To my understanding the 156% on PV source and output circuits is related to the ability of PV to deliver more than rated and be continuous. Therefore, the wire has to be able to carry this current, so now the temperature and fill corrections are applied to find the wire capable of the 156%. I

[RE-wrenches] DC wire sizing

2010-04-10 Thread Kent Osterberg
Here's my challenge to all of you that want to design for 1% or 1.5% voltage drop all the time: Take a 50-ft circuit carrying 40 amps at 12 volts, going to a C40 charge controller, select your wire size for 1% or 1.5% loss. You know that's not a practical solution.  I know that it makes more se

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread Kent Osterberg
Erika, You should refer to NEC 690.8 this information.  There are two issues that contribute to the 1.56 factor.  First is that the maximum current from the PV array is considered the short circuit current multiplied by 1.25 to account for higher than standard irradiance such as cloud edge eff

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread William Miller
Eirka: Although the Imp is your normal operating condition, you need to design wire size for an abnormal occurrence (short circuit or other fault). You do not want the wire to burst in to flame after an unplanned short circuit, do you? Remember, you may have combiner fuses, but you have no o

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread Bill Brooks
olitical statement here, but if the shoe fits.). Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Erika M. Weliczko Sent: Friday, April 02, 2010 6:27 AM To: 'RE-wrenches' Subject: [RE-wrenches] DC wire sizing

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread Bill Brooks
olitical statement here, but if the shoe fits.). Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Erika M. Weliczko Sent: Friday, April 02, 2010 6:27 AM To: 'RE-wrenches' Subject: [RE-wrenches] DC wire sizing

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread robert ellison
I believe that the breakers from CBI, Midnite and Outback are hydraulic / magnetic and may be operated at 100% While the derating applies to all others that are Thermal / magnetic, Bob On Fri, Apr 2, 2010 at 11:14 AM, Kent Osterberg wrote: > Erika, > > You should refer to NEC 690.8 this informa

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread Allan Sindelar
Yes, they are 100% duty rated. Also, a little-known fact about the CBI breakers used by Midnite and Outback, gleaned from conversations with Robin Gudgel: because of this hydraulic/magnetic construction, all are capable of controlling both AC and DC, even if not listed as both.

Re: [RE-wrenches] DC wire sizing

2010-04-02 Thread Darryl Thayer
f Erika M. Weliczko Sent: Friday, April 02, 2010 6:27 AM To: 'RE-wrenches' Subject: [RE-wrenches] DC wire sizing   To my understanding the 156% on PV source and output circuits is related to the ability of PV to deliver more than rated and be continuous. Therefore, the wire has t

Re: [RE-wrenches] DC wire sizing

2010-04-03 Thread Chris Worcester
Brooks wrote: From: Bill Brooks Subject: Re: [RE-wrenches] DC wire sizing To: er...@repowersolutions.com, "'RE-wrenches'" Date: Friday, April 2, 2010, 11:14 AM Erika, The most correct answer (which is a really funny thing to say) is to use John Wiles’ “5-step program

Re: [RE-wrenches] DC wire sizing

2010-04-04 Thread R Ray Walters
And just to be clear, when using these 100% duty rated breakers, you only have to oversize the cable by 125%, not 156%. Also, as William mentioned, even correctly sized wiring can have problems; we just recently had a short circuit that caused quite some damage in a junction box, and the breake

Re: [RE-wrenches] DC wire sizing

2010-04-04 Thread Kent Osterberg
Ray, The exception in 690.8(B)(1) reads: Circuits containing an assembly, together with its overcurrent device(s), that is listed for continuous operation at 100% of its rating shall be permitted to be utilized at 100% of it rating.   The field installed cable used to connect a breaker is not

Re: [RE-wrenches] DC wire sizing

2010-04-05 Thread jay peltz
Since the topic of AFI's has come up I wonder if anyone has actually tested one, even an AC one. From what I've read from some tests on the Mike Holt site for AC breakers is that they couldn't get them to work at anything less than standard ISC for the breaker. thanks, jay peltz power On A

