverters are
exposed to direct sunlight, presumably from fuses that no longer meet their
ampacity rating due to heat.
Anyone else run into this frequently?
Jason
That's good to know. My service call today was a 1-2 year old SunPower
branded SMA SPR-5000m. There was one blown 15A fuse in input 1 and one
spare 15A in input 4.
Jason Szumlanski
Fafco Solar
On Thu, Feb 6, 2014 at 12:56 PM, Glenn Burt glenn.b...@glbcc.com wrote:
read that SMA has changed
/downloads/documents/integrated_battery_rack/integrated_battery_rack_installation_manual.pdf
Jason Szumlanski
On Thu, Feb 6, 2014 at 6:06 PM, Allan Sindelar
al...@positiveenergysolar.com wrote:
Dave,
I'm not really clear what your question is, but let me take a stab at it
anyway.
Parallel
, but now we're back on the Unirac bandwagon.
Interesting times...
Jason Szumlanski
Fafco Solar
On Wed, Feb 5, 2014 at 12:45 PM, Max Balchowsky m...@seesolar.com wrote:
We have been using Snap N' Rack for a while, Have lots of installs in
Hawaii - so far no problems, I like the convenience
manufacturer, but looking at
the big picture I have to consider with whom I'm getting into bed. These
acquisitions are worrisome in that respect.
Jason Szumlanski
Fafco Solar
On Wed, Feb 5, 2014 at 3:27 PM, Ray Walters r...@solarray.com wrote:
Good point, Jason.
I like Snap N Rack's products
it to install a PV system. The good
news is that it should be easy enough to remove the Generlink transfer
switch and provide an inlet for the second AC input on the Radian. The
downside is the homeowner will have to carve out critical loads and can no
longer run any circuit on generator power.
Jason
That worked. The number published in the CDD manual is NOT correct. Thanks!
Jason Szumlanski
On Thu, Jan 30, 2014 at 3:07 PM, August Goers aug...@luminalt.com wrote:
Jason,
We've been able to get a hold of tech support at 877.261.1374 which I
think is the normal number they have
Does anyone know how to get Power-one technical support to call you back about
an Aurora microinverter activation issue? Their technical support line goes
straight to voicemail.
I'm not impressed at all by the activation process.
Jason Szumlanski
—
Jason
agencies. I always do custom design since every job has different
parameters like days of autonomy or remote monitoring/control (SCADA).
Larry Crutcher
On Jan 20, 2014, at 1:17 PM, Jason Szumlanski ja...@fafcosolar.com
wrote:
What do you do for very small off-grid systems that people
to become contractually bound to supply or store a certain amount of
energy. Performance guarantees are tough, especially when you are not the
operator.
Jason Szumlanski
Fafco Solar
On Tue, Jan 21, 2014 at 12:26 PM, Dan Fink danbo...@gmail.com wrote:
I also see lots of load creep Rayoh, forgot
not economical to reinvent the wheel every time.
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches
% of the
customer's service capacity, without regard for the energy consumption, but
doesn't clarify if the utility is obligated to upgrade service capacity
upon request.
They've dug their heels in, and now it's David vs. Goliath. (David did win
that one, right?)
Jason Szumlanski
Fafco Solar
What commonly available MPPT controllers have a user configurable current
output limit? (other than Outback FM##)
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email
3, 2014 at 3:51 PM, Bob-O Schultze bo...@electronconnection.com
wrote:
Midnite Solar has that capability as well. IMO, it's a better CC than the
OB FMs.
Bob-O
On Jan 3, 2014, at 11:37 AM, Jason Szumlanski wrote:
What commonly available MPPT controllers have a user configurable current
job with 300W
72-cell modules.
Jason Szumlanski
Fafco Solar
On Wed, Dec 11, 2013 at 2:38 PM, William Miller will...@millersolar.comwrote:
Roland:
I haven’t used the product but I priced it for one job. I recommend you
verify your expense for AC interconnection cables. You might have
to listen with great interest...
Jason Szumlanski
Fafco Solar
On Mon, Dec 9, 2013 at 9:21 AM, Richard L Ratico
richard.l.rat...@valley.net wrote:
Mr. Holt explicitly stated his desire to create a groundswell of opinion to
immediately eliminate this requirement of the code. Would
...
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re
that
affects warranty. I've seen others with the boot squashed down, but that
pools up water in the boot.
http://www.firestonebpe.com/en/roofing/ultraply-tpo/products/ultraply-tpo-accessories/flashings
Jason Szumlanski
On Tue, Nov 26, 2013 at 12:05 PM, Carl Adams swingjun...@gmail.com wrote:
Don
Speaking of wire management with Enphase, has anyone gone through the
effort and expense of cutting module DC leads and installing new MC4
connectors on wires that are just long enough? I'm assuming this voids
module warranties, but I've never looked close enough to confirm.
Jason Szumlanski
insulation
and into a 24ga metal roof. I'm not sure how the pull out of OSB would
change the calculations, but our spacing was 48 inches here with 160 mph
design wind speeds in Zone 1.
