Re: [RE-wrenches] EMT in attic - vs FMC vs armored cable

2012-11-09 Thread Benn At DayStarSolar
Sounds like you are referring to what we refer to around here as teck cable. Very common stuff for industrial applications. Here, pretty much any electrical wholesaler has stock in several configurations. Can be ordered in 2,3,4,5,6... (Not sure the limit extent) number of conductors and in

Re: [RE-wrenches] EMT in attic - vs FMC vs armored cable

2012-11-09 Thread William Miller
Hilton: This is an intriguing concept: The universal PV AC/DC cable. It has a red, black and white #10, a green #8, it's rated for 600 V AC or DC and for wet locations with a metallic cover. I'd buy a roll. Where do we get it? William Miller At 11:54 AM 11/9/2012, you wrote: This subje

[RE-wrenches] EMT in attic - vs FMC vs armored cable

2012-11-09 Thread Hilton Dier III
This subject interests me as I had been considering using waterproof metallic armored cable. I can get pre-made cable with just about any number of conductors of any size, sheathed in a flexible metallic layer and then a UV resistant waterproof layer. The stuff is direct burial as well. Buying

Re: [RE-wrenches] EMT in attic

2012-11-09 Thread David Brearley
+1. John Wiles is awesome—and he would never mistake PV source or array circuits for a service. Not only are PV power circuits not a service, but PV systems (inverter output circuits) are not a service. The NEC defines all of this as power production equipment (705.2). By definition a service

Re: [RE-wrenches] EMT in attic

2012-11-09 Thread Mark Frye
Dave, You are on to something that has been on my mind for years. I believe that FMC inside the building before a disconnect with DC conductors above 250V is allowed by the Code. And I believe the requirement for bonding in 250 applies regardless of whether or not a separate EGC is run in th

Re: [RE-wrenches] EMT in attic

2012-11-09 Thread Dave Click
Nick, what the AHJ is telling you may actually be in reference to 250.97; for most PV output circuits (yes these are necessarily dc) this bonding requirement applies since array VOC > 250 VDC. As Kent just pointed out, these dc conductors clearly don't meet the NEC definition of a service. "2

Re: [RE-wrenches] EMT in attic

2012-11-08 Thread Kent Osterberg
Article 100 has a definition for service. It doesn't seem like a PV system or a battery based inverter for off-grid fit the definition. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/8/2012 8:22 PM, Nick Vida wrote: Hi Wrenches, Thanks for you comments. Fun for the d

[RE-wrenches] EMT in attic

2012-11-08 Thread Nick Vida
Hi Wrenches, Thanks for you comments. Fun for the day is hearing they want to apply section 230 about service conductors and say that flex is not a metallic raceway because it is no good for bonding. They are defining the pv source circuits as a service.  I am getting a distinct Wiles vibe here

Re: [RE-wrenches] EMT in attic

2012-11-03 Thread Kent Osterberg
There is no need for an exception. Even in the 2008 NEC, 690.31(E) is clearly about the dc wiring. The proposed informational note adds nothing except to explain that ac isn't dc. Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsolar.com On 11/3/2012 11:09 AM, Dan Fink wrote: There

Re: [RE-wrenches] EMT in attic

2012-11-03 Thread Dan Fink
There is an proposal in the pipeline for NEC 2014 that makes an exception for AC PV modules after the wiring enters the building. See: http://www.solarabcs.org/codes-standards/NFPA/pdfs/2014NEC%20690.31(E).pdf -- Dan Fink, Executive Director; Otherpower Buckville Energy Consulting Buckville Public

Re: [RE-wrenches] EMT in attic

2012-11-03 Thread David Brearley
Sorry, per the OP this appears in 690.31(E)... On Nov 3, 2012, at 11:19 AM, David Brearley wrote: > FWIW: In the 2011 Code, Section 690.31(D) is changed to include the following: > > "Where dc photovoltaic source or output circuits…are run inside a building or > restructure, they shall be conta

Re: [RE-wrenches] EMT in attic

2012-11-03 Thread David Brearley
FWIW: In the 2011 Code, Section 690.31(D) is changed to include the following: "Where dc photovoltaic source or output circuits…are run inside a building or restructure, they shall be contained in metal raceways,Type MC metal-clad cable that complies with 250.118(10), or metal enclosures…" On

[RE-wrenches] EMT in attic

2012-11-03 Thread Nick Vida
Hello wrenches, wondering if any of you are running into inspectors wanting EMT in the attics, or allowing flex only if there is a fusible disconnect on the roof. We have heard this a few time lately and havent yet seen a code reference, (except 690.31e saying metal raceways are fine- not speci