Re: [RE-wrenches] DC wire sizing

2010-04-05 Thread R Ray Walters
I think the 100% rating exception is an interpretation issue. I consider the assembly to be defined as the breaker mounted in its listed enclosure. I agree that the AFIs would add cost, but they might actually offer some protection too. (possibly one AFI unit could offer protection for multiple

Re: [RE-wrenches] DC wire sizing

2010-04-05 Thread William Miller
Ray: It is my analysis that combiner breakers (if present) will protect only wiring upstream of the combiner -- that is, the individual string circuits. This protection would happen if there is a fault in one individual string (in the wiring or the modules) that allows current from other str

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread robert ellison
I have seen info from independent tests that convinces me that AFCI's probably don't work for AC and i hate to think what they would do for DC, if anything. Besides drive the costs up. This was a few years ago and maybe they have gotten it together by now. Anyone remember the original ground fault

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread R Ray Walters
I agree that we don't want to create the code first, and try and develop the product after. On the other hand, if a DC AFI can be developed that could stop some of the problems I've seen breakers not help, I'm installing them, and pushing for code requirements. AC GFIs were gimmicky too at first

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread Kent Osterberg
Ray, Considering that we design PV wiring to be efficient with voltage (and power) loss typically less than 2%, the wire size is nearly irrelevant to arcing issues.   Essentially all the energy available from the PV array can be dissipated in the dc arc.   And since the current is limited by t

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread R Ray Walters
Once I have fulfilled NEC min. requirements, I use a spreadsheet to analyze the cost of larger wire vs. the cost of power lost. Going under 2% is usually not worth it, if copper prices are high, and PV cost is low enough (current market). Sizing for under 2% was good economics a few years back,

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread Bob-O Schultze
Ray, A 2% wire loss is the generally accepted metric for battery based systems with relatively low PV voltage input (<150Voc). It's just plain bad design to accept more than a 1% VD on higher voltage systems. PVs ain't THAT cheap. Best, Bob-O On Apr 6, 2010, at 11:44 AM, R Ray Walters wrote: O

Re: [RE-wrenches] DC wire sizing

2010-04-06 Thread R Ray Walters
Just run the numbers sometime. Compare the cost difference of #6 vs. #4 wire say, and then look at how many more watts you're actually saving, then multiply that additional wattage by the installed cost per watt. Very simply, once you've satisfied code requirements, there is a point at which it

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread Brian Crise
Kent, One of the things to take a look at and to make sure that your inspector is aware of is the last paragraph of Section 90.4. This was brought up at the last code meeting to allow new products to come on- line and to implement new technology into the market. Due to the timeliness of c

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread Bob-O Schultze
Ray, Sorry, I'm not buying that argument over a 25+ year design lifespan. Also, -and perhaps something many folks don't consider- the NEC requires a MAX loss of ≤5% over the ENTIRE circuit. That means all the way to the mains panel. Best practices would require no more than 1.5% VD between the i

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread August Goers
Subject: Re: [RE-wrenches] DC wire sizing Ray, Sorry, I'm not buying that argument over a 25+ year design lifespan. Also, -and perhaps something many folks don't consider- the NEC requires a MAX loss of ≤5% over the ENTIRE circuit. That means all the way to the mains panel. Best pract

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread R Ray Walters
ssage- > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob-O Schultze > Sent: Wednesday, April 07, 2010 1:51 PM > To: RE-wrenches > Subject: Re: [RE-wrenches] DC wire sizing > > Ray, > Sorry, I'm not b

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread Joel Davidson
tomer explicitly states that he wants more loss. Joel Davidson - Original Message - From: "Bob-O Schultze" To: "RE-wrenches" Sent: Wednesday, April 07, 2010 1:50 PM Subject: Re: [RE-wrenches] DC wire sizing Ray, Sorry, I'm not buying that argument over a 2

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread R Ray Walters
inverter and the grid and > less than 2% overall wire loss unless the customer explicitly states that he > wants more loss. > Joel Davidson > > - Original Message - From: "Bob-O Schultze" > > To: "RE-wrenches" > Sent: Wednesday, April 07, 20

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread Kent Osterberg
Schultze Sent: Wednesday, April 07, 2010 1:51 PM To: RE-wrenches Subject: Re: [RE-wrenches] DC wire sizing Ray, Sorry, I'm not buying that argument over a 25+ year design lifespan. Also, -and perhaps something many folks don't consider- the NEC requires a MAX loss of ≤5% over the ENTIRE cir

Re: [RE-wrenches] DC wire sizing

2010-04-07 Thread Nick Soleil
a, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax:707-769-9037 From: Kent Osterberg To: RE-wrenches Sent: Wed, April 7, 2010 7:10:58 PM Subject: Re: [RE-wrenches] DC wire sizing August, Thanks for remembering which SolarPro had that article.