Jason Szumlanski
Fafco Solar
On Mon, Nov 25, 2013 at 3:58 PM, Carl Adams swingjun...@gmail.com wrote:
Hello
, and we are
far from standardization and an accepted set of best practices.
Jason Szumlanski
Fafco Solar
On Thu, Nov 14, 2013 at 1:03 PM, Kirpal Khalsa solarwo...@gmail.com wrote:
Augustthank youyou are right they are actually a Heyco
productmy bad!!! Ray, we recently got them thru
Anyone know a supplier/manufacturer of the T-bolts that come with Unirac
mid-clamps?
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re
I had a customer and a potential customer bring this to my attention. Bad
press and misinformation in this industry is rampant.
Jason Szumlanski
Fafco Solar
On Mon, Nov 11, 2013 at 1:09 PM, William Miller will...@millersolar.comwrote:
Friends:
This was brought to my attention:
http
of a
pallet with no apparent external damage to the frames or packaging. Did
that happen at the factory? On the boat? At the distributor? On the
truck(s)? On my forklift?
Jason Szumlanski
Fafco Solar
On Mon, Nov 4, 2013 at 11:47 AM, Luke Christy sgsrenewab...@gmail.comwrote:
Wrenches,
We have been
may disagree with this
approach, but we have never had to use one.
Jason Szumlanski
Fafco Solar
On Wed, Oct 16, 2013 at 8:14 PM, August Goers aug...@luminalt.com wrote:
Hi Mark,
We have lots of Enphase installed on all sorts of home. The most sure fire
way of getting communication
is coming from solar, as the tank has
the thermostat from the grid side as well.
It's a solution still looking for a problem.
Jay
Peltz power
On Oct 3, 2013, at 1:13 PM, Jason Szumlanski ja...@fafcosolar.com wrote:
Anyone else getting inundated with SunBandit Hybrid Solar Water Heating
, is cheaper than a load
controller.
Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
romex rather than EMT?
On 2013/10/3 16:13, Jason Szumlanski wrote:
Anyone else getting inundated with SunBandit Hybrid Solar Water Heating
System marketing emails? Any first impressions? Here are my initial
thoughts:
Pros - provides hot water in utility outages, no interconnection
hassles
.
Come to think of it... that really applies more to 240Vac service. 3-pole
breakers and panels are more pricey.
Jason
Szumlanski
Fafco Solar
On Thu, Oct 3, 2013 at 3:53 PM, Holt Kelly hol...@sbcglobal.net wrote:
Be sure to read Enphase’s tech sheet on center tap of branch circuits
on the outside of a building on the north side. That one works
fine. I observed the fault in the morning during 80 degree ambient temps.
And pointers would be appreciated. All the manual says is Contact Satcon
Service.
Jason Szumlanski
Fafco Solar
On Thu, Sep 26, 2013 at 7:48 PM, Glenn Burt
yeah - forgetting the special Zep tool on a service call is no fun.
Jason Szumlanski
Fafco Solar
On Mon, Sep 16, 2013 at 3:02 PM, Andrew Truitt atru...@gmail.com wrote:
Zep Solar has a nice product for sloped roofs, particularly asphalt
shingle. They have 15 or so module manufacturers
http://ironridge.com/ig
Any first impressions on this new product?
WEEBs require replacement after modules are removed for service. I wonder
of the IronRidge mid-clamps biting into the same module frame locations
after service have been tested and approved. Moving the module to bite into
new
o: 415.641.4000
m: 415.559.1525
*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
*Sent:* Tuesday, September 10, 2013 1:27 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Flat Roof PV Attachments
Let me start be saying that I'm talking about mechanically attached
tilt-mount solutions capable of handling 172 mph design wind speed, ASCE
7-10. Ballasted systems need not apply.
We've used a variety of hardware for TPO membrane flat roofs, which is
becoming more and more popular around here.
, they may not be cut out for battery backup living.
Jason Szumlanski
Fafco Solar
On Mon, Aug 19, 2013 at 8:19 PM, William Miller will...@millersolar.comwrote:
**
Friends:
I wrote a draft white paper to discuss the issues relevant to PV Assist
systems. If you are up for along
relative to the battery and the PV production is
variable (think air conditioning).
I'll watch this discussion with interest...
Jason Szumlanski
Fafco Solar
On Fri, Aug 16, 2013 at 1:53 PM, William Miller will...@millersolar.comwrote:
**
Friends:
We have been receiving a flurry of requests
Are they missing the fact that the inverters used for battery backup RE
applications are also high output sophisticated battery chargers and
transfer switches all built into one integrated unit intended to work
together with available monitoring and coordination with charge controllers?
I
interested if anyone has any low power consumption ideas.
Jason Szumlanski
Fafco Solar
On Tue, Aug 6, 2013 at 7:41 PM, Mick Abraham m...@abrahamsolar.com wrote:
Hello, all~
My client likes to watch what's going on at his remote cabin while he's
away. The problem is the energy impact on his
601 - 700 of 976 matches
Mail list logo