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread Kent Osterberg
expensive.)   Nick Soleil Project Manager Advanced Alternative Energy Solutions, LLC PO Box 657 Petaluma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax: 707-769-9037 From: Kent Osterberg To: RE-wrenches Sent: Wed, April 7, 2010 7:10:58 PM Subject: Re: [RE-wren

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread Bob-O Schultze
Guys, Is it just me being dense or are none of you folks advocating for higher VD looking at the savings over time? If we assume that Kent's wire costs are correct (and even assuming a 33% mark-up, he's paying WAY, WAY too much for wire) , the difference in delivered watts between #10 and # 4 wi

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread Kent Osterberg
Bob-O Your calculation of the savings proves the point.  Going from 10 AWG to 4 AWG costs $2780 today and saves $375 over the next 25 years.  Now think about how much it would cost to put in 91 watts more PV; that'll save $375 over the next 25 years too. Granted the published wire prices are

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread Bob-O Schultze
Kent, In fact, assuming a 33% wire mark-up and the kind of wire pricing that we Wrenches generally get (I got quotes today), the difference between #10 and #4 is $0.90/ft or $900/M which is how your scenario plays out. You say that just adding more PV will cover it. I beg to differ. You installi

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread dave
ject: Re: [RE-wrenches] DC wire sizing ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread Kent Osterberg
Bob-O I just re-opened the spreadsheet that I used to make my example; the spread sheet was using 330 volts not 350 volts for the voltage drop calculation.  That error doesn't change the example in any material way. No, I haven't got any 91-watt PV modules these days.  But you might get 91 wa

Re: [RE-wrenches] DC wire sizing

2010-04-08 Thread R Ray Walters
Over the same amount of time a similar investment in PV would save even more money. R. Walters r...@solarray.com Solar Engineer On Apr 8, 2010, at 4:28 PM, Bob-O Schultze wrote: > Guys, > Is it just me being dense or are none of you folks advocating for higher VD > looking at the savings ov

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread Richard L Ratico
IMHO it seems like we're all really on the same page here.. trying to make the the most out of the the resources we have available to work with..sun hours, pv, copper, labor, dollars, etc. Job specifics come into play. There are definitely times when a detailed cost/ benefit analysis is cal

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread William Miller
Friends: Forgive me if this point has already been made: When designing PV feeders, one typically looks at the Impp of an array for current specifications. Impp is rarely achieved, however -- only a handful of days per year and for only a short period of time per day. This is particularly

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread R Ray Walters
Also consider that most people are figuring volt drop at a wire temperature of 167 deg F (75C). That's really hot, and most of the time the wire will be much cooler, and therefore the volt drop will be less. (use the fine print note #2, NEC table 8 to adjust down for cooler temperature) William's

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread Bill Hoffer
Ray I think that the point is not the cost, but what is good electrical design! Voltage Drop in a wire is still undesirable and equates to an unneeded "heat" load on the wire. Are we advocating that if your water pipe is too small just increase the pressure so you get the same output you desired

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread R Ray Walters
All our economic analysis is based on a 20 to 25 year life. Safety first, but then good design is to spend the customer's money where it does the most good. No matter how big the wire, you will always have losses. It is an exponential curve that never reaches zero. It just costs more and more

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread toddcory
Has anyone included the extra racking costs to add additional modules used to compensate for wire loss? Todd On Friday, April 9, 2010 10:46am, "R Ray Walters" said: All our economic analysis is based on a 20 to 25 year life. Safety first, but then good design is to spend the customer's mon

Re: [RE-wrenches] DC wire sizing

2010-04-09 Thread R Ray Walters
I figure the PV cost at the total installed cost per watt (module, rack, labor) R. Walters r...@solarray.com Solar Engineer On Apr 9, 2010, at 12:55 PM, toddc...@finestplanet.com wrote: > Has anyone included the extra racking costs to add additional modules used to > compensate for wire loss

Re: [RE-wrenches] DC wire sizing

2010-04-10 Thread Kent Osterberg
Bill, The NEC is a minimum design design standard, but voltage drops are not part of the code.  The spots where voltage drop is discussed in the NEC are fine print notes that are not code and are not enforceable as code.  Furthermore those notes were written without any consideration of the ra

Re: [RE-wrenches] DC wire sizing

2010-04-10 Thread Bob-O Schultze
Of course it's not a practical solution, which is why we strived for (but rarely got) 2% VD on low voltage situations as I said in my first post. The obvious reply to this post is that your scenario isn't real world anymore. MPPT controllers fixed that. Or perhaps you advocate that MPPT controll

Re: [RE-wrenches] DC wire sizing

2010-04-11 Thread Kent Osterberg
Bob-O, I neither subscribe to the notation that cheaper is better nor the notion that more expensive is better.  Adding more wire until 1%, or any other arbitrary percent loss figure is attained, does not necessarily make a project better.  It will make the project more efficient to increase t

[RE-wrenches] DC wire sizing perspective

2010-04-11 Thread Dana
One small point and well acknowledged on this issue is that we are starting with a product that only produces at 14-18% [up to19%] efficiencies to begin with. A 5%loss is to an average of 16% efficiencies as 31.25% loss is to100% efficiency. Till PV modules hit 50-75% efficiency in convers

Re: [RE-wrenches] DC wire sizing

2010-04-12 Thread Warren Lauzon
ches Sent: Saturday, April 10, 2010 9:22 AM Subject: [RE-wrenches] DC wire sizing Here's my challenge to all of you that want to design for 1% or 1.5% voltage drop all the time: Take a 50-ft circuit carrying 40 amps at 12 volts, going to a C40 charge controller, select your wire s

Re: [RE-wrenches] DC wire sizing

2010-04-12 Thread Kent Osterberg
tp://www.wind-sun.com/ForumVB/ .. - Original Message - From: Kent Osterberg To: Wrenches Sent: Saturday, April 10, 2010 9:22 AM Subject: [RE-wrenches] DC wire sizing Here's my challenge to all of you that want to design for 1% or 1.5% volta

Re: [RE-wrenches] DC wire sizing

2010-04-12 Thread Nick Soleil
7-769-9037 From: Bob-O Schultze To: RE-wrenches Sent: Sat, April 10, 2010 10:26:56 AM Subject: Re: [RE-wrenches] DC wire sizing Of course it's not a practical solution, which is why we strived for (but rarely got) 2% VD on low voltage situations as I

Re: [RE-wrenches] DC wire sizing

2010-04-12 Thread Kent Osterberg
ox 657 Petaluma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax: 707-769-9037 From: Bob-O Schultze To: RE-wrenches Sent: Sat, April 10, 2010 10:26:56 AM Subject: Re: [RE-wrenches] DC wire sizing Of course it's not a practical solution, which is why we strived fo

Re: [RE-wrenches] DC wire sizing

2010-04-12 Thread Warren Lauzon
un.com/ForumVB/ .. - Original Message - From: Kent Osterberg To: RE-wrenches Sent: Monday, April 12, 2010 10:51 AM Subject: Re: [RE-wrenches] DC wire sizing I know you wouldn't, Warren. Because it is m

Re: [RE-wrenches] DC wire sizing

2010-04-13 Thread Nick Soleil
ince 1979 >>Solar Discussion Forum: http://www.wind-sun.com/ForumVB/ >>.. >- >>Original Message - >>From: Kent Osterberg >>To: Wrenches >>Sent: >>Saturday, April 10, 2010 9:22 AM >>Subject: >>[RE-wrenc

Re: [RE-wrenches] DC Wire Sizing (Ethics & VDrop)

2010-04-12 Thread Ryan LeBlanc
ipant bios: > www.members.re-wrenches.org > > > -- next part -- An HTML attachment was scrubbed... URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachme nts/20100409/204700dc/attachment-0001.htm> -- Me